The hydraulics of a transient event can be quite complex. I recommend animating the Profile path ("path 1" in this case) to get the best visual of what is happening during the transient. At 5.0 seconds, the pump shuts down, causing a downsurge wave to travel downstream. That reaches the downstream reservoir at about 6.5 seconds based on the wave speed, reflects and returns back to the pump at about 8.0 seconds. The pump speed is still decreasing at this point which has an influence. At about 8.0 seconds, the pressure has dropped low enough at high point J-1 that a vapor pocket starts to form.
As the separated water column reaches a flow of zero at around 13.0 s (see time history of flow at P2:J1), the vapor pocket stops increasing and starts to collapse (decrease in volume). At 15.5 s, the vapor pocket is fully collapsed, the adjacent water columns collide, causing an upsurge. The vapor pocket collapse occurs right nex to the pump and quickly reflects off of it (the pump check valve is closed at this point). As that upsurge wave travels toward the downstream reservoir, reflection from the other branch of the network (connected to J2) reaches J2 and a decrease in pressure occurs (16.5 s). By 17.0 s, the first upsurge wave from the vapor pocket collapse reaches the downstream reservoir, then reflects back. As that wave is traveling back, it interacts with the downsurge wave that came through P8 to J2 and combines, causing a high magnitude decrease in pressure (see animated profile between 17.2 and 17.6 s). This travels in opposite directions, reflects off pipe ends and combines with other waves, eventually dropping the pressure low enough at the J3 location to form another vapor pocket. As you can see, the hydraulics can be quite complex.
As a result of the above, the second vapor pocket at J3 eventually collapses, causing another upsurge that travels in both directions, reflects and interacts with other waves, and so on.
Regarding why the flow does not start to increase until a few seconds after the pump speed starts to increase - the reason is because as the speed is starting to increase, the pump at first cannot overcome the discharge head already presnet in the system (essentially operating at its shutoff head - think of the pump curve scaled down at lower speeds). As higher speeds, the pump is able to overcome the shutoff head and starts to be able to pass a positive flow. See related wiki article:
Flow from pump is delayed after pump startup
Jesse Thank you very much for your complete and exact answer: 1- Is it possible to view H-Q graph of a pump while decreasing or increasing in speed? Or it must be done by running Initial Conditions with several Speed factors?
By the way is it possible to make a legend in 'profile' window that identifies each graph (color's graph) referred to what?
1) HAMMER saves results at pipe endpoints, so "P2:J1" shows the results at the end of pipe P2 adjacent to junction J1 and "P1:J1" shows the results at the end of pipe P1 adjacent to junction J1.
2) Yes, a negative flow means the flow is going opposite to the direction of the pipe orientation. So, if the flow is toward the "start node", it will display as negative. The same applies to the initial conditions (steady state/EPS)
3) P2:J1 as at the vapor pocket location, so as long as the vapor pocket is present, the pressure and hydraulic grade result will show as being equal to the vapor pressure limit - vapor pockets can only be present when this condition occurs. The pressure increase that causes them to collapse (decrease in volume) basically applies on the other side of the pocket, which in this example case is not exactly at P2:J1, so the results to not reflect that change in pressure.
4) Try animating profiles "path 1" and "path 2" to understand this better. Path 2 covers the path that goes down P-8. The upsurge wave that travels down P-8 reflects off the partially closed valve VLV1 (which has an operating rule that starts to close at t=10 s). It reflects back as a decrease in head, which then travels up to J-2 and into the other path seen in "path 1", which is why you see a decrease in head around =16.5 s. It may help to decrease the run duration and change the report times calculation option to report at all times, so you can see a more smooth/detailed animation.
5) I'm not sure I understand your question - see previous response for item 4 - animate path 2 to see what's happening.
6) Transient waves can indeed move without flow, but flow is generally required to dampen the waves (from headloss). Read more on wave propogation in the help and in chapter 13 of our AWDM book.