BOMBA BOOSTER

Hola amigos como puedo añadir una bomba booster a mi modelo ya que al hacerlo mi terreno tiene la misma elevación que los juction aguas abajo.... se pone dicha bomba para generar más presión....y es como que mi bomba no funcionara...

gracias por la ayuda de antemano

  • Hello Leonidas,

    Are you able to communicate in English?

    What specifically do you see in the model that shows you that the booster pump is not working? What is the calculated head and flow? If you look at the System Head curve (right click on the pump), does it show an operating point on the pump curve? Screenshots would help – use the “Advanced Reply Editor” button in your reply, then use the “insert media” button to add images.

    Also, can you provide a copy of the model so we can see? To share the model (.WTG and .WTG.SQLITE files, zipped), either attach using the “Advanced Reply Editor” in your forum reply, or if the model is confidential, please use the instructions in the link below to send via Bentley Sharefile. Files uploaded to Sharefile can only be viewed by Bentley employees. Please be sure to reply on this thread with the name of the file after it has been uploaded.

    communities.bentley.com/.../7079.be-communities-secure-file-upload


    Regards,

    Jesse Dringoli
    Technical Support Manager, OpenFlows
    Bentley Communities Site Administrator
    Bentley Systems, Inc.

  • Hi, the question is, added a booster pump on the network as it is to increase pressure upstream network, but does not increase, it will be because it has almost the same elevations as make it work...
  • Hello Leonidas,

    Unfortunately I'm still having a difficult time understanding the question. A booster pump should normally increase the downstream hydraulic grade if it is turned on and able to operate on its pump curve.

    Can you send your model and some screenshots showing the problem? (.WTG and .WTG.SQLITE files in a ZIP). You can use the below link:

    communities.bentley.com/.../secure_file_upload

    Or, you can click "Advanced reply editor" in the lower-right corner of the reply box here and use the "insert media" button to add the ZIP file to the forum thread.


    Regards,

    Jesse Dringoli
    Technical Support Manager, OpenFlows
    Bentley Communities Site Administrator
    Bentley Systems, Inc.

  • Thanks for sending the model.

    Your booster pump is not able to increase the hydraulic grade because it appears to be oriented backwards. Currently the downstream pipe is set to "110 mm PEAD (Polyline)-176" (pointing north). There are some reservoirs in that direction, but there is no water source on the suction side; there are only pipes and junctons upstream of the pump, with no path to a water source.

    So, because the pump has no water source on the upstream side, water flows in reverse from the reservoirs R-1 and R-3. If you look at the bypass pipe "110 mm PEAD (Polyline)-179", you will see 300 L/s flow in reverse. The pump only adds a tiny amount of head, equal to the headloss in the bypass pipe:

    So, this leads me to believe that the "downstream pipe" setting of the pump may need to be reversed, so that it points south, toward pipe "110 mm PEAD (Polyline)-175". If you click "downstream pipe" in the pump properties and choose "reverse", then set the "has check valve?" option to "True" in the bypass pipe, the pump will have a water source on the upstream side (R-1 and R-3) and will supply flow to the demands in the east section of the system. See below screenshot:

    As a side note, based on the names of your pipes, I'm guessing you imported the model from a CAD file. You may want to look at some of the network navigator tools to check for connectivity problems in the model. Related resources:

    Importing A CAD Drawing with Modelbuilder

    Using The Network Navigator

    Using Network Navigator's Powerful Queries


    Regards,

    Jesse Dringoli
    Technical Support Manager, OpenFlows
    Bentley Communities Site Administrator
    Bentley Systems, Inc.

    Answer Verified By: Sushma Choure