Isolated Footing Design
         The isolated footing option given in supports dailogue box in support section. I want to know How to assign the parameters related to that particular support.Waiting for the reply.
  • I do not find "isolated footing" option given in Staad V8i. I can not say about the older version. In Staad V8i It is thefondation which is generally applied for mat foundation not for isolated footing. With the "Fixed But" option Isolated footing can be simulated for which I will request you to refer to Example 3 of the Help. Design for the Isolated footing can be obtained from Staad foundation .
  • I presume you are asking about the ELASTIC FOOTING command described in section 5.27.3 of the Technical Reference manual. Here is an example of that command.
    UNIT KIP FEET
    SUPPORTS
    1 4 ELASTIC FOOTING 12 10 DIRECT Y SUBGRADE 200
    PRINT SUPP INFO
    It is meant to tell STAAD to calculate a spring constant based on the dimensions of an isolated footing located beneath a column, and, the subgrade modulus of the soil. It is not meant for concrete design of the isolated footing. If you are looking for concrete design of an isolated footing, use STAAD.Foundation.
    Here is a sample model that uses that command.
    STAAD PLANE
    UNIT KIP FEET
    JOINT COORDINATES
    1  0.  0. ; 2  0.  15. ;
    3  20.  15. ; 4  20.  0.
    MEMBER INCIDENCE
    1  1  2 ; 2  2  3 ; 3  3  4
    MEMBER PROPERTY AMERICAN
    1  3  TABLE  ST  W12X26
    2  TABLE  ST  W14X34
    CONSTANTS
    E STEEL ALL
    DENS STEEL ALL
    POISSON STEEL ALL
    UNIT KIP FEET
    SUPPORTS
    PRINT SUPP INFO
    LOADING 1 DEAD + LIVE
    SELF Y -1.0
    MEMBER LOAD
    2  UNI GY -2.5
    LOADING 2 WIND FROM LEFT
    JOINT LOAD
    2  FX  10.
    LOAD 3 L1 + L2
    REPEAT LOAD
    1 1.0 2 1.0
    PERFORM ANALYSIS
    PRINT ANALYSIS RESULTS
    FINISH