LEAP Concrete: Maximum spacing for rebars in columns.

Hey,

I have a query regarding the column design on LEAP Concrete. The design output on the 3ft x 3ft reinforced concrete column as per AASHTO LRFD 8th Ed shows this error below for max spacing between longitudinal rebars.

  Using 5 ~ #9 bars on each face with #5 ties.

As per LRFD 5.10.3.2 max spacing of reinforcing bars, it says that it should be less than min of 1.5*thickness of member or 18 in. It looks like the program checks as per LRFD 5.10.4.3 with 6" max clear spacing on each face when the column is designed for plastic hinging capability. I don't have any seismic load group for the bridge and plastic hinge option is disabled already. But when I increase one bar on each face, it passes the check.

Can you please clarify further on the spacing error as per LRFD 5.10.3.2.

Thanks,

Jivesh Kumar

Parents Reply Children