Whenever i export a COBie spreadsheet, the "System" tab is always empty. How do i link the components to a system?
Hi Yehia,Thanks for raising this question. We'll revert you as soon as possible.
Regards,Sayanti
Sayanti ,
Do we have an update on this issue?
SelectSeries 6
Hello Yehia,
Please can you let us know the value of configuration variable IFC_WORKSET for your active project?
Regards
Marc
IFC_Workset is 2. I have no issues exporting a COBie spreadsheet. The issue that I am facing is filling out the "system" tab.
Marc Thomas Sayanti Das
Any help on this issue?
Hi Yehia,
Do you have MEP system or electrical circuit in your OBD dgn model? , I expect that MEP system will be exported to IfcSystem and go to COBie System tab.
If you can share DGN and other details, I'll figure it out.
Rg,
Sandeep
How do i create an MEP/electrical system?
An MEP system would be created using either the Mechanical or Electrical tools; e.g., duct, pipe, lighting, etc.. These components are "system" based vs. individual components such as doors, windows, casework, etc..
Do i have to define the system somewhere? I have multiple ducts, pipes and conduits modeled using AECOsim tools but nothing shows in the system tab when i export the COBie spreadsheet.
Steve Cocchi Sandeep Punewar
MEP system required system ID generated for all source [Ex. AHU ] and terminator device [Ex. Diffusers], once it is setup for your HVAC system , it will be exported as IFCSystem and populate COBIe system tab as shown below.
To generate system ID there is a tool called 'System ID' in Route Assist ribbon group.
HTH,