_BB_SHOW_DATASET_LOAD_MSGS

Hi,

message center asks for:

"Architecture Configuration Check found error(s), please set _BB_SHOW_DATASET_LOAD_MSGS configuration variable and restart to see details."

nowhere is specified what this does, how to "set"      "=1" ?

OBD u8

regards Rik

Parents
  • Filed Defect 1125448: "_BB_SHOW_DATASET_LOAD_MSGS Message Center text should include syntax for use"

    Marc

  • Hello, we have similar error  message in OBD  Message Center: Architecture Configuration Check found error(s).

    It affects automation iModeling process, the same error shows up  in BAS which stop iModeling publishing. Please help us to solve this problem. Thank you. 

  • Hi, next time you open the file please can you follow the steps in The Message Center - Some Tips to create a text file listing all of your messages then post that file to this thread. Many of the messages contain guidance that can help to resolve the messages.

    Marc

  • Thank you Marc. I attached text file here. There is an error message which creates a problem: Architecture Configuration Check found error(s), please review the previous 3 message(s) for details.

    Failed to update ProjectWise project information according to the current document - current project may be incorrect.
    Could not retrieve information from the CONNECTION client.
    SCHEMAMANAGERADDIN loaded.
    
    Title Blocks updated successfully!
    
    Updating Title Blocks... ...\H361269-1950-231-20M-0011.dgn
    
    Updating Title Blocks...
    
    Reading Section
    Reading: ...\dms20692\US_CraneRails.xml
    
    Reading Section
    Reading: ...\dms20692\CONCRETESHAPES.xml
    
    Reading Section
    Reading: ...\dms20692\FiberGrate-FRP-Shapes-2018.xml
    
    Reading Section
    Reading: ...\dms20692\American-Bolts.xml
    
    Reading Section
    Reading: ...\dms20692\projectshapes.xml
    
    Reading Section
    Reading: ...\dms20692\Misc_metric.xml
    
    Reading Section
    Reading: ...\dms20692\USERDEFINED.xml
    
    Reading Section
    Reading: ...\alla.remizova@hatch.com\dms20692\Canada_c.xml
    
    Reading Section
    Reading: ...\alla.remizova@hatch.com\dms20692\Canam_c.xml
    
    Reading Section
    Reading: ...\alla.remizova@hatch.com\dms20692\USA_c.xml
    
    Architecture Configuration Check found error(s), please review the previous 3 message(s) for details.
    
    COLUMNGRID loaded.
    
    File MechanicalMenu.dgnlib could not find SHX font [iso3098b]. Replaced missing SHX font [iso3098b] with [romans.bigfont].
    File c:\pwworking\cacpwis01.corp.hatchglobal.com_pw__cac__datasource01\alla.remizova@hatch.com\dms09210\MechanicalMenu.dgnlib could not find SHX font [iso3098b]. Replaced missing SHX font [iso3098b] with [romans.bigfont]. Some text may not display correctly. Make sure that the appropriate SHX font file (*.shx) is present in a directory specified in MS_FONTPATH or MS_DWGFONTPATH.
    File MechanicalMenu.dgnlib could not find SHX font [ARCHITXT]. Replaced missing SHX font [ARCHITXT] with [romans.bigfont].
    File c:\pwworking\cacpwis01.corp.hatchglobal.com_pw__cac__datasource01\alla.remizova@hatch.com\dms09210\MechanicalMenu.dgnlib could not find SHX font [ARCHITXT]. Replaced missing SHX font [ARCHITXT] with [romans.bigfont]. Some text may not display correctly. Make sure that the appropriate SHX font file (*.shx) is present in a directory specified in MS_FONTPATH or MS_DWGFONTPATH.
    Processing DV Dataset levels
    
    Reading: TFDIR_SETTING
    Reading: ...\dms21400\AnnotationOverrides.xml
    Reading: ...\dms21400\Concrete BeamFilterHierarchy.xml
    Reading: ...\dms21400\Concrete ColumnFilterHierarchy.xml
    Reading: ...\dms21400\Concrete PierFilterHierarchy.xml
    Reading: ...\dms21400\Concrete PileFilterHierarchy.xml
    Reading: ...\alla.remizova@hatch.com\dms21400\default.xml
    Reading: ...\dms21400\HatchAnchorageFilterHierarchy.xml
    Reading: ...\dms21400\HatchHandrailFilterHierarchy.xml
    Reading: ...\dms21400\HatchLaddersFilterHierarchy.xml
    Reading: ...\HatchStructuralSlab-Concrete-ExistFilterHierarchy.xml
    Reading: ...\HatchStructuralSlab-Concrete-FutureFilterHierarchy.xml
    Reading: ...\HatchStructuralSlab-Concrete-NewFilterHierarchy.xml
    Reading: ...\HatchStructuralSlab-Steel-ExistFilterHierarchy.xml
    Reading: ...\HatchStructuralSlab-Steel-FutureFilterHierarchy.xml
    Reading: ...\HatchStructuralSlab-Steel-NewFilterHierarchy.xml
    Reading: ...\HatchStructuralWall-Concrete-ExistFilterHierarchy.xml
    Reading: ...\HatchStructuralWall-Concrete-FutureFilterHierarchy.xml
    Reading: ...\HatchStructuralWall-Concrete-NewFilterHierarchy.xml
    Reading: ...\HatchStructuralWall-Steel-ExistFilterHierarchy.xml
    Reading: ...\HatchStructuralWall-Steel-FutureFilterHierarchy.xml
    Reading: ...\HatchStructuralWall-Steel-NewFilterHierarchy.xml
    Reading: ...\dms21400\JoistGirderSettings.xml
    Reading: ...\dms21400\MechanicalOverrides.xml
    Reading: ...\dms21400\PartMapping_sample.xml
    Reading: ...\dms21400\Settings_FFE.xml
    Reading: ...\dms21400\Settings_Frames.xml
    Reading: ...\dms21400\Steel BeamFilterHierarchy.xml
    Reading: ...\dms21400\Steel CladdingFilterHierarchy.xml
    Reading: ...\dms21400\Steel ColumnFilterHierarchy.xml
    Reading: ...\Steel Horizontal BraceFilterHierarchy.xml
    Reading: ...\dms21400\Steel PileFilterHierarchy.xml
    Reading: ...\dms21400\Steel PurlinFilterHierarchy.xml
    Reading: ...\Steel Vertical BraceFilterHierarchy.xml
    Reading: ...\dms21400\Timber JoistFilterHierarchy.xml
    Reading: ...\dms21400\Timber PlateFilterHierarchy.xml
    Reading: ...\dms21400\Timber PostFilterHierarchy.xml
    Reading: ...\dms21400\Timber StudFilterHierarchy.xml
    
    Reading: TFDIR_COMP
    Reading: ...\dms15136\Construction_comp.xml
    Reading: ...\dms15136\Space_comp.xml
    Reading: ...\dms15136\Structural_comp.xml
    
    Reading: TFDIR_CPART
    Reading: ...\dms15137\Architectural_cparts.xml
    Reading: ...\dms15137\Structural_cparts.xml
    
    Reading: TFDIR_PART
    Reading: ...\dms15171\Architectural_parts.xml
    Reading: ...\dms15171\Building_parts.xml
    Reading: ...\dms15171\Electrical_parts.xml
    Reading: ...\dms15171\Fireproofing_parts.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Concrete-Bridges.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Concrete.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Earthwork.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Energy_Structural.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_FRP.xml
    Reading: ...\HA_ABD_CE_230_M_Rock_Soil_Anchorage.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Structural.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Temporary.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Timber.xml
    Reading: ...\alla.remizova@hatch.com\dms15171\IFC_parts.xml
    Reading: ...\dms15171\Mechanical_parts.xml
    Reading: ...\dms15171\Plumbing_parts.xml
    Reading: ...\dms15171\Reduced-Bentley-Structural_parts.xml
    
    Part assigned an unresolved material definition
    Could not find material definition $(_dgnlib)|building_materials.dgnlib|hatch232.pal : hatch232_gm_checkpl assigned to part: flooring - floor plate
    Could not find material definition $(_dgnlib)|building_materials.dgnlib|hatch232.pal : hatch232_gm_exist_checkpl assigned to part: flooring - floor plate
    
    Reading: TFDIR_SETTING
    Reading: ...\dms21400\AnnotationOverrides.xml
    Reading: ...\dms21400\Concrete BeamFilterHierarchy.xml
    Reading: ...\dms21400\Concrete ColumnFilterHierarchy.xml
    Reading: ...\dms21400\Concrete PierFilterHierarchy.xml
    Reading: ...\dms21400\Concrete PileFilterHierarchy.xml
    Reading: ...\alla.remizova@hatch.com\dms21400\default.xml
    Reading: ...\dms21400\HatchAnchorageFilterHierarchy.xml
    Reading: ...\dms21400\HatchHandrailFilterHierarchy.xml
    Reading: ...\dms21400\HatchLaddersFilterHierarchy.xml
    Reading: ...\HatchStructuralSlab-Concrete-ExistFilterHierarchy.xml
    Reading: ...\HatchStructuralSlab-Concrete-FutureFilterHierarchy.xml
    Reading: ...\HatchStructuralSlab-Concrete-NewFilterHierarchy.xml
    Reading: ...\HatchStructuralSlab-Steel-ExistFilterHierarchy.xml
    Reading: ...\HatchStructuralSlab-Steel-FutureFilterHierarchy.xml
    Reading: ...\HatchStructuralSlab-Steel-NewFilterHierarchy.xml
    Reading: ...\HatchStructuralWall-Concrete-ExistFilterHierarchy.xml
    Reading: ...\HatchStructuralWall-Concrete-FutureFilterHierarchy.xml
    Reading: ...\HatchStructuralWall-Concrete-NewFilterHierarchy.xml
    Reading: ...\HatchStructuralWall-Steel-ExistFilterHierarchy.xml
    Reading: ...\HatchStructuralWall-Steel-FutureFilterHierarchy.xml
    Reading: ...\HatchStructuralWall-Steel-NewFilterHierarchy.xml
    Reading: ...\dms21400\JoistGirderSettings.xml
    Reading: ...\dms21400\MechanicalOverrides.xml
    Reading: ...\dms21400\PartMapping_sample.xml
    Reading: ...\dms21400\Settings_FFE.xml
    Reading: ...\dms21400\Settings_Frames.xml
    Reading: ...\dms21400\Steel BeamFilterHierarchy.xml
    Reading: ...\dms21400\Steel CladdingFilterHierarchy.xml
    Reading: ...\dms21400\Steel ColumnFilterHierarchy.xml
    Reading: ...\Steel Horizontal BraceFilterHierarchy.xml
    Reading: ...\dms21400\Steel PileFilterHierarchy.xml
    Reading: ...\dms21400\Steel PurlinFilterHierarchy.xml
    Reading: ...\Steel Vertical BraceFilterHierarchy.xml
    Reading: ...\dms21400\Timber JoistFilterHierarchy.xml
    Reading: ...\dms21400\Timber PlateFilterHierarchy.xml
    Reading: ...\dms21400\Timber PostFilterHierarchy.xml
    Reading: ...\dms21400\Timber StudFilterHierarchy.xml
    
    Reading: TFDIR_COMP
    Reading: ...\dms15136\Construction_comp.xml
    Reading: ...\dms15136\Space_comp.xml
    Reading: ...\dms15136\Structural_comp.xml
    
    Reading: TFDIR_CPART
    Reading: ...\dms15137\Architectural_cparts.xml
    Reading: ...\dms15137\Structural_cparts.xml
    
    Reading: TFDIR_PART
    Reading: ...\dms15171\Architectural_parts.xml
    Reading: ...\dms15171\Building_parts.xml
    Reading: ...\dms15171\Electrical_parts.xml
    Reading: ...\dms15171\Fireproofing_parts.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Concrete-Bridges.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Concrete.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Earthwork.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Energy_Structural.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_FRP.xml
    Reading: ...\HA_ABD_CE_230_M_Rock_Soil_Anchorage.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Structural.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Temporary.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Timber.xml
    Reading: ...\alla.remizova@hatch.com\dms15171\IFC_parts.xml
    Reading: ...\dms15171\Mechanical_parts.xml
    Reading: ...\dms15171\Plumbing_parts.xml
    Reading: ...\dms15171\Reduced-Bentley-Structural_parts.xml
    
    Cope Dependencies are disabled.
    Cope Dependencies are disabled.  Copes will not be automatically updated. (STR_DISABLE_COPE_DEPENDENCIES)
    Connecting to ProjectWise...
    
    MCM loaded.
    
    
    

  • Regarding these three messages, from the top down:

    Two SHX fonts, iso3098b and ARCHITXT, used (presumably) by a DWG somewhere in the reference files are not available. If the SHX file(s) containing these can be identified and added to a location defined by MS_FONTPATH. The default value for this is C:\Program Files\Bentley\MicroStation CONNECT Edition\MicroStation\Default\fonts\, however adding SHX files in that location is obviously not efficient.

    The best resolution would be for the people/organizations in the supply chain who still use SHX fonts to switch to commonly available Windows TrueType fonts, but this is not going to resolve your immediate problem. I suggest that your ProjectWise administrators do the following:

    • add a Fonts folder in an appropriate shared location 
    • Append the path to this location to MS_FONTPATH in the managed configuration
    • obtain the missing fonts and put them in this folder

    For info, hel says "If AutoCAD is installed, MicroStation searches for SHX fonts in AutoCAD’s Fonts directory (the "Fonts" folder in the installation directory of the most recently used version of AutoCAD). With or without AutoCAD, MicroStation searches the directories specified by MS_FONTPATH, as well as the same directory as the design file requesting the font."

    The other error is that a material palette file, hatch232.pal, is not found. If this palette can be located and copied into a location defined by MS_MATERIAL it should be seen during iModel publishing. Any images used by the materials in this palette will need to be in locations defined by MS_PATTERN and MS_BUMP variables. It could be worth checking what hatch232.pal contains and if the materials are actually needed, they might be duplicates of standard materials.

    Marc

  • Thank you Marc. I solved these 3 problems above    but still have an error message in Message center : Architecture Configuration Check found error(s), please review the previous 3 message(s) for details. It's very confusing, hard to understand what 3 messages should be checked. Text file attached

     

    Load setting file c:\pwworking\cacpwis01.corp.hatchglobal.com_pw__cac__datasource01\alla.remizova@hatch.com\dms15175\IFC_PropertyMapping_local.ifc2x3.set
    c:\pwworking\cacpwis01.corp.hatchglobal.com_pw__cac__datasource01\alla.remizova@hatch.com\dms15175\IFC_PropertyMapping_local.ifc2x3.set
    Load setting file c:\pwworking\cacpwis01.corp.hatchglobal.com_pw__cac__datasource01\alla.remizova@hatch.com\dms15175\IFC_PropertyMapping.ifc2x3.set
    c:\pwworking\cacpwis01.corp.hatchglobal.com_pw__cac__datasource01\alla.remizova@hatch.com\dms15175\IFC_PropertyMapping.ifc2x3.set
    Load setting file c:\pwworking\cacpwis01.corp.hatchglobal.com_pw__cac__datasource01\alla.remizova@hatch.com\dms15175\IFC_Mapping.ifc2x3.set
    c:\pwworking\cacpwis01.corp.hatchglobal.com_pw__cac__datasource01\alla.remizova@hatch.com\dms15175\IFC_Mapping.ifc2x3.set
    Load setting file c:\pwworking\cacpwis01.corp.hatchglobal.com_pw__cac__datasource01\alla.remizova@hatch.com\dms20719\IFC_Mapping_overrides.ifc2x3.set
    c:\pwworking\cacpwis01.corp.hatchglobal.com_pw__cac__datasource01\alla.remizova@hatch.com\dms20719\IFC_Mapping_overrides.ifc2x3.set
    Load setting file c:\pwworking\cacpwis01.corp.hatchglobal.com_pw__cac__datasource01\alla.remizova@hatch.com\dms15175\IFC_QtoMapping.ifc4.set
    c:\pwworking\cacpwis01.corp.hatchglobal.com_pw__cac__datasource01\alla.remizova@hatch.com\dms15175\IFC_QtoMapping.ifc4.set
    Load setting file c:\pwworking\cacpwis01.corp.hatchglobal.com_pw__cac__datasource01\alla.remizova@hatch.com\dms15175\IFC_PropertyMapping_local.ifc4.set
    c:\pwworking\cacpwis01.corp.hatchglobal.com_pw__cac__datasource01\alla.remizova@hatch.com\dms15175\IFC_PropertyMapping_local.ifc4.set
    Load setting file c:\pwworking\cacpwis01.corp.hatchglobal.com_pw__cac__datasource01\alla.remizova@hatch.com\dms15175\IFC_PropertyMapping.ifc4.set
    c:\pwworking\cacpwis01.corp.hatchglobal.com_pw__cac__datasource01\alla.remizova@hatch.com\dms15175\IFC_PropertyMapping.ifc4.set
    Load setting file c:\pwworking\cacpwis01.corp.hatchglobal.com_pw__cac__datasource01\alla.remizova@hatch.com\dms15175\IFC_Mapping.ifc4.set
    c:\pwworking\cacpwis01.corp.hatchglobal.com_pw__cac__datasource01\alla.remizova@hatch.com\dms15175\IFC_Mapping.ifc4.set
    Load setting file c:\pwworking\cacpwis01.corp.hatchglobal.com_pw__cac__datasource01\alla.remizova@hatch.com\dms20719\IFC_Mapping_overrides.ifc4.set
    c:\pwworking\cacpwis01.corp.hatchglobal.com_pw__cac__datasource01\alla.remizova@hatch.com\dms20719\IFC_Mapping_overrides.ifc4.set
    Failed to update ProjectWise project information according to the current document - current project may be incorrect.
    Could not retrieve information from the CONNECTION client.
    SCHEMAMANAGERADDIN loaded.
    
    Title Blocks updated successfully!
    
    Updating Title Blocks... ...\Hxxxxx.dgn
    
    Updating Title Blocks...
    
    Reading Section
    Reading: ...\dms20692\US_CraneRails.xml
    
    Reading Section
    Reading: ...\dms20692\CONCRETESHAPES.xml
    
    Reading Section
    Reading: ...\dms20692\FiberGrate-FRP-Shapes-2018.xml
    
    Reading Section
    Reading: ...\dms20692\American-Bolts.xml
    
    Reading Section
    Reading: ...\dms20692\projectshapes.xml
    
    Reading Section
    Reading: ...\dms20692\Misc_metric.xml
    
    Reading Section
    Reading: ...\dms20692\USERDEFINED.xml
    
    Reading Section
    Reading: ...\alla.remizova@hatch.com\dms20692\Canada_c.xml
    
    Reading Section
    Reading: ...\alla.remizova@hatch.com\dms20692\Canam_c.xml
    
    Reading Section
    Reading: ...\alla.remizova@hatch.com\dms20692\USA_c.xml
    
    Architecture Configuration Check found error(s), please review the previous 3 message(s) for details.
    
    COLUMNGRID loaded.
    
    Processing DV Dataset levels
    
    Reading: TFDIR_SETTING
    Reading: ...\dms21400\AnnotationOverrides.xml
    Reading: ...\dms21400\Concrete BeamFilterHierarchy.xml
    Reading: ...\dms21400\Concrete ColumnFilterHierarchy.xml
    Reading: ...\dms21400\Concrete PierFilterHierarchy.xml
    Reading: ...\dms21400\Concrete PileFilterHierarchy.xml
    Reading: ...\alla.remizova@hatch.com\dms21400\default.xml
    Reading: ...\dms21400\HatchAnchorageFilterHierarchy.xml
    Reading: ...\dms21400\HatchHandrailFilterHierarchy.xml
    Reading: ...\dms21400\HatchLaddersFilterHierarchy.xml
    Reading: ...\HatchStructuralSlab-Concrete-ExistFilterHierarchy.xml
    Reading: ...\HatchStructuralSlab-Concrete-FutureFilterHierarchy.xml
    Reading: ...\HatchStructuralSlab-Concrete-NewFilterHierarchy.xml
    Reading: ...\HatchStructuralSlab-Steel-ExistFilterHierarchy.xml
    Reading: ...\HatchStructuralSlab-Steel-FutureFilterHierarchy.xml
    Reading: ...\HatchStructuralSlab-Steel-NewFilterHierarchy.xml
    Reading: ...\HatchStructuralWall-Concrete-ExistFilterHierarchy.xml
    Reading: ...\HatchStructuralWall-Concrete-FutureFilterHierarchy.xml
    Reading: ...\HatchStructuralWall-Concrete-NewFilterHierarchy.xml
    Reading: ...\HatchStructuralWall-Steel-ExistFilterHierarchy.xml
    Reading: ...\HatchStructuralWall-Steel-FutureFilterHierarchy.xml
    Reading: ...\HatchStructuralWall-Steel-NewFilterHierarchy.xml
    Reading: ...\dms21400\JoistGirderSettings.xml
    Reading: ...\dms21400\MechanicalOverrides.xml
    Reading: ...\dms21400\PartMapping_sample.xml
    Reading: ...\dms21400\Settings_FFE.xml
    Reading: ...\dms21400\Settings_Frames.xml
    Reading: ...\dms21400\Steel BeamFilterHierarchy.xml
    Reading: ...\dms21400\Steel CladdingFilterHierarchy.xml
    Reading: ...\dms21400\Steel ColumnFilterHierarchy.xml
    Reading: ...\Steel Horizontal BraceFilterHierarchy.xml
    Reading: ...\dms21400\Steel PileFilterHierarchy.xml
    Reading: ...\dms21400\Steel PurlinFilterHierarchy.xml
    Reading: ...\Steel Vertical BraceFilterHierarchy.xml
    Reading: ...\dms21400\Timber JoistFilterHierarchy.xml
    Reading: ...\dms21400\Timber PlateFilterHierarchy.xml
    Reading: ...\dms21400\Timber PostFilterHierarchy.xml
    Reading: ...\dms21400\Timber StudFilterHierarchy.xml
    
    Reading: TFDIR_COMP
    Reading: ...\dms15136\Construction_comp.xml
    Reading: ...\dms15136\Space_comp.xml
    Reading: ...\dms15136\Structural_comp.xml
    
    Reading: TFDIR_CPART
    Reading: ...\dms15137\Architectural_cparts.xml
    Reading: ...\dms15137\Structural_cparts.xml
    
    Reading: TFDIR_PART
    Reading: ...\dms15171\Architectural_parts.xml
    Reading: ...\dms15171\Building_parts.xml
    Reading: ...\dms15171\Electrical_parts.xml
    Reading: ...\dms15171\Fireproofing_parts.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Concrete-Bridges.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Concrete.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Earthwork.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Energy_Structural.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_FRP.xml
    Reading: ...\HA_ABD_CE_230_M_Rock_Soil_Anchorage.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Structural.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Temporary.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Timber.xml
    Reading: ...\alla.remizova@hatch.com\dms15171\IFC_parts.xml
    Reading: ...\dms15171\Mechanical_parts.xml
    Reading: ...\dms15171\Plumbing_parts.xml
    Reading: ...\dms15171\Reduced-Bentley-Structural_parts.xml
    
    Reading: TFDIR_SETTING
    Reading: ...\dms21400\AnnotationOverrides.xml
    Reading: ...\dms21400\Concrete BeamFilterHierarchy.xml
    Reading: ...\dms21400\Concrete ColumnFilterHierarchy.xml
    Reading: ...\dms21400\Concrete PierFilterHierarchy.xml
    Reading: ...\dms21400\Concrete PileFilterHierarchy.xml
    Reading: ...\alla.remizova@hatch.com\dms21400\default.xml
    Reading: ...\dms21400\HatchAnchorageFilterHierarchy.xml
    Reading: ...\dms21400\HatchHandrailFilterHierarchy.xml
    Reading: ...\dms21400\HatchLaddersFilterHierarchy.xml
    Reading: ...\HatchStructuralSlab-Concrete-ExistFilterHierarchy.xml
    Reading: ...\HatchStructuralSlab-Concrete-FutureFilterHierarchy.xml
    Reading: ...\HatchStructuralSlab-Concrete-NewFilterHierarchy.xml
    Reading: ...\HatchStructuralSlab-Steel-ExistFilterHierarchy.xml
    Reading: ...\HatchStructuralSlab-Steel-FutureFilterHierarchy.xml
    Reading: ...\HatchStructuralSlab-Steel-NewFilterHierarchy.xml
    Reading: ...\HatchStructuralWall-Concrete-ExistFilterHierarchy.xml
    Reading: ...\HatchStructuralWall-Concrete-FutureFilterHierarchy.xml
    Reading: ...\HatchStructuralWall-Concrete-NewFilterHierarchy.xml
    Reading: ...\HatchStructuralWall-Steel-ExistFilterHierarchy.xml
    Reading: ...\HatchStructuralWall-Steel-FutureFilterHierarchy.xml
    Reading: ...\HatchStructuralWall-Steel-NewFilterHierarchy.xml
    Reading: ...\dms21400\JoistGirderSettings.xml
    Reading: ...\dms21400\MechanicalOverrides.xml
    Reading: ...\dms21400\PartMapping_sample.xml
    Reading: ...\dms21400\Settings_FFE.xml
    Reading: ...\dms21400\Settings_Frames.xml
    Reading: ...\dms21400\Steel BeamFilterHierarchy.xml
    Reading: ...\dms21400\Steel CladdingFilterHierarchy.xml
    Reading: ...\dms21400\Steel ColumnFilterHierarchy.xml
    Reading: ...\Steel Horizontal BraceFilterHierarchy.xml
    Reading: ...\dms21400\Steel PileFilterHierarchy.xml
    Reading: ...\dms21400\Steel PurlinFilterHierarchy.xml
    Reading: ...\Steel Vertical BraceFilterHierarchy.xml
    Reading: ...\dms21400\Timber JoistFilterHierarchy.xml
    Reading: ...\dms21400\Timber PlateFilterHierarchy.xml
    Reading: ...\dms21400\Timber PostFilterHierarchy.xml
    Reading: ...\dms21400\Timber StudFilterHierarchy.xml
    
    Reading: TFDIR_COMP
    Reading: ...\dms15136\Construction_comp.xml
    Reading: ...\dms15136\Space_comp.xml
    Reading: ...\dms15136\Structural_comp.xml
    
    Reading: TFDIR_CPART
    Reading: ...\dms15137\Architectural_cparts.xml
    Reading: ...\dms15137\Structural_cparts.xml
    
    Reading: TFDIR_PART
    Reading: ...\dms15171\Architectural_parts.xml
    Reading: ...\dms15171\Building_parts.xml
    Reading: ...\dms15171\Electrical_parts.xml
    Reading: ...\dms15171\Fireproofing_parts.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Concrete-Bridges.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Concrete.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Earthwork.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Energy_Structural.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_FRP.xml
    Reading: ...\HA_ABD_CE_230_M_Rock_Soil_Anchorage.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Structural.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Temporary.xml
    Reading: ...\dms15171\HA_ABD_CE_230_M_Timber.xml
    Reading: ...\alla.remizova@hatch.com\dms15171\IFC_parts.xml
    Reading: ...\dms15171\Mechanical_parts.xml
    Reading: ...\dms15171\Plumbing_parts.xml
    Reading: ...\dms15171\Reduced-Bentley-Structural_parts.xml
    
    Cope Dependencies are disabled.
    Cope Dependencies are disabled.  Copes will not be automatically updated. (STR_DISABLE_COPE_DEPENDENCIES)
    Connecting to ProjectWise...
    
    MCM loaded.
    
    
    

  • Hmm, it's not clear from the text file which errors are being referred to, we'll need a screenshot of the errors in the message center.

    Also I see "Failed to update ProjectWise project information according to the current document - current project may be incorrect.
    Could not retrieve information from the CONNECTION client." You should talk to your ProjectWise admins about that.

    Marc

Reply Children
No Data