Does anybody know the equation Hevacomp uses to convert loading units to flow rates based on the BS EN 806-2006 method? Thanks.
Hi Liam
It is quite a complex procedure. You need to consider that there are two equations. One that works exclusively with the LU of the outlet, the second that works with the peak outlet in a section.
For LU's larger than 300:
dim = loading units m = (log(9)-log(1.7)) / (log(5000) - log(300))
c= log(1.7)-m*(log(300)
flowrate = exp(m * log(dim) +c)
For LU's smaller than 300:
pdim = peak loading units for section
m = (log(1.7) - log(pdim)/10)) /(log(300)-log(pdim))
c = log(pdim/10) - m * log (pdim)
This differs substantially from BS 6700:
For LU's larger than 2000:
dim = loading units
flow = specified flow rate (if any)m = 11.2 + (dim-2000) * 0.0039
flowrate = flow + m
For LU's smaller than 2000:
flow = specified flow rate (if any)
m = .0.0532 * dim ^ 0.7
For further information on the pipe sizing standards, please consider this document. For more information about the methods considered by BS 6700, please see this document.
Best regards,
Duncan Brown
Duncan BrownHi Duncan,
Appreciate I am a little "late to the party" since this is a follow up to a question raised almost four years ago.
My question - I am looking for clarifcation on whether the formula you gave in this answer for BS EN 806 is 100% correct to the software?
Reason is that when I plug your formula into a rudimental excel sheet for QA'ing my teams Hevacomp BS EN 806 outputs - they do not match. I am wondering if it is how the brackets are displayed in your answer which are affecting the results?
What I am trying to do if have a basic Excel sheet where I am plug in the "dim" or "pdim" figures and it'll tell me the flow rate, and I use this when QA'ing outputs generated. Thanks for your help, and hope you had a good Christmas break.
Kind regards
Hi George, happy new year to you. This would be quite difficult to replicate in an excel spreadsheet as the calculation methodology for BS EN806 utilises the rather complex graph shown here. I would suggest perhaps using the graph to QA your results if suitable. I hope that helps.
Shane Regan | Principle Building Performance Support EngineerHevacomp to OpenBuildings - A complete guide for every user | Bentley Communities
Hi Duncan
Responding to a very old thread here, but do you have the same calculation for the BS 6700 method (now 8558)?
Would you also have the calculation for determination of pipe diameter graph for water at 10oC?
Thanks!
Apologies, I didn't read the full thing and see the load unit vs flow rate calculation is there for BS 6700.
Do you have the calculation for determination of pipe diameter graph for water at 10oC?