Does anybody know the equation Hevacomp uses to convert loading units to flow rates based on the BS EN 806-2006 method? Thanks.
Hi Liam
It is quite a complex procedure. You need to consider that there are two equations. One that works exclusively with the LU of the outlet, the second that works with the peak outlet in a section.
For LU's larger than 300:
dim = loading units m = (log(9)-log(1.7)) / (log(5000) - log(300))
c= log(1.7)-m*(log(300)
flowrate = exp(m * log(dim) +c)
For LU's smaller than 300:
pdim = peak loading units for section
m = (log(1.7) - log(pdim)/10)) /(log(300)-log(pdim))
c = log(pdim/10) - m * log (pdim)
This differs substantially from BS 6700:
For LU's larger than 2000:
dim = loading units
flow = specified flow rate (if any)m = 11.2 + (dim-2000) * 0.0039
flowrate = flow + m
For LU's smaller than 2000:
flow = specified flow rate (if any)
m = .0.0532 * dim ^ 0.7
For further information on the pipe sizing standards, please consider this document. For more information about the methods considered by BS 6700, please see this document.
Best regards,
Duncan Brown