BS EN 806 -2006

Does anybody know the equation Hevacomp uses to convert loading units to flow rates based on the BS EN 806-2006 method? Thanks.

  • Hi Liam

    It is quite a complex procedure. You need to consider that there are two equations. One that works exclusively with the LU of the outlet, the second that works with the peak outlet in a section.

    For LU's larger than 300:

    dim = loading units

    m = (log(9)-log(1.7)) / (log(5000) - log(300))

    c= log(1.7)-m*(log(300)

    flowrate  = exp(m * log(dim) +c)

    For LU's smaller than 300:

    pdim = peak loading units for section

    m = (log(1.7) - log(pdim)/10)) /(log(300)-log(pdim))

    c = log(pdim/10) - m * log (pdim)

    flowrate  = exp(m * log(dim) +c)

    This differs substantially from BS 6700:

    For LU's larger than 2000:

    dim = loading units 

    flow = specified flow rate (if any)

    m = 11.2 + (dim-2000) * 0.0039

    flowrate = flow + m

    For LU's smaller than 2000:

    dim = loading units 

    flow = specified flow rate (if any)

    m = .0.0532 * dim ^ 0.7

    flowrate = flow + m

    For further information on the pipe sizing standards, please consider this document. For more information about the methods considered by BS 6700, please see this document

    Best regards,

    Duncan Brown





  • Hi Duncan, 

    Appreciate I am a little "late to the party" since this is a follow up to a question raised almost four years ago.

    My question - I am looking for clarifcation on whether the formula you gave in this answer for BS EN 806 is 100% correct to the software?

    Reason is that when I plug your formula into a rudimental excel sheet for QA'ing my teams Hevacomp BS EN 806 outputs - they do not match. I am wondering if it is how the brackets are displayed in your answer which are affecting the results?

    What I am trying to do if have a basic Excel sheet where I am plug in the "dim" or "pdim" figures and it'll tell me the flow rate, and I use this when QA'ing outputs generated. 

    Thanks for your help, and hope you had a good Christmas break.

    Kind regards

  • Hi George, happy new year to you. This would be quite difficult to replicate in an excel spreadsheet as the calculation methodology for BS EN806 utilises the rather complex graph shown here. I would suggest perhaps using the graph to QA your results if suitable. I hope that helps.

    Shane Regan | Principle Building Performance Support Engineer