Hi I've just come across an calculation error with connect, where a cable has been sized for the motor load input data not the motor protection device size, can you explain why this happened?
Hi Matt - As the cable only has to withstand the start current for a very short period, then the cable is sized on the circuit current. For more information please see this document.Regards,
Duncan Brown