Hi Tony - The software doesn't force you to do anything. if the cable fails the checks you will get a report of the failures. It would be up to yourself to decide whether to use a different cable.I would strongly recommend considering section 4.6 in the manual for details on how operting temperature are implemented. This is quite a detailed section and should be of help.The manual can be accessed by running the Connect program, clicking on the file menu and selecting "manual" - the section that should interest you would be "17th Edition Calculations"Regards,
View online
If you encounter issues clicking "View online", check here.
You received this notification because you are subscribed to the forum. To unsubscribe from only this thread, go here. To unsubscribe from a forum, please see this note.
Flag this post as spam/abuse.
Tony – If a specific cable isn’t available that suits your requirements then you should consider a different cable that has similar characteristics. As the PVC cable doesn’t meet your requirements you should consider an equivelent other cable.
Duncan Brown
Hi Tony, are you saying that you want to use the LSF cable but somehow limit it's operating temperature to 70deg to match the device and connected equipment?
In terms of the software cables are initially sized based on the current carrying capacity defined in the data. This is assumed to be a loaded cable and therefore the cable will be assumed at operating temperature. Adjustments are made for grouping, ambient temperature etc but there is not adjustment in initial cable sizing for operating temperature. Duncan has already pointed you to the section in the help files for details on that.
Cable Initial and Final temperatures do come into play in the Volt Drop and Fault Current Calculations but I don't think this affects what you are asking.
To take advantage of the capacity of LSF you set it as you chosen cable. We don't hold any details of device operating temperature in the data and so we don't do any check against the cable operating temp to check validity. We leave that to the discretion of the engineer.
Steve Brown | Bentley Systems
Hey Tony - We don't have the data available for the LSZH cable that you require. Please see Steven Brown's reply, above.Regards,