Hi,
Try to place the system marker. but it says "Cannot find a pipe to place fitting"
Another issue if I need to calculate pipe sizes I need to place the marker on each floor? Where is the video on the website hoe to use floor connector, I have seen before somewhere?
Thank you a lot for your support.
Thank you
Maryna - You have to have your pipe height set to the same height as the pipe you are trying to add the system marker to. For example, if you're pipe is drawn at low level, then you current height should be set to low level. If you are unsure of your pipe height, use the Pipe Info option.And no - you can only have one system marker per system. Floors are connected using floor change connectors. For information on the best methods to generate floor change connectors please see this document.Note that again, this information is contained in the software manual. I strongly recommend becoming familiar with the manual.Regards,
Duncan Brown