Hi,
In the CAD input within thermal design within the a/c rate this is where we are inputting the infiltration rate of the building.
When it comes to the heatloss section where we are selecting the fixed air supply temperature and then inputting the air change rate here it does this globally. Is there a way to do this individually for each room as the air change rates are not the same for all rooms?
George
Hi George - You cannot specify different figures. You would need to run each room calculation on an individual or group of rooms basis, and then add up the plant loads after running all the rooms you required.Regards,