<?xml version="1.0" encoding="UTF-8" ?>
<?xml-stylesheet type="text/xsl" href="https://communities.bentley.com/cfs-file/__key/system/syndication/rss.xsl" media="screen"?><rss version="2.0" xmlns:dc="http://purl.org/dc/elements/1.1/" xmlns:slash="http://purl.org/rss/1.0/modules/slash/" xmlns:wfw="http://wellformedweb.org/CommentAPI/"><channel><title>Part L SFP</title><link>https://communities.bentley.com/products/building/performance/f/hevacomp-forum/171177/part-l-sfp</link><description>I am dealing with the entry of Specific Fan Powers for the Part L compliance. 
 Previously I have been advised when using Hevacomp I should calculate the average SFP for the fan as Hevacomp doesn&amp;#39;t take into account the switching off of the fan using</description><dc:language>en-US</dc:language><generator>Telligent Community 12</generator><item><title>RE: Part L SFP</title><link>https://communities.bentley.com/thread/492423?ContentTypeID=1</link><pubDate>Tue, 20 Nov 2018 12:28:53 GMT</pubDate><guid isPermaLink="false">6dad98f5-dbc9-4c4d-a9ba-e9da8dc6aa8e:b9e0b57c-0a87-4bda-97a3-0c5b0aebca6a</guid><dc:creator>Duncan Brown</dc:creator><description>&lt;p&gt;Rob - that sounds reasonable to me.&lt;br /&gt;&lt;br /&gt;Regards,&lt;/p&gt;&lt;div style="clear:both;"&gt;&lt;/div&gt;</description></item><item><title>RE: Part L SFP</title><link>https://communities.bentley.com/thread/492389?ContentTypeID=1</link><pubDate>Tue, 20 Nov 2018 09:58:19 GMT</pubDate><guid isPermaLink="false">6dad98f5-dbc9-4c4d-a9ba-e9da8dc6aa8e:26f644b0-e1ec-4e88-aff6-3d3df4d2a586</guid><dc:creator>Robert Smelt</dc:creator><description>&lt;p&gt;Thanks Duncan,&amp;nbsp;&lt;/p&gt;
&lt;p&gt;Just for clarification you are confirming that we should continue to calculate the average SFP for a fan. This is based on its actual SFP average over an hour as the extract rate is l/s/m2&lt;/p&gt;
&lt;p&gt;&lt;/p&gt;
&lt;p&gt;Regards&lt;/p&gt;
&lt;p&gt;&lt;/p&gt;
&lt;p&gt;Rob&lt;/p&gt;&lt;div style="clear:both;"&gt;&lt;/div&gt;</description></item><item><title>RE: Part L SFP</title><link>https://communities.bentley.com/thread/492388?ContentTypeID=1</link><pubDate>Tue, 20 Nov 2018 09:53:14 GMT</pubDate><guid isPermaLink="false">6dad98f5-dbc9-4c4d-a9ba-e9da8dc6aa8e:d12a3563-2c4f-41bf-a89a-010739e1b212</guid><dc:creator>Duncan Brown</dc:creator><description>&lt;p&gt;Hi Rob - Bentley Hevacomp software has no involvement in the PartL calculation. We take the information you provide and pass it to the SBEM calculation engine. As SBEM takes no consideration of occupancy for SFP I would recommend continuing with this model.&lt;br /&gt;&lt;br /&gt;Regards,&lt;/p&gt;&lt;div style="clear:both;"&gt;&lt;/div&gt;</description></item></channel></rss>