Hi,
With reference to the post in "Changes for the 18th Edition", what is the reason for considering 1 Sec (see snap below) disconnection time for Other circutis in TN system.
As per BS 7671:2018 Regulation 411.3.2.3 - In a TN system, a disconnection time not exceeding 5 s is permitted for a distribution circuit and for a circuit not covered by Regulation 411.3.2.2.
So is this supposed to be 5 Sec as per the BS 7671?
Hi Yadagani,
The reference here to the previous 17th edition regs is included for consistency with older 17th edition projects so that they are compatible in the latest version . This option will be disabled if you create a new project as the 18th edition will be chosen by default.
Shane Regan | Principle Building Performance Support Engineer