Electrical Calculations vs Manufacturers information.

Hi,

We have a scheme on site with a sub-main sized and selected using Hevacomp.

The contractor has reported that the measured Zs value of the circuit is greater than the Manufacturer's maximum Zs value for the MCCB at 0.28ohms.

The calculated Zs in Hevacomp is 0.334ohms and has not been identified as a failure.

We have solutions to overcome the issue but are surprised that it has not be identified by the software. I'd hate to have other issues to resolve like this on future schemes.

Details attached.

Any comments / ideas? 

Thanks in anticipation