Hi,
Typically I would calculate my Heat gains in summer time in order to get a peak coincidental load. However, I have been asked to produce a number of Heat gain calculations - one for each week of the year. I have noticed that when I run a heat gain calculation and set the outside conditions design day/month to January 7th, between the hours of 9pm to 7am, instead of a heat gain figure I am presented an asterix (*). Above the table it mentions that the asterix (*) = Sensible fresh air load excluded. Why is this figure being excluded from the Heat gain calculation?
Kind regards,
Tony
No problem Tony.
Shane Regan | Principle Building Performance Support Engineer
Thanks
Thanks Tony, the limited results were just due to your settings for Cooling Plant operation time, in Building Data, as below. If you set this to 1-24 all hours will be reported.
Answer Verified By: Tony Carter
Hi Shane,
Thanks, project has been uploaded as a zip file.
Hi Tony,
No problem, I'd like to have a look at your project if you could please upload the project folder to this link.
Thanks,
Shane