I am working on a open plant office project however some of the locations seem to have very high latent gains. The design criteria is pretty standard, 1Person/10m2, 12L/s/p, Casual Gains 90/50W, Small Power Gain 25W/m2, Lighting Gains 8W/m2. Good U-values generally, but some rooms have latent loads > sensible loads.
Hello Grant, are you running the CIBSE Gain calculation?
Shane Regan | Principle Building Performance Support Engineer
Hi Shane yes running the CiBSE Heat Gain Calculaton on Hevacomp.
Hi Grant, without seeing the project I could only really give general advice such as this info here. If you need us to look into this in depth we would need to see the project - could you please upload to this link? And also please let us know one specific room that is of concern.
Thanks Shane, I have uploaed the files.
The latents seem high generally across the board but in particular:
G01-01
G05
G06
G07
G12
G13
G18
F02
F15
F21
F22
Hi Grant, the latent loads themselves are calculating fine - the reason they seem comparatively large in relation to the sensible gains is that temperature rise of 2 degrees has been allowed.
The effect of this is to reduce the Sensible load - eg see below for room G05, with Temperature Rise allowed and disabled:
You can find further info on the effect of this setting here.
Answer Verified By: Shane Regan