Fail Type 7

Connect Fail Type 7

I noticed a question back in 2019 with regard to fail type 7 as below.

Under the fail help, fail type 7 is determined as "Fails as no I2t data is available for the devices, assume a failure by default".

I assume that the I2t data for the specific devices is not present in the data file for that particular device, in this instance Schneider Mirologic ACB's.

With no I2t data the calculation defaults to unlimited energy let through, which then fails the k2s2 > I2t test.

As such I'm left with a failure on the main supply where I'm using Schenider ACB's on both the LV supply (in this case an outgoing transformer) and on the incoming side of the main panel board.

Using the generic ACB on the LV feeder overcomes the issues, but then gives me a discrimination problem with the down stream Schneider ACB.    

Why is the I2t data not included in the calculation? And how do I overcome the issues?

Schneider ACB's must be one of the most commonly used protective devices of this type. 

I too have the need to produce calculations for scrutiny by a Consultant.

When will this issue be resolved?  Using a Generic ACB does not satisfy the Consultant, they require the verified calculations using the devices we will be installing.

Please advise when a fix will be provided.

Parents
  • Thanks Shane
     
     
    Kind regards
     
    Paul Trenter
    Ceetech Limited
     
    Tel:      01473 830095
    Mob     07947 359 293
     
    As many of you know each year at Christmas some suppliers bring gifts into us at Ceetech, we have decided to ask that instead of gifts, charitable donations are sent, that we will then pass on to The Ipswich Bus Shelter.  
    Further we will not be sending any gifts or cards this year instead making a donation of ÂŁ500 to Ipswich Bus Shelter which will go towards the good work that they carry out for the less fortunate.
                   
    The Ipswich Bus Shelter supports the homeless and those in need within Suffolk. (More information can be found at www.thebusshelteripswich.com)
     
    On behalf of all staff at Ceetech we thank you for your support during another challenging year and wish you a Very Happy Christmas and a prosperous New Year.  We look forward to continue working with you in 2022.
    Follow us on     Visit our website www.ceetech.co.uk
     
    Disclaimer
    This message is intended only for the use of the person(s) ("Intended Recipient") to whom it is addressed. It may contain information, which is privileged and confidential. Accordingly any dissemination, distribution,
    copying or other use of this message or any of its content by any person other than the Intended Recipient may constitute a breach of civil or criminal law and is strictly prohibited. If you are not the Intended Recipient,
    please contact the sender as soon as possible.
    Registered Office : Ceetech Ltd, 8 The Courtyards, Wyncolls Road, Severalls Industrial Park, Colchester, CO4 9PE. Registered in England No. 4242024. VAT Registration No. 786 6131 01.
     
     
  • Does this mean that traditional Connect software is being ignored?

    Not all users have the funds or inclination to adopt OpenBuildings Designer.

  • Paul,

    I would suggest connect has been neglected for some time. I raised the issue of missing data from the Schneider range back in 2019, along with my concerns over the calculation method for Zs and cable sizing, over sized armour on SWA cables compared to the actual amount of SWA incorporated by the cable manufacturers, no Eaton IZM data.

    The UI of the software hasn't changed for 20 years, I've been using connect since 1999.     

  • Hi Paul and Stuart, 

    Apologies for the late response!

    Based on Prduct management's response on this, I'm afraid that we do not have any immediate plans of developing Hevacomp connect, or transitting the facilities in OpenBuildings. 

    Thanks for raising this and I genuinely appreciate your concern! 

    Regards, 

    Krishnendu

Reply Children
No Data