Sub-main cable sizing - Connect

I have an issue in Connect, where an undersized sub-main cable is being allowed to pass and not show up as an error.

16mm2 XLPE/SWA cables to table 4E4A (3 phase 4-c) under ground in a duct max load is 75A.

The sub-main is protected by a 100A MCCB, therefore the minimum size in accordance with 4E4A is 35mm2 (rated to 115A for underground)

If I un-tick the fix it button on the cable size, Connect will calculate the cable size to be 16mm2 with no errors. If however I fix it at 16mm2 it comes up as a red warning that the cable cannot carry the required current.

I have had this issue before where Connect undersized an underground sub-main with out an error warning, and I picked it up when I did my checks on the data. At the time I put it down to a glitch with the model, as I had re saved a previous project .

Can you please advise why this would occur.