Parallel Cable runs
What's the best way to create a wire symbol for parallel runs for motor leads? We usually add multiple cable symbols to the wire to show number of parallel runs but the cable report and engineering consideration doesn't like multiple cables on one line, and the cable report doesn't always work. We also need these cables to show up accurately in the cables pull report.
  • Hi Andrew,
    Yes, using multiple cable symbols on a single wire may not be a good way to do things.
    A cable symbol signifies that the wire is a single cable or a core in case of multicore cable. What family do you usually assign to a cable symbol? One better way might be to create a family which serves your purpose.
    Sarvesh Kulkarni
    Product Engineer - Bentley Systems
  • Andrew,
    There is an existing Enhancement Request #16181:Paralleled cables: support for assigning and labeling parallel cable conductors. We have added you to the requestor list for the same (SR #7000821270).
    My colleagues suggested following workarounds that may be useful:
    - One way to do this is to use families so that all conductors are part of the same cable id but each “set” of cables are all children of the same family.  So something like CAB1 family is for 3 sets of 3 parallel cables so it has 9 children: child1    conductor1_1
    Child2    conductor1_2
    Child3    conductor1_3
    Child4    conductor2_1
    Child5    conductor2_2
    Child6    conductor2_3
    Child7    conductor3_1
    Child8    conductor3_2
    Child9    conductor3_3
    Then all conductors still have the same cable ID and show up in reports
    - You can get around the limits in the software by having extra connections points on one of the symbols, normally the motor.  Then each of the parallel cable could start at the same source but end on a different point on the motor.
    With some careful symbol design and cable tag naming you can get a decent approximation.
    Hope this helps !
    Sarvesh Kulkarni
  • Hi Sarvesh,
    please add me to the requestor list of that feature.
    I have tried a "family" solution mentioned above, but it does not work as expected.
    My test family:
    Then I have tried to assing two conductors to one wire:
    But still I get error message, and cable manager doesn't show that connection properly:
    In the same cable (e.g. 14 condutors of 1 mm2) sometimes we are not using paraller run at all, sometimes 1-2 conductors, sometimes 3-4 and so on. Only depends on needs, every time it could be different.
    Extra connection points are not a good solution.
    Wojtek
    Best regards, Wojtek
    SW: Promis.e 08.11.13.96/23.00.00.46
  • Hi Wojtek,
    I would like to inform you that, I have added you to the requestor list of the Enhancement #16181: Paralleled Cables : Support for assigning and labeling parallel cable conductors (SR # 7000856624).
    Sarvesh Kulkarni