Factor of safety drop below 1.0 when running a C-phi reduction

I'm working on plaxis 3d for a excavation and lateral support system in cement mixing treated reclamation ground. But the computed factor of safety suddenly drop after reaching its peak and then fall to close 0... any one have similar experience before for this problem?

Parents
  • Dear James,

    Rarely Safety calculations could give the user the SumMsf value lower than 1.0. 

    It means most likely that the previous phase is not stable, probably there is no equilibrium on this phase.

    First of all I will advice you to refine the mesh and increase Max steps on the Safety phase (500–1000). We need to know that for defined number of steps we receive the stable value of SumMsf.

    If it does not help, please add Nil-phase after the previous phase (Safety phase − 1): just add a phase with Plastic type of calculation and calculate it. There is no changes on the phase. The Soil body seems to be collapse likely appears.

    Maybe the reason is in material parameters, geometry, loads, mesh quality and coarseness, phase settings (including iterative procedure settings) etc.

    Might be interesting:

    — Article Safety analysis and displacements
    — Webinar Using PLAXIS to Determine Factors of Safety

    Hope it helps.

Reply
  • Dear James,

    Rarely Safety calculations could give the user the SumMsf value lower than 1.0. 

    It means most likely that the previous phase is not stable, probably there is no equilibrium on this phase.

    First of all I will advice you to refine the mesh and increase Max steps on the Safety phase (500–1000). We need to know that for defined number of steps we receive the stable value of SumMsf.

    If it does not help, please add Nil-phase after the previous phase (Safety phase − 1): just add a phase with Plastic type of calculation and calculate it. There is no changes on the phase. The Soil body seems to be collapse likely appears.

    Maybe the reason is in material parameters, geometry, loads, mesh quality and coarseness, phase settings (including iterative procedure settings) etc.

    Might be interesting:

    — Article Safety analysis and displacements
    — Webinar Using PLAXIS to Determine Factors of Safety

    Hope it helps.