Flow/Capacity (Design) while using Darcy-Weisbach method

Hi, 

The Flow/Capacity design while designing sewer using Darcy-Weisbach method goes upto 102%. 

Can any one please tell why it happens? When we use manning's for designing sewer network Flow/Capacity design is restricted to 100%.

Best Regards

Jatin Talwar

  • Hello Jatin,

    There might not be a better design available with the constraints defined.

    Check the diameter of the conduit that has a "Flow/Capacity (Design)" of 102%.
    Check your conduit catalog to see if there is a larger diameter available for design.

    If that is not the reason then please provide the model files so we can see all of the constraints in your design.
    See: Sharing Hydraulic Model Files on the Haestad Forum

     

    Regards,

    Craig Calvin

    Bentley Technical Support

  • Hi Craig, Had it been occurring only for the biggest diameter pipe in conduit catalog it was ok. But the problem is, it happens for all the pipes .

    Best Regards
    Jatin Talwar
  • Please provide the model files using one of the options in the link below.

    Sharing Hydraulic Model Files on the Haestad Forum

     

    Regards,

    Craig Calvin

    Bentley Technical Support

  • Hi Craig,

    Sorry for replying to this thread after such a long gap. I am still facing the issue while using using Darcy-Weisbach method. The model has been uploaded separately today under the name "For Bentley.zip".
    The model contains new proposed network as well as existing network, some of which is undersized and not of concern. I have mentioned "Existing" in a user defined field of "Status" in conduits for clarity.
    The concern is the proposed network where the Flow/Capacity design value exceeds 100%. This is happening for pipes ranging in diameter from 200 mm to 1800 mm pipe.
    Also, there is a new proposed 1800 mm dia pipe which has a flow/capacity design value of greater than 100%. regarding this particular 1800 mm dia pipe, my concern is that although 1800 mm is the maximum size of conduit defined in conduit catalog, the range of slope and velocity at which it can be designed (defined in constraints) is large 200 to 2000 and 0.7 to 3 m/sec respectively. Still the pipe is getting designed at the flattest possible slope of 2000 with a velocity of 1 m/sec and a flow/capacity design value of greater than 100%.

    Request you to please look into it.

    Best Regards
    Jatin Talwar
  • Hello Jatin,

    In the model you sent, I see 21 conduits out of 1988 that are "existing" (Design Conduit = True) and that have a Flow/Capacity (Design) above 100%. With the exception of the 1800mm conduits, they are all under 103%. This may be due to exceptional cases during the design iterations. In such rare cases, you may want to simply adjust the sizes yourself.

    The automated design feature is not meant to replace the engineer, and some judgment and tweaks may be necessary.

    As for the 1800mm conduits at 117%; I suspect that this is due to hitting the maximum size available, and the prioritization of minimizing excavation (cover). If a larger size (say, 2000 mm) was available, it would prefer that over an increase in slope, since that would increase excavation. Since 1800 mm is the maximum though, it selects that and "stops", settling on the minimum slope. With that being said though, similar to the above, could you adjust these few pipes manually?

    Regarding the Mannings method not seeming to cause the same issue; in my testing it does not appear that the Mannings n (0.01) that you have entered are equivalent to the Darcy-Weisbach e (1.5mm). If you compute the model in analysis mode with just those 1800 mm pipes, set at 1800 mm and the same slope (2000 1/S), you will see they have different capacity. Flow/Capacity (design) will be at about 83% for the same flow, vs 117% with the Darcy coefficients.


    Regards,

    Jesse Dringoli
    Technical Support Manager, OpenFlows
    Bentley Communities Site Administrator
    Bentley Systems, Inc.