Hi
I think "Element Property Inferencing" in the SewerGems has an issue in the manholes that " Allow Drop Structure" is being set to true!
Please fine the attached file and correct me if I am wrong.
In the attached file, in the manhole MH-3, Actually,I want to interpolate the invert elevation between MH-1and Invert (In) MH-3 Not Invert(out)!
Thanks and look forward to hearing from you.
Hamid
Hello Hamid,
It looks from the picture that start & stop inverts of conduits are different that from the manholes, i.e. you have specified set invert to start/stop to false.
You want the drops in the system, so obviously the start invert of conduit & invert of manhole would be different. So inverts of conduits will not be updated in the element property inferencing tool.
As already suggested by Scott in this thread, element property inferencing would work only when Set invert to start/stop is set to true. So please check your inputs again.
Sushma Choure
Bentley Technical Suppport
With Sushma's response in mind, one possible workaround in this example case is to:
1) manually set the invert of MH-3 equal to the stop invert of CO-2 (it looks like this is around -1.00 m)2) Choose "true" for "set invert to start" and "set invert to stop" for CO-1 and CO-23) Run the element property inferencing tool to interpolate a constant slope between MH-1 and MH-34) Choose false for "set invert to stop" in CO-2 and re-enter the stop invert5) Set the invert of MH-3 back to the original value (-1.54 m)
Answer Verified By: Hamid.AKbari
Also if you consider to the 3d object viewer something like attached capture will be grate to user be able to see utilities and terrain as 3d furthermore profile.