I am setting up an EPS for a client that has logic within their SCADA system to rotate which well is being called for according to a fixed sequence.  For example, if well 1 was the last well to operate, the next time a well is needed well 2 is started...  Is there a way to recreate this rotation within the EPS controls?

  • Hello Ken,

    The following link as information on how to do this, as well as a sample model: Controls for alternating or cycling between pumps. Basically, you would use a couple of dummy pipes to help with the simulation, changing the status of the dummy pipe to act as a sort of counter. The link above goes into details on doing this. Please let us know if you have any questions on this.

    Regards,

    Scott

  • I think I can make that work for what I need.  Just a bit more complicated as I have three wells to cycle and am starting or stopping the wells based on elevations from two different elevated tanks...

  • Please see below for a summary of my proposed control logic.  My intent is to use a series of "and" statements to represent the items in parenthesis with those conditions detailed in the tables below.  CP1 and CP2 are fake control pipes I plan on running between two reservoirs that will otherwise be disconnected from the system.  T1, T2, Pmp-On and Pmp-Off values are my tank levels and start and stop points.  Any glaring mistakes before I start detailing all this out within WaterGEMS?  Thanks...

    Summary of Needed Control Language

    Starting Pumps

    IF (Combo 1) and (next well = 1) and T1 < Pmp-On1 or T2< Pmp-On2, Then Pmp 1 = on and (Next Well = 2)

    IF (Combo 1) and (next well = 2) and T1 < Pmp-On1 or T2< Pmp-On2, Then Pmp 2 = on and (Next Well = 3)

    IF (Combo 1) and (next well = 3) and T1 < Pmp-On1 or T2< Pmp-On2, Then Pmp 2 = on and (Next Well = 1)

    IF (Combo 2) and T1 < Pmp-On1 or T2< Pmp-On2, Then Pmp 2 = on and (Next Well = 3)

    IF (Combo 3) and T1 < Pmp-On1 or T2< Pmp-On2, Then Pmp 3 = on and (Next Well = 1)

    IF (Combo 4) and T1 < Pmp-On1 or T2< Pmp-On2, Then Pmp 1 = on and (Next Well = 2)

    IF (Combo 5) and T1 < Pmp-On1 or T2< Pmp-On2, Then Pmp 3 = on and (Next Well = 1)

    IF (Combo 6) and T1 < Pmp-On1 or T2< Pmp-On2, Then Pmp 2 = on and (Next Well = 3)

    IF (Combo 7) and T1 < Pmp-On1 or T2< Pmp-On2, Then Pmp 2 = on and (Next Well = 3)

    Stopping Pumps

    IF (Combo 2) and T1 > Pmp-Off1 or T2> Pmp-Off2, Then Pmp 1 = off

    IF (Combo 3) and T1 > Pmp-Off1 or T2> Pmp-Off2, Then Pmp 2 = off

    IF (Combo 4) and T1 > Pmp-Off1 or T2> Pmp-Off2, Then Pmp 3 = off

    IF (Combo 5) and T1 > Pmp-Off1 or T2> Pmp-Off2, Then Pmp 1 = off

    IF (Combo 6) and T1 > Pmp-Off1 or T2> Pmp-Off2, Then Pmp 3 = off

    IF (Combo 7) and T1 > Pmp-Off1 or T2> Pmp-Off2, Then Pmp 2 = off

    IF (Combo 8) and (Next Well = 1) and T1 > Pmp-Off1 or T2> Pmp-Off2, Then Pmp 1 = off

    IF (Combo 8) and (Next Well = 2) and T1 > Pmp-Off1 or T2> Pmp-Off2, Then Pmp 2 = off

    IF (Combo 8) and (Next Well = 2) and T1 > Pmp-Off1 or T2> Pmp-Off2, Then Pmp 3 = off

     

     

     

     

     

     

    Eight Possible Running states

     

    Combo #

    Wells On

    Well 1

    Well 2

    Well 3

    1

    All off

    Off

    Off

    Off

    2

    Well 1 on

    On

    Off

    Off

    3

    Well 2 on

    Off

    On

    Off

    4

    Well 3 on

    Off

    Off

    On

    5

    Well 1 and 2 on

    On

    On

    Off

    6

    Well 1 and 3 on

    On

    Off

    On

    7

    Well 2 and 3 on

    Off

    On

    On

    8

    All On

    On

    On

    On

     

    Next Well to Start

    Well #

    CP1

    CP2

    1

    Open

    Closed

    2

    Closed

    Closed

    3

    Closed

    Open

     

     

     

  • I don't see any glaring mistakes, but from experience troubleshooting controls I find it easier when they are separated into the most simplistic or a more simplistic form rather than using combination control statements. It might take longer to enter the controls, but if one part of the control is not working it's easier to find the mistake.

    Mark