Hello,
In addition to Tanay's response you can find out more about extended period simulation and tank operating range from the following articles;
Run an Extended Period Simulation (EPS)
Understanding Tank Operating Range
Hope this helps.
Regards,
Yashodhan Joshi
Thanks for the reply...what does warning status message Tank T-1 is emptying at 1m mean?
Hello Vishal,
The notification means that tank becomes empty at 1 m as the water is drained out completely before it becomes full. You can add controls on pump -on& off, if you have in the model based on the tank levels. So that tank is continuously filled as per the levels.
Below technote explains how to setup controls in the model, please go through it.
Creating Controls - Conditions, Actions, and Control Sets (CONNECT Edition and V8i SELECTseries 6)
Since you are a new user, please go through the below learning resource of WaterGEMS/WaterCAD.
https://communities.bentley.com/products/hydraulics___hydrology/w/hydraulics_and_hydrology__wiki/11933/learning-resource-guide-for-new-users-of-bentley-watergems-and-watercad
Sushma Choure
Bentley Technical Suppport
Thank you so much for the reply...I have one last question...i have given the tank elevation lesser than the junction elevations...but still the flow is taking place and I don't have any pump near the tank... how is it possible for water to flow when tank is at lower elevation then junctions without any energy?
What is the "operating range type" for the Tank? Is it set to Levels or Elevations?
In such cases we also need to see the upstream and downstream conditions. What are the pressures in the downstream of the tank?
Better if you share the model with us.
Thank you.
Vishal, the model solves around the assumed boundary conditions and demands. The elevation of the junctions only allow the pressure to be calculated. For example if there is a local high point, the energy balance does not know that more head needs to be added to overcome that elevation, with potential part-full flow if an air valve is open. See more details on that here.
In your case water will flow out of the tank based on any assumed demands you have entered downstream, or assumed hydraulic grade you have defined at reservoirs or other tanks, and the model solves the energy balance around that. In your case you would see a negative pressure reported at the junction whose HGL is below the node physical elevation. More details on that can be found in this Wiki article:
Troubleshooting negative pressures at pumps, junctions, & other node elements
What this tells you is that the real system may not be able to operate and that you must change something in order to resolve the problem.
Jesse DringoliTechnical Support Manager, OpenFlowsBentley Communities Site AdministratorBentley Systems, Inc.
Answer Verified By: Vishal Cn