Hi guys,
I am trying to Fix an issue in my water gem model for industrial area project. The model is running seamlessly perfect, But I am not able to achieve the required pressure (2.5 bar) at node point PW-12. This node connecting to the underground water tank from there water will be pumped to the industrial building. I tried to fix the issue with many trials but can't to solve this. I have attached my model kindly review and let me know the solution.
5.8_Industrial_WaterStudy_AppA_WaterGEM.zip
Hello Ragavendra,
You can use a PRV to reduce pressure at node PW-1. Here is a relevant article that can help you on that;
How does the Pressure Reducing Valve (PRV) work in WaterGEMS and WaterCAD?
I was able to achieve a pressure of 2.5 bars at junction PW-1 by using the following setup;
In the above setup you can see I have first created a node J-110 at an elevation same as PW-1 (i.e. 16.5 m), then I have connected it to a PRV (also at elevation 16.5 m and diameter 250 mm same as pipe) which connects to your existing node PW-1. Prior to creating this modification the length of pipe between reservoir R-2 to PW-1 was 13 m. I manually put my "User Defined" length as 13 m for the pipe connecting PRV-1 to PW-1. For the rest of the two pipes I used very small user defined lengths, (order of 0.001 m). This way it is negligible and the total length from reservoir to PW-1 is 13 m only.
I have annotated junctions for pressure, as you can see the pressure is reduced from 2.7 bars to 2.5 bars.
Hope this helps.
Yashodhan Joshi
Sorry, it's my mistake Actually I mean it getting less pressure (1.49 bar) at PW-12. So I need more head to satisfy the requirements
Ragavendra,
why do you need to archive 2.5 bars at PW-12? your system downstream has tanks and pump.
your HGL at the Reservoir is 44m and the elevation at PW-12 is 16m, the static deference is 28m = 2.8 bars; with that configuration of FCV, pipe size and flow you cannot get 2.5 bars, try to increase the HGL at the reservoir and try change pipe size.