Hello

How can i resolve a problem of negative pressure in water hammer intial condation??
i am delling with a system of 16 km leangth & 2 working pumps with 162m3/h @ 98.8m each at 14 Km i have some high points where gravity flow for 1.2 Km has been considered from the most higher point (310.15m) to the discharge tank(MWL =298m)
the pump head has been calculated based on the assumption of gravity flow. hence, water to be pumped only to 310.15m.

i tried many time to insert som air valves but still the problem as it is

please helpe me

HGL for the system is in shown below:

  • Hello Bushra,

    When using the air valve element, you will need to set the "treat as junction" property to "false" in order for the initial conditions calculations to "see" it and have the upstream pump know that it needs to add enough head to overcome the high point. See more in these articles from our Wiki:

    Why do I get a negative pressure at a high point in my system? Shouldn't the pump add enough head to push the water over the hill?

    Modeling Air Valves At High Points in WaterCAD or WaterGEMS

    However, this doesn't work well for a transient run because the real system would have part-full flow in the piping downstream of the high point when the air valve is open, and there would be an air gap that the transient wave wouldn't pass through. An option to consider here is to replace the high point with a Discharge To Atmosphere element and delete all the piping downstream of it. See the section called "Transient Simulation Implications in HAMMER" in the second article above.


    Regards,

    Jesse Dringoli
    Technical Support Manager, OpenFlows
    Bentley Communities Site Administrator
    Bentley Systems, Inc.

  • If discharge to atmosphere element has been considered, the transit results would be accurate enough considering that high point??

  • Yes, if the high point experiences part-full flow under normal operating conditions (and in the initial conditions for your transient event), then the D2A approach would be a better model representation of the conditions, and should yield better results than if you tried modeling it as an air valve. Meaning, if your air valve is normally open, with some air in the downstrream side, then there would be an air gap and any transient in the upstream pipeline would not pass further. It would act as a free discharge into the part-full pipeline and some wave reflection would occur - hence the D2A. I made a little diagram for you, and have added it to the related articles:


    Regards,

    Jesse Dringoli
    Technical Support Manager, OpenFlows
    Bentley Communities Site Administrator
    Bentley Systems, Inc.

  • actually in real situation only 1 pump is in operation while the second one will be operated in emergency case at this time the pipeline is already fully filled with water and from the highest point (311m) water will flow by gravity for 1.200 km from 311 to 286m( inlet of tank). i have designed my pumps based on this situation where i have reduced the pumps size considering the help of gravity flow at last portion ( design head is 98.5 considering the static difference between the highest point 311m and suction tank 271 plus the losses in all pipes minus the static difference between the discharge tank and highest point )so water will be pressurized up to the highest point only then gravity flow will start. could you please suggest the best way to represent this situation. since the transite study shall be based on 2 pumps operation. I have problem with negative pressure at high points as i mentioned above. pump head is more than enough in reality wile because of program assumptions that not enough since boundary levels are only considered ignoring the high points

    Please help with batter approach to represent the reality

    Thanks & Regards

  • Please see the link in my first post:

    Modeling Air Valves At High Points in WaterCAD or WaterGEMS

    If you add an air valve element at the high point and set the "treat as junction?" property to "false", the upstream pump will "see" it as a hydraulic boundary so that it adds enough head to reach the high point, with part-full flow downstream.


    Regards,

    Jesse Dringoli
    Technical Support Manager, OpenFlows
    Bentley Communities Site Administrator
    Bentley Systems, Inc.