Weird Simulatoin Results with Pump SCADA Data

Hi All,

I'm running a pump+network model and got a werid result. I built and calibrated the pump model and network model seperately, all both ran well. And the weird result happened after I combined the pump and network together.

For the pump, it has five pumps with its operation data from SCADA system. Since the pump has "ON & OFF" status depanding on the time, I used the VSP + pump pattern to present different pump operation status (as below) and the result in the second pic. Shown in the result, the calculatoin fails somehow, but will need some guidance on how to check the model. 

    

Thanks,

Meng

  • Hello Meng,

    Do you see any user notification for this? From the second image I can make out that the pressure is zero after the pump. Is my assumption correct?

    Is there flow in the pumps? Have you checked if the pipes are active / open, or, if the pumps are on?

    We would need to take a look at the model files to see what is happening here.

    Please share the model files, following the steps provided in the below article;

    Sharing Hydraulic Model Files on the OpenFlows | Hydraulics & Hydrology Forum

    Let me know when you share the model files.


    Regards,

    Yashodhan Joshi

  • Thanks for the reply, Yashodhan. 

    There are no flow in the pumps during the fail calculations. And yes, all necessary pipes and components are active. The pump ON/OFF status shows in the pump pattern. 

    Also, I've attached the model thro the confidential link. The file name is "weird model" and the address here https://communities.bentley.com/p/secure_file_upload

    Eager to learn what went wrong.

    Thanks,

    Meng

  • Hi Meng,

    I've taken a look at the model. The main reason why the calculated results do not match the assigned patterns is because your calculation options are set to use a constant, one hour reporting time step. So, although the calculation timestep is five minutes, the results were only showing datapoints at every hour. Change the reporting time step to "all" (see more here).

    The other reason for mismatch is that the big negative pressure results during unbalanced timesteps throws off the graph scale. The unbalanced times are caused by a few periods of time where multiple pumps are switching on and off (1.0 and 0.0 multipliers) at the same time. Pumps 2 and 5 flip-flop at 305 minutes, pumps 1 and 2 at 410 minutes and the change at pump 1 at 1060 minutes coincides with other changes) Try making the following timing changes to the pump patterns:

    "#1" - For row 212 (1060.02 minutes) change the multiplier to 0.98 

    "#2变频"

    • For row 61 (304.98 minutes) change the time from start to 305.00 minutes
    • For row 81 (405.00 minutes) change the multiplier to 0.890

    "#5变频"For row 61 (304.98 minutes) change the time from start to 305.00 minutes

    With this, the model balances at all timesteps for a 24 hour simulation and the results appear reasonable. More guidance on model stability can be found here: Troubleshooting the Network Unbalanced or Cannot solve network hydraulic equations user notification


    Regards,

    Jesse Dringoli
    Technical Support Manager, OpenFlows
    Bentley Communities Site Administrator
    Bentley Systems, Inc.

    Answer Verified By: MENG ZHANG 

  • Hi Jesse,

    Happy New Year!

    Thanks for the quick and detailed answer. I'm having trouble to follow when you suggest "For row 61 (304.98 minutes) change the time from start to 305.00 minutes". Can you be more specific what to change?

    Best,

    Meng

  • Hello Meng,

    Thanks for the quick and detailed answer. I'm having trouble to follow when you suggest "For row 61 (304.98 minutes) change the time from start to 305.00 minutes". Can you be more specific what to change?

    Here, Jesse is suggesting to make the changes in the patterns used for your VSP pumps. See the screenshots below of the said times where changes are proposed;

    Here instead of time 304.98 try using 305.00 mins

    Here for 405 mins try using a multiplier or 0.89

    As suggested the model balances with the above inputs at all timesteps.


    Regards,

    Yashodhan Joshi