Flow supplied and flow demanded is zero

Parents Reply
  • Hi Khushwant,

    Your demands are entered with units of L/Day, but the calculated Demand (in the Calculation Summary and junction properties for example) are set to L/s. Change the units to L/Day to match the input units and you'll see values greater than zero. (see below)

    For example junction F10 has a demand of 630 L/day which shows as 0.0 L/s because of decimal precision. 630 L/Day = 0.007292 L/s


    Regards,

    Jesse Dringoli
    Technical Support Manager, OpenFlows
    Bentley Communities Site Administrator
    Bentley Systems, Inc.

    Answer Verified By: Sushma Choure 