Constituent Types

Hello,

I want to know that which option is better constituent type to carry out booster chlorination study at node in Water Distribution Network?

Thank You.

Parents Reply Children
  • It all depends on how you want to control feed:

    If you want to continuously feed a known flow and concentration, use Concentration

    If you want to feed a constant mass flow rate , use Mass Booster.

    If you want to modify feed based on flow, use Flow Paced.

    If you wan to maintain a constant outflow concentration, use Set Point.

    I would say that most people who can afford it, use Set Point but it is the most complicated and expensive setup. It requires chlorine sensors and .a logical controller, while Concentration is the simplest/least expensive in terms of  equipment  but is limited in flexibility.