Model is negative at the water plant and I don't exactly know what is causing it.

When I run my contour map my model is showing negative pressure at the water plant. 

WaterGems 

Parents
  • Hello Andrea,

    Do you have a junction near the "water plant" that has an elevation set too high? Take a look at a profile of the area to help visualize the hydraulic grade versus elevation. Negative pressure will occur when the hydraulic grade is below the physical elevation. See more here: Troubleshooting negative pressures at pumps, junctions, & other node elements

    If this does not help, please provide a copy of the model for review along with a screenshot of what you are seeing: Sharing Hydraulic Model Files on the OpenFlows Forum


    Regards,

    Jesse Dringoli
    Technical Support Manager, OpenFlows
    Bentley Communities Site Administrator
    Bentley Systems, Inc.

  • MUD 36AA.wtgpkg.wtgpkg.zip

    There's my file please let me know if it works for you.

  • Can you clarify what you mean by "running through"? Are you encountering a specific problem? Please clarify the steps to reproduce and clarify what you are seeing.

    If you are referring to the scenario named "Peak Demand", I took a general look at the demands:

    • Most of the demand is from Unit Demands, consisting of a varying number of units for each junction, for a unit demand called "unit demand - 1" which has a base flow of 1 gpm. The pattern is set to fixed for all unit demands and there is no pattern defined.
    • Many demand nodes also have a base flow demand consisting of 1 gpm with a fixed pattern, except for "MUD36_Nodes-81" which is set to 1200 gpm. Perhaps this represents a fire? Because the pattern is fixed, the same 1200 gpm applies for the entire EPS duration. If this represents a fire that occurs for a certain duration, a pattern should be assigned. See: Running a fire flow analysis in EPS (Extended Period Simulation) 
    • In your calculation options, you have set to multiply the base demand by 1.3 for all nodes in the selection set called "Elements added via ModelBuilder..." . The 1200 gpm demand node is included in this selection set so you will see a calculated demand of 1,560 gpm in the Results section of the properties.
    • You will notice in the Calculation Summary the flow demanded column shows a value of 2127 gpm at all times. This is because all demand patterns are fixed. This model may not be set up for an EPS yet as you would typically have a diurnal pattern assigned.


    Regards,

    Jesse Dringoli
    Technical Support Manager, OpenFlows
    Bentley Communities Site Administrator
    Bentley Systems, Inc.

  • Yes, that does represent a fire is there a better way of doing that -- that won't mess with the rest of my scenarios? I could not get my fire flow alterative to work.

  • Hi Andrea, the best approach may depend on what you need the model to tell you about your fire.

    Do you need to see what the instantaneous pressures are in the system when 1200 gpm is flowing at a hydrant nearby that junction? If so, you could run a steady state simulation (instead of the current EPS) with that fixed demand added to that node. To ensure that the 1200 gpm demand does not appear in other non-fire scenarios, you would need to ensure that they use separate Demand alternatives.

    If you need to assess the impact the fire has on your tanks, you may need to run an EPS like you have it now, but configure a pattern so that the fire only lasts for a certain period of time. This is what the article I mentioned in my previous reply explains: Running a fire flow analysis in EPS (Extended Period Simulation) 

    If you need to assess exactly how much fire flow is available at one or more hydrant locations based on constraints like minimum residual and minimum zone pressure, you would use the automated fireflow feature. In this case you would model the junction demands as the normal demands (remove the 1200 gpm fixed demand) and use the Fireflow alternative instead of a new Demand alternative. You mentioned that you could not get your fire flow alternative to work - if you attempted to use automated fireflow and encountered a problem, please review the information in the following article and if it does not help, provide more details: Understanding Automated Fire Flow Results


    Regards,

    Jesse Dringoli
    Technical Support Manager, OpenFlows
    Bentley Communities Site Administrator
    Bentley Systems, Inc.

  • Okay am looking to set up for an instantaneous pressure. How would I find the pressure at that node with a greater demand?

  • To see the pressure when the "fire" happens, look at the "Results" section of the properties of the junction after computing a steady state simulation with the fire demand added to the node. You can also use the hydrant flow curve option to see a range of demand and resulting residual pressure (remove the 1200 gpm demand from the node first).


    Regards,

    Jesse Dringoli
    Technical Support Manager, OpenFlows
    Bentley Communities Site Administrator
    Bentley Systems, Inc.

Reply
  • To see the pressure when the "fire" happens, look at the "Results" section of the properties of the junction after computing a steady state simulation with the fire demand added to the node. You can also use the hydrant flow curve option to see a range of demand and resulting residual pressure (remove the 1200 gpm demand from the node first).


    Regards,

    Jesse Dringoli
    Technical Support Manager, OpenFlows
    Bentley Communities Site Administrator
    Bentley Systems, Inc.