c-factor vs roughness height extremes
In the bookAdvanced Water Distribution Modeling and Management” I found the following:
If the differences in pressures and flows between actual conditions and predicted conditions are so great that unrealistic and unexplainable pipe roughness values (less than 30 or more than 150) or major adjustments in demands must be used to achieve calibration, then chances are good that the discrepancy is the result of a closed or partially closed valve or errors in system mapping.
The numbers less than 30 or more than 150 are Hazen-Williams c-factor. But when talking in terms of Darcy-Weisbach roughness height (e) what would be the extremes that one could draw the same conclusions from?
  • The key here is that you should not focus your calibration solely on pipe roughness but determine WHY the model and the field data differ and correct the parameter that is different.  Here is a list of a few of the things that can make the model and field data differ. You need to be a bit of a detective to determine which applies in your situation.
    Physical
    Pipe size/location
    Pipe connectivity
    Pipe roughness
    Pressure zone boundary
    Pump curves
    Pipe material/age in GIS
    System changes since model built
    Elevation data
    Operational
    Valve open/closed/throttled status
    Control valve operation/settings
    Transient events
    Actual operations not matching control rules
    Unusual operations when data were collected
    Tank water levels
    Pump status/speed
    Lack of sufficient sensors/gages
    Water quality reaction rates
    Demands
    Spatial allocation
    Model does not reflect conditions when data collected
    Large customers with atypical demand patterns
    Not accounting for seasonal changes in demand
    Data
    Inaccurate/uncalibrated gages/meters
    “Latched” data from SCADA
    Understanding SCADA data – average vs. instantaneous
  • Note that I have incorporated Dr. Walski's advice into the following related article: Water Model Calibration Tips
    Jesse Dringoli
    Bentley Systems, Inc.