RAM Concept - Design Details

I am using RAM concept to design an elevated slab supported by both interior columns and edge walls. This is an existing structure, so I have modeled all of the existing steel with hopes of checking it against the current and proposed future loading scenarios. After running my design, I'm getting some (not all) of the design strips to show "Failed: 7.12." When I go to that section of the code, it is referring to the minimum temperature and shrinkage steel section.

My slab is 14" thick with #5@12 each way, top and bottom. This would give me about 0.31 sq. in. per foot for both top and bottom in each direction. Based on the code checks, I would require ~0.0018(14")(12") = 0.3024 sq. in. of steel per foot. Is there a way I can look at a more detailed version and see WHY they noting this location as a failure? Any thoughts as to why this might be flagged?

I have another location where I have some failures but wanted to be able to gut check this first failure before moving on to the more specific locations.