Hi!
In STAAD Pro v8i, how are you going to model a runway footing on top of suspended slab(roof slab) and analyze & design the runway footing considering the strength of existing suspended slab?
Thank you!
Answer Verified By: Master Mac
Hi Sye,
Thank you for that very informative explanation/advice and also for spending time reading and answering my question. Appreciated much.
Initially what i did is as per below:
1) I modeled the suspended slab as mesh of plates supported by FIXED SUPPORTS at the perimeter only and defined the thickness which is 3.0M THK concrete (Compressive Strength = 30Mpa).
2) I then modeled the runway slab foundation as a BEAM at the middle of the mesh of plates (suspended slab) and make used of OFFSET to put it on top of the sus. slab. My runway slab now was a beam with defined properties of 1000m W x 400m THK sitting on middle top of the suspended slab.
3) Finally, i applied my computed loads (Vertical, Longitudinal & Transverse Wheel Load) and PERFORM ANALYSIS. I take the MAX Values of Mz. My, Mx and Vy and execute manual calculation for the beam rebars assuming simply supported.
Now, here is my follow up questions:
1) Is my appproach correct or can be considered?
2) I will also do what you advised to me as above but how can i define the spring value of the suspended slab with Compression Strength of 30Mpa and Thickness of 3.0M? How to design footing of mesh plate model in STAAD?
3) I want to use STAAD to design my beam and obtain the required steel area on top and bottom as well as the shear & torsion requirements. Is that ok?
4) Since i will be putting my runway foundation on top of suspended slab, shear connectors between these two structure is required, How can i determine the required steel to resist shear force between runway foundation and suspended slab?
5) Lastly, how am i going to check the deflection for both runway foundation and the existing suspended slab?
Thank you in advance attached image below is my initial model as explain above.
Master mac