I noticed that a skewed shear tab wouldn't work for a particular beam to beam connection, but a bent plate with the same bolts and eccentricity did. Looking at the results with View Formulas enabled, I see that the equivalent bolt factor C = the number of bolts for the bent plate (no reduction for eccentricity) while the shear tab takes the normal reduction in C based on bolt layout. This seems a little suspicious that we don't have to take any reduction for the bent plate like we do the shear tab. Anybody (at Bentley or another user) aware of where that is specifically allowed? Otherwise, I would err on the side of caution and assume they're both reduced. This is a bent plate welded to the support and bolted to the supported beam, compared to the normal shear tab, both with a=3", SSLT holes, t=3/8", 2-3/4" A325, AISC-LRFD-2010 code in version 10.0.0.129.
Thanks,
Jason
In my test with 10.00.00.138 I do see a C factor being applied in checks such as the bolt shear check (beam side) for a bent plate designed to AISC 360-10, and in fact my bent plate fails when my shear plate passes.
I don't think that build is any different than yours in regard to bent plates, but send back your file so I can test it to be sure.
Here is a screenshot of the 2 done in the current v11 release. Am I missing something?