ON MY OUTPUT FILE I ENCOUNTER A * WARNING NO MEMBER LOADED FOR A FLOOR LOAD GENERATION ... TWICE IT APPEAR . HOW CAN A ERASE THIS WARNING & WHAT IS THE MEANING OF THESE WARNING ? I AM USING STAAD PRO V8i, I AM DESIGNING A NEW SIDE WALK EXTENSION OF A BRIDGE
In LC 3, change the line YRANGE 2.5 2.5 FLOAD -2.4 XRANGE 12.813 14.09 ZRANGE 0 1.5 GY to line YRANGE 2.5 2.5 FLOAD -2.4 XRANGE 12.813 14.10 ZRANGE 0 1.5 GY.
In LC4 change the line YRANGE 2.5 2.5 FLOAD -5.33 XRANGE 12.813 14.09 ZRANGE 0 1.5 GY to line YRANGE 2.5 2.5 FLOAD -5.33 XRANGE 12.813 14.10 ZRANGE 0 1.5 GY
This modification should take care of those warnings.
SIDE WALK DESIGN 1-18-16 C.std
Hi Dennis,
Please have a look at the tips for load generation here:
If that won't help troubleshooting - please upload the model.