Hi there,
I'm hoping this will upload correctly, if so please find related model attached, with which I have a couple of questions.
1. My first question is in regards to large reinforcement it places directly adjacent to the inner triangle of walls. There are cores that actually exist in the centre of the slab where there is a large void. Initially I got huge reo (say 200 N16 bars) around the inner perimeter. For the most part it was due to clause 9.4.2 and some was concerning 8.1.5. (both these clauses seem to be the popular reason for reo).
Conceptually I thought this was due to the slab being restricted free "sliding" movement by the inner perimeter walls. I hadn't yet correctly unticked the shear wall box in wall properties to allow the slab above to slide. So I unticked the box to have compression only wall (ie conceptually a roller support?).
However this did not have the effect I intuitively thought. It actually increased the reo outputted around the inner perimeter of walls? The solution to getting rid of the error reo in the end involved decreasing the number of strands in the tendons around the inner perimeter walls?
Why would turning it into a compression only wall do this?
2. The second question relates to clause 8.1.6.1 "minimum strength requirements". It is currently the cause for a lot of the remaining reo in my model which I need to get rid of (it is expected that I only have reo around the perimeters and edges, none running the same span as the tendons, which I have a little of at the moment).
It reads Muo.min = 1.2[Z(fct.f + Pe / Ag) + Pe] and says the ultimate strength in bending shall not be less than Muo.min.
And Muo = prestress tensile force x depth prestress + steel tensile force x tension steel depth - concrete compressive force x depth concrete - steel compressive force x compression steel depth
So keeping Z, fct.f, Ag and e (not changing tendon profile) constant, but changing number of strands per tendon, say increase;
increasing strands increases Muomin but also Muo. Obviously at different rates. My question is for the most part, is clause 8.1.6.1 an indicator of not enough strands/tendons?
3.Final question is whether you'd have any general comments about the model. Trimming wasn't a big issue due to the plate nature of the slab but I'm curious to get expert opinions on the general style of it.
thanks a lot in advance
I ran your file with the CONNECT edition (v6.0).
1. I’m not seeing anything that I would call excessive reinforcement around the innder triangular core, not parallel to the walls, nor perpendicular.
Since the slab terminates at the wall centerline and since the design strips also extend to the slab edge (rather than stopping at the wall face) it’s going to be hard to have bars with any development at all. One consequence of this is that the program bays may be anchored at the edges. I generally prefer to model the slab edges to the far side of the walls and strop my strips at the inside face to help alleviate this problem.
As sent, the walls are “compressible” and “not shear walls”. Compressible means that vertical deformation of the walls is possible (i.e. shortening of the walls under compression), it does not mean that the walls are compression only members (tension is still possible). Not shear walls means that the slab can slide around along the top of the walls, but not lift off.
The geometry is complicated enough with a triangle of walls that it’s difficult to say for sure why these settings make such a difference without looking at it strip by strip, comparing the envelope demand forces, etc.
2. AS 3600-2009 8.1.6.1 implementation notes are below:
Cross sections within 1/6 span from supports or 1/6 span from midspan are considered “at critical sections”.
It’s a little simplistic to say that 8.1.6.1 rebar indicates a need for more strands, but having more, or draping them to better balance the forces is the first solution I would consider so long as that’s practical and does not lead to an overbalancing of forces.
3. Triangles are really tricky because the strips in some direction always end up meeting at acute angles. Your strip layout seems quite clean in my opinion. For some strips, e.g. long. Strip 73-1, you may want to force the program to consider a support condition at the end of the first segment.