Problem with DFF command not check in steel design with STAAD Pro SS6 built 20071150 (Latest built)

Please see STAAD input command below. I try to change DFF parameter in any value (not 0) but the result still show all member pass all code check.

Please verify if I'm wrong...

Best regard.

STAAD SPACE
START JOB INFORMATION
ENGINEER DATE 06-Feb-16
END JOB INFORMATION
INPUT WIDTH 79
UNIT METER KG
JOINT COORDINATES
1 0 5 0; 2 10 5 0; 3 0 4.91 1.7; 4 10 4.91 1.7; 5 0 4.93656 1.19832;
6 10 4.93656 1.19832; 7 0 3.8 0; 8 10 3.8 0; 9 0 4.99207 0.14979;
10 10 4.99207 0.14979; 11 0 4.9511 0.923706; 12 10 4.9511 0.923706;
MEMBER INCIDENCES
1 1 9; 2 2 10; 3 3 4; 4 5 3; 5 6 4; 6 7 5; 7 8 6; 8 9 11; 9 10 12; 10 9 10;
11 11 5; 12 12 6; 13 11 12;
START GROUP DEFINITION
FLOOR
_CP1 3 TO 5 8 TO 13
END GROUP DEFINITION
DEFINE MATERIAL START
ISOTROPIC STEEL
E 2.09042e+010
POISSON 0.3
DENSITY 7833.41
ALPHA 1.2e-005
DAMP 0.03
TYPE STEEL
STRENGTH FY 2.58192e+007 FU 4.1584e+007 RY 1.5 RT 1.2
END DEFINE MATERIAL
MEMBER PROPERTY JAPANESE
1 2 4 5 8 9 11 12 TABLE ST C150X75X9
3 10 13 TABLE ST RHS150X75X2.3
6 7 TABLE ST C100X50X5
CONSTANTS
BETA 180 MEMB 2 5 7 9 12
MATERIAL STEEL ALL
SUPPORTS
1 2 7 8 PINNED
LOAD 1 LOADTYPE None TITLE DL
SELFWEIGHT Y -1
FLOOR LOAD
_CP1 FLOAD -10 GY
LOAD 2 LOADTYPE None TITLE LR
FLOOR LOAD
_CP1 FLOAD -30 GY
LOAD 3 LOADTYPE None TITLE WX
FLOOR LOAD
_CP1 FLOAD 50 GY
LOAD 4 LOADTYPE None TITLE WZ
FLOOR LOAD
_CP1 FLOAD 70 GY
LOAD COMB 101 DL+LR
1 1.0 2 1.0
LOAD COMB 102 DL+0.75[LR+WX]
1 1.0 2 0.75 3 0.75
LOAD COMB 103 DL+0.75[LR+WZ]
1 1.0 2 0.75 4 0.75
LOAD COMB 104 DL+WX
1 1.0 3 1.0
LOAD COMB 105 DL+WZ
1 1.0 4 1.0
LOAD COMB 106 0.6DL+WX
1 0.6 3 1.0
LOAD COMB 107 0.6DL+WZ
1 0.6 4 1.0
PERFORM ANALYSIS
LOAD LIST 101 TO 107
PARAMETER 1
CODE AISC UNIFIED 2005
METHOD ASD
MAIN 1 MEMB 3 10 13
TMAIN 1 MEMB 3 10 13
*LY 5 MEMB 3 10 13
DFF 1000 MEMB 3 10 13
DJ1 9 MEMB 10
DJ2 12 MEMB 10
CHECK CODE ALL
FINISH

Parents Reply Children
  • Please see my first code.
    If I prefer to use ASD not LRFD why I must use "STRENGTH ENVELOPE"?
    Do you understand me?
    Regard
  • I have attached a modified file with SERVICE and STRENGTH envelopes which has subsequently been used to do a CODE CHECK.

    Here are some points which should be noted.

    1. For both service and strength and checks to be carried out, you have to have 2 separate envelopes. In the attached model, you will find 2 separate envelopes namely service ( cases 101 to 107 ) and strength ( cases 201 to 207 ).

    2. The LOAD LIST ENV 1 2 has been used just before the design so that the design accounts for both envelopes during design.

    3. DFF has to be specified as part of the design parameters if deflection check is to be carried out. This is in addition to defining the service envelope. Since you specified DFF for members 3 10 and 13, the deflection check will be carried out for these members only. If you need to check other members for deflection, specify DFF for those too.

    4. Since you need the same combos to be checked for service and strength (ASD), you need to add the combos 201 to 207 which are basically same load combos as 101 to 107 but still needed as STAAD.Pro cannot consider same load combos for both service and strength envelopes.

    I hope this helps.

    2330.Structure1_rev.std



  • Hi all,
    Im using SS6 20.07.11.70 version. I used DFF and service envelope in my design. But still it is not performing deflection check.

    I have clearly defined service envelope then why STAAD showing the below warning.

    **WARNING- Deflection check of member # 4 will not be performed as service envelope not provided.

    Here is the code.

    STAAD SPACE
    START JOB INFORMATION
    ENGINEER DATE 07-Apr-16
    END JOB INFORMATION
    INPUT WIDTH 79
    UNIT METER KN
    JOINT COORDINATES
    1 0 0 0; 2 5 0 0; 3 0 3 0; 4 5 3 0; 5 0 0 3; 6 5 0 3; 7 0 3 3; 8 5 3 3;
    MEMBER INCIDENCES
    1 1 3; 2 2 4; 3 3 4; 4 3 7; 5 4 8; 6 5 7; 7 6 8; 8 7 8;
    DEFINE MATERIAL START
    ISOTROPIC STEEL
    E 2.05e+008
    POISSON 0.3
    DENSITY 76.8195
    ALPHA 1.2e-005
    DAMP 0.03
    TYPE STEEL
    STRENGTH FY 253200 FU 407800 RY 1.5 RT 1.2
    END DEFINE MATERIAL
    MEMBER PROPERTY EUROPEAN
    1 TO 8 TABLE ST IPE500
    CONSTANTS
    MATERIAL STEEL ALL
    *
    SUPPORTS
    1 2 5 6 PINNED
    *
    LOAD 1 LOADTYPE Dead TITLE LOAD CASE 1
    SELFWEIGHT Y -1
    LOAD 2 LOADTYPE Live TITLE LOAD CASE 2
    MEMBER LOAD
    3 TO 5 8 CON GY -50
    LOAD COMB 3 GENERATED AISC GENERAL 1
    1 1.0
    LOAD COMB 4 GENERATED AISC GENERAL 2
    1 1.0 2 1.0
    LOAD COMB 5 GENERATED AISC GENERAL 3
    1 1.0 2 0.75
    LOAD COMB 6 GENERATED AISC GENERAL 4
    1 0.6
    PERFORM ANALYSIS
    *
    DEFINE ENVELOPE
    1 3 TO 6 ENVELOPE 1 TYPE SERVICEABILITY
    1 3 TO 6 ENVELOPE 2 TYPE STRESS
    END DEFINE ENVELOPE
    *
    LOAD LIST ENV 1 2
    *
    PARAMETER 1
    CODE AISC UNIFIED 2005
    DFF 500 MEMB 3 TO 5 8
    FYLD 248213 MEMB 3 TO 5 8
    FU 413688 MEMB 3 TO 5 8
    CHECK CODE MEMB 3 TO 5 8
    FINISH

    -Vivek

  • You have created Service and Strength envelop with the same load case / combination. Please refer to the attached model.

    2465.a1.std



  • Thanks.

    In service and stress load combination will be same so I used same load combinations in different envelopes.
    In engineering calculation there is no restrictions to use one combination for different type of designs. The why STAAD is restricted?

    Even if that is restricted how it shows "service envelope not provided". I have clearly defined service envelope then why STAAD showing the below warning.

    **WARNING- Deflection check of member # 4 will not be performed as service envelope not provided.

    -Vivek