Shear wall analysis results
Hi everyone,
I have modeled a building containing shear walls as well as a moment frame. In modelling the shear walls I used surface entities and applied uniformly distributed loads onto the beams (udls) above them, I've also run the design shear wall command in staad as well. After the analysis of the structure I realized that when I am in post-processing and under the tab surface, the forces are split into surface forces at X (local) and surface forces at Y (local), and are reported as per the division of the surface. I am trying to design the reinforcement for the walls manually so as to confirm the design result from staad, however I am not sure which values to use from the tables in the post processing section. Could anyone help me in deriving the shear, axial and bending moments required for manually designing the wall from these tables.
NOTE: Staad file is attached below.
STAAD SPACE
START JOB INFORMATION
ENGINEER DATE 14-Sep-15
END JOB INFORMATION
INPUT WIDTH 79
UNIT METER KN
JOINT COORDINATES
1 -8.55 -0.0749998 20.1; 2 -7.63107 -0.0749998 16.9826;
3 -6.56933 -0.0749998 13.3808; 4 -5.39593 -0.0749998 9.4001;
5 -4.80923 -0.0749998 7.40978; 6 -4.61862 -0.0749998 21.1723;
8 -3.70062 -0.0749998 18.0547; 9 -3.7 -0.0749998 0;
10 -3.67823 -0.0749998 3.573; 11 -2.67782 -0.0749998 14.5811;
13 -1.54273 -0.0749998 10.7262; 17 1.54273 -0.0749998 10.7262;
19 2.67782 -0.0749998 14.5811; 20 3.67823 -0.0749998 3.573;
21 3.7 -0.0749998 0; 22 4.04664 -0.0749998 19.2298;
23 4.61862 -0.0749998 21.1723; 24 4.80923 -0.0749998 7.40978;
25 5.39593 -0.0749998 9.4001; 26 6.56933 -0.0749998 13.3808;
27 8.55 -0.0749998 20.1; 28 -8.55 4.65 20.1; 29 -7.63107 4.65 16.9826;
30 -6.56933 4.65 13.3808; 31 -5.39593 4.65 9.4001; 32 -4.80923 4.65 7.40978;
33 -4.61862 4.65 21.1723; 35 -3.70062 4.65 18.0547; 36 -3.7 4.65 0;
37 -3.67823 4.65 3.573; 38 -2.67782 4.65 14.5811; 39 -2.625 4.65 0;
40 -1.54273 4.65 10.7262; 41 0 4.65 8.3; 42 0 4.65 11.2571;
44 1.54273 4.65 10.7262; 45 2.625 4.65 0; 46 2.67782 4.65 14.5811;
47 3.67823 4.65 3.573; 48 3.7 4.65 0; 49 4.04664 4.65 19.2298;
50 4.61862 4.65 21.1723; 51 4.80923 4.65 7.40978; 52 5.39593 4.65 9.4001;
53 6.56933 4.65 13.3808; 54 8.55 4.65 20.1; 55 -8.55 8.3 20.1;
56 -7.63107 8.3 16.9826; 57 -6.56933 8.3 13.3808; 58 -5.39593 8.3 9.4001;
59 -4.80923 8.3 7.40978; 60 -4.61862 8.3 21.1723; 61 -4.04664 8.3 19.2298;
62 -3.70062 8.3 18.0547; 63 -3.7 8.3 0; 64 -3.67823 8.3 3.573;
65 -2.67782 8.3 14.5811; 66 -2.625 8.3 0; 67 -1.54273 8.3 10.7262;
68 0 8.3 8.3; 69 0 8.3 11.2571; 70 0 8.3 20.4071; 71 1.54273 8.3 10.7262;
72 2.625 8.3 0; 73 2.67782 8.3 14.5811; 74 3.67823 8.3 3.573; 75 3.7 8.3 0;
76 4.04664 8.3 19.2298; 77 4.61862 8.3 21.1723; 78 4.80923 8.3 7.40978;
79 5.39593 8.3 9.4001; 80 6.56933 8.3 13.3808; 81 8.55 8.3 20.1;
83 0 -0.0749998 8.3; 84 3.16507 4.65 16.2359; 85 -3.16506 4.65 16.2359;
86 0 4.65 16.9071;
MEMBER INCIDENCES
1 29 28; 2 55 56; 3 30 29; 4 56 57; 5 28 33; 6 55 60; 7 31 30; 8 57 58;
9 35 29; 10 62 56; 11 31 4; 12 58 31; 13 32 31; 14 59 58; 15 30 38; 16 57 65;
17 37 32; 18 64 59; 19 35 33; 20 62 60; 21 10 37; 22 37 64; 23 38 85; 24 65 62;
25 39 37; 26 66 64; 27 31 42; 28 58 69; 29 41 32; 30 68 59; 31 40 38; 32 67 65;
34 70 61; 35 39 45; 36 47 37; 37 66 72; 38 74 64; 40 76 70; 41 44 46; 42 71 73;
43 41 51; 44 68 78; 45 52 42; 46 79 69; 47 45 47; 48 72 74; 49 46 84; 50 73 77;
51 20 47; 52 47 74; 53 47 51; 54 74 78; 55 53 46; 56 80 73; 57 51 52; 58 78 79;
59 52 25; 60 79 52; 61 52 53; 62 79 80; 63 54 50; 64 81 77; 65 53 54; 66 80 81;
67 84 50; 68 85 35; 76 85 86; 77 86 84;
SURFACE INCIDENCE
2 29 28 1 SURFACE 1
29 35 8 2 SURFACE 2
35 33 6 8 SURFACE 3
28 33 6 1 SURFACE 4
56 55 28 29 SURFACE 5
56 62 35 29 SURFACE 6
62 60 33 35 SURFACE 7
55 60 33 28 SURFACE 8
30 38 11 3 SURFACE 9
30 57 65 38 SURFACE 10
38 40 67 65 SURFACE 11
40 38 11 13 SURFACE 12
59 68 41 32 SURFACE 13
68 78 51 41 SURFACE 14
41 83 5 32 SURFACE 15
51 41 83 24 SURFACE 16
63 75 48 36 SURFACE 17
36 48 21 9 SURFACE 18
49 50 23 22 SURFACE 19
76 77 50 49 SURFACE 20
77 81 54 50 SURFACE 21
50 54 27 23 SURFACE 22
80 81 54 53 SURFACE 23
53 54 27 26 SURFACE 24
79 80 53 52 SURFACE 25
52 53 26 25 SURFACE 26
19 46 53 26 SURFACE 27
73 80 53 46 SURFACE 28
46 44 71 73 SURFACE 29
19 17 44 46 SURFACE 30
4 31 30 3 SURFACE 31
31 58 57 30 SURFACE 32
DEFINE MATERIAL START
ISOTROPIC CONCRETE
E 2.17185e+007
POISSON 0.17
DENSITY 23.5616
ALPHA 1e-005
DAMP 0.05
TYPE CONCRETE
STRENGTH FCU 27579
END DEFINE MATERIAL
MEMBER PROPERTY AMERICAN
1 TO 10 13 TO 20 23 TO 32 34 TO 38 40 TO 50 53 TO 58 61 TO 68 76 -
77 PRIS YD 0.5 ZD 0.4
11 12 21 22 51 52 59 60 PRIS YD 0.4 ZD 0.4
SURFACE PROPERTY
1 TO 32 THICKNESS 0.25
CONSTANTS
MATERIAL CONCRETE ALL
SURFACE CONSTANTS
MEMBER CRACKED
1 TO 32 34 TO 38 40 TO 67 -
68 REDUCTION RAX 0.350000 RIX 0.350000 RIY 0.350000 RIZ 0.350000
1 TO 32 34 TO 38 40 TO 68 76 -
77 REDUCTION RAX 0.700000 RIX 0.700000 RIY 0.700000 RIZ 0.700000
SUPPORTS
1 TO 6 8 TO 11 13 17 19 TO 27 83 FIXED
SLAVE RIGID MASTER 48 JOINT 28 TO 33 35 TO 42 44 TO 47 49 TO 54 84 TO 86
SLAVE RIGID MASTER 75 JOINT 55 TO 74 76 TO 81
DEFINE IBC 2012
SS 1.1 S1 0.375 I 1.5 RX 7 RZ 7 SCLASS 4 CT 0.0466 PX 0.2943 PZ 0.2943 TL 12 -
FA 1.06 FV 1.65 K 0.9
SELFWEIGHT 1
MEMBER WEIGHT
36 38 UNI 3.29
35 37 UNI 3.67
25 26 47 48 UNI 2.21
29 30 43 44 UNI 4.765
36 38 UNI 4.89
17 18 53 54 UNI 2.5
27 28 45 46 UNI 2.58
29 30 43 44 UNI 3.01
7 8 31 32 41 42 61 62 UNI 3.42
9 10 15 16 27 28 45 46 55 56 UNI 3.24
3 4 24 68 UNI 3.3
5 6 9 10 UNI 3.11
1 2 19 20 UNI 2.59
49 50 65 TO 67 UNI 4.69
55 56 63 64 UNI 3.24
24 32 42 50 UNI 6.42
34 40 UNI 4.79
76 77 UNI 3.57
23 31 41 49 UNI 4.77
LOAD 1 LOADTYPE Seismic TITLE EQ +X
IBC LOAD X 1 DEC 0 ACC 0
PDELTA ANALYSIS SMALLDELTA PRINT LOAD DATA
CHANGE
LOAD 2 LOADTYPE Seismic TITLE EQ -X
IBC LOAD X -1 DEC 0 ACC 0
CHANGE
LOAD 3 LOADTYPE Seismic TITLE EQ +Z
IBC LOAD Z 1 DEC 0 ACC 0
CHANGE
LOAD 4 LOADTYPE Seismic TITLE EQ -Z
IBC LOAD Z -1 DEC 0 ACC 0
CHANGE
LOAD 5 LOADTYPE Dead TITLE DEAD LOAD
SELFWEIGHT Y -1
MEMBER LOAD
36 38 UNI GY -6.58
35 37 UNI GY -7.33
25 26 47 48 UNI GY -4.42
29 30 43 44 UNI GY -9.53
36 38 UNI GY -9.77
17 18 53 54 UNI GY -4.99
27 28 45 46 UNI GY -5.15
29 30 43 44 UNI GY -6.01
7 8 31 32 41 42 61 62 UNI GY -6.83
9 10 15 16 27 28 45 46 55 56 UNI GY -6.48
3 4 24 68 UNI GY -6.6
5 6 9 10 UNI GY -6.21
1 2 19 20 UNI GY -5.17
49 50 65 TO 67 UNI GY -9.38
55 56 63 64 UNI GY -6.48
24 32 42 50 UNI GY -12.84
34 40 UNI GY -9.58
76 77 UNI GY -7.14
23 31 41 49 UNI GY -9.54
SSELFWT Y -1 LIST ALL
CHANGE
LOAD 6 LOADTYPE Live REDUCIBLE TITLE LIVE LOAD
MEMBER LOAD
36 38 UNI GY -5.85
35 37 UNI GY -6.38
25 26 47 48 UNI GY -4.31
29 30 43 44 UNI GY -7.95
36 38 UNI GY -8.12
17 18 53 54 UNI GY -5.39
27 28 45 46 UNI GY -4.83
29 30 43 44 UNI GY -5.44
7 8 31 32 41 42 61 62 UNI GY -4.86
9 10 15 16 27 28 45 46 55 56 UNI GY -4.61
3 4 24 68 UNI GY -4.7
5 6 9 10 UNI GY -4.61
1 2 19 20 UNI GY -4.42
49 50 65 TO 67 UNI GY -3.68
55 56 63 64 UNI GY -6.68
24 32 42 50 UNI GY -10.3
34 40 UNI GY -7.99
76 77 UNI GY -6.25
23 31 41 49 UNI GY -7.95
CHANGE
LOAD 7 LOADTYPE None TITLE DL + LL
REPEAT LOAD
5 1.0 6 1.0
LOAD 17 LOADTYPE None TITLE 1.4DL
REPEAT LOAD
5 1.4
LOAD 18 LOADTYPE None TITLE 1.2DL + 1.6LL
REPEAT LOAD
5 1.2 6 1.6
LOAD 19 LOADTYPE None TITLE 1.2DL + 0.5LL
REPEAT LOAD
5 1.2 6 0.5
LOAD 20 LOADTYPE None TITLE 1.2DL + 1EQ+X + 0.5LL
REPEAT LOAD
5 1.2 6 0.5 1 1.0
LOAD 21 LOADTYPE None TITLE 1.2DL + 1EQ-X + 0.5LL
REPEAT LOAD
2 1.0 5 1.2 6 0.5
LOAD 22 LOADTYPE None TITLE 1.2DL + 1EQ+Z + 0.5LL
REPEAT LOAD
3 1.0 5 1.2 6 0.5
LOAD 23 LOADTYPE None TITLE 1.2DL + 1EQ-Z + 0.5LL
REPEAT LOAD
4 1.0 5 1.2 6 0.5
LOAD 24 LOADTYPE None TITLE 0.9DL + 1EQ+X
REPEAT LOAD
1 1.0 5 0.9
LOAD 25 LOADTYPE None TITLE 0.9DL + 1EQ-X
REPEAT LOAD
2 1.0 5 0.9
LOAD 26 LOADTYPE None TITLE 0.9DL + 1EQ+Z
REPEAT LOAD
3 1.0 5 0.9
LOAD 27 LOADTYPE None TITLE 0.9DL + 1EQ-Z
REPEAT LOAD
4 1.0 5 0.9
PDELTA 30 ANALYSIS SMALLDELTA
CHANGE
PRINT STORY DRIFT 0.010000
PDELTA ANALYSIS SMALLDELTA PRINT ALL
START CONCRETE DESIGN
CODE ACI
MAXMAIN 25 MEMB 1 TO 32 34 TO 38 40 TO 68
MINMAIN 16 MEMB 1 TO 32 34 TO 38 40 TO 68
MINSEC 10 MEMB 1 TO 32 34 TO 38 40 TO 68
RHOMN 0.01 MEMB 11 12 21 22 51 52 59 60
TRACK 2 MEMB 1 TO 32 34 TO 38 40 TO 68
DESIGN BEAM 1 TO 10 13 TO 20 23 TO 32 34 TO 38 40 TO 50 53 TO 58 61 TO 68
DESIGN COLUMN 11 12 21 22 51 52 59 60
CONCRETE TAKE
END CONCRETE DESIGN
START SHEARWALL DESIGN
CODE ACI
FC 28000 LIST 1 TO 30
FYMAIN 420000 LIST 1 TO 30
TRACK 1
TWO 1 LIST 1 TO 30
DESIGN SHEARWALL LIST 1 TO 30
END SHEARWALL DESIGN
FINISH
  • You can go to Surface Forces at Y (Local) tab inside the Surface Results table and look at the FXY ( shear force ), FY ( vertical force) and Mz ( in-plane moment). Please refer to section 1.6.3 of the Technical Reference Manual titled Surface Element where the local axis system for surface and the various forces, along with sign convention, are explained through a few diagrams. To display the local axes for the surface elements, you can right click the mouse, go to Labels and check the box titled Surface Orientation.
    On a different note, here are some observations regarding your model. Surface 17 is defined with nodes 63 75 48 and 36 as part of the surface incidence. However you have beams meeting the surface at nodes 66 72 45 and 39. Now by default the surface would be internally subdivided into 10 divisions by STAAD.Pro and unless these internally generated nodes match with the location of these nodes (66 72 45 and 39), no connectivity between the beams and the surfaces would be established. To ensure that connectivity is established between the surface and the beams 26,48 etc. when you define the surface element, you should consider the nodes 66 72 45 39 as part of the surface incidence.
    Just to demonstrate, I replaced the SURFACE 17 by a SURFACE 33. You can check out the incidence data for that surface and also note that the number of divisions along each edge is also specified to minimize the model size as otherwise each edge would be divided into 10 divisions which would lead to a larger model size. You can control the edge divisions along the edges by going to Geometry > Surface page on the left. From inside the Surface dialog box on the right, expand the node corresponding to a surface and adjust the EDGE PROPERTY. You may want to check for other such occurrences.
    Also please note that when a surface is internally converted by STAAD.Pro into a plate mesh, the beams along the edges are not split to match the mesh. For example the beam 37 in your model would not be automatically split when the surface 33 is meshed. What that means is, the connectivity between the beam 37 and the surface 33 would be at the nodes 66 and 72 only. So the loads applied on the beam 37 would be transmitted to the surface at these node locations. If you would like the connectivity to be established along the length of the beam, you should split the beam 37 manually into 5 divisions to match with the edge division for the surface 33. In that case the load transfer will happen at all the nodes along the length of the member. I have split the beam to demonstrate this.
    Finally you have defined supports at the corners of the surfaces. However when the software generates an internal plate mesh, the intermediate nodes will not have these supports. This is fine if you have the wall supported on isolated footings at corners but if you have a continuous support below the wall, you may want to use the GENERATE option for the supports to define a continuous support underneath the surface. Please refer to the section 5.27.1 of the Technical Reference for discussion on this GENERATE option. There is actually no GUI option to specify this and so you need to add this command in using the editor.
    For example you can have a series of fixed supports created along the internally generated nodes along the base of the wall between the nodes 9 and 21 using the command as shown next
    SUPPORTS
    9 TO 21 GENERATE FIXED
    Also I would suggest that you go through the entire section 1.6.3 in general, as it contains valuable information on modeling/analysis & design of surfaces.
    A modified file with the changes applied to just surface 33 and beam 37 is uploaded for your reference. You can apply the same principles to make the necessary changes at other locations in your model.
    4341.Structure1.std
    Answer Verified By: Gilbert Fontenard
Reply
    SUPPORTS
    4341.Structure1.std