Hi there, I modelled a square footing slab on 4 piles using Ram concept "mat foundation", and found the results for the reo are conservative compared with RAPT's.
So should I try using suspended floor template in Ram Concept?
Bill
According to the program manual, for one-way slabs, two-way slabs or beams, the program checks AS 3600-2009 section 8.1.6 and 9.4.3.2. If you turn on "Controlling Criteria" through visible objects in Ram Concept you should be able to see which is controlling in your case.
A few details for how each is implemented is posted below, but the formatting is not as clean as the RamConcept.pdf.
62.6.5 8.1.6 Minimum Flexural Strength• Cross sections within 1/6 span from supports or 1/6 span from midspan are considered “at critical sections”.• If the design section is not declared as post-tensioned in the design section or design strip segment, then the Pe/Ag and Pee terms of 8.1.6.1 are assumed to be zero (even if the cross section includes tendons), where Pe is the total effective prestress force considered.• Cracking is assumed to be top (negative moment) or bottom (positive moment) based on the “Min. Reinforcement Pattern” selected in the design strip segment or design section.• See ““Cracking Moment” Used in Design Calculations” for a theoretical discussion of the “cracking load”.
62.6.15 Section 9.4.3.2 Shrinkage and Temperature• This criterion is applied as part of the minimum reinforcement designer as it is independent of the magnitude of forces upon a cross section.• This criterion is applied to both beams and slabs, although its application to beams is not required by AS 3600.• The cracking is assumed to be top (negative moment) or bottom (positive moment) based on the “Min. Reinforcement Pattern” selected in the design strip segment or design section.• Reinforcement may be applied to both faces if the cross section is subject to both positive and negative moments and the “tension face” reinforcement location is chosen.• User defined reinforcement that is at an angle to the cross section will only have the component perpendicular to the cross section considered.• The amount of reinforcement provided is equal to 0.75 (per 9.4.3.2(b)) times the amount specified by either 9.4.3.4(a)(i), 9.4.3.4(b)(i), or 9.4.3.4(c).• For “protected” environments, the amount of reinforcement provided is: As = (0.75)(1.75 – 2.5 σ cp )(Ag)/1000• For “normal” environments, the amount of reinforcement provided is: As = (0.75)(3.5 – 2.5 σ cp )(Ag)/1000• For “corrosive” or “very corrosive” environments, the amount of reinforcement provided is: As = (0.75)(6.0 – 2.5 σ cp )(Ag)/1000• For non-PT design strips and design sections, σ cp is taken as zero.