shear wall and slab design
Hello fellow colleagues,
I have model a structure that incorporates a shear wall system with that of a special moment frame, however I have come across a few problems and would also like to make some other queries. The questions are as follows:
1: How should the shear wall design results be interpreted as the description in the output is a little difficult to understand (a diagram would also prove helpful)?
2. I have specified #5 (16mm) bars as my minimum for the shear wall design, however the results give me bar sizes below the amount I specified. I have tried to input both the imperial (5) and the metric units (16), but this hasn't change anything. Why is this happening and how can I fix it?
3. Which results should I use if I wish to do the shear wall design by hand, as the results under the surface tab>surface results are quite cumbersome and unclear.
3. I have tried to export the model to ram concept to complete the advanced slab design, however every time I try I receive an error message about "centre of mass", after which the program crashes. What is the cause of this and how can it be resolved? (I have included a screen shot of this error)
4.How can I get the analysis and design results for a complete beam as the beams currently in my model have been broken up due to the plate meshing and for connectivity to the walls.
Please see the staad input file below: (might take a while to analyze with basic solver due to shear walls and plate meshing)
STAAD SPACE
START JOB INFORMATION
ENGINEER DATE 20-May-16
END JOB INFORMATION
INPUT WIDTH 79
UNIT METER KN
JOINT COORDINATES
1 0 0 20.193; 4 3.668 0 21.248; 13 4.88893 0 3.813; 15 1.85827 0 13.967;
18 3.1405 0 9.671; 22 0.860787 0 17.309; 23 6.80246 0 10.7468;
24 4.52883 0 18.364; 25 5.52628 0 15.0223; 28 16.738 0 20.193;
30 13.07 0 21.248; 31 11.8491 0 3.813; 32 14.8797 0 13.967; 33 13.5975 0 9.671;
35 9.93554 0 10.7468; 37 11.2117 0 15.0223; 41 12.516 0 19.3919;
44 0 4.831 20.193; 45 6.027 4.831 0; 46 3.668 4.831 21.248;
47 4.88893 4.831 3.813; 48 1.85827 4.831 13.967; 49 3.1405 4.831 9.671;
50 8.369 4.831 11.207; 51 0.860787 4.831 17.309; 52 6.80246 4.831 10.7468;
53 4.52883 4.831 18.364; 54 5.52628 4.831 15.0223; 55 16.738 4.831 20.193;
56 10.711 4.831 0; 57 13.07 4.831 21.248; 58 11.8491 4.831 3.813;
59 14.8797 4.831 13.967; 60 13.5975 4.831 9.671; 62 9.93554 4.831 10.7468;
63 11.2117 4.831 15.0223; 64 8.36901 4.831 3.813; 66 12.516 4.831 19.3919;
68 8.369 4.831 15.86; 69 0 8.501 20.193; 70 6.027 8.501 0;
71 3.668 8.501 21.248; 72 4.88893 8.501 3.813; 73 1.85827 8.501 13.967;
74 3.1405 8.501 9.671; 75 8.369 8.501 11.207; 76 0.860787 8.501 17.309;
77 6.80246 8.501 10.7468; 78 4.52883 8.501 18.364; 79 5.52628 8.501 15.0223;
80 16.738 8.501 20.193; 81 10.711 8.501 0; 82 13.07 8.501 21.248;
83 11.8491 8.501 3.813; 84 14.8797 8.501 13.967; 85 13.5975 8.501 9.671;
87 9.93554 8.501 10.7468; 88 11.2117 8.501 15.0223; 89 8.36901 8.501 3.813;
90 8.369 8.501 20.251; 91 12.516 8.501 19.3919; 92 4.22201 8.501 19.3919;
95 4.677 0 0; 96 12.061 0 0; 97 4.677 4.831 0; 98 12.061 4.831 0;
99 4.677 8.501 0; 100 12.061 8.501 0; 101 6.9638 8.501 0; 102 7.9006 8.501 0;
103 8.8374 8.501 0; 104 9.7742 8.501 0; 105 6.9638 4.831 0; 106 7.9006 4.831 0;
107 8.8374 4.831 0; 108 9.7742 4.831 0; 109 2.11472 4.831 13.1078;
110 2.37116 4.831 12.2486; 111 2.62761 4.831 11.3894;
112 2.88405 4.831 10.5302; 113 2.59187 4.831 14.1781;
114 3.32547 4.831 14.3891; 115 4.05908 4.831 14.6002;
116 4.79268 4.831 14.8112; 117 5.78152 4.831 14.1672;
118 6.03675 4.831 13.3121; 119 6.29199 4.831 12.457; 120 6.54722 4.831 11.6019;
121 1.5944 4.831 17.52; 122 2.328 4.831 17.731; 123 3.06161 4.831 17.942;
124 3.79522 4.831 18.153; 125 0.172157 4.831 19.6162;
126 0.344315 4.831 19.0394; 127 0.516472 4.831 18.4626;
128 0.68863 4.831 17.8858; 129 0.7336 4.831 20.404; 130 1.4672 4.831 20.615;
131 2.2008 4.831 20.826; 132 2.9344 4.831 21.037; 133 3.84017 4.831 20.6712;
134 4.01233 4.831 20.0944; 135 4.1845 4.831 19.5176; 136 4.35666 4.831 18.9408;
137 10.9565 4.831 14.1672; 138 10.7012 4.831 13.3121; 139 10.446 4.831 12.457;
140 10.1908 4.831 11.6019; 141 14.6233 4.831 13.1078;
142 14.3668 4.831 12.2486; 143 14.1104 4.831 11.3894;
144 13.8539 4.831 10.5302; 145 14.1461 4.831 14.1781;
146 13.4125 4.831 14.3891; 147 12.6789 4.831 14.6002;
148 11.9453 4.831 14.8112; 149 16.3663 4.831 18.9478;
150 15.9947 4.831 17.7026; 151 15.623 4.831 16.4574; 152 15.2514 4.831 15.2122;
153 16.0044 4.831 20.404; 154 15.2708 4.831 20.615; 155 14.5372 4.831 20.826;
156 13.8036 4.831 21.037; 157 12.9592 4.831 20.8768; 158 12.8484 4.831 20.5056;
159 12.7376 4.831 20.1343; 160 12.6268 4.831 19.7631;
161 2.11472 8.501 13.1078; 162 2.37116 8.501 12.2486;
163 2.62761 8.501 11.3894; 164 2.88405 8.501 10.5302;
165 5.78152 8.501 14.1672; 166 6.03675 8.501 13.3121; 167 6.29199 8.501 12.457;
168 6.54722 8.501 11.6019; 169 2.59187 8.501 14.1781;
170 3.32547 8.501 14.3891; 171 4.05908 8.501 14.6002;
172 4.79268 8.501 14.8112; 173 0.172157 8.501 19.6162;
174 0.344315 8.501 19.0394; 175 0.516472 8.501 18.4626;
176 0.68863 8.501 17.8858; 177 0.7336 8.501 20.404; 178 1.4672 8.501 20.615;
179 2.2008 8.501 20.826; 180 2.9344 8.501 21.037; 181 3.7788 8.501 20.8768;
182 3.8896 8.501 20.5056; 183 4.00041 8.501 20.1343; 184 4.11121 8.501 19.7631;
185 1.5944 8.501 17.52; 186 2.328 8.501 17.731; 187 3.06161 8.501 17.942;
188 3.79522 8.501 18.153; 189 16.0044 8.501 20.404; 190 15.2708 8.501 20.615;
191 14.5372 8.501 20.826; 192 13.8036 8.501 21.037; 193 14.6233 8.501 13.1078;
194 14.3668 8.501 12.2486; 195 14.1104 8.501 11.3894;
196 13.8539 8.501 10.5302; 197 10.9565 8.501 14.1672;
198 10.7012 8.501 13.3121; 199 10.446 8.501 12.457; 200 10.1908 8.501 11.6019;
201 14.1461 8.501 14.1781; 202 13.4125 8.501 14.3891;
203 12.6789 8.501 14.6002; 204 11.9453 8.501 14.8112;
205 12.9592 8.501 20.8768; 206 12.8484 8.501 20.5056;
207 12.7376 8.501 20.1343; 208 12.6268 8.501 19.7631;
209 16.3663 8.501 18.9478; 210 15.9947 8.501 17.7026; 211 15.623 8.501 16.4574;
212 15.2514 8.501 15.2122; 213 9.0541 4.831 0.566919;
214 8.76657 4.831 1.06381; 215 8.14665 4.831 0.825298;
216 8.94341 4.831 2.98437; 217 8.36903 4.831 2.4572; 218 9.18794 4.831 2.45717;
219 10.4564 4.831 1.97704; 220 11.3939 4.831 2.2878; 221 10.5135 4.831 2.62668;
222 9.06011 4.831 1.96026; 223 8.3028 4.831 1.64436; 224 7.55015 4.831 2.45717;
225 8.13703 4.831 3.36102; 226 7.23285 4.831 3.13507;
227 7.35315 4.831 1.24965; 228 6.60392 4.831 0.847296;
229 7.23815 4.831 0.557509; 230 11.1531 4.831 3.813; 231 11.6215 4.831 3.0504;
232 10.9476 4.831 3.03148; 233 10.2422 4.831 3.05971; 234 10.4571 4.831 3.813;
235 9.76105 4.831 3.813; 236 9.797 4.831 2.2877; 237 9.50521 4.831 3.13507;
238 10.7079 4.831 3.41751; 239 9.5583 4.831 0.637013;
240 6.15249 4.831 1.44982; 241 7.04848 4.831 1.77936;
242 6.28165 4.831 1.97704; 243 6.22457 4.831 2.62668; 244 5.34416 4.831 2.2878;
245 5.79939 4.831 0.7626; 246 6.9411 4.831 2.2877; 247 10.1341 4.831 0.847296;
248 10.5856 4.831 1.44981; 249 9.68956 4.831 1.77936;
250 6.49591 4.831 3.05971; 251 6.28096 4.831 3.813; 252 6.0302 4.831 3.41751;
253 5.79048 4.831 3.03148; 254 5.58495 4.831 3.813; 255 5.11654 4.831 3.0504;
256 10.9386 4.831 0.7626; 257 9.06503 4.831 3.813; 258 6.97698 4.831 3.813;
259 11.1662 4.831 1.5252; 260 7.78717 4.831 1.40583; 261 9.33815 4.831 1.16003;
262 7.67299 4.831 3.813; 263 5.57177 4.831 1.5252; 264 7.37298 4.831 5.85432;
265 7.01105 4.831 7.50646; 266 5.36156 4.831 6.50569; 267 8.36901 4.831 6.7706;
268 5.28303 4.831 4.35263; 269 6.15711 4.831 4.77656; 270 4.53924 4.831 4.9846;
271 5.59886 4.831 7.96705; 272 7.6035 4.831 10.673; 273 7.93381 4.831 10.2522;
274 7.93338 4.831 10.8291; 275 4.18956 4.831 6.1562; 276 7.67085 4.831 4.5793;
277 3.83987 4.831 7.3278; 278 4.59387 4.831 9.02497; 279 4.60528 4.831 10.1013;
280 3.87289 4.831 9.88616; 281 3.49019 4.831 8.4994; 282 5.6798 4.831 9.63382;
283 6.67113 4.831 10.1355; 284 7.33615 4.831 9.96995;
285 7.16074 4.831 10.5337; 286 7.05164 4.831 9.11256; 287 8.369 4.831 8.2494;
288 6.07007 4.831 10.5316; 289 7.42908 4.831 10.9309; 290 8.369 4.831 9.7282;
291 5.33768 4.831 10.3165; 292 8.36901 4.831 5.2918; 293 8.05569 4.831 11.115;
294 7.74238 4.831 11.0229; 295 7.11577 4.831 10.8388;
296 11.4264 4.831 5.12811; 297 10.2749 4.831 5.45151;
298 11.3265 4.831 5.90639; 299 12.1988 4.831 4.9846; 300 9.4369 4.831 9.51572;
301 10.6745 4.831 8.77816; 302 10.7668 4.831 7.19956; 303 12.5485 4.831 6.1562;
304 11.0108 4.831 9.6852; 305 12.2264 4.831 9.15843; 306 12.1327 4.831 10.1013;
307 12.8651 4.831 9.88616; 308 13.2478 4.831 8.4994; 309 12.8981 4.831 7.3278;
310 9.16873 4.831 10.1537; 311 8.71737 4.831 10.6716; 312 10.0113 4.831 10.284;
313 9.54489 4.831 10.5748; 314 9.17269 4.831 10.6581;
315 10.9213 4.831 4.53136; 316 9.41325 4.831 4.42077;
317 10.6679 4.831 10.5316; 318 11.4003 4.831 10.3165;
319 8.71093 4.831 10.9524; 320 8.68231 4.831 11.115; 321 8.99562 4.831 11.0229;
322 9.30892 4.831 10.9309; 323 9.62223 4.831 10.8388;
324 5.37592 4.831 12.8904; 325 4.8769 4.831 12.9592; 326 5.22283 4.831 12.283;
327 3.1485 4.831 12.4892; 328 3.55257 4.831 11.9811; 329 3.9129 4.831 12.5002;
330 4.73457 4.831 13.5101; 331 4.90798 4.831 14.2055;
332 4.34175 4.831 14.0549; 333 2.66872 4.831 13.035; 334 3.52162 4.831 13.2379;
335 4.47323 4.831 12.6542; 336 4.57069 4.831 12.1214;
337 3.27623 4.831 11.5488; 338 3.52492 4.831 10.7424;
339 3.64836 4.831 11.2758; 340 3.19668 4.831 13.7117;
341 4.05906 4.831 13.4343; 342 2.74279 4.831 13.5079;
343 4.06635 4.831 11.0043; 344 4.04222 4.831 10.4211;
345 5.03773 4.831 11.0031; 346 5.96149 4.831 11.1702;
347 5.30953 4.831 11.6267; 348 5.18589 4.831 13.8163;
349 5.82546 4.831 11.9701; 350 2.93202 4.831 12.0956;
351 4.21057 4.831 11.8062; 352 4.50833 4.831 11.3159; 353 2.20461 4.831 17.138;
354 1.56816 4.831 16.8613; 355 2.04964 4.831 16.4234;
356 1.57387 4.831 16.3005; 357 1.06028 4.831 16.6406;
358 3.99237 4.831 17.5915; 359 4.72832 4.831 17.6957;
360 3.85859 4.831 15.3161; 361 3.65673 4.831 16.0912;
362 3.30328 4.831 15.3863; 363 4.21332 4.831 15.9617;
364 4.19823 4.831 16.6383; 365 3.93959 4.831 17.201; 366 3.50253 4.831 17.4864;
367 4.47632 4.831 15.2051; 368 4.7061 4.831 15.9362; 369 4.77761 4.831 15.4879;
370 2.86316 4.831 15.8115; 371 2.91511 4.831 16.2403;
372 4.37283 4.831 17.0857; 373 3.34181 4.831 16.4191;
374 2.71753 4.831 16.8216; 375 3.49581 4.831 15.0305;
376 2.75541 4.831 15.1241; 377 2.05526 4.831 15.2526;
378 1.65877 4.831 14.6354; 379 2.3354 4.831 14.6459; 380 1.89351 4.831 16.0679;
381 1.25978 4.831 15.9722; 382 1.45928 4.831 15.3038;
383 3.09392 4.831 17.4167; 384 3.45349 4.831 16.9258;
385 4.67723 4.831 16.3111; 386 5.32679 4.831 15.6906; 387 2.37096 4.831 15.808;
388 5.1273 4.831 16.359; 389 4.92781 4.831 17.0273; 390 1.21573 4.831 19.3931;
391 1.35554 4.831 20.0339; 392 0.781056 4.831 19.6521;
393 3.57253 4.831 20.061; 394 3.36996 4.831 20.4492; 395 3.04661 4.831 18.9896;
396 3.65432 4.831 19.3428; 397 3.33524 4.831 19.6393;
398 2.95152 4.831 18.5856; 399 3.44317 4.831 18.8714;
400 2.94567 4.831 20.0237; 401 2.95153 4.831 20.4795;
402 1.55006 4.831 18.4377; 403 1.24014 4.831 18.114; 404 1.97266 4.831 18.2628;
405 3.86503 4.831 18.6551; 406 2.72677 4.831 19.4696;
407 1.86845 4.831 19.2381; 408 2.61886 4.831 20.0486;
409 2.29023 4.831 18.8612; 410 1.06467 4.831 18.5043;
411 0.85426 4.831 19.2093; 412 2.18977 4.831 20.2042; 413 1.8658 4.831 19.8559;
414 2.41743 4.831 18.1932; 415 1.43727 4.831 18.9362;
416 13.9953 4.831 13.5079; 417 12.814 4.831 12.5173; 418 13.2165 4.831 13.2379;
419 12.6959 4.831 13.4233; 420 13.5415 4.831 13.7116;
421 12.0036 4.831 13.5101; 422 11.8301 4.831 14.2055;
423 11.5523 4.831 13.8162; 424 12.265 4.831 12.6541; 425 11.5153 4.831 12.283;
426 12.1675 4.831 12.1213; 427 10.9127 4.831 11.97; 428 10.7766 4.831 11.1701;
429 11.8034 4.831 11.7533; 430 12.5276 4.831 11.8061;
431 12.3808 4.831 14.0402; 432 13.5896 4.831 12.4892;
433 13.1856 4.831 11.9811; 434 12.6718 4.831 11.0042;
435 11.7004 4.831 11.0031; 436 12.6959 4.831 10.4211;
437 14.0694 4.831 13.0349; 438 13.2132 4.831 10.7423;
439 11.3622 4.831 12.8904; 440 13.6286 4.831 11.9532;
441 13.3286 4.831 11.4395; 442 12.2297 4.831 11.3159;
443 11.8624 4.831 12.9981; 444 14.339 4.831 17.8258; 445 14.7607 4.831 19.002;
446 13.0241 4.831 18.9051; 447 12.894 4.831 18.069; 448 13.8591 4.831 18.6835;
449 13.0297 4.831 19.6718; 450 13.781 4.831 19.4099; 451 14.0072 4.831 20.4223;
452 12.2551 4.831 18.518; 453 11.9943 4.831 17.6441; 454 12.6051 4.831 16.5999;
455 15.5837 4.831 19.5907; 456 16.0852 4.831 19.8687; 457 13.1827 4.831 20.9;
458 14.9573 4.831 20.0155; 459 13.1257 4.831 20.4495;
460 14.0019 4.831 16.5017; 461 13.3327 4.831 15.3694;
462 14.3514 4.831 15.3948; 463 14.6533 4.831 14.7135;
464 12.3519 4.831 15.6203; 465 11.7334 4.831 16.7701;
466 11.4726 4.831 15.8962; 467 13.5149 4.831 17.2963;
468 8.45008 4.831 14.1511; 469 8.01975 4.831 13.6273; 470 8.69766 4.831 13.11;
471 7.25069 4.831 11.4847; 472 7.2735 4.831 11.9392; 473 8.01943 4.831 14.6012;
474 8.52982 4.831 15.0856; 475 7.80046 4.831 15.6925;
476 6.74165 4.831 13.2915; 477 7.32859 4.831 13.7373;
478 6.72986 4.831 14.1964; 479 6.94935 4.831 11.2472;
480 7.63394 4.831 11.3734; 481 8.00436 4.831 12.8252;
482 7.71971 4.831 12.3591; 483 8.26174 4.831 11.9767;
484 7.29551 4.831 12.8802; 485 9.26398 4.831 11.6191;
486 9.54845 4.831 12.5038; 487 9.61577 4.831 11.1659;
488 9.19258 4.831 11.2205; 489 8.99411 4.831 12.1244;
490 6.09483 4.831 15.1898; 491 7.86925 4.831 11.7693;
492 9.39381 4.831 14.9405; 493 9.26706 4.831 14.0083;
494 10.1578 4.831 14.5477; 495 8.93754 4.831 15.6925;
496 6.63699 4.831 14.9131; 497 7.35662 4.831 14.4041;
498 10.6432 4.831 15.1898; 499 7.89946 4.831 11.3299;
500 7.04254 4.831 14.8103; 501 7.44084 4.831 14.9366;
502 7.23191 4.831 15.5249; 503 10.0746 4.831 15.3574;
504 9.50608 4.831 15.5249; 505 6.66337 4.831 15.3574; 506 8.84792 4.831 11.343;
507 9.0541 8.50101 0.566919; 508 8.76657 8.50101 1.06381;
509 8.14665 8.50101 0.825298; 510 8.94341 8.501 2.98437;
511 8.36903 8.501 2.4572; 512 9.18794 8.501 2.45717; 513 10.4564 8.501 1.97704;
514 11.3939 8.501 2.2878; 515 10.5135 8.501 2.62668; 516 9.06011 8.501 1.96026;
517 8.3028 8.501 1.64436; 518 7.55015 8.501 2.45717; 519 8.13703 8.501 3.36102;
520 7.23285 8.501 3.13507; 521 7.35315 8.50101 1.24965;
522 6.60392 8.50101 0.847296; 523 7.23815 8.50101 0.557509;
524 11.1531 8.501 3.813; 525 11.6215 8.501 3.0504; 526 10.9476 8.501 3.03148;
527 10.2422 8.501 3.05971; 528 10.4571 8.501 3.813; 529 9.76105 8.501 3.813;
530 9.797 8.501 2.2877; 531 9.50521 8.501 3.13507; 532 10.7079 8.501 3.41751;
533 9.5583 8.50101 0.637013; 534 6.15249 8.50101 1.44982;
535 7.04848 8.501 1.77936; 536 6.28165 8.501 1.97704;
537 6.22457 8.501 2.62668; 538 5.34416 8.501 2.2878; 539 5.79939 8.501 0.7626;
540 6.9411 8.501 2.2877; 541 10.1341 8.50101 0.847296;
542 10.5856 8.50101 1.44981; 543 9.68956 8.501 1.77936;
544 6.49591 8.501 3.05971; 545 6.28096 8.501 3.813; 546 6.0302 8.501 3.41751;
547 5.79048 8.501 3.03148; 548 5.58495 8.501 3.813; 549 5.11654 8.501 3.0504;
550 10.9386 8.501 0.7626; 551 9.06503 8.501 3.813; 552 6.97698 8.501 3.813;
553 11.1662 8.501 1.5252; 554 7.78717 8.50101 1.40583;
555 9.33815 8.50101 1.16003; 556 7.67299 8.501 3.813; 557 5.57177 8.501 1.5252;
558 7.37298 8.501 5.85432; 559 7.01105 8.501 7.50646;
560 5.36156 8.501 6.50569; 561 8.36901 8.501 6.7706;
562 5.28303 8.50101 4.35263; 563 6.15711 8.501 4.77656;
564 4.53924 8.501 4.9846; 565 5.59886 8.501 7.96705; 566 7.6035 8.501 10.673;
567 7.93381 8.501 10.2522; 568 7.93338 8.501 10.8291; 569 4.18956 8.501 6.1562;
570 7.67085 8.501 4.5793; 571 3.83987 8.501 7.3278;
572 4.59387 8.50101 9.02497; 573 4.60528 8.501 10.1013;
574 3.87289 8.501 9.88616; 575 3.49019 8.501 8.4994; 576 5.6798 8.501 9.63382;
577 6.67113 8.501 10.1355; 578 7.33615 8.501 9.96995;
579 7.16074 8.501 10.5337; 580 7.05164 8.501 9.11256; 581 8.369 8.501 8.2494;
582 6.07007 8.501 10.5316; 583 7.42908 8.501 10.9309; 584 8.369 8.501 9.7282;
585 5.33768 8.501 10.3165; 586 8.36901 8.501 5.2918; 587 8.05569 8.501 11.115;
588 7.74238 8.501 11.0229; 589 7.11577 8.501 10.8388;
590 9.41097 8.50101 9.22418; 591 10.34 8.501 9.84103;
592 9.26296 8.50101 10.3538; 593 11.195 8.501 4.42335;
594 12.1988 8.501 4.9846; 595 10.2622 8.501 5.10249; 596 9.23568 8.501 4.47282;
597 10.1469 8.501 7.18016; 598 12.8981 8.501 7.3278; 599 10.6862 8.501 8.7131;
600 12.8651 8.501 9.88616; 601 13.2478 8.501 8.4994; 602 11.5596 8.501 6.27371;
603 10.543 8.501 4.38535; 604 9.34541 8.50101 10.6748;
605 8.70111 8.50101 10.9037; 606 8.70033 8.50101 10.454;
607 9.30892 8.501 10.9309; 608 8.99562 8.501 11.0229;
609 11.4003 8.501 10.3165; 610 12.0928 8.501 9.22171;
611 12.1327 8.501 10.1013; 612 12.5485 8.501 6.1562; 613 8.68231 8.501 11.115;
614 10.6679 8.501 10.5316; 615 9.62223 8.501 10.8388;
616 5.37592 8.501 12.8904; 617 4.8769 8.501 12.9592; 618 5.22283 8.501 12.283;
619 3.1485 8.501 12.4892; 620 3.55257 8.501 11.9811; 621 3.9129 8.501 12.5002;
622 4.73457 8.501 13.5101; 623 4.90798 8.501 14.2055;
624 4.34175 8.501 14.0549; 625 2.66872 8.501 13.035; 626 3.52162 8.501 13.2379;
627 4.47323 8.501 12.6542; 628 4.57069 8.501 12.1214;
629 3.27623 8.501 11.5488; 630 3.52492 8.501 10.7424;
631 3.64836 8.501 11.2758; 632 3.19668 8.501 13.7117;
633 4.05906 8.501 13.4343; 634 2.74279 8.501 13.5079;
635 4.06635 8.501 11.0043; 636 4.04222 8.501 10.4211;
637 5.03773 8.501 11.0031; 638 5.96149 8.501 11.1702;
639 5.30953 8.501 11.6267; 640 5.18589 8.501 13.8163;
641 5.82546 8.501 11.9701; 642 2.93202 8.501 12.0956;
643 4.21057 8.501 11.8062; 644 4.50833 8.501 11.3159; 645 2.20461 8.501 17.138;
646 1.56816 8.501 16.8613; 647 2.04964 8.501 16.4234;
648 1.57387 8.501 16.3005; 649 1.06028 8.501 16.6406;
650 3.99237 8.501 17.5915; 651 4.72832 8.501 17.6957;
652 3.85859 8.501 15.3161; 653 3.65673 8.501 16.0912;
654 3.30328 8.501 15.3863; 655 4.21332 8.501 15.9617;
656 4.19823 8.501 16.6383; 657 3.93959 8.501 17.201; 658 3.50253 8.501 17.4864;
659 4.47632 8.501 15.2051; 660 4.7061 8.501 15.9362; 661 4.77761 8.501 15.4879;
662 2.86316 8.501 15.8115; 663 2.91511 8.501 16.2403;
664 4.37283 8.501 17.0857; 665 3.34181 8.501 16.4191;
666 2.71753 8.501 16.8216; 667 3.49581 8.501 15.0305;
668 2.75541 8.501 15.1241; 669 2.05526 8.501 15.2526;
670 1.65877 8.501 14.6354; 671 2.3354 8.501 14.6459; 672 1.89351 8.501 16.0679;
673 1.25978 8.501 15.9722; 674 1.45928 8.501 15.3038;
675 3.09392 8.501 17.4167; 676 3.45349 8.501 16.9258;
677 4.67723 8.501 16.3111; 678 5.32679 8.501 15.6906; 679 2.37096 8.501 15.808;
680 5.1273 8.501 16.359; 681 4.92781 8.501 17.0273; 682 1.52863 8.501 20.0437;
683 0.887279 8.501 19.547; 684 1.43511 8.501 19.3673;
685 2.08838 8.501 19.0781; 686 2.10403 8.501 18.3935;
687 2.88305 8.501 18.7723; 688 2.21999 8.501 20.1614;
689 2.79942 8.501 20.0644; 690 2.50683 8.501 19.4364;
691 2.97112 8.501 19.7031; 692 3.54746 8.501 18.8483;
693 3.53004 8.501 19.8989; 694 3.29813 8.501 20.5799;
695 3.40279 8.501 20.2629; 696 2.94471 8.501 20.5402;
697 4.26243 8.50101 18.6556; 698 4.04512 8.501 18.4365;
699 4.34474 8.501 18.9807; 700 3.38941 8.50101 20.8902;
701 1.24367 8.501 18.1179; 702 1.21029 8.501 18.8197; 703 1.8044 8.501 19.6648;
704 4.03323 8.50101 19.1706; 705 2.25787 8.501 19.7406;
706 4.46747 8.501 18.5696; 707 4.28337 8.501 19.1863; 708 4.4061 8.501 18.7752;
709 9.47899 8.501 11.8048; 710 9.12016 8.501 12.8354;
711 9.73327 8.501 11.2579; 712 9.33817 8.501 11.2567;
713 7.77184 8.50101 19.2675; 714 7.5396 8.501 20.0792;
715 6.8819 8.50101 16.7249; 716 7.14428 8.50101 17.4906;
717 7.93143 8.50101 17.2252; 718 8.47001 8.501 12.3586;
719 8.80016 8.501 11.5174; 720 4.64211 8.50101 18.599;
721 8.72139 8.50101 19.1256; 722 5.56171 8.50101 17.2807;
723 6.11056 8.50101 16.7434; 724 4.69961 8.50101 18.8139;
725 5.07932 8.50101 18.4972; 726 4.42067 8.50101 19.2002;
727 4.67851 8.50101 19.2698; 728 6.93234 8.50101 18.0202;
729 6.55521 8.50101 17.3447; 730 5.88081 8.501 19.7355;
731 6.66535 8.50101 18.9318; 732 6.06566 8.501 15.9763;
733 7.66267 8.501 15.9301; 734 6.85166 8.501 15.2923;
735 10.92 8.50101 17.3134; 736 11.9943 8.501 17.6441;
737 11.7334 8.501 16.7701; 738 7.55219 8.501 14.6007;
739 7.02676 8.501 14.0774; 740 10.1415 8.50101 18.2028;
741 11.2614 8.50101 18.7099; 742 10.6222 8.50101 16.2803;
743 9.58942 8.50101 16.8223; 744 9.86304 8.501 13.3872;
745 10.1472 8.501 14.3369; 746 9.34715 8.501 14.9482;
747 8.65986 8.501 13.6485; 748 8.18517 8.50101 18.1393;
749 9.07094 8.50101 17.8909; 750 10.3689 8.50101 19.1048;
751 9.65722 8.50101 18.9749; 752 10.0278 8.501 19.9074;
753 12.2551 8.501 18.518; 754 11.6866 8.501 19.5637; 755 10.8572 8.501 19.7355;
756 8.78137 8.50101 15.878; 757 8.49899 8.501 14.6193;
758 7.24275 8.501 12.5034; 759 7.53664 8.501 13.3866; 760 10.338 8.501 15.3853;
761 9.68388 8.50101 15.9219; 762 7.98375 8.501 11.7986;
763 8.13762 8.501 13.0223; 764 7.46238 8.501 11.2821;
765 6.92682 8.501 11.2044; 766 7.24977 8.501 11.0383;
767 7.43864 8.50101 18.5135; 768 6.43385 8.501 14.5448;
769 9.1984 8.501 20.0792; 770 5.05141 8.501 19.5637; 771 11.4726 8.501 15.8962;
772 6.7102 8.501 19.9074; 773 6.13476 8.50101 17.9722;
774 7.55443 8.50101 17.936; 775 13.9953 8.501 13.5079;
776 12.814 8.501 12.5173; 777 13.2165 8.501 13.2379; 778 12.6959 8.501 13.4233;
779 13.5415 8.501 13.7116; 780 12.0036 8.501 13.5101;
781 11.8301 8.501 14.2055; 782 11.5523 8.501 13.8162; 783 12.265 8.501 12.6541;
784 11.5153 8.501 12.283; 785 12.1675 8.501 12.1213; 786 10.9127 8.501 11.97;
787 10.7766 8.501 11.1701; 788 11.8034 8.501 11.7533;
789 12.5276 8.501 11.8061; 790 12.3808 8.501 14.0402;
791 13.5896 8.501 12.4892; 792 13.1856 8.501 11.9811;
793 12.6718 8.501 11.0042; 794 11.7004 8.501 11.0031;
795 12.6959 8.501 10.4211; 796 14.0694 8.501 13.0349;
797 13.2132 8.501 10.7423; 798 11.3622 8.501 12.8904;
799 13.6286 8.501 11.9532; 800 13.3286 8.501 11.4395;
801 12.2297 8.501 11.3159; 802 11.8624 8.501 12.9981; 803 14.339 8.501 17.8258;
804 14.7607 8.501 19.002; 805 13.0241 8.501 18.9051; 806 12.894 8.501 18.069;
807 13.8591 8.501 18.6835; 808 13.0297 8.501 19.6718; 809 13.781 8.501 19.4099;
810 14.0072 8.501 20.4223; 811 12.6051 8.501 16.5999;
812 15.5837 8.50101 19.5907; 813 16.0852 8.50101 19.8687;
814 13.1827 8.501 20.9; 815 14.9573 8.501 20.0155; 816 13.1257 8.501 20.4495;
817 14.0019 8.501 16.5017; 818 13.3327 8.501 15.3694;
819 14.3514 8.50101 15.3948; 820 14.6533 8.50101 14.7135;
821 12.3519 8.501 15.6203; 822 13.5149 8.501 17.2963;
MEMBER INCIDENCES
57 13 47; 59 18 49; 68 31 58; 70 33 60; 79 44 125; 80 44 129; 81 47 255;
82 48 109; 83 49 281; 84 49 280; 85 51 357; 86 52 295; 88 53 359; 89 54 117;
90 48 113; 91 51 121; 93 55 153; 94 58 231; 95 59 141; 96 60 308; 97 60 307;
99 62 323; 100 63 137; 101 59 145; 102 47 254; 103 45 105; 104 64 257;
105 64 292; 106 57 157; 107 66 452; 111 68 495; 112 68 475; 116 47 72;
118 49 74; 127 58 83; 129 60 85; 138 69 173; 139 69 177; 140 72 549;
141 73 161; 142 74 575; 143 74 574; 144 76 649; 145 77 589; 146 71 181;
147 78 651; 148 79 165; 149 73 169; 150 76 185; 152 80 189; 153 83 525;
154 84 193; 155 85 601; 156 85 600; 158 87 615; 159 88 197; 160 84 201;
161 72 548; 162 70 101; 163 89 551; 164 89 586; 165 82 205; 166 91 753;
167 92 707; 168 92 770; 169 90 769; 172 45 97; 173 56 98; 174 70 99;
175 81 100; 180 46 133; 181 80 209; 182 55 149; 183 101 102; 184 102 103;
185 103 104; 186 104 81; 187 105 106; 188 106 107; 189 107 108; 190 108 56;
191 109 110; 192 110 111; 193 111 112; 194 112 49; 195 113 114; 196 114 115;
197 115 116; 198 116 54; 199 117 118; 200 118 119; 201 119 120; 202 120 52;
203 121 122; 204 122 123; 205 123 124; 206 124 53; 207 125 126; 208 126 127;
209 127 128; 210 128 51; 211 129 130; 212 130 131; 213 131 132; 214 132 46;
215 133 134; 216 134 135; 217 135 136; 218 136 53; 219 137 138; 220 138 139;
221 139 140; 222 140 62; 223 141 142; 224 142 143; 225 143 144; 226 144 60;
227 145 146; 228 146 147; 229 147 148; 230 148 63; 231 149 150; 232 150 151;
233 151 152; 234 152 59; 235 153 154; 236 154 155; 237 155 156; 238 156 57;
239 157 158; 240 158 159; 241 159 160; 242 160 66; 243 161 162; 244 162 163;
245 163 164; 246 164 74; 247 165 166; 248 166 167; 249 167 168; 250 168 77;
251 169 170; 252 170 171; 253 171 172; 254 172 79; 255 173 174; 256 174 175;
257 175 176; 258 176 76; 259 177 178; 260 178 179; 261 179 180; 262 180 71;
263 181 182; 264 182 183; 265 183 184; 266 184 92; 267 185 186; 268 186 187;
269 187 188; 270 188 78; 271 189 190; 272 190 191; 273 191 192; 274 192 82;
275 193 194; 276 194 195; 277 195 196; 278 196 85; 279 197 198; 280 198 199;
281 199 200; 282 200 87; 283 201 202; 284 202 203; 285 203 204; 286 204 88;
287 205 206; 288 206 207; 289 207 208; 290 208 91; 291 209 210; 292 210 211;
293 211 212; 294 212 84; 297 220 259; 302 230 58; 303 231 220; 306 234 230;
307 235 234; 313 244 263; 315 245 45; 321 251 258; 323 254 251; 325 255 244;
329 256 56; 333 257 235; 337 258 262; 340 259 256; 346 262 64; 352 263 245;
405 267 287; 407 270 47; 412 275 270; 417 277 275; 419 279 291; 420 280 279;
423 281 277; 428 287 290; 430 288 52; 432 289 294; 436 290 50; 445 291 288;
447 292 267; 460 293 50; 461 294 293; 464 295 289; 476 299 58; 480 303 299;
484 306 318; 485 307 306; 487 308 309; 489 309 303; 499 317 62; 516 318 317;
518 320 50; 519 321 320; 522 322 321; 535 323 322; 621 357 381; 623 359 389;
635 378 48; 639 381 382; 640 382 378; 645 386 54; 655 388 386; 656 389 388;
850 452 453; 852 453 465; 868 465 466; 869 466 63; 915 475 502; 928 490 54;
933 495 504; 942 498 63; 948 502 505; 952 503 498; 958 504 503; 960 505 490;
1013 514 553; 1018 524 83; 1019 525 514; 1022 528 524; 1023 529 528;
1029 538 557; 1031 539 70; 1037 545 552; 1039 548 545; 1041 549 538;
1045 550 81; 1049 551 529; 1053 552 556; 1056 553 550; 1062 556 89;
1068 557 539; 1121 561 581; 1123 564 72; 1128 569 564; 1133 571 569;
1135 573 585; 1136 574 573; 1139 575 571; 1144 581 584; 1146 582 77;
1148 583 588; 1152 584 75; 1161 585 582; 1163 586 561; 1176 587 75;
1177 588 587; 1180 589 583; 1192 594 83; 1196 598 612; 1198 600 611;
1199 601 598; 1210 607 608; 1211 608 613; 1215 609 614; 1217 611 609;
1222 612 594; 1232 613 75; 1234 614 87; 1251 615 607; 1333 649 673;
1335 651 681; 1347 670 73; 1351 673 674; 1352 674 670; 1357 678 79;
1367 680 678; 1368 681 680; 1429 699 708; 1448 706 78; 1457 707 699;
1470 708 706; 1489 714 90; 1506 730 772; 1509 736 737; 1510 737 771;
1518 752 755; 1520 753 736; 1521 754 91; 1523 755 754; 1547 769 752;
1549 770 730; 1557 771 88; 1562 772 714;
ELEMENT INCIDENCES SHELL
295 213 214 215; 296 216 217 218; 298 219 220 221; 299 222 217 223;
300 224 225 226; 301 227 228 229; 304 230 231 58; 305 232 221 220;
308 233 234 235; 309 236 237 218; 310 232 230 238; 311 213 108 239;
312 240 241 242; 314 242 243 244; 316 228 245 45; 317 246 224 226;
318 247 108 56; 319 248 219 249; 320 246 243 242; 322 250 251 252;
324 253 252 254; 326 255 254 47; 327 253 250 252; 328 233 237 236;
330 248 247 256; 331 224 217 225; 332 227 229 215; 334 216 237 257;
335 223 215 214; 336 253 255 244; 338 250 226 258; 339 232 238 233;
341 219 259 220; 342 229 106 215; 343 224 241 260; 344 261 239 247;
345 215 106 107; 347 226 262 258; 348 225 262 226; 349 237 235 257;
350 233 238 234; 351 228 45 105; 353 240 263 245; 354 247 56 256;
355 239 108 247; 356 225 64 262; 357 216 257 64; 358 223 217 224;
359 246 241 224; 360 222 223 214; 361 216 225 217; 362 252 251 254;
363 250 258 251; 364 238 230 234; 365 232 231 230; 366 240 228 241;
367 242 244 263; 368 248 259 219; 369 236 249 219; 370 229 105 106;
371 223 260 215; 372 229 228 105; 373 227 241 228; 374 223 224 260;
375 222 218 217; 376 213 107 108; 377 213 239 261; 378 236 218 222;
379 261 249 222; 380 216 64 225; 381 216 218 237; 382 246 242 241;
383 250 243 246; 384 236 219 221; 385 236 222 249; 386 261 222 214;
387 261 247 249; 388 240 245 228; 389 240 242 263; 390 248 256 259;
391 248 249 247; 392 233 236 221; 393 233 235 237; 394 250 246 226;
395 253 243 250; 396 227 260 241; 397 227 215 260; 398 213 215 107;
399 213 261 214; 400 253 244 243; 401 253 254 255; 402 232 220 231;
403 232 233 221; 404 264 265 266; 406 264 267 265; 408 268 269 270;
409 265 271 266; 410 272 273 274; 411 268 254 269; 413 266 275 270;
414 269 251 258; 415 276 262 64; 416 276 269 258; 418 266 271 277;
421 278 279 280; 422 278 277 271; 424 280 49 281; 425 282 279 278;
426 282 278 271; 427 283 284 285; 429 286 265 287; 431 283 288 282;
433 272 289 285; 434 272 285 284; 435 272 284 273; 437 273 290 50;
438 264 266 269; 439 269 254 251; 440 265 267 287; 441 278 281 277;
442 266 270 269; 443 266 277 275; 444 278 280 281; 446 282 291 279;
448 276 64 292; 449 276 258 262; 450 284 290 273; 451 274 273 50;
452 286 290 284; 453 283 286 284; 454 286 271 265; 455 264 292 267;
456 282 288 291; 457 283 282 286; 458 268 47 254; 459 268 270 47;
462 274 293 294; 463 274 50 293; 465 285 295 52; 466 285 289 295;
467 272 294 289; 468 272 274 294; 469 264 276 292; 470 264 269 276;
471 286 287 290; 472 286 282 271; 473 283 52 288; 474 283 285 52;
475 298 297 296; 477 58 299 296; 478 287 301 300; 479 302 267 297;
481 303 302 298; 482 301 287 302; 483 301 305 304; 486 307 306 305;
488 308 60 307; 490 301 309 305; 491 311 290 310; 492 313 310 312;
493 309 301 302; 494 311 310 314; 495 297 316 315; 496 50 290 311;
497 314 310 313; 498 310 300 312; 500 304 317 312; 501 305 306 304;
502 297 292 316; 503 296 297 315; 504 64 257 316; 505 287 267 302;
506 309 308 305; 507 267 292 297; 508 303 309 302; 509 292 64 316;
510 316 234 315; 511 299 303 298; 512 302 297 298; 513 58 296 315;
514 299 298 296; 515 308 307 305; 517 306 318 304; 520 321 320 319;
521 311 321 319; 523 322 314 313; 524 310 290 300; 525 257 235 316;
526 235 234 316; 527 318 317 304; 528 300 304 312; 529 234 230 315;
530 230 58 315; 531 320 50 319; 532 50 311 319; 533 322 321 314;
534 321 311 314; 536 62 323 313; 537 323 322 313; 538 290 287 300;
539 301 304 300; 540 317 62 312; 541 62 313 312; 542 324 325 326;
543 327 328 329; 544 330 331 332; 545 333 327 334; 546 335 329 336;
547 337 338 339; 548 340 334 341; 549 342 113 48; 550 340 113 342;
551 343 338 344; 552 338 112 49; 553 345 346 347; 554 348 324 118;
555 331 117 54; 556 338 280 344; 557 349 347 346; 558 346 288 52;
559 345 344 279; 560 350 337 328; 561 349 326 347; 562 330 348 331;
563 324 349 119; 564 333 334 342; 565 332 115 114; 566 351 328 339;
567 350 111 337; 568 349 346 120; 569 351 336 329; 570 345 291 346;
571 336 352 347; 572 332 331 116; 573 330 341 335; 574 343 344 345;
575 337 112 338; 576 329 341 334; 577 335 336 326; 578 331 54 116;
579 348 117 331; 580 336 347 326; 581 351 352 336; 582 333 109 110;
583 327 329 334; 584 344 280 279; 585 338 49 280; 586 342 48 109;
587 340 114 113; 588 346 52 120; 589 346 291 288; 590 324 326 349;
591 349 120 119; 592 348 325 324; 593 324 119 118; 594 348 118 117;
595 330 325 348; 596 337 111 112; 597 343 339 338; 598 340 341 114;
599 340 342 334; 600 343 352 351; 601 351 329 328; 602 345 279 291;
603 345 347 352; 604 333 110 327; 605 333 342 109; 606 332 114 341;
607 332 116 115; 608 335 341 329; 609 335 326 325; 610 343 351 339;
611 343 345 352; 612 330 335 325; 613 330 332 341; 614 350 110 111;
615 337 339 328; 616 350 327 110; 617 350 328 327; 618 353 354 355;
619 354 121 51; 620 353 121 354; 622 356 354 357; 624 358 359 53;
625 360 361 362; 626 361 363 364; 627 365 358 366; 628 367 360 115;
629 368 363 369; 630 369 116 54; 631 370 361 371; 632 372 359 358;
633 373 374 371; 634 375 362 376; 636 377 378 379; 637 377 379 376;
638 379 378 48; 641 380 381 382; 642 383 384 366; 643 366 358 124;
644 385 363 368; 646 368 369 386; 647 375 115 360; 648 376 113 114;
649 370 362 361; 650 371 374 355; 651 383 123 122; 652 380 387 355;
653 356 380 355; 654 365 364 372; 657 385 388 389; 658 379 113 376;
659 370 387 376; 660 373 361 364; 661 360 363 361; 662 358 53 124;
663 372 389 359; 664 371 355 387; 665 373 384 374; 666 367 369 363;
667 375 114 115; 668 369 54 386; 669 367 116 369; 670 354 51 357;
671 353 122 121; 672 383 122 353; 673 353 355 374; 674 379 48 113;
675 377 382 378; 676 380 382 377; 677 377 376 387; 678 383 374 384;
679 366 124 123; 680 385 389 372; 681 365 384 364; 682 385 364 363;
683 368 386 388; 684 383 353 374; 685 383 366 123; 686 370 376 362;
687 370 371 387; 688 380 377 387; 689 356 381 380; 690 367 115 116;
691 367 363 360; 692 373 364 384; 693 373 371 361; 694 375 376 114;
695 375 360 362; 696 356 357 381; 697 356 355 354; 698 365 366 384;
699 365 372 358; 700 385 372 364; 701 385 368 388; 702 390 391 392;
703 129 44 125; 704 391 129 392; 705 392 125 126; 706 393 133 394;
707 395 396 397; 708 398 124 399; 709 400 394 401; 710 402 403 404;
711 396 399 405; 712 405 124 53; 713 395 397 406; 714 394 133 46;
715 407 406 408; 716 404 403 121; 717 402 409 407; 718 410 128 403;
719 403 128 51; 720 411 126 127; 721 412 130 413; 722 401 132 131;
723 393 397 396; 724 414 123 398; 725 407 408 413; 726 396 405 136;
727 398 123 124; 728 390 392 411; 729 412 131 130; 730 393 394 400;
731 396 135 134; 732 392 129 125; 733 391 130 129; 734 403 51 121;
735 410 127 128; 736 414 398 409; 737 404 121 122; 738 394 46 132;
739 393 134 133; 740 414 122 123; 741 395 406 409; 742 391 413 130;
743 390 407 413; 744 407 409 406; 745 400 408 406; 746 402 404 409;
747 390 415 407; 748 410 415 411; 749 411 392 126; 750 412 408 401;
751 401 394 132; 752 412 401 131; 753 412 413 408; 754 405 53 136;
755 405 399 124; 756 410 411 127; 757 402 415 410; 758 396 136 135;
759 395 399 396; 760 414 404 122; 761 414 409 404; 762 390 413 391;
763 390 411 415; 764 402 410 403; 765 402 407 415; 766 400 406 397;
767 400 401 408; 768 393 396 134; 769 393 400 397; 770 395 398 399;
771 395 409 398; 772 416 141 59; 773 417 418 419; 774 420 418 416;
775 421 422 423; 776 424 425 426; 777 427 428 429; 778 430 417 426;
779 431 148 422; 780 422 148 63; 781 432 417 433; 782 434 435 436;
783 428 140 62; 784 435 318 306; 785 437 432 142; 786 427 140 428;
787 438 307 60; 788 434 436 438; 789 428 317 318; 790 439 427 425;
791 440 433 441; 792 423 138 439; 793 420 146 419; 794 420 416 145;
795 440 142 432; 796 438 144 143; 797 430 433 417; 798 426 425 429;
799 439 138 139; 800 435 442 429; 801 435 429 428; 802 421 431 422;
803 431 419 146; 804 438 436 307; 805 434 441 430; 806 424 417 419;
807 432 418 417; 808 422 63 137; 809 431 147 148; 810 426 429 442;
811 424 443 425; 812 437 416 418; 813 440 143 142; 814 436 306 307;
815 435 306 436; 816 416 59 145; 817 437 141 416; 818 428 62 317;
819 427 139 140; 820 439 139 427; 821 427 429 425; 822 423 137 138;
823 439 425 443; 824 423 439 443; 825 423 422 137; 826 438 143 441;
827 438 60 144; 828 420 419 418; 829 420 145 146; 830 430 441 433;
831 430 426 442; 832 434 442 435; 833 435 428 318; 834 437 142 141;
835 437 418 432; 836 431 146 147; 837 421 419 431; 838 421 443 424;
839 424 426 417; 840 434 430 442; 841 434 438 441; 842 421 424 419;
843 421 423 443; 844 440 441 143; 845 440 432 433; 846 444 150 445;
847 446 447 448; 848 449 450 451; 849 444 151 150; 851 446 452 447;
853 447 453 454; 854 455 149 456; 855 457 57 157; 856 458 155 451;
857 459 449 451; 858 458 451 445; 859 459 451 156; 860 450 445 451;
861 460 461 462; 862 462 146 145; 863 445 150 149; 864 456 149 55;
865 463 462 145; 866 460 462 151; 867 461 464 147; 870 454 465 466;
871 148 466 63; 872 464 454 466; 873 446 450 449; 874 455 456 153;
875 462 152 151; 876 467 454 460; 877 461 454 464; 878 454 453 465;
879 463 152 462; 880 461 147 146; 881 459 159 449; 882 451 155 156;
883 448 445 450; 884 449 160 66; 885 449 159 160; 886 459 158 159;
887 459 157 158; 888 457 157 459; 889 464 148 147; 890 464 466 148;
891 447 452 453; 892 446 66 452; 893 458 154 155; 894 455 153 154;
895 457 156 57; 896 457 459 156; 897 455 445 149; 898 456 55 153;
899 463 59 152; 900 463 145 59; 901 455 458 445; 902 455 154 458;
903 448 444 445; 904 448 447 444; 905 446 449 66; 906 446 448 450;
907 460 454 461; 908 461 146 462; 909 467 447 454; 910 460 151 444;
911 467 444 447; 912 467 460 444; 913 468 469 470; 914 471 472 120;
916 473 474 475; 917 476 477 478; 918 479 471 120; 919 471 480 472;
920 481 482 483; 921 472 484 119; 922 485 140 486; 923 487 323 62;
924 488 322 487; 925 488 487 485; 926 489 486 470; 927 487 140 485;
929 117 490 54; 930 491 472 480; 931 492 493 494; 932 489 470 483;
934 474 495 68; 935 496 117 478; 936 478 117 118; 937 468 474 473;
938 486 138 493; 939 497 478 477; 940 494 493 138; 941 492 474 493;
943 498 137 63; 944 494 137 498; 945 491 499 50; 946 476 118 119;
947 496 490 117; 949 500 501 502; 950 471 289 480; 951 472 119 120;
953 492 494 503; 954 486 139 138; 955 486 140 139; 956 491 480 499;
957 474 68 475; 959 492 504 495; 961 500 505 496; 962 501 475 502;
963 506 320 321; 964 488 485 506; 965 494 498 503; 966 494 138 137;
967 481 470 469; 968 470 486 493; 969 489 483 506; 970 482 472 491;
971 499 480 294; 972 480 289 294; 973 479 295 289; 974 479 289 471;
975 477 484 469; 976 497 477 469; 977 487 62 140; 978 487 322 323;
979 496 505 490; 980 500 502 505; 981 506 50 320; 982 506 483 50;
983 488 321 322; 984 488 506 321; 985 492 495 474; 986 492 503 504;
987 489 485 486; 988 489 506 485; 989 479 52 295; 990 479 120 52;
991 499 293 50; 992 499 294 293; 993 482 484 472; 994 491 50 483;
995 481 484 482; 996 482 491 483; 997 481 469 484; 998 481 483 470;
999 497 469 473; 1000 500 496 478; 1001 473 475 501; 1002 468 493 474;
1003 468 470 493; 1004 468 473 469; 1005 476 484 477; 1006 497 500 478;
1007 476 119 484; 1008 476 478 118; 1009 497 501 500; 1010 497 473 501;
1011 507 508 509; 1012 510 511 512; 1014 513 514 515; 1015 516 511 517;
1016 518 519 520; 1017 521 522 523; 1020 524 525 83; 1021 526 515 514;
1024 527 528 529; 1025 530 531 512; 1026 526 524 532; 1027 507 104 533;
1028 534 535 536; 1030 536 537 538; 1032 522 539 70; 1033 540 518 520;
1034 541 104 81; 1035 542 513 543; 1036 540 537 536; 1038 544 545 546;
1040 547 546 548; 1042 549 548 72; 1043 547 544 546; 1044 527 531 530;
1046 542 541 550; 1047 518 511 519; 1048 521 523 509; 1050 510 531 551;
1051 517 509 508; 1052 547 549 538; 1054 544 520 552; 1055 526 532 527;
1057 513 553 514; 1058 523 102 509; 1059 518 535 554; 1060 555 533 541;
1061 509 102 103; 1063 520 556 552; 1064 519 556 520; 1065 531 529 551;
1066 527 532 528; 1067 522 70 101; 1069 534 557 539; 1070 541 81 550;
1071 533 104 541; 1072 519 89 556; 1073 510 551 89; 1074 517 511 518;
1075 540 535 518; 1076 516 517 508; 1077 510 519 511; 1078 546 545 548;
1079 544 552 545; 1080 532 524 528; 1081 526 525 524; 1082 534 522 535;
1083 536 538 557; 1084 542 553 513; 1085 530 543 513; 1086 523 101 102;
1087 517 554 509; 1088 523 522 101; 1089 521 535 522; 1090 517 518 554;
1091 516 512 511; 1092 507 103 104; 1093 507 533 555; 1094 530 512 516;
1095 555 543 516; 1096 510 89 519; 1097 510 512 531; 1098 540 536 535;
1099 544 537 540; 1100 530 513 515; 1101 530 516 543; 1102 555 516 508;
1103 555 541 543; 1104 534 539 522; 1105 534 536 557; 1106 542 550 553;
1107 542 543 541; 1108 527 530 515; 1109 527 529 531; 1110 544 540 520;
1111 547 537 544; 1112 521 554 535; 1113 521 509 554; 1114 507 509 103;
1115 507 555 508; 1116 547 538 537; 1117 547 548 549; 1118 526 514 525;
1119 526 527 515; 1120 558 559 560; 1122 558 561 559; 1124 562 563 564;
1125 559 565 560; 1126 566 567 568; 1127 562 548 563; 1129 560 569 564;
1130 563 545 552; 1131 570 556 89; 1132 570 563 552; 1134 560 565 571;
1137 572 573 574; 1138 572 571 565; 1140 574 74 575; 1141 576 573 572;
1142 576 572 565; 1143 577 578 579; 1145 580 559 581; 1147 577 582 576;
1149 566 583 579; 1150 566 579 578; 1151 566 578 567; 1153 567 584 75;
1154 558 560 563; 1155 563 548 545; 1156 559 561 581; 1157 572 575 571;
1158 560 564 563; 1159 560 571 569; 1160 572 574 575; 1162 576 585 573;
1164 570 89 586; 1165 570 552 556; 1166 578 584 567; 1167 568 567 75;
1168 580 584 578; 1169 577 580 578; 1170 580 565 559; 1171 558 586 561;
1172 576 582 585; 1173 577 576 580; 1174 562 72 548; 1175 562 564 72;
1178 568 587 588; 1179 568 75 587; 1181 579 589 77; 1182 579 583 589;
1183 566 588 583; 1184 566 568 588; 1185 558 570 586; 1186 558 563 570;
1187 580 581 584; 1188 580 576 565; 1189 577 77 582; 1190 577 579 77;
1191 590 591 592; 1193 593 594 595; 1194 596 586 89; 1195 595 597 561;
1197 597 598 599; 1200 85 600 601; 1201 602 597 595; 1202 596 529 595;
1203 603 524 593; 1204 595 561 586; 1205 603 593 595; 1206 590 581 597;
1207 604 592 87; 1208 605 75 606; 1209 605 606 592; 1212 604 607 608;
1213 591 87 592; 1214 590 599 591; 1216 591 599 609; 1218 610 611 609;
1219 610 609 599; 1220 610 599 598; 1221 610 601 600; 1223 602 612 598;
1224 590 592 584; 1225 602 595 594; 1226 597 581 561; 1227 603 595 529;
1228 596 551 529; 1229 606 584 592; 1230 604 608 592; 1231 606 75 584;
1233 605 613 75; 1235 591 614 87; 1236 591 609 614; 1237 610 600 611;
1238 610 598 601; 1239 596 89 551; 1240 596 595 586; 1241 602 598 597;
1242 602 594 612; 1243 593 83 594; 1244 593 524 83; 1245 603 528 524;
1246 603 529 528; 1247 590 597 599; 1248 590 584 581; 1249 605 608 613;
1250 605 592 608; 1252 604 615 607; 1253 604 87 615; 1254 616 617 618;
1255 619 620 621; 1256 622 623 624; 1257 625 619 626; 1258 627 621 628;
1259 629 630 631; 1260 632 626 633; 1261 634 169 73; 1262 632 169 634;
1263 635 630 636; 1264 630 164 74; 1265 637 638 639; 1266 640 616 166;
1267 623 165 79; 1268 630 574 636; 1269 641 639 638; 1270 638 582 77;
1271 637 636 573; 1272 642 629 620; 1273 641 618 639; 1274 622 640 623;
1275 616 641 167; 1276 625 626 634; 1277 624 171 170; 1278 643 620 631;
1279 642 163 629; 1280 641 638 168; 1281 643 628 621; 1282 637 585 638;
1283 628 644 639; 1284 624 623 172; 1285 622 633 627; 1286 635 636 637;
1287 629 164 630; 1288 621 633 626; 1289 627 628 618; 1290 623 79 172;
1291 640 165 623; 1292 628 639 618; 1293 643 644 628; 1294 625 161 162;
1295 619 621 626; 1296 636 574 573; 1297 630 74 574; 1298 634 73 161;
1299 632 170 169; 1300 638 77 168; 1301 638 585 582; 1302 616 618 641;
1303 641 168 167; 1304 640 617 616; 1305 616 167 166; 1306 640 166 165;
1307 622 617 640; 1308 629 163 164; 1309 635 631 630; 1310 632 633 170;
1311 632 634 626; 1312 635 644 643; 1313 643 621 620; 1314 637 573 585;
1315 637 639 644; 1316 625 162 619; 1317 625 634 161; 1318 624 170 633;
1319 624 172 171; 1320 627 633 621; 1321 627 618 617; 1322 635 643 631;
1323 635 637 644; 1324 622 627 617; 1325 622 624 633; 1326 642 162 163;
1327 629 631 620; 1328 642 619 162; 1329 642 620 619; 1330 645 646 647;
1331 646 185 76; 1332 645 185 646; 1334 648 646 649; 1336 650 651 78;
1337 652 653 654; 1338 653 655 656; 1339 657 650 658; 1340 659 652 171;
1341 660 655 661; 1342 661 172 79; 1343 662 653 663; 1344 664 651 650;
1345 665 666 663; 1346 667 654 668; 1348 669 670 671; 1349 669 671 668;
1350 671 670 73; 1353 672 673 674; 1354 675 676 658; 1355 658 650 188;
1356 677 655 660; 1358 660 661 678; 1359 667 171 652; 1360 668 169 170;
1361 662 654 653; 1362 663 666 647; 1363 675 187 186; 1364 672 679 647;
1365 648 672 647; 1366 657 656 664; 1369 677 680 681; 1370 671 169 668;
1371 662 679 668; 1372 665 653 656; 1373 652 655 653; 1374 650 78 188;
1375 664 681 651; 1376 663 647 679; 1377 665 676 666; 1378 659 661 655;
1379 667 170 171; 1380 661 79 678; 1381 659 172 661; 1382 646 76 649;
1383 645 186 185; 1384 675 186 645; 1385 645 647 666; 1386 671 73 169;
1387 669 674 670; 1388 672 674 669; 1389 669 668 679; 1390 675 666 676;
1391 658 188 187; 1392 677 681 664; 1393 657 676 656; 1394 677 656 655;
1395 660 678 680; 1396 675 645 666; 1397 675 658 187; 1398 662 668 654;
1399 662 663 679; 1400 672 669 679; 1401 648 673 672; 1402 659 171 172;
1403 659 655 652; 1404 665 656 676; 1405 665 663 653; 1406 667 668 170;
1407 667 652 654; 1408 648 649 673; 1409 648 647 646; 1410 657 658 676;
1411 657 664 650; 1412 677 664 656; 1413 677 660 680; 1414 682 683 684;
1415 177 69 173; 1416 685 686 687; 1417 682 688 178; 1418 682 177 683;
1419 689 690 691; 1420 691 692 693; 1421 694 695 182; 1422 694 182 181;
1423 696 179 688; 1424 687 187 188; 1425 691 693 695; 1426 697 692 698;
1427 686 187 687; 1428 692 687 188; 1430 697 699 692; 1431 698 692 188;
1432 698 188 78; 1433 694 181 700; 1434 701 185 686; 1435 701 686 702;
1436 701 702 175; 1437 701 176 76; 1438 702 174 175; 1439 682 703 688;
1440 704 92 184; 1441 686 186 187; 1442 685 705 703; 1443 696 694 180;
1444 704 184 692; 1445 704 692 699; 1446 693 183 182; 1447 693 182 695;
1449 697 698 706; 1450 698 78 706; 1451 683 174 702; 1452 688 179 178;
1453 686 185 186; 1454 685 702 686; 1455 683 173 174; 1456 683 177 173;
1458 704 707 92; 1459 704 699 707; 1460 701 76 185; 1461 701 175 176;
1462 700 71 180; 1463 700 181 71; 1464 693 184 183; 1465 693 692 184;
1466 691 687 692; 1467 690 687 691; 1468 684 702 685; 1469 690 705 685;
1471 697 708 699; 1472 697 706 708; 1473 684 685 703; 1474 684 683 702;
1475 690 685 687; 1476 689 705 690; 1477 696 695 694; 1478 688 703 705;
1479 689 688 705; 1480 689 691 695; 1481 682 178 177; 1482 682 684 703;
1483 696 689 695; 1484 694 700 180; 1485 696 688 689; 1486 696 180 179;
1487 199 710 709; 1488 709 712 711; 1490 90 714 713; 1491 717 716 715;
1492 200 709 711; 1493 712 615 711; 1494 719 709 718; 1495 708 706 720;
1496 608 712 719; 1497 721 90 713; 1498 680 723 722; 1499 725 724 720;
1500 78 651 725; 1501 724 727 726; 1502 727 92 726; 1503 699 708 724;
1504 651 722 725; 1505 729 716 728; 1507 731 730 725; 1508 734 733 732;
1511 737 736 735; 1512 734 739 738; 1513 741 740 735; 1514 743 742 735;
1515 197 745 744; 1516 747 745 746; 1517 749 721 748; 1519 752 751 750;
1522 91 754 753; 1524 741 755 750; 1525 743 740 749; 1526 733 757 756;
1527 743 717 756; 1528 759 166 758; 1529 742 761 760; 1530 745 760 746;
1531 758 762 718; 1532 763 758 718; 1533 168 765 764; 1534 765 589 766;
1535 764 765 766; 1536 587 762 764; 1537 762 168 764; 1538 767 713 731;
1539 734 79 768; 1540 166 759 739; 1541 745 88 760; 1542 709 710 718;
1543 199 198 744; 1544 712 709 719; 1545 200 199 709; 1546 736 753 741;
1548 769 721 751; 1550 730 770 725; 1551 651 681 722; 1552 739 759 738;
1553 166 167 758; 1554 761 743 756; 1555 742 737 735; 1556 757 759 747;
1558 771 742 760; 1559 715 716 729; 1560 79 734 732; 1561 721 713 748;
1563 713 772 731; 1564 721 749 751; 1565 769 90 721; 1566 167 168 758;
1567 758 168 762; 1568 744 745 747; 1569 197 88 745; 1570 723 715 729;
1571 680 678 732; 1572 166 739 768; 1573 759 757 738; 1574 587 75 762;
1575 762 75 719; 1576 724 770 727; 1577 724 708 720; 1578 770 92 727;
1579 92 707 726; 1580 753 754 741; 1581 754 755 741; 1582 717 743 749;
1583 749 740 751; 1584 608 607 712; 1585 607 615 712; 1586 771 737 742;
1587 743 761 742; 1588 732 733 715; 1589 79 165 768; 1590 75 613 719;
1591 613 608 719; 1592 714 772 713; 1593 713 767 748; 1594 736 741 735;
1595 740 743 735; 1596 168 77 765; 1597 77 589 765; 1598 615 87 711;
1599 87 200 711; 1600 723 680 732; 1601 678 79 732; 1602 722 773 725;
1603 681 680 722; 1604 772 730 731; 1605 731 773 728; 1606 773 731 725;
1607 770 724 725; 1608 751 740 750; 1609 752 769 751; 1610 710 199 744;
1611 198 197 744; 1612 747 759 763; 1613 710 744 747; 1614 710 747 763;
1615 759 758 763; 1616 716 717 774; 1617 717 749 748; 1618 717 748 774;
1619 773 729 728; 1620 757 733 738; 1621 733 734 738; 1622 723 732 715;
1623 733 717 715; 1624 762 719 718; 1625 710 763 718; 1626 583 588 764;
1627 588 587 764; 1628 740 741 750; 1629 755 752 750; 1630 760 761 746;
1631 88 771 760; 1632 746 761 756; 1633 757 747 746; 1634 717 733 756;
1635 757 746 756; 1636 773 722 729; 1637 722 723 729; 1638 707 699 726;
1639 699 724 726; 1640 706 78 720; 1641 78 725 720; 1642 165 166 768;
1643 739 734 768; 1644 728 716 774; 1645 767 731 728; 1646 748 767 774;
1647 767 728 774; 1648 589 583 766; 1649 583 764 766; 1650 775 193 84;
1651 776 777 778; 1652 779 777 775; 1653 780 781 782; 1654 783 784 785;
1655 786 787 788; 1656 789 776 785; 1657 790 204 781; 1658 781 204 88;
1659 791 776 792; 1660 793 794 795; 1661 787 200 87; 1662 794 609 611;
1663 796 791 194; 1664 786 200 787; 1665 797 600 85; 1666 793 795 797;
1667 787 614 609; 1668 798 786 784; 1669 799 792 800; 1670 782 198 798;
1671 779 202 778; 1672 779 775 201; 1673 799 194 791; 1674 797 196 195;
1675 789 792 776; 1676 785 784 788; 1677 798 198 199; 1678 794 801 788;
1679 794 788 787; 1680 780 790 781; 1681 790 778 202; 1682 797 795 600;
1683 793 800 789; 1684 783 776 778; 1685 791 777 776; 1686 781 88 197;
1687 790 203 204; 1688 785 788 801; 1689 783 802 784; 1690 796 775 777;
1691 799 195 194; 1692 795 611 600; 1693 794 611 795; 1694 775 84 201;
1695 796 193 775; 1696 787 87 614; 1697 786 199 200; 1698 798 199 786;
1699 786 788 784; 1700 782 197 198; 1701 798 784 802; 1702 782 798 802;
1703 782 781 197; 1704 797 195 800; 1705 797 85 196; 1706 779 778 777;
1707 779 201 202; 1708 789 800 792; 1709 789 785 801; 1710 793 801 794;
1711 794 787 609; 1712 796 194 193; 1713 796 777 791; 1714 790 202 203;
1715 780 778 790; 1716 780 802 783; 1717 783 785 776; 1718 793 789 801;
1719 793 797 800; 1720 780 783 778; 1721 780 782 802; 1722 799 800 195;
1723 799 791 792; 1724 803 210 804; 1725 805 806 807; 1726 808 809 810;
1727 803 211 210; 1728 805 753 806; 1729 806 736 811; 1730 812 209 813;
1731 814 82 205; 1732 815 191 810; 1733 816 808 810; 1734 815 810 804;
1735 816 810 192; 1736 809 804 810; 1737 817 818 819; 1738 819 202 201;
1739 804 210 209; 1740 813 209 80; 1741 820 819 201; 1742 817 819 211;
1743 818 821 203; 1744 811 737 771; 1745 204 771 88; 1746 821 811 771;
1747 805 809 808; 1748 812 813 189; 1749 819 212 211; 1750 822 811 817;
1751 818 811 821; 1752 811 736 737; 1753 820 212 819; 1754 818 203 202;
1755 816 207 808; 1756 810 191 192; 1757 807 804 809; 1758 808 208 91;
1759 808 207 208; 1760 816 206 207; 1761 816 205 206; 1762 814 205 816;
1763 821 204 203; 1764 821 771 204; 1765 806 753 736; 1766 805 91 753;
1767 815 190 191; 1768 812 189 190; 1769 814 192 82; 1770 814 816 192;
1771 812 804 209; 1772 813 80 189; 1773 820 84 212; 1774 820 201 84;
1775 812 815 804; 1776 812 190 815; 1777 807 803 804; 1778 807 806 803;
1779 805 808 91; 1780 805 807 809; 1781 817 811 818; 1782 818 202 819;
1783 822 806 811; 1784 817 211 803; 1785 822 803 806; 1786 822 817 803;
SURFACE INCIDENCE
1 44 46 4 SURFACE 1 DIV 5 5 5 5
1 22 51 44 SURFACE 2 DIV 5 5 5 5
24 4 46 53 SURFACE 3 DIV 5 5 5 5
53 51 22 24 SURFACE 4 DIV 5 5 5 5
15 25 54 48 SURFACE 5 DIV 5 5 5 5
15 18 49 48 SURFACE 6 DIV 5 5 5 5
25 54 52 23 SURFACE 7 DIV 5 5 5 5
37 35 62 63 SURFACE 8 DIV 5 5 5 5
37 32 59 63 SURFACE 9 DIV 5 5 5 5
32 33 60 59 SURFACE 10 DIV 5 5 5 5
30 41 66 57 SURFACE 11 DIV 5 5 5 5
30 28 55 57 SURFACE 12 DIV 5 5 5 5
28 32 59 55 SURFACE 13 DIV 5 5 5 5
44 46 71 69 SURFACE 17 DIV 5 5 5 5
71 78 53 46 SURFACE 18 DIV 6 5 5 5
51 53 78 76 SURFACE 19 DIV 5 5 5 5
69 76 51 44 SURFACE 20 DIV 5 5 5 5
48 49 74 73 SURFACE 21 DIV 5 5 5 5
48 54 79 73 SURFACE 22 DIV 5 5 5 5
54 52 77 79 SURFACE 23 DIV 5 5 5 5
57 55 80 82 SURFACE 24 DIV 5 5 5 5
55 59 84 80 SURFACE 25 DIV 5 5 5 5
59 60 85 84 SURFACE 26 DIV 5 5 5 5
84 88 63 59 SURFACE 27 DIV 5 5 5 5
63 62 87 88 SURFACE 28 DIV 5 5 5 5
57 66 91 82 SURFACE 32 DIV 5 5 5 5
95 97 45 56 98 96 SURFACE 33 DIV 3 1 5 1 3 5
97 99 70 81 100 98 56 45 SURFACE 34 DIV 3 1 5 1 3 1 5 1
ELEMENT PROPERTY
295 296 298 TO 301 304 305 308 TO 312 314 316 TO 320 322 324 326 TO 328 330 -
331 TO 332 334 TO 336 338 339 341 TO 345 347 TO 351 353 TO 404 406 -
408 TO 411 413 TO 416 418 421 422 424 TO 427 429 431 433 TO 435 437 TO 444 -
446 448 TO 459 462 463 465 TO 475 477 TO 479 481 TO 483 486 488 490 TO 498 -
500 TO 515 517 520 521 523 TO 534 536 TO 620 622 624 TO 634 636 TO 638 641 -
642 TO 644 646 TO 654 657 TO 849 851 853 TO 867 870 TO 914 916 TO 927 929 -
930 TO 932 934 TO 941 943 TO 947 949 TO 951 953 TO 957 959 961 TO 1012 1014 -
1015 TO 1017 1020 1021 1024 TO 1028 1030 1032 TO 1036 1038 1040 1042 TO 1044 -
1046 TO 1048 1050 TO 1052 1054 1055 1057 TO 1061 1063 TO 1067 1069 TO 1120 -
1122 1124 TO 1127 1129 TO 1132 1134 1137 1138 1140 TO 1143 1145 1147 1149 -
1150 TO 1151 1153 TO 1160 1162 1164 TO 1175 1178 1179 1181 TO 1191 -
1193 TO 1195 1197 1200 TO 1209 1212 TO 1214 1216 1218 TO 1221 1223 TO 1231 -
1233 1235 TO 1250 1252 TO 1332 1334 1336 TO 1346 1348 TO 1350 1353 TO 1356 -
1358 TO 1366 1369 TO 1428 1430 TO 1447 1449 TO 1456 1458 TO 1469 -
1471 TO 1488 1490 TO 1505 1507 1508 1511 TO 1517 1519 1522 1524 TO 1546 1548 -
1550 TO 1556 1558 TO 1561 1563 TO 1786 THICKNESS 0.175
DEFINE MATERIAL START
ISOTROPIC CONCRETE
E 2.17185e+007
POISSON 0.17
DENSITY 23.5616
ALPHA 1e-005
DAMP 0.05
TYPE CONCRETE
STRENGTH FCU 27579
END DEFINE MATERIAL
MEMBER PROPERTY AMERICAN
79 TO 86 88 TO 91 93 TO 97 99 TO 107 111 112 138 TO 150 152 TO 156 -
158 TO 169 172 TO 175 180 TO 294 297 302 303 306 307 313 315 321 323 325 -
329 333 337 340 346 352 405 407 412 417 419 420 423 428 430 432 436 445 447 -
460 461 464 476 480 484 485 487 489 499 516 518 519 522 535 621 623 635 639 -
640 645 655 656 850 852 868 869 915 928 933 942 948 952 958 960 1013 1018 -
1019 1022 1023 1029 1031 1037 1039 1041 1045 1049 1053 1056 1062 1068 1121 -
1123 1128 1133 1135 1136 1139 1144 1146 1148 1152 1161 1163 1176 1177 1180 -
1192 1196 1198 1199 1210 1211 1215 1217 1222 1232 1234 1251 1333 1335 1347 -
1351 1352 1357 1367 1368 1429 1448 1457 1470 1489 1506 1509 1510 1518 1520 -
1521 1523 1547 1549 1557 1562 PRIS YD 0.5 ZD 0.4
57 59 68 70 116 118 127 129 PRIS YD 0.4 ZD 0.4
SURFACE PROPERTY
1 TO 13 17 TO 28 32 TO 34 THICKNESS 0.2
CONSTANTS
MATERIAL CONCRETE MEMB 57 59 68 70 79 TO 86 88 TO 91 93 TO 97 99 TO 107 111 -
112 116 118 127 129 138 TO 150 152 TO 156 158 TO 169 172 TO 175 180 TO 1786
SURFACE CONSTANTS
MATERIAL CONCRETE ALL
MEMBER CRACKED
57 59 68 70 116 118 127 -
129 REDUCTION RAX 0.700000 RIX 0.700000 RIY 0.700000 RIZ 0.700000
158 TO 169 180 181 183 TO 230 235 TO 293 -
294 REDUCTION RAX 0.350000 RIX 0.350000 RIY 0.350000 RIZ 0.350000
SUPPORTS
1 4 13 15 18 22 TO 25 28 30 TO 33 35 37 41 95 -
96 ELASTIC MAT DIRECT Y SUBGRADE 34000 PRINT
DEFINE REFERENCE LOADS
LOAD R1 LOADTYPE Mass TITLE REF USED FOR MASS DEFINITION
SELFWEIGHT Y -1
SSELFWT Y -1 ALL
ELEMENT LOAD
930 TO 932 934 TO 941 943 TO 947 949 TO 951 953 TO 957 959 961 TO 1009 -
1010 PR 2.55
1011 1012 1014 TO 1017 1020 1021 1024 TO 1028 1030 1032 TO 1036 1038 1040 -
1042 TO 1044 1046 TO 1048 1050 TO 1052 1054 1055 1057 TO 1061 1063 TO 1067 -
1069 TO 1120 1122 1124 TO 1127 1129 TO 1132 1134 1137 1138 1140 TO 1143 1145 -
1147 1149 TO 1151 1153 TO 1160 1162 1164 TO 1175 1178 1179 1181 TO 1191 1193 -
1194 TO 1195 1197 1200 TO 1209 1212 TO 1214 1216 1218 TO 1221 1223 TO 1231 -
1550 TO 1556 1558 TO 1561 1563 TO 1786 PR 1.54
END DEFINE REFERENCE LOADS
FLOOR DIAPHRAGM
DIA 1 TYPE RIG HEI 4.831
DIA 2 TYPE RIG HEI 8.501
DEFINE IBC 2012
SS 1.1 S1 0.375 I 1.25 RX 7 RZ 7 SCLASS 4 TL 12 FA 1.06 FV 1.65 K 0.9
LOAD 1 LOADTYPE Seismic TITLE EQ +X (+ACC)
IBC LOAD X 1 DEC 1 ACC 0.05
PDELTA ANALYSIS SMALLDELTA
CHANGE
LOAD 2 LOADTYPE Seismic TITLE EQ +X (-ACC)
IBC LOAD X 1 DEC 1 ACC -0.05
CHANGE
LOAD 3 LOADTYPE Seismic TITLE EQ -X (+ACC)
IBC LOAD X -1 DEC 1 ACC 0.05
CHANGE
LOAD 4 LOADTYPE Seismic TITLE EQ -X (-ACC)
IBC LOAD X -1 DEC 1 ACC -0.05
CHANGE
LOAD 5 LOADTYPE Seismic TITLE EQ +Z (+ACC)
IBC LOAD Z 1 DEC 1 ACC 0.05
CHANGE
LOAD 6 LOADTYPE Seismic TITLE EQ +Z (-ACC)
IBC LOAD Z 1 DEC 1 ACC -0.05
CHANGE
LOAD 7 LOADTYPE Seismic TITLE EQ -Z (+ACC)
IBC LOAD Z -1 DEC 1 ACC 0.05
CHANGE
LOAD 8 LOADTYPE Seismic TITLE EQ -Z (-ACC)
IBC LOAD Z -1 DEC 1 ACC -0.05
CHANGE
LOAD 9 LOADTYPE Dead TITLE DEAD LOAD
SELFWEIGHT Y -1
SSELFWT Y -1 ALL
MEMBER LOAD
81 83 TO 86 94 96 97 99 105 297 303 313 315 325 329 340 352 405 407 412 417 -
419 420 423 428 430 432 436 445 447 460 461 464 476 480 484 485 487 489 499 -
516 518 519 522 535 621 635 639 640 UNI GY -11.59
146 165 263 TO 266 287 TO 290 UNI GY -40.51
168 169 1489 1506 1518 1521 1523 1547 1549 1562 UNI GY -12.36
ELEMENT LOAD
1010 PR 2.55
CHANGE
LOAD 10 LOADTYPE Live TITLE LIVE LOAD
MEMBER LOAD
168 169 1489 1506 1518 1521 1523 1547 1549 1562 UNI GY -4.43
146 165 263 TO 266 287 TO 290 UNI GY -17.84
ELEMENT LOAD
1550 TO 1556 1558 TO 1561 1563 TO 1786 PR 2.7
1010 PR 4.79
CHANGE
LOAD 11 LOADTYPE None TITLE DL + LL
REPEAT LOAD
9 1.0 10 1.0
LOAD 12 LOADTYPE None TITLE 1.4DL
REPEAT LOAD
9 1.4
LOAD 13 LOADTYPE None TITLE 1.2DL + 1.6LL
REPEAT LOAD
9 1.2 10 1.6
LOAD 14 LOADTYPE None TITLE 1.2DL + 0.5LL
REPEAT LOAD
9 1.2 10 0.5
LOAD 15 LOADTYPE None TITLE 1.2DL + 1EQ+X + 0.5LL (+ACC)
REPEAT LOAD
9 1.2 10 0.5 1 1.0
LOAD 16 LOADTYPE None TITLE 1.2DL + 1EQ+X + 0.5LL (-ACC)
REPEAT LOAD
9 1.2 10 0.5 2 1.0
LOAD 17 LOADTYPE None TITLE 1.2DL + 1EQ-X + 0.5LL (+ACC)
REPEAT LOAD
3 1.0 9 1.2 10 0.5
LOAD 18 LOADTYPE None TITLE 1.2DL + 1EQ-X + 0.5LL (-ACC)
REPEAT LOAD
4 1.0 9 1.2 10 0.5
LOAD 19 LOADTYPE None TITLE 1.2DL + 1EQ+Z + 0.5LL (+ACC)
REPEAT LOAD
5 1.0 9 1.2 10 0.5
LOAD 20 LOADTYPE None TITLE 1.2DL + 1EQ+Z + 0.5LL (-ACC)
REPEAT LOAD
6 1.0 9 1.2 10 0.5
LOAD 21 LOADTYPE None TITLE 1.2DL + 1EQ-Z + 0.5LL (+ACC)
REPEAT LOAD
7 1.0 9 1.2 10 0.5
LOAD 22 LOADTYPE None TITLE 1.2DL + 1EQ-Z + 0.5LL (-ACC)
REPEAT LOAD
8 1.0 9 1.2 10 0.5
LOAD 23 LOADTYPE None TITLE 0.9DL + 1EQ+X (+ACC)
REPEAT LOAD
1 1.0 9 0.9
LOAD 24 LOADTYPE None TITLE 0.9DL + 1EQ+X (-ACC)
REPEAT LOAD
2 1.0 9 0.9
LOAD 25 LOADTYPE None TITLE 0.9DL + 1EQ-X (+ACC)
REPEAT LOAD
3 1.0 9 0.9
LOAD 26 LOADTYPE None TITLE 0.9DL + 1EQ-X (-ACC)
REPEAT LOAD
4 1.0 9 0.9
LOAD 27 LOADTYPE None TITLE 0.9DL + 1EQ+Z (+ACC)
REPEAT LOAD
5 1.0 9 0.9
LOAD 28 LOADTYPE None TITLE 0.9DL + 1EQ+Z (-ACC)
REPEAT LOAD
6 1.0 9 0.9
LOAD 29 LOADTYPE None TITLE 0.9DL + 1EQ-Z (+ACC)
REPEAT LOAD
7 1.0 9 0.9
LOAD 30 LOADTYPE None TITLE 0.9DL + 1EQ-Z (-ACC)
REPEAT LOAD
8 1.0 9 0.9
PDELTA 30 ANALYSIS SMALLDELTA
CHANGE
LOAD LIST 11 TO 30
PRINT DIA CR
PRINT STORY DRIFT 0.004100
START SHEARWALL DESIGN
CODE ACI
TRACK 1
DESIGN SHEARWALL ALL
EMIN 5 LIST ALL
HMIN 5 LIST ALL
VMIN 5 LIST ALL
END SHEARWALL DESIGN
START CONCRETE DESIGN
CODE ACI
CLB 0.05 MEMB 79 TO 86 88 TO 91 93 TO 97 99 TO 107 111 112 138 TO 150 152 -
153 TO 156 158 TO 169 172 TO 175 180 TO 294 297 302 303 306 307 313 315 321 -
323 325 329 333 337 340 346 352 405 407 412 417 419 420 423 428 430 432 436 -
445 447 460 461 464 476 480 484 485 487 489 499 516 518 519 522 535 621 623 -
635 639 640 645 655 656 850 852 868 869 915 928 933 942 948 952 958 960 1013 -
1018 1019 1022 1023 1029 1031 1037 1039 1041 1045 1049 1053 1056 1062 1068 -
1121 1123 1128 1133 1135 1136 1139 1144 1146 1148 1152 1161 1163 1176 1177 -
1180 1192 1196 1198 1199 1210 1211 1215 1217 1222 1232 1234 1251 1333 1335 -
1347 1351 1352 1357 1367 1368 1429 1448 1457 1470 1489 1506 1509 1510 1518 -
1520 1521 1523 1547 1549 1557 1562
CLS 0.05 MEMB 79 TO 86 88 TO 91 93 TO 97 99 TO 107 111 112 138 TO 150 152 -
CLT 0.05 MEMB 79 TO 86 88 TO 91 93 TO 97 99 TO 107 111 112 138 TO 150 152 -
MINMAIN 25 ALL
TRACK 2 ALL
DESIGN BEAM 79 TO 86 88 TO 91 93 TO 97 99 TO 107 111 112 138 TO 150 -
152 TO 156 158 TO 169 172 TO 175 180 TO 294 297 302 303 306 307 313 315 321 -
DESIGN COLUMN 57 59 68 70 116 118 127 129
DESIGN ELEMENT 295 296 298 TO 301 304 305 308 TO 312 314 316 TO 320 322 324 -
326 TO 328 330 TO 332 334 TO 336 338 339 341 TO 345 347 TO 351 353 TO 404 -
406 408 TO 411 413 TO 416 418 421 422 424 TO 427 429 431 433 TO 435 -
437 TO 444 446 448 TO 459 462 463 465 TO 475 477 TO 479 481 TO 483 486 488 -
490 TO 498 500 TO 515 517 520 521 523 TO 534 536 TO 620 622 624 TO 634 636 -
637 TO 638 641 TO 644 646 TO 654 657 TO 849 851 853 TO 867 870 TO 914 916 -
917 TO 927 929 TO 932 934 TO 941 943 TO 947 949 TO 951 953 TO 957 959 961 -
962 TO 1012 1014 TO 1017 1020 1021 1024 TO 1028 1030 1032 TO 1036 1038 1040 -
CONCRETE TAKE
END CONCRETE DESIGN
FINISH