          ACI 318-11   BEAM  NO.     2   DESIGN RESULTS
   LEN -  1500. MM  FY -  415.  FC -  25.  MPA, SIZE -  300. X  400. MMS
   LEVEL    HEIGHT     BAR INFO       FROM          TO           ANCHOR
             (MM)                     (MM)         (MM)         STA  END
   _____________________________________________________________________
     1         49.     3 - 12MM         0.         1500.        YES  YES
   |   CRITICAL POS MOMENT=     22.27 KN-MET  AT     0.MM, LOAD  609|
   |   REQD STEEL=   229.MM2, RHO=0.0022, RHOMX=0.0193 RHOMN=0.0033 |
   |   MAX/MIN/ACTUAL BAR SPACING=   273./   37./  106. MMS         |
   |   REQD. DEVELOPMENT LENGTH =   360. MMS                       |
     Cracked Moment of Inertia Iz at above location =    26089.3 cm^4
     2        354.     2 - 16MM         0.         1500.        YES  YES
   |   CRITICAL NEG MOMENT=     45.35 KN-MET  AT     0.MM, LOAD  606|
   |   REQD STEEL=   354.MM2, RHO=0.0033, RHOMX=0.0193 RHOMN=0.0033 |
   |   MAX/MIN/ACTUAL BAR SPACING=   273./   41./  209. MMS         |
   |   REQD. DEVELOPMENT LENGTH =   480. MMS                       |
     Cracked Moment of Inertia Iz at above location =    30686.7 cm^4
          B E A M  N O.     2 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   19.89 KNS  Vc=   87.49 KNS  Vs=    0.00 KNS
    Tu=   18.07 KN-MET  Tc=    3.2 KN-MET  Ts=   24.1 KN-MET  LOAD   608
    STIRRUPS ARE REQUIRED FOR TORSION.
    REINFORCEMENT FOR SHEAR IS PER CL.11.5.5.1.
    PROVIDE 12 MM 2-LEGGED STIRRUPS AT 143. MM  C/C FOR  405. MM
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   4.92 SQ.CM.
    AT END   SUPPORT - Vu=   16.74 KNS  Vc=   87.49 KNS  Vs=    0.00 KNS
    STAAD SPACE                                              -- PAGE NO.   45
  ___   4J____________________  1499X 300X  400_____________________  62J____
 | 2No16 H 354.   0.TO 1500|                       |       |       |       | |
 |  4*12c/c143     |       |                       |       |   4*12c/c143  | |
 | 3No12 H |49.   0.TO 1500|                       |       |       |       | |
 |___________________________________________________________________________|
  ___________     ___________     ___________     ___________     ___________
 |    oo     |   |    oo     |   |    oo     |   |    oo     |   |    oo     |
 | 2#16      |   | 2#16      |   | 2#16      |   | 2#16      |   | 2#16      |
 | 3#12      |   | 3#12      |   | 3#12      |   | 3#12      |   | 3#12      |
 |    ooo    |   |    ooo    |   |    ooo    |   |    ooo    |   |    ooo    |
 |___________|   |___________|   |___________|   |___________|   |___________|
          ACI 318-11   BEAM  NO.     4   DESIGN RESULTS
     1         49.     2 - 12MM         0.         1500.        YES  YES
   |   CRITICAL POS MOMENT=     18.39 KN-MET  AT  1500.MM, LOAD  605|
   |   REQD STEEL=   189.MM2, RHO=0.0018, RHOMX=0.0193 RHOMN=0.0033 |
   |   MAX/MIN/ACTUAL BAR SPACING=   273./   37./  213. MMS         |
     Cracked Moment of Inertia Iz at above location =    18373.0 cm^4
   |   CRITICAL NEG MOMENT=     40.65 KN-MET  AT     0.MM, LOAD  606|
   |   REQD STEEL=   353.MM2, RHO=0.0033, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.     4 D E S I G N  R E S U L T S - SHEAR
    STAAD SPACE                                              -- PAGE NO.   46
    AT START SUPPORT - Vu=   18.70 KNS  Vc=   88.86 KNS  Vs=    0.00 KNS
    Tu=   17.85 KN-MET  Tc=    3.2 KN-MET  Ts=   23.8 KN-MET  LOAD   607
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   4.86 SQ.CM.
    AT END   SUPPORT - Vu=   15.56 KNS  Vc=   85.16 KNS  Vs=    0.00 KNS
  ___   5J____________________  1499X 300X  400_____________________  63J____
 | 2No12 H |49.   0.TO 1500|                       |       |       |       | |
 | 2#12      |   | 2#12      |   | 2#12      |   | 2#12      |   | 2#12      |
          ACI 318-11   BEAM  NO.     6   DESIGN RESULTS
   LEN -  4600. MM  FY -  415.  FC -  25.  MPA, SIZE -  300. X  400. MMS
     1         49.     2 - 12MM         0.         4600.        YES  YES
   |   CRITICAL POS MOMENT=     21.77 KN-MET  AT  4600.MM, LOAD  610|
   |   REQD STEEL=   224.MM2, RHO=0.0021, RHOMX=0.0193 RHOMN=0.0033 |
    STAAD SPACE                                              -- PAGE NO.   47
     2        356.     2 - 12MM         0.          851.        YES  NO
   |   CRITICAL NEG MOMENT=      8.26 KN-MET  AT     0.MM, LOAD  610|
   |   REQD STEEL=    83.MM2, RHO=0.0008, RHOMX=0.0193 RHOMN=0.0033 |
     Cracked Moment of Inertia Iz at above location =    18932.3 cm^4
     3        354.     2 - 16MM      1485.         4600.        NO   YES
   |   CRITICAL NEG MOMENT=     40.73 KN-MET  AT  4600.MM, LOAD  605|
          B E A M  N O.     6 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=    2.36 KNS  Vc=   84.02 KNS  Vs=    0.00 KNS
    Tu=    0.15 KN-MET  Tc=    3.2 KN-MET  Ts=    0.0 KN-MET  LOAD   500
                       STIRRUPS ARE NOT REQUIRED.
    AT END   SUPPORT - Vu=    7.56 KNS  Vc=   85.32 KNS  Vs=    0.00 KNS
  ___   6J____________________  4600X 300X  400_____________________   9J____
 | 2No12 H 356.   0.TO  851No16 H 354.1485.TO 4600                           |
 | 2No12 H  49.   0.TO 4600                                                  |
 |    oo     |   |           |   |    oo     |   |    oo     |   |    oo     |
 | 2#12      |   |           |   | 2#16      |   | 2#16      |   | 2#16      |
    STAAD SPACE                                              -- PAGE NO.   48
          ACI 318-11   BEAM  NO.     7   DESIGN RESULTS
   LEN -  4500. MM  FY -  415.  FC -  25.  MPA, SIZE -  300. X  400. MMS
     1         49.     3 - 12MM         0.         4500.        YES  YES
   |   CRITICAL POS MOMENT=     30.79 KN-MET  AT     0.MM, LOAD  611|
   |   REQD STEEL=   319.MM2, RHO=0.0030, RHOMX=0.0193 RHOMN=0.0033 |
     2        356.     4 - 12MM         0.         3093.        YES  NO
   |   CRITICAL NEG MOMENT=     53.51 KN-MET  AT     0.MM, LOAD  608|
   |   REQD STEEL=   418.MM2, RHO=0.0039, RHOMX=0.0193 RHOMN=0.0033 |
   |   MAX/MIN/ACTUAL BAR SPACING=   273./   37./   71. MMS         |
     Cracked Moment of Inertia Iz at above location =    34262.3 cm^4
     3        356.     2 - 12MM      2720.         4500.        NO   YES
   |   CRITICAL NEG MOMENT=     17.47 KN-MET  AT  4500.MM, LOAD  611|
   |   REQD STEEL=   177.MM2, RHO=0.0017, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.     7 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=    7.60 KNS  Vc=   87.06 KNS  Vs=    0.00 KNS
    Tu=    0.36 KN-MET  Tc=    3.2 KN-MET  Ts=    0.0 KN-MET  LOAD   500
    AT END   SUPPORT - Vu=    2.41 KNS  Vc=   87.06 KNS  Vs=    0.00 KNS
    STAAD SPACE                                              -- PAGE NO.   49
  ___   1J____________________  4500X 300X  400_____________________   2J____
 | 4No12 H 356.   0.TO 3093                    2No12 H 356.2720.TO 4500      |
 | 3No12 H  49.   0.TO 4500                                                  |
 |   oooo    |   |   oooo    |   |   oooo    |   |    oo     |   |    oo     |
 | 4#12      |   | 4#12      |   | 4#12      |   | 2#12      |   | 2#12      |
          ACI 318-11   BEAM  NO.     8   DESIGN RESULTS
     1         51.     2 - 16MM         0.         1500.        YES  YES
   |   CRITICAL POS MOMENT=     34.17 KN-MET  AT  1500.MM, LOAD  612|
   |   REQD STEEL=   348.MM2, RHO=0.0033, RHOMX=0.0193 RHOMN=0.0033 |
     Cracked Moment of Inertia Iz at above location =    29758.5 cm^4
   |   CRITICAL NEG MOMENT=     47.75 KN-MET  AT  1500.MM, LOAD  607|
   |   REQD STEEL=   374.MM2, RHO=0.0035, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.     8 D E S I G N  R E S U L T S - SHEAR
    STAAD SPACE                                              -- PAGE NO.   50
    AT START SUPPORT - Vu=    4.19 KNS  Vc=   86.56 KNS  Vs=    0.00 KNS
    AT END   SUPPORT - Vu=    6.25 KNS  Vc=   86.56 KNS  Vs=    0.00 KNS
  ___   2J____________________  1499X 300X  400_____________________   3J____
 | 2No16 H 354.   0.TO 1500                                                  |
 | 2No16 H  51.   0.TO 1500                                                  |
          ACI 318-11   BEAM  NO.    11   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     22.16 KN-MET  AT  4500.MM, LOAD  608|
   |   REQD STEEL=   228.MM2, RHO=0.0022, RHOMX=0.0193 RHOMN=0.0033 |
     2        354.     2 - 16MM         0.         2874.        YES  NO
    STAAD SPACE                                              -- PAGE NO.   51
   |   CRITICAL NEG MOMENT=     45.22 KN-MET  AT     0.MM, LOAD  608|
     3        356.     2 - 12MM      3095.         4500.        NO   YES
   |   CRITICAL NEG MOMENT=     10.25 KN-MET  AT  4500.MM, LOAD  611|
   |   REQD STEEL=   103.MM2, RHO=0.0010, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.    11 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   13.63 KNS  Vc=   87.02 KNS  Vs=    0.00 KNS
    Tu=    3.69 KN-MET  Tc=    3.2 KN-MET  Ts=    4.9 KN-MET  LOAD   605
    PROVIDE 12 MM 2-LEGGED STIRRUPS AT 143. MM  C/C FOR 1905. MM
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   1.01 SQ.CM.
    AT END   SUPPORT - Vu=    1.16 KNS  Vc=   87.02 KNS  Vs=    0.00 KNS
  ___   7J____________________  4500X 300X  400_____________________   8J____
 | 2No16 H 354.|  0.TO 2874|  |  |  |  |  |  |  |   2No12|H 356.3095.TO 4500 |
 | 15*12c/c143 |  |  |  |  |  |  |  |  |  |  |  |     |  |  | 15*12c/c143  | |
 | 3No12 H  49.|  0.TO 4500|  |  |  |  |  |  |  |     |  |  |  |  |  |  |  | |
 | 2#16      |   | 2#16      |   | 2#16      |   | 2#12      |   | 2#12      |
    STAAD SPACE                                              -- PAGE NO.   52
          ACI 318-11   BEAM  NO.    12   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     24.63 KN-MET  AT  1500.MM, LOAD  612|
   |   REQD STEEL=   254.MM2, RHO=0.0024, RHOMX=0.0193 RHOMN=0.0033 |
   |   CRITICAL NEG MOMENT=     49.15 KN-MET  AT  1500.MM, LOAD  607|
   |   REQD STEEL=   385.MM2, RHO=0.0036, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.    12 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   19.70 KNS  Vc=   86.94 KNS  Vs=    0.00 KNS
    Tu=   10.30 KN-MET  Tc=    3.2 KN-MET  Ts=   13.7 KN-MET  LOAD   605
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   2.80 SQ.CM.
    AT END   SUPPORT - Vu=   22.72 KNS  Vc=   86.94 KNS  Vs=    0.00 KNS
    STAAD SPACE                                              -- PAGE NO.   53
  ___   8J____________________  1499X 300X  400_____________________   9J____
          ACI 318-11   BEAM  NO.    13   DESIGN RESULTS
   LEN -  3350. MM  FY -  415.  FC -  25.  MPA, SIZE -  300. X  400. MMS
     1         49.     4 - 12MM         0.         3350.        YES  YES
   |   CRITICAL POS MOMENT=     52.81 KN-MET  AT  3350.MM, LOAD  600|
   |   REQD STEEL=   419.MM2, RHO=0.0040, RHOMX=0.0193 RHOMN=0.0033 |
     Cracked Moment of Inertia Iz at above location =    33227.6 cm^4
     2        354.     3 - 16MM         0.         2578.        YES  NO
   |   CRITICAL NEG MOMENT=     73.76 KN-MET  AT     0.MM, LOAD  606|
   |   REQD STEEL=   589.MM2, RHO=0.0055, RHOMX=0.0193 RHOMN=0.0033 |
   |   MAX/MIN/ACTUAL BAR SPACING=   273./   41./  104. MMS         |
     Cracked Moment of Inertia Iz at above location =    42844.9 cm^4
          B E A M  N O.    13 D E S I G N  R E S U L T S - SHEAR
    STAAD SPACE                                              -- PAGE NO.   54
    AT START SUPPORT - Vu=   36.04 KNS  Vc=   86.40 KNS  Vs=    0.00 KNS
    Tu=   12.28 KN-MET  Tc=    3.2 KN-MET  Ts=   16.4 KN-MET  LOAD   608
    PROVIDE 12 MM 2-LEGGED STIRRUPS AT 143. MM  C/C FOR 1330. MM
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   3.34 SQ.CM.
    AT END   SUPPORT - Vu=    8.47 KNS  Vc=   86.40 KNS  Vs=    0.00 KNS
  ___  10J____________________  3350X 300X  400_____________________  64J____
 | 3No16 H 354.|  0.TO 2578|   |   |   |   |   |   |   |   |                 |
 | 11*12c/c143 |   |   |   |   |   |   |   |   |   |   |   |  11*12c/c143    |
 | 4No12 H |49.|  0.TO 3350|   |   |   |   |   |   |   |   |                 |
 |    ooo    |   |    ooo    |   |    ooo    |   |    ooo    |   |           |
 | 3#16      |   | 3#16      |   | 3#16      |   | 3#16      |   |           |
 | 4#12      |   | 4#12      |   | 4#12      |   | 4#12      |   | 4#12      |
 |   oooo    |   |   oooo    |   |   oooo    |   |   oooo    |   |   oooo    |
          ACI 318-11   BEAM  NO.    14   DESIGN RESULTS
     1         51.     2 - 16MM         0.         4600.        YES  YES
   |   CRITICAL POS MOMENT=     37.56 KN-MET  AT  4600.MM, LOAD  610|
    STAAD SPACE                                              -- PAGE NO.   55
     2        354.     3 - 16MM         0.         2157.        YES  NO
   |   CRITICAL NEG MOMENT=     71.72 KN-MET  AT     0.MM, LOAD  606|
   |   REQD STEEL=   572.MM2, RHO=0.0054, RHOMX=0.0193 RHOMN=0.0033 |
     3        356.     5 - 12MM      2024.         4600.        NO   YES
   |   CRITICAL NEG MOMENT=     60.27 KN-MET  AT  4600.MM, LOAD  605|
   |   REQD STEEL=   473.MM2, RHO=0.0044, RHOMX=0.0193 RHOMN=0.0033 |
   |   MAX/MIN/ACTUAL BAR SPACING=   273./   37./   53. MMS         |
   |   REQD. DEVELOPMENT LENGTH =   406. MMS                       |
     Cracked Moment of Inertia Iz at above location =    41156.5 cm^4
          B E A M  N O.    14 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   41.86 KNS  Vc=   86.36 KNS  Vs=    0.00 KNS
    Tu=    1.15 KN-MET  Tc=    3.2 KN-MET  Ts=    0.0 KN-MET  LOAD   600
    NO STIRRUPS ARE REQUIRED FOR TORSION.
    PROVIDE 12 MM 2-LEGGED STIRRUPS AT 175. MM  C/C FOR 1955. MM
    AT END   SUPPORT - Vu=   39.18 KNS  Vc=   87.06 KNS  Vs=    0.00 KNS
    Tu=    0.79 KN-MET  Tc=    3.2 KN-MET  Ts=    0.0 KN-MET  LOAD   605
    STAAD SPACE                                              -- PAGE NO.   56
  ___  11J____________________  4600X 300X  400_____________________  12J____
 | 3No16 H 354.|  0.TO 2157|  |  | 5No12 H|356.2024.TO|4600 |  |  |  |  |  | |
 | 13*12c/c175 |  |  |  |  |  |  |  |  |  |  |  |  |  |  |  | 13*12c/c175  | |
 | 2No16 H  51.|  0.TO 4600|  |  |  |  |  |  |  |  |  |  |  |  |  |  |  |  | |
 |    ooo    |   |    ooo    |   |   ooooo   |   |   ooooo   |   |   ooooo   |
 | 3#16      |   | 3#16      |   | 5#12      |   | 5#12      |   | 5#12      |
          ACI 318-11   BEAM  NO.    15   DESIGN RESULTS
     1         51.     2 - 16MM         0.         3350.        YES  YES
   |   CRITICAL POS MOMENT=     33.30 KN-MET  AT  1954.MM, LOAD  600|
     2        356.     2 - 12MM         0.          747.        YES  NO
   |   CRITICAL NEG MOMENT=      7.58 KN-MET  AT     0.MM, LOAD  606|
   |   REQD STEEL=    76.MM2, RHO=0.0007, RHOMX=0.0193 RHOMN=0.0033 |
     3        356.     2 - 12MM      2463.         3350.        NO   YES
    STAAD SPACE                                              -- PAGE NO.   57
   |   CRITICAL NEG MOMENT=      6.27 KN-MET  AT  3350.MM, LOAD  611|
   |   REQD STEEL=    63.MM2, RHO=0.0006, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.    15 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   23.89 KNS  Vc=   92.28 KNS  Vs=    0.00 KNS
    Tu=    6.10 KN-MET  Tc=    3.2 KN-MET  Ts=    8.1 KN-MET  LOAD   608
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   1.66 SQ.CM.
    AT END   SUPPORT - Vu=   11.41 KNS  Vc=   83.92 KNS  Vs=    0.00 KNS
  ___  13J____________________  3350X 300X  400_____________________  57J____
 | 2No12 H 356.|  0.TO  747                         2No12 H|356.2463.TO|3350 |
 | 11*12c/c143 |                                           |  11*12c/c143  | |
 | 2No16 H |51.|  0.TO 3350                                |   |   |   |   | |
 |    oo     |   |           |   |           |   |    oo     |   |    oo     |
 | 2#12      |   |           |   |           |   | 2#12      |   | 2#12      |
    STAAD SPACE                                              -- PAGE NO.   58
          ACI 318-11   BEAM  NO.    16   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     37.03 KN-MET  AT  2683.MM, LOAD  600|
     2        356.     6 - 12MM         0.         2384.        YES  NO
   |   CRITICAL NEG MOMENT=     83.26 KN-MET  AT     0.MM, LOAD  600|
   |   REQD STEEL=   670.MM2, RHO=0.0063, RHOMX=0.0193 RHOMN=0.0033 |
   |   MAX/MIN/ACTUAL BAR SPACING=   273./   37./   43. MMS         |
   |   REQD. DEVELOPMENT LENGTH =   508. MMS                       |
     Cracked Moment of Inertia Iz at above location =    47065.5 cm^4
     3        356.     2 - 12MM      3557.         4600.        NO   YES
   |   CRITICAL NEG MOMENT=     13.28 KN-MET  AT  4600.MM, LOAD  605|
   |   REQD STEEL=   134.MM2, RHO=0.0013, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.    16 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   42.77 KNS  Vc=   85.78 KNS  Vs=    0.00 KNS
    Tu=    7.50 KN-MET  Tc=    3.2 KN-MET  Ts=   10.0 KN-MET  LOAD   607
    PROVIDE 12 MM 2-LEGGED STIRRUPS AT 143. MM  C/C FOR 1955. MM
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   2.04 SQ.CM.
    STAAD SPACE                                              -- PAGE NO.   59
    AT END   SUPPORT - Vu=   24.38 KNS  Vc=   92.57 KNS  Vs=    0.00 KNS
  ___  14J____________________  4600X 300X  400_____________________  15J____
 | 6No12 H 356.|  0.TO 2384|  |  |  |  |            2No12 H 356.3557.TO 4600 |
 | 15*12c/c143 |  |  |  |  |  |  |  |  |                    | 15*12c/c143  | |
 |  oooooo   |   |  oooooo   |   |  oooooo   |   |           |   |    oo     |
 | 6#12      |   | 6#12      |   | 6#12      |   |           |   | 2#12      |
          ACI 318-11   BEAM  NO.    19   DESIGN RESULTS
     1         51.     2 - 16MM         0.         4500.        YES  YES
   |   CRITICAL POS MOMENT=     48.98 KN-MET  AT  3375.MM, LOAD  600|
   |   REQD STEEL=   390.MM2, RHO=0.0037, RHOMX=0.0193 RHOMN=0.0033 |
     2        354.     4 - 16MM         0.         2874.        YES  NO
   |   CRITICAL NEG MOMENT=     94.96 KN-MET  AT     0.MM, LOAD  608|
   |   REQD STEEL=   772.MM2, RHO=0.0073, RHOMX=0.0193 RHOMN=0.0033 |
   |   MAX/MIN/ACTUAL BAR SPACING=   273./   41./   70. MMS         |
   |   REQD. DEVELOPMENT LENGTH =   552. MMS                       |
    STAAD SPACE                                              -- PAGE NO.   60
     Cracked Moment of Inertia Iz at above location =    53814.1 cm^4
     3        356.     2 - 12MM      3845.         4500.        NO   YES
   |   CRITICAL NEG MOMENT=      5.81 KN-MET  AT  4500.MM, LOAD  611|
   |   REQD STEEL=    58.MM2, RHO=0.0005, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.    19 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   54.52 KNS  Vc=   85.51 KNS  Vs=    0.00 KNS
    Tu=    0.07 KN-MET  Tc=    3.1 KN-MET  Ts=    0.0 KN-MET  LOAD   600
    PROVIDE 12 MM 2-LEGGED STIRRUPS AT 175. MM  C/C FOR 1905. MM
    AT END   SUPPORT - Vu=    9.54 KNS  Vc=   86.38 KNS  Vs=    0.00 KNS
    Tu=    4.60 KN-MET  Tc=    3.2 KN-MET  Ts=    6.1 KN-MET  LOAD   605
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   1.25 SQ.CM.
  ___  10J____________________  4500X 300X  400_____________________  13J____
 | 4No16 H 354.|  0.TO 2874|  |  |  |  |  |  |  |   2No12 H 356.3845.TO 4500 |
 | 12*12c/c175 |  |  |  |  |  |  |  |  |  |  |  |             15*12c/c143  | |
 | 2No16 H  51.|  0.TO 4500|  |  |  |  |  |  |  |                 |  |  |  | |
 |   oooo    |   |   oooo    |   |   oooo    |   |           |   |    oo     |
 | 4#16      |   | 4#16      |   | 4#16      |   |           |   | 2#12      |
    STAAD SPACE                                              -- PAGE NO.   61
          ACI 318-11   BEAM  NO.    21   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     40.49 KN-MET  AT  2250.MM, LOAD  600|
     2        352.     2 - 20MM         0.         2280.        YES  NO
   |   CRITICAL NEG MOMENT=     75.19 KN-MET  AT     0.MM, LOAD  608|
   |   REQD STEEL=   605.MM2, RHO=0.0057, RHOMX=0.0193 RHOMN=0.0033 |
   |   MAX/MIN/ACTUAL BAR SPACING=   273./   45./  205. MMS         |
   |   REQD. DEVELOPMENT LENGTH =   600. MMS                       |
     Cracked Moment of Inertia Iz at above location =    43715.6 cm^4
     3        356.     5 - 12MM      2345.         4500.        NO   YES
   |   CRITICAL NEG MOMENT=     68.40 KN-MET  AT  4500.MM, LOAD  607|
   |   REQD STEEL=   541.MM2, RHO=0.0051, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.    21 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   54.40 KNS  Vc=   85.00 KNS  Vs=    0.00 KNS
    Tu=    1.48 KN-MET  Tc=    3.1 KN-MET  Ts=    0.0 KN-MET  LOAD   600
    STAAD SPACE                                              -- PAGE NO.   62
    AT END   SUPPORT - Vu=   52.61 KNS  Vc=   85.00 KNS  Vs=    0.00 KNS
  ___  11J____________________  4500X 300X  400_____________________  14J____
 | 2No20 H 352.|  0.TO 2280|  |  |  |    5No12 H|356.2345.TO|4500 |  |  |  | |
 | 12*12c/c175 |  |  |  |  |  |  |  |     |  |  |  |  |  |  | 12*12c/c175  | |
 | 2No16 H  51.|  0.TO 4500|  |  |  |     |  |  |  |  |  |  |  |  |  |  |  | |
 |    oo     |   |    oo     |   |    oo     |   |   ooooo   |   |   ooooo   |
 | 2#20      |   | 2#20      |   | 2#20      |   | 5#12      |   | 5#12      |
          ACI 318-11   BEAM  NO.    22   DESIGN RESULTS
   LEN -  1500. MM  FY -  415.  FC -  25.  MPA, SIZE -  200. X  350. MMS
     1         49.     2 - 12MM       687.          876.        NO   NO
   |   CRITICAL POS MOMENT=      0.05 KN-MET  AT   750.MM, LOAD  611|
   |   REQD STEEL=     1.MM2, RHO=0.0000, RHOMX=0.0193 RHOMN=0.0033 |
   |   MAX/MIN/ACTUAL BAR SPACING=   273./   37./  113. MMS         |
     Cracked Moment of Inertia Iz at above location =    12494.8 cm^4
     2         49.     2 - 12MM       910.         1500.        NO   YES
   |   CRITICAL POS MOMENT=      8.01 KN-MET  AT  1500.MM, LOAD  608|
   |   REQD STEEL=    96.MM2, RHO=0.0016, RHOMX=0.0193 RHOMN=0.0033 |
    STAAD SPACE                                              -- PAGE NO.   63
     3        306.     3 - 12MM         0.         1500.        YES  YES
   |   CRITICAL NEG MOMENT=     31.22 KN-MET  AT     0.MM, LOAD  608|
   |   REQD STEEL=   286.MM2, RHO=0.0047, RHOMX=0.0193 RHOMN=0.0033 |
   |   MAX/MIN/ACTUAL BAR SPACING=   273./   37./   56. MMS         |
   |   REQD. DEVELOPMENT LENGTH =   383. MMS                       |
     Cracked Moment of Inertia Iz at above location =    18091.4 cm^4
          B E A M  N O.    22 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   17.76 KNS  Vc=   50.11 KNS  Vs=    0.00 KNS
    Tu=    7.83 KN-MET  Tc=    1.4 KN-MET  Ts=   10.4 KN-MET  LOAD   606
    PROVIDE 12 MM 2-LEGGED STIRRUPS AT 105. MM  C/C FOR  455. MM
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   3.19 SQ.CM.
    AT END   SUPPORT - Vu=    9.70 KNS  Vc=   50.11 KNS  Vs=    0.00 KNS
  ___  14J____________________  1499X 200X  350_____________________  17J____
 | 3No12 H 306.   0.TO 1500                  |     |     |     |     |     | |
 |  6*12c/c105                               |     |     |     6*12c/c105  | |
 |                                  2No12 H  49.2687.TO  876 910.TO 1500   | |
  _______          _______          _______          _______          _______
 |       |        |       |        | 2#12  |        | 2#12  |        | 2#12  |
 |       |        |       |        |  oo   |        |  oo   |        |  oo   |
 |_______|        |_______|        |_______|        |_______|        |_______|
    STAAD SPACE                                              -- PAGE NO.   64
          ACI 318-11   BEAM  NO.    23   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     47.59 KN-MET  AT  3000.MM, LOAD  600|
   |   REQD STEEL=   378.MM2, RHO=0.0036, RHOMX=0.0193 RHOMN=0.0033 |
     2        352.     2 - 20MM         0.         2655.        YES  NO
   |   CRITICAL NEG MOMENT=     77.81 KN-MET  AT     0.MM, LOAD  608|
   |   REQD STEEL=   620.MM2, RHO=0.0058, RHOMX=0.0193 RHOMN=0.0033 |
     Cracked Moment of Inertia Iz at above location =    44814.0 cm^4
   |   CRITICAL NEG MOMENT=      2.40 KN-MET  AT  4500.MM, LOAD  611|
   |   REQD STEEL=    24.MM2, RHO=0.0002, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.    23 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   38.60 KNS  Vc=   86.15 KNS  Vs=    0.00 KNS
    Tu=    5.69 KN-MET  Tc=    3.2 KN-MET  Ts=    7.6 KN-MET  LOAD   605
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   1.55 SQ.CM.
    STAAD SPACE                                              -- PAGE NO.   65
    AT END   SUPPORT - Vu=    8.48 KNS  Vc=   86.15 KNS  Vs=    0.00 KNS
  ___  12J____________________  4500X 300X  400_____________________  15J____
 | 2No20 H 352.|  0.TO 2655|  |  |  |  |  |  |      2No12 H 356.3845.TO 4500 |
 | 15*12c/c143 |  |  |  |  |  |  |  |  |  |  |                15*12c/c143  | |
 |    oo     |   |    oo     |   |    oo     |   |           |   |    oo     |
 | 2#20      |   | 2#20      |   | 2#20      |   |           |   | 2#12      |
          ACI 318-11   BEAM  NO.    24   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     35.72 KN-MET  AT     0.MM, LOAD  600|
   |   REQD STEEL=   338.MM2, RHO=0.0057, RHOMX=0.0193 RHOMN=0.0033 |
     Cracked Moment of Inertia Iz at above location =    17196.9 cm^4
     2        302.     3 - 20MM         0.         1500.        YES  YES
   |   CRITICAL NEG MOMENT=     65.79 KN-MET  AT  1500.MM, LOAD  607|
   |   REQD STEEL=   651.MM2, RHO=0.0108, RHOMX=0.0193 RHOMN=0.0033 |
   |   MAX/MIN/ACTUAL BAR SPACING=   273./   45./   52. MMS         |
   |   REQD. DEVELOPMENT LENGTH =  1147. MMS                       |
    STAAD SPACE                                              -- PAGE NO.   66
     Cracked Moment of Inertia Iz at above location =    37981.1 cm^4
          B E A M  N O.    24 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   43.39 KNS  Vc=   49.08 KNS  Vs=    8.77 KNS
    Tu=    7.59 KN-MET  Tc=    1.4 KN-MET  Ts=   10.1 KN-MET  LOAD   605
    STIRRUPS ARE REQUIRED FOR SHEAR AND TORSION.
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   3.09 SQ.CM.
    AT END   SUPPORT - Vu=   48.41 KNS  Vc=   49.08 KNS  Vs=   15.46 KNS
  ___  15J____________________  1499X 200X  350_____________________  18J____
 | 3No20 H 302.|  0.TO 1500|     |           |     |     |     |     |     | |
 |  6*12c/c105 |     |     |     |           |     |     |     6*12c/c105  | |
 | 3No12 H  49.|  0.TO 1500|     |           |     |     |     |     |     | |
 | 3#20  |        | 3#20  |        | 3#20  |        | 3#20  |        | 3#20  |
          ACI 318-11   BEAM  NO.    25   DESIGN RESULTS
    STAAD SPACE                                              -- PAGE NO.   67
   |   CRITICAL POS MOMENT=     53.48 KN-MET  AT  3350.MM, LOAD  600|
   |   REQD STEEL=   424.MM2, RHO=0.0040, RHOMX=0.0193 RHOMN=0.0033 |
     2        356.     5 - 12MM         0.         2143.        YES  NO
   |   CRITICAL NEG MOMENT=     65.47 KN-MET  AT     0.MM, LOAD  606|
   |   REQD STEEL=   516.MM2, RHO=0.0048, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.    25 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   36.39 KNS  Vc=   87.55 KNS  Vs=    0.00 KNS
    Tu=   12.46 KN-MET  Tc=    3.2 KN-MET  Ts=   16.6 KN-MET  LOAD   608
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   3.39 SQ.CM.
    AT END   SUPPORT - Vu=    8.82 KNS  Vc=   83.90 KNS  Vs=    0.00 KNS
  ___  19J____________________  3350X 300X  400_____________________  65J____
 | 5No12 H 356.|  0.TO 2143|   |   |   |   |   |                             |
 | 11*12c/c143 |   |   |   |   |   |   |   |   |              11*12c/c143    |
 |   ooooo   |   |   ooooo   |   |   ooooo   |   |           |   |           |
 | 5#12      |   | 5#12      |   | 5#12      |   |           |   |           |
    STAAD SPACE                                              -- PAGE NO.   68
          ACI 318-11   BEAM  NO.    26   DESIGN RESULTS
     1         49.     3 - 12MM         0.         4600.        YES  YES
   |   CRITICAL POS MOMENT=     26.02 KN-MET  AT  4600.MM, LOAD  610|
   |   REQD STEEL=   269.MM2, RHO=0.0026, RHOMX=0.0193 RHOMN=0.0033 |
     2        356.     5 - 12MM         0.         2001.        YES  NO
   |   CRITICAL NEG MOMENT=     61.33 KN-MET  AT     0.MM, LOAD  606|
   |   REQD STEEL=   482.MM2, RHO=0.0045, RHOMX=0.0193 RHOMN=0.0033 |
     3        354.     2 - 16MM      1868.         4600.        NO   YES
   |   CRITICAL NEG MOMENT=     49.85 KN-MET  AT  4600.MM, LOAD  605|
   |   REQD STEEL=   391.MM2, RHO=0.0037, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.    26 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   41.29 KNS  Vc=   87.41 KNS  Vs=    0.00 KNS
    Tu=    0.56 KN-MET  Tc=    3.2 KN-MET  Ts=    0.0 KN-MET  LOAD   600
    PROVIDE 12 MM 2-LEGGED STIRRUPS AT 176. MM  C/C FOR 1955. MM
    STAAD SPACE                                              -- PAGE NO.   69
    AT END   SUPPORT - Vu=   34.96 KNS  Vc=   87.46 KNS  Vs=    0.00 KNS
    Tu=    0.41 KN-MET  Tc=    3.2 KN-MET  Ts=    0.0 KN-MET  LOAD   605
  ___  20J____________________  4600X 300X  400_____________________  21J____
 | 5No12 H 356.|  0.TO 2001|  | 2No16 H|354.1868.TO|4600 |  |  |  |  |  |  | |
 | 13*12c/c176 |  |  |  |  |  |  |  |  |  |  |  |  |  |  |  | 13*12c/c176  | |
 | 3No12 H  49.|  0.TO 4600|  |  |  |  |  |  |  |  |  |  |  |  |  |  |  |  | |
 |   ooooo   |   |   ooooo   |   |    oo     |   |    oo     |   |    oo     |
 | 5#12      |   | 5#12      |   | 2#16      |   | 2#16      |   | 2#16      |
          ACI 318-11   BEAM  NO.    27   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     33.16 KN-MET  AT  1954.MM, LOAD  600|
   |   REQD STEEL=   347.MM2, RHO=0.0033, RHOMX=0.0193 RHOMN=0.0033 |
   |   CRITICAL NEG MOMENT=      7.45 KN-MET  AT     0.MM, LOAD  606|
   |   REQD STEEL=    75.MM2, RHO=0.0007, RHOMX=0.0193 RHOMN=0.0033 |
    STAAD SPACE                                              -- PAGE NO.   70
     3        356.     2 - 12MM      2743.         3350.        NO   YES
   |   CRITICAL NEG MOMENT=      1.93 KN-MET  AT  3350.MM, LOAD  611|
   |   REQD STEEL=    19.MM2, RHO=0.0002, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.    27 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   23.13 KNS  Vc=   86.70 KNS  Vs=    0.00 KNS
    Tu=    6.17 KN-MET  Tc=    3.2 KN-MET  Ts=    8.2 KN-MET  LOAD   608
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   1.68 SQ.CM.
    AT END   SUPPORT - Vu=   12.18 KNS  Vc=   86.70 KNS  Vs=    0.00 KNS
  ___  22J____________________  3350X 300X  400_____________________  67J____
 | 2No12 H 356.|  0.TO  747                         2No12 H 356.2743.TO|3350 |
 | 11*12c/c143 |                                              11*12c/c143  | |
 |    oo     |   |           |   |           |   |           |   |    oo     |
 | 2#12      |   |           |   |           |   |           |   | 2#12      |
    STAAD SPACE                                              -- PAGE NO.   71
          ACI 318-11   BEAM  NO.    28   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     38.74 KN-MET  AT  2683.MM, LOAD  600|
     2        352.     2 - 20MM         0.         2696.        YES  NO
   |   CRITICAL NEG MOMENT=     76.78 KN-MET  AT     0.MM, LOAD  600|
   |   REQD STEEL=   619.MM2, RHO=0.0059, RHOMX=0.0193 RHOMN=0.0033 |
   |   CRITICAL NEG MOMENT=     11.12 KN-MET  AT  4600.MM, LOAD  605|
   |   REQD STEEL=   112.MM2, RHO=0.0010, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.    28 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   42.38 KNS  Vc=   85.86 KNS  Vs=    0.00 KNS
    Tu=    6.46 KN-MET  Tc=    3.2 KN-MET  Ts=    8.6 KN-MET  LOAD   607
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   1.76 SQ.CM.
    STAAD SPACE                                              -- PAGE NO.   72
    AT END   SUPPORT - Vu=   24.76 KNS  Vc=   93.32 KNS  Vs=    0.00 KNS
  ___  23J____________________  4600X 300X  400_____________________  24J____
 | 2No20 H 352.|  0.TO 2696|  |  |  |  |  |  |      2No12 H 356.3557.TO 4600 |
 | 15*12c/c143 |  |  |  |  |  |  |  |  |  |  |              | 15*12c/c143  | |
          ACI 318-11   BEAM  NO.    31   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     44.27 KN-MET  AT  3375.MM, LOAD  600|
   |   REQD STEEL=   351.MM2, RHO=0.0033, RHOMX=0.0193 RHOMN=0.0033 |
   |   CRITICAL NEG MOMENT=     90.28 KN-MET  AT     0.MM, LOAD  608|
   |   REQD STEEL=   731.MM2, RHO=0.0069, RHOMX=0.0193 RHOMN=0.0033 |
    STAAD SPACE                                              -- PAGE NO.   73
   |   CRITICAL NEG MOMENT=      2.25 KN-MET  AT  4500.MM, LOAD  611|
   |   REQD STEEL=    23.MM2, RHO=0.0002, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.    31 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   56.24 KNS  Vc=   83.75 KNS  Vs=    0.00 KNS
    Tu=    1.12 KN-MET  Tc=    3.1 KN-MET  Ts=    0.0 KN-MET  LOAD   600
    AT END   SUPPORT - Vu=    3.81 KNS  Vc=   84.88 KNS  Vs=    0.00 KNS
    Tu=    4.10 KN-MET  Tc=    3.1 KN-MET  Ts=    5.5 KN-MET  LOAD   606
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   1.12 SQ.CM.
  ___  19J____________________  4500X 300X  400_____________________  22J____
    STAAD SPACE                                              -- PAGE NO.   74
          ACI 318-11   BEAM  NO.    32   DESIGN RESULTS
   LEN -   900. MM  FY -  415.  FC -  25.  MPA, SIZE -  200. X  350. MMS
     1         51.     2 - 16MM         0.          900.        YES  YES
   |   CRITICAL POS MOMENT=     35.85 KN-MET  AT     0.MM, LOAD  608|
   |   REQD STEEL=   339.MM2, RHO=0.0057, RHOMX=0.0193 RHOMN=0.0033 |
   |   MAX/MIN/ACTUAL BAR SPACING=   273./   41./  109. MMS         |
     Cracked Moment of Inertia Iz at above location =    19700.8 cm^4
     2        306.     3 - 12MM         0.          900.        YES  YES
   |   CRITICAL NEG MOMENT=     30.55 KN-MET  AT   900.MM, LOAD  607|
   |   REQD STEEL=   279.MM2, RHO=0.0046, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.    32 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   46.39 KNS  Vc=   46.02 KNS  Vs=   15.83 KNS
    Tu=    4.20 KN-MET  Tc=    1.3 KN-MET  Ts=    5.6 KN-MET  LOAD   600
    PROVIDE 12 MM 2-LEGGED STIRRUPS AT 105. MM  C/C FOR  155. MM
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   1.71 SQ.CM.
    AT END   SUPPORT - Vu=   48.54 KNS  Vc=   46.02 KNS  Vs=   18.71 KNS
    STAAD SPACE                                              -- PAGE NO.   75
  ___  22J____________________   899X 200X  350_____________________  77J____
 | 3No12 H 306.   0.TO  900                              |        |        | |
 |  3*12c/c105       |                                   |     3*12c/c105  | |
 | 2No16 H  51.   0.TO  900                              |        |        | |
          ACI 318-11   BEAM  NO.    33   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     39.04 KN-MET  AT  2250.MM, LOAD  600|
     2        356.     5 - 12MM         0.         1968.        YES  NO
   |   CRITICAL NEG MOMENT=     66.92 KN-MET  AT     0.MM, LOAD  608|
   |   REQD STEEL=   528.MM2, RHO=0.0049, RHOMX=0.0193 RHOMN=0.0033 |
    STAAD SPACE                                              -- PAGE NO.   76
   |   CRITICAL NEG MOMENT=     59.77 KN-MET  AT  4500.MM, LOAD  607|
   |   REQD STEEL=   469.MM2, RHO=0.0044, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.    33 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   55.19 KNS  Vc=   87.95 KNS  Vs=    0.00 KNS
    Tu=    2.00 KN-MET  Tc=    3.2 KN-MET  Ts=    0.0 KN-MET  LOAD   600
    AT END   SUPPORT - Vu=   51.82 KNS  Vc=   89.55 KNS  Vs=    0.00 KNS
  ___  20J____________________  4500X 300X  400_____________________  23J____
 | 5No12 H 356.|  0.TO 1968|  |  |       5No12 H|356.2345.TO|4500 |  |  |  | |
 | 12*12c/c175 |  |  |  |  |  |  |        |  |  |  |  |  |  | 12*12c/c175  | |
 |   ooooo   |   |   ooooo   |   |           |   |   ooooo   |   |   ooooo   |
 | 5#12      |   | 5#12      |   |           |   | 5#12      |   | 5#12      |
    STAAD SPACE                                              -- PAGE NO.   77
          ACI 318-11   BEAM  NO.    34   DESIGN RESULTS
     1         49.     2 - 12MM       191.         1500.        NO   YES
   |   CRITICAL POS MOMENT=      6.40 KN-MET  AT  1500.MM, LOAD  608|
   |   REQD STEEL=    76.MM2, RHO=0.0013, RHOMX=0.0193 RHOMN=0.0033 |
     2        306.     3 - 12MM         0.         1485.        YES  NO
   |   CRITICAL NEG MOMENT=     26.17 KN-MET  AT     0.MM, LOAD  608|
   |   REQD STEEL=   238.MM2, RHO=0.0039, RHOMX=0.0193 RHOMN=0.0033 |
     3        306.     2 - 12MM      1078.         1500.        NO   YES
   |   CRITICAL NEG MOMENT=      0.09 KN-MET  AT  1500.MM, LOAD  611|
     Cracked Moment of Inertia Iz at above location =    12946.8 cm^4
          B E A M  N O.    34 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   15.87 KNS  Vc=   48.34 KNS  Vs=    0.00 KNS
    Tu=    6.45 KN-MET  Tc=    1.4 KN-MET  Ts=    8.6 KN-MET  LOAD   606
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   2.63 SQ.CM.
    STAAD SPACE                                              -- PAGE NO.   78
    AT END   SUPPORT - Vu=    7.67 KNS  Vc=   49.75 KNS  Vs=    0.00 KNS
  ___  23J____________________  1499X 200X  350_____________________  26J____
 | 3No12 H 306.|  0.TO 1485|     |           |     |2No12|H 306.1078.TO 1500 |
 |         2No12 H  49. 191.TO 1500          |     |     |     |     |     | |
 |  ooo  |        |  ooo  |        |  ooo  |        |  ooo  |        |  oo   |
 | 3#12  |        | 3#12  |        | 3#12  |        | 2#12  |        | 2#12  |
 |       |        | 2#12  |        | 2#12  |        | 2#12  |        | 2#12  |
 |       |        |  oo   |        |  oo   |        |  oo   |        |  oo   |
          ACI 318-11   BEAM  NO.    35   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     45.27 KN-MET  AT  3000.MM, LOAD  600|
   |   REQD STEEL=   359.MM2, RHO=0.0034, RHOMX=0.0193 RHOMN=0.0033 |
     2        356.     5 - 12MM         0.         2343.        YES  NO
   |   CRITICAL NEG MOMENT=     67.39 KN-MET  AT     0.MM, LOAD  608|
   |   REQD STEEL=   532.MM2, RHO=0.0050, RHOMX=0.0193 RHOMN=0.0033 |
    STAAD SPACE                                              -- PAGE NO.   79
          B E A M  N O.    35 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   54.43 KNS  Vc=   86.33 KNS  Vs=    0.00 KNS
    Tu=    2.38 KN-MET  Tc=    3.2 KN-MET  Ts=    0.0 KN-MET  LOAD   600
    AT END   SUPPORT - Vu=    8.89 KNS  Vc=   86.64 KNS  Vs=    0.00 KNS
    Tu=    5.17 KN-MET  Tc=    3.2 KN-MET  Ts=    6.9 KN-MET  LOAD   605
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   1.41 SQ.CM.
  ___  21J____________________  4500X 300X  400_____________________  24J____
 | 5No12 H 356.|  0.TO 2343|  |  |  |  |                                     |
 | 12*12c/c175 |  |  |  |  |  |  |  |  |                      15*12c/c143    |
          ACI 318-11   BEAM  NO.    36   DESIGN RESULTS
    STAAD SPACE                                              -- PAGE NO.   80
   |   CRITICAL POS MOMENT=     33.90 KN-MET  AT     0.MM, LOAD  600|
   |   REQD STEEL=   318.MM2, RHO=0.0053, RHOMX=0.0193 RHOMN=0.0033 |
     Cracked Moment of Inertia Iz at above location =    17450.1 cm^4
     2        304.     3 - 16MM         0.         1500.        YES  YES
   |   CRITICAL NEG MOMENT=     58.86 KN-MET  AT  1500.MM, LOAD  607|
   |   REQD STEEL=   570.MM2, RHO=0.0094, RHOMX=0.0193 RHOMN=0.0033 |
   |   MAX/MIN/ACTUAL BAR SPACING=   273./   41./   54. MMS         |
   |   REQD. DEVELOPMENT LENGTH =   707. MMS                       |
     Cracked Moment of Inertia Iz at above location =    27936.3 cm^4
          B E A M  N O.    36 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   42.87 KNS  Vc=   49.43 KNS  Vs=    7.73 KNS
    Tu=    5.96 KN-MET  Tc=    1.4 KN-MET  Ts=    7.9 KN-MET  LOAD   605
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   2.43 SQ.CM.
    AT END   SUPPORT - Vu=   48.03 KNS  Vc=   49.43 KNS  Vs=   14.62 KNS
  ___  24J____________________  1499X 200X  350_____________________  27J____
 | 3No16 H 304.|  0.TO 1500|     |           |     |     |     |     |     | |
 | 3#16  |        | 3#16  |        | 3#16  |        | 3#16  |        | 3#16  |
    STAAD SPACE                                              -- PAGE NO.   81
          ACI 318-11   BEAM  NO.    37   DESIGN RESULTS
   LEN -  3350. MM  FY -  415.  FC -  25.  MPA, SIZE -  200. X  350. MMS
     1         49.     3 - 12MM         0.         3350.        YES  YES
   |   CRITICAL POS MOMENT=     34.29 KN-MET  AT  3350.MM, LOAD  600|
   |   REQD STEEL=   321.MM2, RHO=0.0053, RHOMX=0.0193 RHOMN=0.0033 |
     2        306.     4 - 12MM         0.         2035.        YES  NO
   |   CRITICAL NEG MOMENT=     43.82 KN-MET  AT     0.MM, LOAD  606|
   |   REQD STEEL=   410.MM2, RHO=0.0067, RHOMX=0.0193 RHOMN=0.0033 |
   |   MAX/MIN/ACTUAL BAR SPACING=   273./   37./   38. MMS         |
   |   REQD. DEVELOPMENT LENGTH =   575. MMS                       |
     Cracked Moment of Inertia Iz at above location =    22738.5 cm^4
          B E A M  N O.    37 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   24.86 KNS  Vc=   49.64 KNS  Vs=    0.00 KNS
    Tu=    4.77 KN-MET  Tc=    1.4 KN-MET  Ts=    6.4 KN-MET  LOAD   608
    PROVIDE 12 MM 2-LEGGED STIRRUPS AT 105. MM  C/C FOR 1380. MM
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   1.94 SQ.CM.
    AT END   SUPPORT - Vu=    5.92 KNS  Vc=   49.64 KNS  Vs=    0.00 KNS
    STAAD SPACE                                              -- PAGE NO.   82
  ___  28J____________________  3350X 200X  350_____________________  66J____
 | 4No12 H 306.|  0.TO 2035|  |  |  |  |  |  |                               |
 | 15*12c/c105 |  |  |  |  |  |  |  |  |  |  |                15*12c/c105    |
 | 3No12 H  49.|  0.TO 3350|  |  |  |  |  |  |                               |
 | oooo  |        | oooo  |        | oooo  |        |       |        |       |
 | 4#12  |        | 4#12  |        | 4#12  |        |       |        |       |
          ACI 318-11   BEAM  NO.    38   DESIGN RESULTS
   LEN -  4600. MM  FY -  415.  FC -  25.  MPA, SIZE -  200. X  350. MMS
   |   CRITICAL POS MOMENT=     15.97 KN-MET  AT  2300.MM, LOAD  600|
   |   REQD STEEL=   193.MM2, RHO=0.0032, RHOMX=0.0193 RHOMN=0.0033 |
     2        306.     3 - 12MM         0.         1893.        YES  NO
   |   CRITICAL NEG MOMENT=     33.28 KN-MET  AT     0.MM, LOAD  606|
   |   REQD STEEL=   306.MM2, RHO=0.0050, RHOMX=0.0193 RHOMN=0.0033 |
     3        306.     2 - 12MM      2515.         4600.        NO   YES
    STAAD SPACE                                              -- PAGE NO.   83
   |   CRITICAL NEG MOMENT=     24.94 KN-MET  AT  4600.MM, LOAD  605|
   |   REQD STEEL=   226.MM2, RHO=0.0037, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.    38 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   27.73 KNS  Vc=   49.17 KNS  Vs=    0.00 KNS
    Tu=    0.70 KN-MET  Tc=    1.4 KN-MET  Ts=    0.0 KN-MET  LOAD   600
    PROVIDE 12 MM 2-LEGGED STIRRUPS AT 151. MM  C/C FOR 2005. MM
    AT END   SUPPORT - Vu=   22.42 KNS  Vc=   50.58 KNS  Vs=    0.00 KNS
  ___  29J____________________  4600X 200X  350_____________________  30J____
 | 3No12 H 306.|  0.TO 1893|  |           |2No12|H 306.2515.TO 4600  |  |  | |
 | 15*12c/c151 |  |  |  |  |  |           |  |  |  |  |  |  | 15*12c/c151  | |
 | 2No12 H  49.|  0.TO 4600|  |           |  |  |  |  |  |  |  |  |  |  |  | |
 |  ooo  |        |  ooo  |        |       |        |  oo   |        |  oo   |
 | 3#12  |        | 3#12  |        |       |        | 2#12  |        | 2#12  |
    STAAD SPACE                                              -- PAGE NO.   84
          ACI 318-11   BEAM  NO.    39   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     38.79 KN-MET  AT  2233.MM, LOAD  600|
   |   REQD STEEL=   369.MM2, RHO=0.0062, RHOMX=0.0193 RHOMN=0.0033 |
     2        306.     2 - 12MM         0.          639.        YES  NO
   |   CRITICAL NEG MOMENT=      9.86 KN-MET  AT     0.MM, LOAD  600|
   |   REQD STEEL=   116.MM2, RHO=0.0019, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.    39 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   33.97 KNS  Vc=   47.39 KNS  Vs=    0.00 KNS
    Tu=    2.94 KN-MET  Tc=    1.3 KN-MET  Ts=    3.9 KN-MET  LOAD   600
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   1.20 SQ.CM.
    AT END   SUPPORT - Vu=    9.23 KNS  Vc=   47.39 KNS  Vs=    0.00 KNS
    STAAD SPACE                                              -- PAGE NO.   85
  ___  31J____________________  3350X 200X  350_____________________  68J____
 | 2No12 H 306.|  0.TO  639                                                  |
 | 15*12c/c105 |                                              15*12c/c105    |
 | 2No16 H  51.|  0.TO 3350                                                  |
 |  oo   |        |       |        |       |        |       |        |       |
 | 2#12  |        |       |        |       |        |       |        |       |
          ACI 318-11   BEAM  NO.    40   DESIGN RESULTS
     1         49.     2 - 12MM       220.         4600.        NO   YES
   |   CRITICAL POS MOMENT=     24.17 KN-MET  AT  2683.MM, LOAD  600|
   |   REQD STEEL=   223.MM2, RHO=0.0037, RHOMX=0.0193 RHOMN=0.0033 |
     2        302.     2 - 20MM         0.         2516.        YES  NO
   |   CRITICAL NEG MOMENT=     61.54 KN-MET  AT     0.MM, LOAD  600|
   |   REQD STEEL=   604.MM2, RHO=0.0100, RHOMX=0.0193 RHOMN=0.0033 |
   |   MAX/MIN/ACTUAL BAR SPACING=   273./   45./  105. MMS         |
     Cracked Moment of Inertia Iz at above location =    28369.4 cm^4
     3        306.     2 - 12MM      3665.         4600.        NO   YES
    STAAD SPACE                                              -- PAGE NO.   86
   |   CRITICAL NEG MOMENT=      5.07 KN-MET  AT  4600.MM, LOAD  605|
   |   REQD STEEL=    59.MM2, RHO=0.0010, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.    40 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   48.90 KNS  Vc=   48.86 KNS  Vs=   16.34 KNS
    Tu=    2.66 KN-MET  Tc=    1.4 KN-MET  Ts=    3.6 KN-MET  LOAD   600
    PROVIDE 12 MM 2-LEGGED STIRRUPS AT 105. MM  C/C FOR 2005. MM
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   1.08 SQ.CM.
    AT END   SUPPORT - Vu=   15.04 KNS  Vc=   53.54 KNS  Vs=    0.00 KNS
    Tu=    2.90 KN-MET  Tc=    1.4 KN-MET  Ts=    3.9 KN-MET  LOAD   607
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   1.18 SQ.CM.
  ___  32J____________________  4600X 200X  350_____________________  33J____
 | 2No20 H 302.| |0.TO 2516| | | | | | | |          2No12 H 306.3665.TO|4600 |
 | 21*12c/c105 | | | | | | | | | | | | | |                   |21*12c/c105| | |
 |   2No12 H |49.|220.TO 4600| | | | | | |                   | | | | | | | | |
    STAAD SPACE                                              -- PAGE NO.   87
          ACI 318-11   BEAM  NO.    41   DESIGN RESULTS
     1         49.     2 - 12MM         0.         3350.        YES  YES
   |   CRITICAL POS MOMENT=     11.07 KN-MET  AT     0.MM, LOAD  609|
   |   REQD STEEL=   133.MM2, RHO=0.0022, RHOMX=0.0193 RHOMN=0.0033 |
     2        306.     2 - 12MM         0.         1756.        YES  NO
   |   CRITICAL NEG MOMENT=     13.24 KN-MET  AT     0.MM, LOAD  606|
   |   REQD STEEL=   157.MM2, RHO=0.0026, RHOMX=0.0193 RHOMN=0.0033 |
     3        306.     2 - 12MM      1455.         3350.        NO   YES
   |   CRITICAL NEG MOMENT=     21.18 KN-MET  AT  3350.MM, LOAD  605|
   |   REQD STEEL=   204.MM2, RHO=0.0033, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.    41 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=    7.01 KNS  Vc=   88.84 KNS  Vs=    0.00 KNS
    Tu=    6.37 KN-MET  Tc=    1.4 KN-MET  Ts=    8.5 KN-MET  LOAD   600
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   2.59 SQ.CM.
    STAAD SPACE                                              -- PAGE NO.   88
    AT END   SUPPORT - Vu=   14.73 KNS  Vc=   48.91 KNS  Vs=    0.00 KNS
  ___  34J____________________  3350X 200X  350_____________________  78J____
 | 2No12 H 306.|  0.TO 1756|  |  | 2No12 H|306.1455.TO|3350 |  |  |  |  |  | |
 | 15*12c/c105 |  |  |  |  |  |  |  |  |  |  |  |  |  |  |  | 15*12c/c105  | |
 | 2No12 H  49.|  0.TO 3350|  |  |  |  |  |  |  |  |  |  |  |  |  |  |  |  | |
          ACI 318-11   BEAM  NO.    42   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     14.45 KN-MET  AT  1917.MM, LOAD  600|
   |   REQD STEEL=   174.MM2, RHO=0.0029, RHOMX=0.0193 RHOMN=0.0033 |
     2        306.     2 - 12MM         0.         1126.        YES  NO
   |   CRITICAL NEG MOMENT=      5.58 KN-MET  AT     0.MM, LOAD  612|
   |   REQD STEEL=    65.MM2, RHO=0.0011, RHOMX=0.0193 RHOMN=0.0033 |
    STAAD SPACE                                              -- PAGE NO.   89
   |   CRITICAL NEG MOMENT=     19.72 KN-MET  AT  4600.MM, LOAD  605|
          B E A M  N O.    42 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   12.04 KNS  Vc=   51.19 KNS  Vs=    0.00 KNS
    Tu=    1.93 KN-MET  Tc=    1.4 KN-MET  Ts=    2.6 KN-MET  LOAD   600
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   0.78 SQ.CM.
    AT END   SUPPORT - Vu=   18.95 KNS  Vc=   49.70 KNS  Vs=    0.00 KNS
  ___  35J____________________  4600X 200X  350_____________________  36J____
 | 2No12 H 306.| |0.TO 1126                2No12 H 306.2515.TO 4600| | | | | |
 | 21*12c/c105 | | |                       | | | | | | | | | |21*12c/c105| | |
 | 2No12 H |49.| |0.TO 4600                | | | | | | | | | | | | | | | | | |
    STAAD SPACE                                              -- PAGE NO.   90
          ACI 318-11   BEAM  NO.    43   DESIGN RESULTS
   LEN -  4500. MM  FY -  415.  FC -  25.  MPA, SIZE -  200. X  350. MMS
     1         53.     3 - 20MM         0.         4500.        YES  YES
   |   CRITICAL POS MOMENT=     65.46 KN-MET  AT  4500.MM, LOAD  600|
   |   REQD STEEL=   661.MM2, RHO=0.0111, RHOMX=0.0193 RHOMN=0.0033 |
     Cracked Moment of Inertia Iz at above location =    36547.4 cm^4
     2        302.     3 - 20MM         0.         2864.        YES  NO
   |   CRITICAL NEG MOMENT=     65.48 KN-MET  AT     0.MM, LOAD  600|
   |   REQD STEEL=   648.MM2, RHO=0.0107, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.    43 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   51.58 KNS  Vc=   50.85 KNS  Vs=   17.93 KNS
    Tu=    2.30 KN-MET  Tc=    1.6 KN-MET  Ts=    3.1 KN-MET  LOAD   600
    PROVIDE 12 MM 2-LEGGED STIRRUPS AT 105. MM  C/C FOR 1955. MM
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   0.94 SQ.CM.
    AT END   SUPPORT - Vu=    6.08 KNS  Vc=   47.49 KNS  Vs=    0.00 KNS
    Tu=    2.74 KN-MET  Tc=    1.5 KN-MET  Ts=    3.7 KN-MET  LOAD   606
    STAAD SPACE                                              -- PAGE NO.   91
  ___  28J____________________  4500X 200X  350_____________________  31J____
 | 3No20 H 302.| |0.TO 2864| | | | | | | | | | | |                           |
 | 20*12c/c105 | | | | | | | | | | | | | | | | | |            20*12c/c105    |
 | 3No20 H |53.| |0.TO 4500| | | | | | | | | | | |                           |
 |  ooo  |        |  ooo  |        |  ooo  |        |       |        |       |
 | 3#20  |        | 3#20  |        | 3#20  |        |       |        |       |
          ACI 318-11   BEAM  NO.    44   DESIGN RESULTS
     1         53.     3 - 20MM         0.         1500.        YES  YES
   |   CRITICAL POS MOMENT=     68.41 KN-MET  AT     0.MM, LOAD  600|
   |   REQD STEEL=   695.MM2, RHO=0.0117, RHOMX=0.0193 RHOMN=0.0033 |
   |   CRITICAL NEG MOMENT=     74.86 KN-MET  AT  1500.MM, LOAD  600|
   |   REQD STEEL=   755.MM2, RHO=0.0125, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.    44 D E S I G N  R E S U L T S - SHEAR
    STAAD SPACE                                              -- PAGE NO.   92
    AT START SUPPORT - Vu=   92.66 KNS  Vc=   56.20 KNS  Vs=   67.34 KNS
    Tu=    7.56 KN-MET  Tc=    1.6 KN-MET  Ts=   10.1 KN-MET  LOAD   600
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   3.08 SQ.CM.
    AT END   SUPPORT - Vu=   98.37 KNS  Vc=   55.70 KNS  Vs=   75.46 KNS
  ___  31J____________________  1499X 200X  350_____________________  34J____
 | 3No20 H  53.|  0.TO 1500|     |           |     |     |     |     |     | |
          ACI 318-11   BEAM  NO.    45   DESIGN RESULTS
     1         49.     2 - 12MM         0.         4500.        YES  YES
   |   CRITICAL POS MOMENT=     23.32 KN-MET  AT  2250.MM, LOAD  600|
   |   REQD STEEL=   215.MM2, RHO=0.0036, RHOMX=0.0193 RHOMN=0.0033 |
    STAAD SPACE                                              -- PAGE NO.   93
     2        304.     2 - 16MM         0.         1980.        YES  NO
   |   CRITICAL NEG MOMENT=     37.17 KN-MET  AT     0.MM, LOAD  608|
   |   REQD STEEL=   346.MM2, RHO=0.0057, RHOMX=0.0193 RHOMN=0.0033 |
     Cracked Moment of Inertia Iz at above location =    20435.2 cm^4
     3        304.     2 - 16MM      2333.         4500.        NO   YES
   |   CRITICAL NEG MOMENT=     40.90 KN-MET  AT  4500.MM, LOAD  607|
   |   REQD STEEL=   383.MM2, RHO=0.0063, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.    45 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   35.99 KNS  Vc=   50.14 KNS  Vs=    0.00 KNS
    Tu=    0.63 KN-MET  Tc=    1.4 KN-MET  Ts=    0.0 KN-MET  LOAD   600
    PROVIDE 12 MM 2-LEGGED STIRRUPS AT 151. MM  C/C FOR 1955. MM
    AT END   SUPPORT - Vu=   39.13 KNS  Vc=   49.61 KNS  Vs=    2.57 KNS
    REINFORCEMENT IS REQUIRED FOR SHEAR.
    STAAD SPACE                                              -- PAGE NO.   94
  ___  29J____________________  4500X 200X  350_____________________  32J____
 | 2No16 H 304.|  0.TO 1980|  |  |       2No16 H|304.2333.TO|4500 |  |  |  | |
 | 14*12c/c151 |  |  |  |  |  |  |        |  |  |  |  |  |  | 14*12c/c151  | |
 | 2No12 H  49.|  0.TO 4500|  |  |        |  |  |  |  |  |  |  |  |  |  |  | |
 |  oo   |        |  oo   |        |       |        |  oo   |        |  oo   |
 | 2#16  |        | 2#16  |        |       |        | 2#16  |        | 2#16  |
          ACI 318-11   BEAM  NO.    46   DESIGN RESULTS
   |   CRITICAL POS MOMENT=      5.33 KN-MET  AT  1500.MM, LOAD  608|
   |   REQD STEEL=    64.MM2, RHO=0.0011, RHOMX=0.0193 RHOMN=0.0033 |
     2        306.     2 - 12MM         0.         1360.        YES  NO
   |   CRITICAL NEG MOMENT=     18.25 KN-MET  AT     0.MM, LOAD  608|
     3        306.     2 - 12MM       828.         1500.        NO   YES
    STAAD SPACE                                              -- PAGE NO.   95
   |   CRITICAL NEG MOMENT=      1.53 KN-MET  AT  1500.MM, LOAD  611|
   |   REQD STEEL=    18.MM2, RHO=0.0003, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.    46 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=    9.97 KNS  Vc=   48.46 KNS  Vs=    0.00 KNS
    Tu=    8.30 KN-MET  Tc=    1.4 KN-MET  Ts=   11.1 KN-MET  LOAD   606
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   3.38 SQ.CM.
    AT END   SUPPORT - Vu=    3.63 KNS  Vc=   49.85 KNS  Vs=    0.00 KNS
  ___  32J____________________  1499X 200X  350_____________________  35J____
 | 2No12 H 306.|  0.TO 1360|     |         2No12 H 306. 828.TO 1500  |     | |
 | 2No12 H  49.|  0.TO 1500|     |           |     |     |     |     |     | |
    STAAD SPACE                                              -- PAGE NO.   96
          ACI 318-11   BEAM  NO.    47   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     30.41 KN-MET  AT  3000.MM, LOAD  600|
   |   REQD STEEL=   283.MM2, RHO=0.0047, RHOMX=0.0193 RHOMN=0.0033 |
   |   CRITICAL NEG MOMENT=     36.65 KN-MET  AT     0.MM, LOAD  600|
   |   REQD STEEL=   341.MM2, RHO=0.0056, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.    47 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   36.24 KNS  Vc=   50.01 KNS  Vs=    0.00 KNS
    Tu=    0.60 KN-MET  Tc=    1.5 KN-MET  Ts=    0.0 KN-MET  LOAD   600
    AT END   SUPPORT - Vu=    4.25 KNS  Vc=   48.59 KNS  Vs=    0.00 KNS
    Tu=    0.21 KN-MET  Tc=    1.4 KN-MET  Ts=    0.0 KN-MET  LOAD   500
    STAAD SPACE                                              -- PAGE NO.   97
  ___  30J____________________  4500X 200X  350_____________________  33J____
 | 2No16 H 304.|  0.TO 1980|  |  |                                           |
 |  oo   |        |  oo   |        |       |        |       |        |       |
 | 2#16  |        | 2#16  |        |       |        |       |        |       |
          ACI 318-11   BEAM  NO.    48   DESIGN RESULTS
     1         49.     2 - 12MM         0.         1319.        YES  NO
   |   CRITICAL POS MOMENT=     20.77 KN-MET  AT     0.MM, LOAD  600|
   |   REQD STEEL=   200.MM2, RHO=0.0033, RHOMX=0.0193 RHOMN=0.0033 |
     2        304.     2 - 16MM         0.         1500.        YES  YES
   |   CRITICAL NEG MOMENT=     40.87 KN-MET  AT  1500.MM, LOAD  600|
          B E A M  N O.    48 D E S I G N  R E S U L T S - SHEAR
    STAAD SPACE                                              -- PAGE NO.   98
    AT START SUPPORT - Vu=   28.14 KNS  Vc=   53.01 KNS  Vs=    0.00 KNS
    Tu=    3.62 KN-MET  Tc=    1.5 KN-MET  Ts=    4.8 KN-MET  LOAD   605
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   1.48 SQ.CM.
    AT END   SUPPORT - Vu=   32.30 KNS  Vc=   49.57 KNS  Vs=    0.00 KNS
  ___  33J____________________  1499X 200X  350_____________________  36J____
 | 2No16 H 304.|  0.TO 1500|     |           |     |     |     |             |
 | 2No12 H  49.|  0.TO 1319|     |           |     |     |     |             |
 | 2#12  |        | 2#12  |        | 2#12  |        | 2#12  |        |       |
 |  oo   |        |  oo   |        |  oo   |        |  oo   |        |       |
          ACI 318-11   BEAM  NO.    49   DESIGN RESULTS
   LEN -  2700. MM  FY -  415.  FC -  25.  MPA, SIZE -  200. X  350. MMS
     1         51.     2 - 16MM         0.         2700.        YES  YES
   |   CRITICAL POS MOMENT=     40.82 KN-MET  AT  2700.MM, LOAD  600|
   |   REQD STEEL=   390.MM2, RHO=0.0065, RHOMX=0.0193 RHOMN=0.0033 |
    STAAD SPACE                                              -- PAGE NO.   99
     2        306.     3 - 12MM         0.         1710.        YES  NO
   |   CRITICAL NEG MOMENT=     36.29 KN-MET  AT     0.MM, LOAD  600|
   |   REQD STEEL=   338.MM2, RHO=0.0055, RHOMX=0.0193 RHOMN=0.0033 |
     Cracked Moment of Inertia Iz at above location =    17833.2 cm^4
          B E A M  N O.    49 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   36.98 KNS  Vc=   50.65 KNS  Vs=    0.00 KNS
    Tu=    3.29 KN-MET  Tc=    1.5 KN-MET  Ts=    4.4 KN-MET  LOAD   600
    PROVIDE 12 MM 2-LEGGED STIRRUPS AT 105. MM  C/C FOR 1055. MM
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   1.34 SQ.CM.
    AT END   SUPPORT - Vu=   20.14 KNS  Vc=   48.59 KNS  Vs=    0.00 KNS
  ___  37J____________________  2700X 200X  350_____________________  70J____
 | 3No12 H 306.|  0.TO 1710|  |  |  |     |  |  |                            |
 | 12*12c/c105 |  |  |  |  |  |  |  |     |  |  |             12*12c/c105    |
 | 2No16 H  51.|  0.TO 2700|  |  |  |     |  |  |                            |
 | 3#12  |        | 3#12  |        | 3#12  |        |       |        |       |
    STAAD SPACE                                              -- PAGE NO.  100
          ACI 318-11   BEAM  NO.    51   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     40.71 KN-MET  AT  2700.MM, LOAD  600|
   |   REQD STEEL=   389.MM2, RHO=0.0065, RHOMX=0.0193 RHOMN=0.0033 |
   |   CRITICAL NEG MOMENT=     27.51 KN-MET  AT     0.MM, LOAD  600|
   |   REQD STEEL=   250.MM2, RHO=0.0041, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.    51 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   33.69 KNS  Vc=   51.60 KNS  Vs=    0.00 KNS
    Tu=    5.76 KN-MET  Tc=    1.5 KN-MET  Ts=    7.7 KN-MET  LOAD   600
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   2.35 SQ.CM.
    AT END   SUPPORT - Vu=   16.85 KNS  Vc=   48.32 KNS  Vs=    0.00 KNS
    STAAD SPACE                                              -- PAGE NO.  101
  ___  40J____________________  2700X 200X  350_____________________  71J____
 | 3No12 H 306.|  0.TO 1485|  |  |  |     |                                  |
 | 12*12c/c105 |  |  |  |  |  |  |  |     |                   12*12c/c105    |
          ACI 318-11   BEAM  NO.    55   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     15.48 KN-MET  AT  2250.MM, LOAD  600|
   |   REQD STEEL=   187.MM2, RHO=0.0031, RHOMX=0.0193 RHOMN=0.0033 |
     2        306.     2 - 12MM         0.         1860.        YES  NO
   |   CRITICAL NEG MOMENT=     21.89 KN-MET  AT     0.MM, LOAD  608|
     3        306.     2 - 12MM      2828.         4500.        NO   YES
    STAAD SPACE                                              -- PAGE NO.  102
   |   CRITICAL NEG MOMENT=     17.26 KN-MET  AT  4500.MM, LOAD  607|
          B E A M  N O.    55 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   20.21 KNS  Vc=   50.46 KNS  Vs=    0.00 KNS
    Tu=    0.86 KN-MET  Tc=    1.4 KN-MET  Ts=    0.0 KN-MET  LOAD   600
    AT END   SUPPORT - Vu=    5.95 KNS  Vc=   57.62 KNS  Vs=    0.00 KNS
    Tu=    0.33 KN-MET  Tc=    1.4 KN-MET  Ts=    0.0 KN-MET  LOAD   500
  ___  37J____________________  4500X 200X  350_____________________  40J____
 | 2No12 H 306.|  0.TO 1860|  |                  2No12 H 306.2828.TO 4500    |
 | 2#12  |        | 2#12  |        |       |        | 2#12  |        | 2#12  |
    STAAD SPACE                                              -- PAGE NO.  103
          ACI 318-11   BEAM  NO.    57   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     13.76 KN-MET  AT  2250.MM, LOAD  600|
   |   REQD STEEL=   166.MM2, RHO=0.0028, RHOMX=0.0193 RHOMN=0.0033 |
     2        306.     2 - 12MM         0.         1485.        YES  NO
   |   CRITICAL NEG MOMENT=     15.85 KN-MET  AT     0.MM, LOAD  608|
   |   REQD STEEL=   188.MM2, RHO=0.0031, RHOMX=0.0193 RHOMN=0.0033 |
     3        306.     2 - 12MM      2453.         4500.        NO   YES
   |   CRITICAL NEG MOMENT=     21.80 KN-MET  AT  4500.MM, LOAD  607|
          B E A M  N O.    57 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   17.18 KNS  Vc=   54.92 KNS  Vs=    0.00 KNS
    Tu=    1.64 KN-MET  Tc=    1.5 KN-MET  Ts=    2.2 KN-MET  LOAD   600
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   0.67 SQ.CM.
    AT END   SUPPORT - Vu=   20.77 KNS  Vc=   49.63 KNS  Vs=    0.00 KNS
    STAAD SPACE                                              -- PAGE NO.  104
  ___  38J____________________  4500X 200X  350_____________________  41J____
 | 2No12 H 306.| |0.TO 1485                2No12 H 306.2453.TO 4500| | | | | |
 | 20*12c/c105 | | | | | |                 | | | | | | | | | |20*12c/c105| | |
 | 2No12 H |49.| |0.TO 4500                | | | | | | | | | | | | | | | | | |
          ACI 318-11   BEAM  NO.   106   DESIGN RESULTS
   LEN -  2050. MM  FY -  415.  FC -  25.  MPA, SIZE -  300. X  400. MMS
     1         49.     2 - 12MM         0.         2050.        YES  YES
   |   CRITICAL POS MOMENT=     21.43 KN-MET  AT  2050.MM, LOAD  610|
   |   REQD STEEL=   221.MM2, RHO=0.0021, RHOMX=0.0193 RHOMN=0.0033 |
     2        354.     2 - 16MM         0.         2050.        YES  YES
   |   CRITICAL NEG MOMENT=     40.37 KN-MET  AT  2050.MM, LOAD  605|
          B E A M  N O.   106 D E S I G N  R E S U L T S - SHEAR
    STAAD SPACE                                              -- PAGE NO.  105
    AT START SUPPORT - Vu=    5.97 KNS  Vc=   87.48 KNS  Vs=    0.00 KNS
    Tu=   13.72 KN-MET  Tc=    3.2 KN-MET  Ts=   18.3 KN-MET  LOAD   607
    PROVIDE 12 MM 2-LEGGED STIRRUPS AT 143. MM  C/C FOR  680. MM
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   3.74 SQ.CM.
    AT END   SUPPORT - Vu=    0.69 KNS  Vc=   87.48 KNS  Vs=    0.00 KNS
  ___  55J____________________  2049X 300X  400_____________________   5J____
 | 2No16 H 354.|  0.TO 2050|     |           |     |     |     |     |     | |
 |  6*12c/c143 |     |     |     |           |     |     |     6*12c/c143  | |
 | 2No12 H  49.|  0.TO 2050|     |           |     |     |     |     |     | |
          ACI 318-11   BEAM  NO.   107   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     21.63 KN-MET  AT     0.MM, LOAD  609|
   |   REQD STEEL=   223.MM2, RHO=0.0021, RHOMX=0.0193 RHOMN=0.0033 |
    STAAD SPACE                                              -- PAGE NO.  106
   |   CRITICAL NEG MOMENT=     42.94 KN-MET  AT     0.MM, LOAD  606|
          B E A M  N O.   107 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=    7.57 KNS  Vc=   85.31 KNS  Vs=    0.00 KNS
    AT END   SUPPORT - Vu=    4.11 KNS  Vc=   85.80 KNS  Vs=    0.00 KNS
  ___  56J____________________  2049X 300X  400_____________________   6J____
 | 2No16 H 354.   0.TO 2050                                                  |
 | 2No12 H  49.   0.TO 2050                                                  |
    STAAD SPACE                                              -- PAGE NO.  107
          ACI 318-11   BEAM  NO.   108   DESIGN RESULTS
     1         49.     3 - 12MM         0.         2050.        YES  YES
   |   CRITICAL POS MOMENT=     31.03 KN-MET  AT     0.MM, LOAD  608|
   |   REQD STEEL=   322.MM2, RHO=0.0031, RHOMX=0.0193 RHOMN=0.0033 |
     2        354.     4 - 16MM         0.         2050.        YES  YES
   |   CRITICAL NEG MOMENT=     90.93 KN-MET  AT  2050.MM, LOAD  605|
   |   REQD STEEL=   737.MM2, RHO=0.0069, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.   108 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   12.18 KNS  Vc=  116.80 KNS  Vs=    0.00 KNS
    Tu=   16.68 KN-MET  Tc=    3.2 KN-MET  Ts=   22.2 KN-MET  LOAD   607
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   4.54 SQ.CM.
    AT END   SUPPORT - Vu=   28.68 KNS  Vc=   85.42 KNS  Vs=    0.00 KNS
    STAAD SPACE                                              -- PAGE NO.  108
  ___  57J____________________  2049X 300X  400_____________________  14J____
 | 4No16 H 354.|  0.TO 2050|     |           |     |     |     |     |     | |
 | 3No12 H  49.|  0.TO 2050|     |           |     |     |     |     |     | |
 | 4#16      |   | 4#16      |   | 4#16      |   | 4#16      |   | 4#16      |
          ACI 318-11   BEAM  NO.   112   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     16.03 KN-MET  AT   171.MM, LOAD  606|
   |   REQD STEEL=   164.MM2, RHO=0.0016, RHOMX=0.0193 RHOMN=0.0033 |
   |   CRITICAL NEG MOMENT=     44.09 KN-MET  AT  2050.MM, LOAD  605|
          B E A M  N O.   112 D E S I G N  R E S U L T S - SHEAR
    STAAD SPACE                                              -- PAGE NO.  109
    AT START SUPPORT - Vu=   16.69 KNS  Vc=   86.83 KNS  Vs=    0.00 KNS
    Tu=   15.60 KN-MET  Tc=    3.2 KN-MET  Ts=   20.8 KN-MET  LOAD   608
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   4.25 SQ.CM.
    AT END   SUPPORT - Vu=   21.97 KNS  Vc=   86.83 KNS  Vs=    0.00 KNS
  ___  61J____________________  2049X 300X  400_____________________   4J____
          ACI 318-11   BEAM  NO.   113   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     20.31 KN-MET  AT  4500.MM, LOAD  612|
   |   REQD STEEL=   209.MM2, RHO=0.0020, RHOMX=0.0193 RHOMN=0.0033 |
    STAAD SPACE                                              -- PAGE NO.  110
     2        356.     2 - 12MM         0.         1968.        YES  NO
   |   CRITICAL NEG MOMENT=     22.17 KN-MET  AT     0.MM, LOAD  608|
   |   REQD STEEL=   225.MM2, RHO=0.0021, RHOMX=0.0193 RHOMN=0.0033 |
     3        356.     3 - 12MM      2345.         4500.        NO   YES
   |   CRITICAL NEG MOMENT=     23.00 KN-MET  AT  4500.MM, LOAD  607|
   |   REQD STEEL=   234.MM2, RHO=0.0022, RHOMX=0.0193 RHOMN=0.0033 |
     Cracked Moment of Inertia Iz at above location =    26893.5 cm^4
          B E A M  N O.   113 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=    5.24 KNS  Vc=   87.36 KNS  Vs=    0.00 KNS
    AT END   SUPPORT - Vu=    4.77 KNS  Vc=   87.36 KNS  Vs=    0.00 KNS
  ___  61J____________________  4500X 300X  400_____________________  55J____
 | 2No12 H 356.   0.TO 1968              3No12 H 356.2345.TO 4500            |
 | 2No12 H  49.   0.TO 4500                                                  |
 |    oo     |   |    oo     |   |           |   |    ooo    |   |    ooo    |
 | 2#12      |   | 2#12      |   |           |   | 3#12      |   | 3#12      |
    STAAD SPACE                                              -- PAGE NO.  111
          ACI 318-11   BEAM  NO.   114   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     30.26 KN-MET  AT  1500.MM, LOAD  612|
   |   REQD STEEL=   314.MM2, RHO=0.0030, RHOMX=0.0193 RHOMN=0.0033 |
   |   CRITICAL NEG MOMENT=     50.06 KN-MET  AT  1500.MM, LOAD  607|
   |   REQD STEEL=   392.MM2, RHO=0.0037, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.   114 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=    8.27 KNS  Vc=   86.68 KNS  Vs=    0.00 KNS
    Tu=   12.73 KN-MET  Tc=    3.2 KN-MET  Ts=   17.0 KN-MET  LOAD   605
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   3.47 SQ.CM.
    AT END   SUPPORT - Vu=    5.25 KNS  Vc=   86.68 KNS  Vs=    0.00 KNS
    STAAD SPACE                                              -- PAGE NO.  112
  ___  55J____________________  1499X 300X  400_____________________  56J____
          ACI 318-11   BEAM  NO.   115   DESIGN RESULTS
   LEN -  3100. MM  FY -  415.  FC -  25.  MPA, SIZE -  300. X  400. MMS
     1         49.     3 - 12MM         0.         3100.        YES  YES
   |   CRITICAL POS MOMENT=     31.04 KN-MET  AT  3100.MM, LOAD  610|
     2        356.     2 - 12MM         0.          726.        YES  NO
   |   CRITICAL NEG MOMENT=      5.86 KN-MET  AT     0.MM, LOAD  610|
   |   REQD STEEL=    59.MM2, RHO=0.0005, RHOMX=0.0193 RHOMN=0.0033 |
     3        354.     2 - 16MM       280.         3100.        NO   YES
    STAAD SPACE                                              -- PAGE NO.  113
   |   CRITICAL NEG MOMENT=     45.13 KN-MET  AT  3100.MM, LOAD  605|
          B E A M  N O.   115 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=    2.30 KNS  Vc=   87.64 KNS  Vs=    0.00 KNS
    Tu=    3.49 KN-MET  Tc=    3.2 KN-MET  Ts=    4.7 KN-MET  LOAD   608
    PROVIDE 12 MM 2-LEGGED STIRRUPS AT 143. MM  C/C FOR 1205. MM
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   0.95 SQ.CM.
    AT END   SUPPORT - Vu=   11.66 KNS  Vc=   87.64 KNS  Vs=    0.00 KNS
  ___  62J____________________  3100X 300X  400_____________________   7J____
 | 2No122Ho356.|350.TO80726|3100   |   |   |   |   |   |   |   |   |   |   | |
 | 10*12c/c143 |   |   |   |   |   |   |   |   |   |   |   |  10*12c/c143  | |
 | 3No12 H |49.|  0.TO 3100|   |   |   |   |   |   |   |   |   |   |   |   | |
 | 2#12      |   | 2#16      |   | 2#16      |   | 2#16      |   | 2#16      |
    STAAD SPACE                                              -- PAGE NO.  114
          ACI 318-11   BEAM  NO.   116   DESIGN RESULTS
     1         49.     2 - 12MM         0.         3100.        YES  YES
   |   CRITICAL POS MOMENT=     16.72 KN-MET  AT     0.MM, LOAD  605|
   |   REQD STEEL=   171.MM2, RHO=0.0016, RHOMX=0.0193 RHOMN=0.0033 |
     2        356.     2 - 12MM         0.         1243.        YES  NO
   |   CRITICAL NEG MOMENT=      7.74 KN-MET  AT     0.MM, LOAD  610|
   |   REQD STEEL=    78.MM2, RHO=0.0007, RHOMX=0.0193 RHOMN=0.0033 |
     3        356.     2 - 12MM      1470.         3100.        NO   YES
   |   CRITICAL NEG MOMENT=     13.99 KN-MET  AT  3100.MM, LOAD  605|
   |   REQD STEEL=   141.MM2, RHO=0.0013, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.   116 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=    1.74 KNS  Vc=   83.71 KNS  Vs=    0.00 KNS
    Tu=    0.42 KN-MET  Tc=    3.2 KN-MET  Ts=    0.0 KN-MET  LOAD   500
    AT END   SUPPORT - Vu=    4.60 KNS  Vc=   88.07 KNS  Vs=    0.00 KNS
    STAAD SPACE                                              -- PAGE NO.  115
  ___  63J____________________  3100X 300X  400_____________________   8J____
 | 2No12 H 356.   0.TO 1243           2No12 H 356.1470.TO 3100               |
 | 2No12 H  49.   0.TO 3100                                                  |
          ACI 318-11   BEAM  NO.   117   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     13.14 KN-MET  AT     0.MM, LOAD  611|
   |   CRITICAL NEG MOMENT=     21.56 KN-MET  AT     0.MM, LOAD  608|
   |   REQD STEEL=   219.MM2, RHO=0.0020, RHOMX=0.0193 RHOMN=0.0033 |
    STAAD SPACE                                              -- PAGE NO.  116
   |   CRITICAL NEG MOMENT=     14.78 KN-MET  AT  4500.MM, LOAD  607|
   |   REQD STEEL=   149.MM2, RHO=0.0014, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.   117 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=    5.57 KNS  Vc=   87.50 KNS  Vs=    0.00 KNS
    Tu=    0.44 KN-MET  Tc=    3.2 KN-MET  Ts=    0.0 KN-MET  LOAD   500
    AT END   SUPPORT - Vu=    4.45 KNS  Vc=   87.50 KNS  Vs=    0.00 KNS
  ___  62J____________________  4500X 300X  400_____________________  63J____
 | 2No12 H 356.   0.TO 1968                    2No12 H 356.2720.TO 4500      |
          ACI 318-11   BEAM  NO.   118   DESIGN RESULTS
     1         49.     4 - 12MM         0.         2050.        YES  YES
    STAAD SPACE                                              -- PAGE NO.  117
   |   CRITICAL POS MOMENT=     51.16 KN-MET  AT     0.MM, LOAD  600|
   |   REQD STEEL=   405.MM2, RHO=0.0038, RHOMX=0.0193 RHOMN=0.0033 |
     2        356.     6 - 12MM         0.         2050.        YES  YES
   |   CRITICAL NEG MOMENT=     82.19 KN-MET  AT  2050.MM, LOAD  605|
   |   REQD STEEL=   657.MM2, RHO=0.0061, RHOMX=0.0193 RHOMN=0.0033 |
     Cracked Moment of Inertia Iz at above location =    47653.7 cm^4
          B E A M  N O.   118 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   40.27 KNS  Vc=   86.13 KNS  Vs=    0.00 KNS
    Tu=   16.54 KN-MET  Tc=    3.1 KN-MET  Ts=   22.1 KN-MET  LOAD   608
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   4.50 SQ.CM.
    AT END   SUPPORT - Vu=   51.27 KNS  Vc=   86.13 KNS  Vs=    0.00 KNS
  ___  64J____________________  2049X 300X  400_____________________  11J____
 | 6No12 H 356.|  0.TO 2050|     |           |     |     |     |     |     | |
 | 4No12 H  49.|  0.TO 2050|     |           |     |     |     |     |     | |
 |  oooooo   |   |  oooooo   |   |  oooooo   |   |  oooooo   |   |  oooooo   |
 | 6#12      |   | 6#12      |   | 6#12      |   | 6#12      |   | 6#12      |
    STAAD SPACE                                              -- PAGE NO.  118
          ACI 318-11   BEAM  NO.   119   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     52.31 KN-MET  AT     0.MM, LOAD  600|
   |   REQD STEEL=   415.MM2, RHO=0.0039, RHOMX=0.0193 RHOMN=0.0033 |
     2        354.     3 - 16MM         0.         2050.        YES  YES
   |   CRITICAL NEG MOMENT=     72.38 KN-MET  AT  2050.MM, LOAD  605|
   |   REQD STEEL=   578.MM2, RHO=0.0054, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.   119 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   38.81 KNS  Vc=   87.10 KNS  Vs=    0.00 KNS
    Tu=   14.33 KN-MET  Tc=    3.2 KN-MET  Ts=   19.1 KN-MET  LOAD   608
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   3.90 SQ.CM.
    AT END   SUPPORT - Vu=   49.81 KNS  Vc=   86.99 KNS  Vs=    0.00 KNS
    STAAD SPACE                                              -- PAGE NO.  119
  ___  65J____________________  2049X 300X  400_____________________  20J____
 | 3No16 H 354.|  0.TO 2050|     |           |     |     |     |     |     | |
          ACI 318-11   BEAM  NO.   120   DESIGN RESULTS
   LEN -  2050. MM  FY -  415.  FC -  25.  MPA, SIZE -  200. X  350. MMS
     1         49.     3 - 12MM         0.         2017.        YES  NO
   |   CRITICAL POS MOMENT=     31.16 KN-MET  AT     0.MM, LOAD  600|
   |   REQD STEEL=   291.MM2, RHO=0.0048, RHOMX=0.0193 RHOMN=0.0033 |
     2        304.     3 - 16MM         0.         2050.        YES  YES
   |   CRITICAL NEG MOMENT=     47.75 KN-MET  AT  2050.MM, LOAD  600|
   |   REQD STEEL=   453.MM2, RHO=0.0074, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.   120 D E S I G N  R E S U L T S - SHEAR
    STAAD SPACE                                              -- PAGE NO.  120
    AT START SUPPORT - Vu=   33.14 KNS  Tu=    9.5 KN-MET
                       Vc=   49.5 KNS, ACI 318:CLAUSE 11.6.3.1
  LOAD   600 TORSION VALUE TOO HIGH, INCREASE MEMBER SIZE.
    AT END   SUPPORT - Vu=   43.85 KNS  Tu=    9.5 KN-MET
  ___  66J____________________  2049X 200X  350_____________________  29J____
 | 3No16 H 304.   0.TO 2050                                                  |
 | 3No12 H  49.   0.TO 2017                                                  |
 | 3#12  |        | 3#12  |        | 3#12  |        | 3#12  |        |       |
          ACI 318-11   BEAM  NO.   121   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     25.78 KN-MET  AT     0.MM, LOAD  600|
   |   REQD STEEL=   266.MM2, RHO=0.0025, RHOMX=0.0193 RHOMN=0.0033 |
     2        352.     2 - 20MM         0.         2050.        YES  YES
   |   CRITICAL NEG MOMENT=     77.98 KN-MET  AT  2050.MM, LOAD  605|
   |   REQD STEEL=   621.MM2, RHO=0.0058, RHOMX=0.0193 RHOMN=0.0033 |
    STAAD SPACE                                              -- PAGE NO.  121
          B E A M  N O.   121 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   15.82 KNS  Vc=   86.75 KNS  Vs=    0.00 KNS
    Tu=   16.25 KN-MET  Tc=    3.2 KN-MET  Ts=   21.7 KN-MET  LOAD   607
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   4.42 SQ.CM.
    AT END   SUPPORT - Vu=   32.32 KNS  Vc=   86.75 KNS  Vs=    0.00 KNS
  ___  67J____________________  2049X 300X  400_____________________  23J____
 | 2No20 H 352.|  0.TO 2050|     |           |     |     |     |     |     | |
 | 2#20      |   | 2#20      |   | 2#20      |   | 2#20      |   | 2#20      |
          ACI 318-11   BEAM  NO.   122   DESIGN RESULTS
     1         49.     3 - 12MM         0.         1382.        YES  NO
    STAAD SPACE                                              -- PAGE NO.  122
   |   CRITICAL POS MOMENT=     35.54 KN-MET  AT     0.MM, LOAD  600|
   |   REQD STEEL=   336.MM2, RHO=0.0056, RHOMX=0.0193 RHOMN=0.0033 |
     2        302.     3 - 20MM         0.         2050.        YES  YES
   |   CRITICAL NEG MOMENT=     86.40 KN-MET  AT  2050.MM, LOAD  600|
   |   REQD STEEL=   894.MM2, RHO=0.0148, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.   122 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   50.10 KNS  Vc=   47.47 KNS  Vs=   19.34 KNS
    Tu=    6.80 KN-MET  Tc=    1.3 KN-MET  Ts=    9.1 KN-MET  LOAD   600
    PROVIDE 12 MM 2-LEGGED STIRRUPS AT 105. MM  C/C FOR  730. MM
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   2.77 SQ.CM.
    AT END   SUPPORT - Vu=   68.49 KNS  Vc=   47.47 KNS  Vs=   43.85 KNS
  ___  68J____________________  2049X 200X  350_____________________  32J____
 | 3No20 H 302.|  0.TO 2050|   |               |   |                         |
 |  8*12c/c105 |   |   |   |   |               |   |           8*12c/c105    |
 | 3No12 H |49.|  0.TO 1382|   |               |   |                         |
    STAAD SPACE                                              -- PAGE NO.  123
          ACI 318-11   BEAM  NO.   123   DESIGN RESULTS
     1         49.     5 - 12MM         0.         4500.        YES  YES
   |   CRITICAL POS MOMENT=     62.71 KN-MET  AT  2250.MM, LOAD  600|
   |   REQD STEEL=   501.MM2, RHO=0.0048, RHOMX=0.0193 RHOMN=0.0033 |
     Cracked Moment of Inertia Iz at above location =    39903.1 cm^4
     2        356.     3 - 12MM         0.         1218.        YES  NO
   |   CRITICAL NEG MOMENT=     28.82 KN-MET  AT     0.MM, LOAD  608|
   |   REQD STEEL=   294.MM2, RHO=0.0027, RHOMX=0.0193 RHOMN=0.0033 |
     3        356.     2 - 12MM      3470.         4500.        NO   YES
   |   REQD STEEL=   175.MM2, RHO=0.0016, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.   123 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   54.59 KNS  Vc=   86.69 KNS  Vs=    0.00 KNS
    Tu=    1.65 KN-MET  Tc=    3.2 KN-MET  Ts=    0.0 KN-MET  LOAD   600
    PROVIDE 12 MM 2-LEGGED STIRRUPS AT 176. MM  C/C FOR 1905. MM
    STAAD SPACE                                              -- PAGE NO.  124
    AT END   SUPPORT - Vu=   47.84 KNS  Vc=   86.69 KNS  Vs=    0.00 KNS
  ___  64J____________________  4500X 300X  400_____________________  57J____
 | 3No12 H 356.|  0.TO 1218                         2No12 H 356.3470.TO 4500 |
 | 12*12c/c176 |  |  |                                      | 12*12c/c176  | |
 | 5No12 H  49.|  0.TO 4500                                 |  |  |  |  |  | |
 |    ooo    |   |    ooo    |   |           |   |           |   |    oo     |
 | 3#12      |   | 3#12      |   |           |   |           |   | 2#12      |
 | 5#12      |   | 5#12      |   | 5#12      |   | 5#12      |   | 5#12      |
 |   ooooo   |   |   ooooo   |   |   ooooo   |   |   ooooo   |   |   ooooo   |
          ACI 318-11   BEAM  NO.   124   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     42.25 KN-MET  AT     0.MM, LOAD  608|
   |   REQD STEEL=   402.MM2, RHO=0.0067, RHOMX=0.0193 RHOMN=0.0033 |
     Cracked Moment of Inertia Iz at above location =    19993.1 cm^4
   |   CRITICAL NEG MOMENT=     34.40 KN-MET  AT   900.MM, LOAD  607|
   |   REQD STEEL=   317.MM2, RHO=0.0052, RHOMX=0.0193 RHOMN=0.0033 |
    STAAD SPACE                                              -- PAGE NO.  125
          B E A M  N O.   124 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   47.33 KNS  Vc=   48.49 KNS  Vs=   14.61 KNS
    Tu=    3.59 KN-MET  Tc=    1.3 KN-MET  Ts=    4.8 KN-MET  LOAD   600
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   1.46 SQ.CM.
    AT END   SUPPORT - Vu=   49.48 KNS  Vc=   48.49 KNS  Vs=   17.49 KNS
  ___  13J____________________   899X 200X  350_____________________  72J____
          ACI 318-11   BEAM  NO.   125   DESIGN RESULTS
     1         49.     4 - 12MM         0.         4500.        YES  YES
    STAAD SPACE                                              -- PAGE NO.  126
   |   CRITICAL POS MOMENT=     42.83 KN-MET  AT  2250.MM, LOAD  600|
   |   REQD STEEL=   407.MM2, RHO=0.0068, RHOMX=0.0193 RHOMN=0.0033 |
     Cracked Moment of Inertia Iz at above location =    21922.7 cm^4
     2        306.     2 - 12MM         0.          735.        YES  NO
   |   CRITICAL NEG MOMENT=     14.07 KN-MET  AT     0.MM, LOAD  600|
   |   REQD STEEL=   167.MM2, RHO=0.0027, RHOMX=0.0193 RHOMN=0.0033 |
     3        306.     2 - 12MM      3953.         4500.        NO   YES
   |   CRITICAL NEG MOMENT=      4.00 KN-MET  AT  4500.MM, LOAD  607|
   |   REQD STEEL=    47.MM2, RHO=0.0008, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.   125 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   38.24 KNS  Vc=   50.10 KNS  Vs=    0.89 KNS
    Tu=    3.13 KN-MET  Tc=    1.4 KN-MET  Ts=    4.2 KN-MET  LOAD   600
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   1.27 SQ.CM.
    AT END   SUPPORT - Vu=   33.70 KNS  Vc=   50.10 KNS  Vs=    0.00 KNS
    STAAD SPACE                                              -- PAGE NO.  127
  ___  66J____________________  4500X 200X  350_____________________  68J____
 | 2No12 H 306.   0.TO  735                         2No12 H 306.3953.TO|4500 |
 | 20*12c/c105                                                20*12c/c105| | |
 | 4No12 H |49.   0.TO 4500                                        | | | | | |
          ACI 318-11   BEAM  NO.   126   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     39.03 KN-MET  AT     0.MM, LOAD  600|
   |   REQD STEEL=   372.MM2, RHO=0.0062, RHOMX=0.0193 RHOMN=0.0033 |
     2        306.     3 - 12MM       878.         2700.        NO   YES
   |   CRITICAL NEG MOMENT=     29.61 KN-MET  AT  2700.MM, LOAD  605|
   |   REQD STEEL=   271.MM2, RHO=0.0044, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.   126 D E S I G N  R E S U L T S - SHEAR
    STAAD SPACE                                              -- PAGE NO.  128
    AT START SUPPORT - Vu=   16.75 KNS  Vc=   48.34 KNS  Vs=    0.00 KNS
    Tu=    6.48 KN-MET  Tc=    1.5 KN-MET  Ts=    8.6 KN-MET  LOAD   600
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   2.64 SQ.CM.
    AT END   SUPPORT - Vu=   33.59 KNS  Vc=   51.26 KNS  Vs=    0.00 KNS
  ___  70J____________________  2700X 200X  350_____________________  38J____
 |                        3No12 H|306. 878.TO|2700 |  |  |  |  |  |  |  |  | |
 | 12*12c/c105             |  |  |  |     |  |  |  |  |  |  | 12*12c/c105  | |
 | 2No16 H  51.   0.TO 2700|  |  |  |     |  |  |  |  |  |  |  |  |  |  |  | |
 |       |        |       |        |  ooo  |        |  ooo  |        |  ooo  |
 |       |        |       |        | 3#12  |        | 3#12  |        | 3#12  |
          ACI 318-11   BEAM  NO.   127   DESIGN RESULTS
   LEVEL    HEIGHT     BAR INFO       FROM          TO           ANCHOR
             (MM)                     (MM)         (MM)         STA  END
     1         49.     4 - 12MM         0.         2700.        YES  YES
   |   CRITICAL POS MOMENT=     42.51 KN-MET  AT     0.MM, LOAD  600|
   |   REQD STEEL=   404.MM2, RHO=0.0067, RHOMX=0.0193 RHOMN=0.0033 |
    STAAD SPACE                                              -- PAGE NO.  129
   |   CRITICAL NEG MOMENT=     33.84 KN-MET  AT  2700.MM, LOAD  600|
   |   REQD STEEL=   311.MM2, RHO=0.0051, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.   127 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   19.85 KNS  Vc=   48.84 KNS  Vs=    0.00 KNS
    Tu=    3.59 KN-MET  Tc=    1.5 KN-MET  Ts=    4.8 KN-MET  LOAD   600
    AT END   SUPPORT - Vu=   36.70 KNS  Vc=   51.32 KNS  Vs=    0.00 KNS
    REINFORCEMENT FOR SHEAR IS PER CL.11.5.5.1.
  ___  71J____________________  2700X 200X  350_____________________  41J____
 | 4No12 H  49.   0.TO 2700|  |  |  |     |  |  |  |  |  |  |  |  |  |  |  | |
    STAAD SPACE                                              -- PAGE NO.  130
          ACI 318-11   BEAM  NO.   128   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     38.08 KN-MET  AT  2250.MM, LOAD  600|
   |   REQD STEEL=   362.MM2, RHO=0.0060, RHOMX=0.0193 RHOMN=0.0033 |
   |   REQD. DEVELOPMENT LENGTH =   480. MMS                       |
   |   CRITICAL NEG MOMENT=      9.77 KN-MET  AT     0.MM, LOAD  600|
   |   REQD STEEL=   115.MM2, RHO=0.0019, RHOMX=0.0193 RHOMN=0.0033 |
   |   REQD. DEVELOPMENT LENGTH =   360. MMS                       |
     3        306.     2 - 12MM      3578.         4500.        NO   YES
   |   CRITICAL NEG MOMENT=      9.35 KN-MET  AT  4500.MM, LOAD  600|
   |   REQD STEEL=   110.MM2, RHO=0.0018, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.   128 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   33.54 KNS  Vc=   49.81 KNS  Vs=    0.00 KNS
    Tu=    1.79 KN-MET  Tc=    1.4 KN-MET  Ts=    2.4 KN-MET  LOAD   600
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   0.73 SQ.CM.
    STAAD SPACE                                              -- PAGE NO.  131
    AT END   SUPPORT - Vu=   33.35 KNS  Vc=   49.81 KNS  Vs=    0.00 KNS
  ___  70J____________________  4500X 200X  350_____________________  71J____
 | 2No12 H 306.   0.TO  735                         2No12 H 306.3578.TO|4500 |
 | 20*12c/c105                                               |20*12c/c105| | |
 | 2No16 H |51.   0.TO 4500                                  | | | | | | | | |
 |___________________________________________________________________________|
 | 2#16  |        | 2#16  |        | 2#16  |        | 2#16  |        | 2#16  |
 |  oo   |        |  oo   |        |  oo   |        |  oo   |        |  oo   |
          ACI 318-11   BEAM  NO.   130   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     15.73 KN-MET  AT  2683.MM, LOAD  606|
   |   REQD STEEL=   190.MM2, RHO=0.0032, RHOMX=0.0193 RHOMN=0.0033 |
   |   CRITICAL NEG MOMENT=      8.12 KN-MET  AT     0.MM, LOAD  606|
    STAAD SPACE                                              -- PAGE NO.  132
     3        306.     3 - 12MM      1749.         4600.        NO   YES
   |   CRITICAL NEG MOMENT=     32.35 KN-MET  AT  4600.MM, LOAD  605|
   |   REQD STEEL=   297.MM2, RHO=0.0048, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.   130 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=    5.70 KNS  Vc=   49.89 KNS  Vs=    0.00 KNS
    Tu=    0.34 KN-MET  Tc=    1.4 KN-MET  Ts=    0.0 KN-MET  LOAD   500
    AT END   SUPPORT - Vu=   24.06 KNS  Vc=   49.55 KNS  Vs=    0.00 KNS
    Tu=    0.82 KN-MET  Tc=    1.4 KN-MET  Ts=    0.0 KN-MET  LOAD   600
  ___  26J____________________  4600X 200X  350_____________________  27J____
 | 2No12 H 306.   0.TO 1126   3No12 H 306.1749.TO|4600 |  |  |  |  |  |  |   |
 |                                         |  |  |  |  |  |  |15*12c/c151|   |
 | 2No12 H  49.   0.TO 4600                |  |  |  |  |  |  |  |  |  |  |   |
 |  oo   |        |       |        |  ooo  |        |  ooo  |        |  ooo  |
 | 2#12  |        |       |        | 3#12  |        | 3#12  |        | 3#12  |
 | 2#12  |        | 2#12  |        | 2#12  |        | 2#12  |        | 2#12  |
    STAAD SPACE                                              -- PAGE NO.  133
          ACI 318-11   BEAM  NO.   132   DESIGN RESULTS
     1         49.     2 - 12MM         0.         4600.        YES  YES
   |   CRITICAL POS MOMENT=     19.38 KN-MET  AT  3067.MM, LOAD  606|
   |   CRITICAL NEG MOMENT=     12.22 KN-MET  AT     0.MM, LOAD  606|
   |   REQD STEEL=   145.MM2, RHO=0.0024, RHOMX=0.0193 RHOMN=0.0033 |
     3        304.     2 - 16MM      1628.         4600.        NO   YES
   |   CRITICAL NEG MOMENT=     38.48 KN-MET  AT  4600.MM, LOAD  605|
   |   REQD STEEL=   359.MM2, RHO=0.0059, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.   132 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   14.45 KNS  Vc=   49.98 KNS  Vs=    0.00 KNS
    Tu=    2.13 KN-MET  Tc=    1.4 KN-MET  Ts=    2.8 KN-MET  LOAD   608
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   0.87 SQ.CM.
    STAAD SPACE                                              -- PAGE NO.  134
    AT END   SUPPORT - Vu=   12.58 KNS  Vc=   52.50 KNS  Vs=    0.00 KNS
  ___  17J____________________  4600X 200X  350_____________________  18J____
 | 2No12 H 306.| |0.TO 1126|2No16|H|304.1628.TO|4600 | | | | | | | | | | | | |
 | 21*12c/c105 | | |       | | | | | | | | | | | | | | | | | |21*12c/c105| | |
 | 2No12 H |49.| |0.TO 4600| | | | | | | | | | | | | | | | | | | | | | | | | |
 |  oo   |        |       |        |  oo   |        |  oo   |        |  oo   |
 | 2#12  |        |       |        | 2#16  |        | 2#16  |        | 2#16  |
          ACI 318-11   BEAM  NO.   133   DESIGN RESULTS
   LEN -  4500. MM  FY -  415.  FC -  25.  MPA, SIZE -  300. X  400. MMS
   |   CRITICAL POS MOMENT=     61.93 KN-MET  AT  2250.MM, LOAD  600|
   |   REQD STEEL=   495.MM2, RHO=0.0047, RHOMX=0.0193 RHOMN=0.0033 |
   |   CRITICAL NEG MOMENT=     26.78 KN-MET  AT     0.MM, LOAD  608|
   |   REQD STEEL=   273.MM2, RHO=0.0026, RHOMX=0.0193 RHOMN=0.0033 |
   |   MAX/MIN/ACTUAL BAR SPACING=   273./   37./  106. MMS         |
    STAAD SPACE                                              -- PAGE NO.  135
   |   CRITICAL NEG MOMENT=     12.72 KN-MET  AT  4500.MM, LOAD  607|
   |   REQD STEEL=   128.MM2, RHO=0.0012, RHOMX=0.0193 RHOMN=0.0033 |
   |   MAX/MIN/ACTUAL BAR SPACING=   273./   37./  213. MMS         |
     Cracked Moment of Inertia Iz at above location =    18932.3 cm^4
          B E A M  N O.   133 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   41.89 KNS  Vc=   87.65 KNS  Vs=    0.00 KNS
    Tu=    1.54 KN-MET  Tc=    3.2 KN-MET  Ts=    0.0 KN-MET  LOAD   608
    AT END   SUPPORT - Vu=   46.97 KNS  Vc=   93.97 KNS  Vs=    0.00 KNS
    Tu=    1.17 KN-MET  Tc=    3.2 KN-MET  Ts=    0.0 KN-MET  LOAD   600
  ___  65J____________________  4500X 300X  400_____________________  67J____
  ___________     ___________     ___________     ___________     ___________
 |___________|   |___________|   |___________|   |___________|   |___________|
    STAAD SPACE                                              -- PAGE NO.  136
          ACI 318-11   BEAM  NO.   134   DESIGN RESULTS
   LEN -   600. MM  FY -  415.  FC -  25.  MPA, SIZE -  200. X  350. MMS
     1         49.     3 - 12MM         0.          600.        YES  YES
   |   CRITICAL POS MOMENT=     27.84 KN-MET  AT     0.MM, LOAD  612|
   |   REQD STEEL=   258.MM2, RHO=0.0043, RHOMX=0.0193 RHOMN=0.0033 |
     2        302.     3 - 20MM         0.          600.        YES  YES
   |   CRITICAL NEG MOMENT=     69.01 KN-MET  AT   600.MM, LOAD  607|
   |   REQD STEEL=   688.MM2, RHO=0.0114, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.   134 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   35.65 KNS  Tu=   13.7 KN-MET
                       Vc=   49.6 KNS, ACI 318:CLAUSE 11.6.3.1
  LOAD   605 TORSION VALUE TOO HIGH, INCREASE MEMBER SIZE.
    AT END   SUPPORT - Vu=   35.67 KNS  Tu=   13.7 KN-MET
    STAAD SPACE                                              -- PAGE NO.  137
  ___  72J____________________   600X 200X  350_____________________  69J____
 | 3No20 H 302.   0.TO  600                                                  |
 | 3No12 H  49.   0.TO  600                                                  |
 |  ooo  |        |  ooo  |        |  ooo  |        |  ooo  |        |  ooo  |
 | 3#12  |        | 3#12  |        | 3#12  |        | 3#12  |        | 3#12  |
          ACI 318-11   BEAM  NO.   135   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     17.22 KN-MET  AT     0.MM, LOAD  609|
     2        304.     2 - 16MM         0.         2050.        YES  YES
   |   CRITICAL NEG MOMENT=     38.34 KN-MET  AT     0.MM, LOAD  606|
   |   REQD STEEL=   358.MM2, RHO=0.0059, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.   135 D E S I G N  R E S U L T S - SHEAR
    STAAD SPACE                                              -- PAGE NO.  138
    AT START SUPPORT - Vu=    4.50 KNS  Vc=   48.34 KNS  Vs=    0.00 KNS
    Tu=    5.88 KN-MET  Tc=    1.4 KN-MET  Ts=    7.8 KN-MET  LOAD   608
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   2.40 SQ.CM.
    AT END   SUPPORT - Vu=    4.36 KNS  Vc=   48.33 KNS  Vs=    0.00 KNS
  ___  73J____________________  2049X 200X  350_____________________  17J____
 | 2No16 H 304.|  0.TO 2050|   |               |   |   |   |   |   |   |   | |
 |  8*12c/c105 |   |   |   |   |               |   |   |   |   8*12c/c105  | |
 | 2No12 H |49.|  0.TO 2050|   |               |   |   |   |   |   |   |   | |
          ACI 318-11   BEAM  NO.   136   DESIGN RESULTS
   LEN -   900. MM  FY -  415.  FC -  25.  MPA, SIZE -  300. X  400. MMS
     1         49.     3 - 12MM         0.          900.        YES  YES
   |   CRITICAL POS MOMENT=     26.70 KN-MET  AT   900.MM, LOAD  612|
   |   REQD STEEL=   276.MM2, RHO=0.0026, RHOMX=0.0193 RHOMN=0.0033 |
    STAAD SPACE                                              -- PAGE NO.  139
     Cracked Moment of Inertia Iz at above location =    26089.3 cm^4
     2        354.     2 - 16MM         0.          900.        YES  YES
   |   CRITICAL NEG MOMENT=     49.98 KN-MET  AT   900.MM, LOAD  607|
   |   MAX/MIN/ACTUAL BAR SPACING=   273./   41./  209. MMS         |
     Cracked Moment of Inertia Iz at above location =    30686.7 cm^4
          B E A M  N O.   136 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   12.88 KNS  Vc=   86.14 KNS  Vs=    0.00 KNS
    Tu=   18.16 KN-MET  Tc=    3.1 KN-MET  Ts=   24.2 KN-MET  LOAD   605
    PROVIDE 12 MM 2-LEGGED STIRRUPS AT 143. MM  C/C FOR  105. MM
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   4.95 SQ.CM.
    AT END   SUPPORT - Vu=   14.84 KNS  Vc=   86.14 KNS  Vs=    0.00 KNS
  ___  57J____________________   899X 300X  400_____________________  74J____
 | 2No16 H 354. | 0.TO  900                                   |            | |
 |  2*12c/c143  |                                              2*12c/c143  | |
 | 3No12 H  49. | 0.TO  900                                   |            | |
    STAAD SPACE                                              -- PAGE NO.  140
          ACI 318-11   BEAM  NO.   137   DESIGN RESULTS
   LEN -   600. MM  FY -  415.  FC -  25.  MPA, SIZE -  300. X  400. MMS
   |   CRITICAL POS MOMENT=     26.12 KN-MET  AT   500.MM, LOAD  612|
   |   REQD STEEL=   270.MM2, RHO=0.0026, RHOMX=0.0193 RHOMN=0.0033 |
     2        354.     4 - 16MM         0.          600.        YES  YES
   |   CRITICAL NEG MOMENT=     93.18 KN-MET  AT   600.MM, LOAD  607|
   |   REQD STEEL=   757.MM2, RHO=0.0071, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.   137 D E S I G N  R E S U L T S - SHEAR
   ** LOCATION FOR DESIGN FOR SHEAR AT START OF MEMBER   137 IS BEYOND
      THE MIDPOINT OF MEMBER. DESIGN FOR SHEAR AND TORSION NOT PERFORMED.
   ** LOCATION FOR DESIGN FOR SHEAR AT END OF MEMBER   137 IS BEYOND
    STAAD SPACE                                              -- PAGE NO.  141
  ___  74J____________________   600X 300X  400_____________________  73J____
 | 4No16 H 354.   0.TO  600                                                  |
 |   oooo    |   |   oooo    |   |   oooo    |   |   oooo    |   |   oooo    |
          ACI 318-11   BEAM  NO.   138   DESIGN RESULTS
   LEN -  3350. MM  FY -  415.  FC -  25.  MPA, SIZE -  300. X  400. MMS
   |   CRITICAL POS MOMENT=     22.19 KN-MET  AT  3350.MM, LOAD  606|
   |   REQD STEEL=   229.MM2, RHO=0.0022, RHOMX=0.0193 RHOMN=0.0033 |
     2        356.     2 - 12MM         0.         1305.        YES  NO
   |   CRITICAL NEG MOMENT=     16.63 KN-MET  AT     0.MM, LOAD  606|
   |   REQD STEEL=   168.MM2, RHO=0.0016, RHOMX=0.0193 RHOMN=0.0033 |
     3        356.     2 - 12MM      1347.         3350.        NO   YES
    STAAD SPACE                                              -- PAGE NO.  142
   |   CRITICAL NEG MOMENT=     20.38 KN-MET  AT  3350.MM, LOAD  609|
   |   REQD STEEL=   207.MM2, RHO=0.0019, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.   138 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=    5.34 KNS  Vc=   87.45 KNS  Vs=    0.00 KNS
    Tu=    0.52 KN-MET  Tc=    3.2 KN-MET  Ts=    0.0 KN-MET  LOAD   500
                       STIRRUPS ARE NOT REQUIRED.
    AT END   SUPPORT - Vu=    5.14 KNS  Vc=   87.45 KNS  Vs=    0.00 KNS
  ___  72J____________________  3350X 300X  400_____________________  74J____
 | 2No12 H 356.   0.TO 1305     2No12 H 356.1347.TO 3350                     |
 | 3No12 H  49.   0.TO 3350                                                  |
          ACI 318-11   BEAM  NO.   139   DESIGN RESULTS
    STAAD SPACE                                              -- PAGE NO.  143
   |   CRITICAL POS MOMENT=     22.67 KN-MET  AT     0.MM, LOAD  608|
   |   CRITICAL NEG MOMENT=     37.47 KN-MET  AT   900.MM, LOAD  607|
   |   REQD STEEL=   353.MM2, RHO=0.0033, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.   139 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   18.00 KNS  Vc=  154.89 KNS  Vs=    0.00 KNS
    Tu=   14.75 KN-MET  Tc=    3.3 KN-MET  Ts=   19.7 KN-MET  LOAD   605
    STIRRUPS ARE REQUIRED FOR TORSION.
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   4.02 SQ.CM.
    AT END   SUPPORT - Vu=   19.96 KNS  Vc=   94.35 KNS  Vs=    0.00 KNS
  ___  67J____________________   899X 300X  400_____________________  75J____
    STAAD SPACE                                              -- PAGE NO.  144
          ACI 318-11   BEAM  NO.   140   DESIGN RESULTS
   |   CRITICAL POS MOMENT=      9.19 KN-MET  AT     0.MM, LOAD  609|
     2        306.     3 - 12MM         0.         2050.        YES  YES
   |   CRITICAL NEG MOMENT=     34.22 KN-MET  AT     0.MM, LOAD  606|
   |   REQD STEEL=   315.MM2, RHO=0.0051, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.   140 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=    7.85 KNS  Vc=   50.05 KNS  Vs=    0.00 KNS
    Tu=    5.10 KN-MET  Tc=    1.4 KN-MET  Ts=    6.8 KN-MET  LOAD   608
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   2.08 SQ.CM.
    AT END   SUPPORT - Vu=    1.01 KNS  Vc=   50.05 KNS  Vs=    0.00 KNS
    STAAD SPACE                                              -- PAGE NO.  145
  ___  76J____________________  2049X 200X  350_____________________  26J____
 | 3No12 H 306.|  0.TO 2050|   |               |   |   |   |   |   |   |   | |
          ACI 318-11   BEAM  NO.   141   DESIGN RESULTS
     1         49.     2 - 12MM         0.          600.        YES  YES
   |   CRITICAL POS MOMENT=     16.66 KN-MET  AT     0.MM, LOAD  612|
     Cracked Moment of Inertia Iz at above location =    18373.0 cm^4
     2        354.     3 - 16MM         0.          600.        YES  YES
   |   CRITICAL NEG MOMENT=     73.54 KN-MET  AT   600.MM, LOAD  607|
   |   REQD STEEL=   587.MM2, RHO=0.0055, RHOMX=0.0193 RHOMN=0.0033 |
   |   MAX/MIN/ACTUAL BAR SPACING=   273./   41./  104. MMS         |
     Cracked Moment of Inertia Iz at above location =    42844.9 cm^4
          B E A M  N O.   141 D E S I G N  R E S U L T S - SHEAR
    STAAD SPACE                                              -- PAGE NO.  146
   ** LOCATION FOR DESIGN FOR SHEAR AT START OF MEMBER   141 IS BEYOND
   ** LOCATION FOR DESIGN FOR SHEAR AT END OF MEMBER   141 IS BEYOND
  ___  75J____________________   600X 300X  400_____________________  76J____
 | 3No16 H 354.   0.TO  600                                                  |
 | 2No12 H  49.   0.TO  600                                                  |
          ACI 318-11   BEAM  NO.   142   DESIGN RESULTS
   |   CRITICAL POS MOMENT=     20.10 KN-MET  AT     0.MM, LOAD  612|
    STAAD SPACE                                              -- PAGE NO.  147
   |   CRITICAL NEG MOMENT=     65.94 KN-MET  AT   600.MM, LOAD  607|
   |   REQD STEEL=   653.MM2, RHO=0.0108, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.   142 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=   55.12 KNS  Tu=   17.6 KN-MET
                       Vc=   47.1 KNS, ACI 318:CLAUSE 11.6.3.1
  LOAD   606 TORSION VALUE TOO HIGH, INCREASE MEMBER SIZE.
    AT END   SUPPORT - Vu=   55.15 KNS  Tu=   17.6 KN-MET
  ___  77J____________________   600X 200X  350_____________________  25J____
          ACI 318-11   BEAM  NO.   143   DESIGN RESULTS
    STAAD SPACE                                              -- PAGE NO.  148
   |   CRITICAL POS MOMENT=     17.70 KN-MET  AT  3071.MM, LOAD  606|
   |   REQD STEEL=   182.MM2, RHO=0.0017, RHOMX=0.0193 RHOMN=0.0033 |
   |   CRITICAL NEG MOMENT=     14.25 KN-MET  AT     0.MM, LOAD  606|
   |   REQD STEEL=   144.MM2, RHO=0.0013, RHOMX=0.0193 RHOMN=0.0033 |
     3        356.     2 - 12MM      1626.         3350.        NO   YES
   |   CRITICAL NEG MOMENT=     15.40 KN-MET  AT  3350.MM, LOAD  609|
   |   REQD STEEL=   156.MM2, RHO=0.0015, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.   143 D E S I G N  R E S U L T S - SHEAR
    AT START SUPPORT - Vu=    5.57 KNS  Vc=   88.26 KNS  Vs=    0.00 KNS
    Tu=    0.41 KN-MET  Tc=    3.2 KN-MET  Ts=    0.0 KN-MET  LOAD   500
    AT END   SUPPORT - Vu=    4.91 KNS  Vc=   85.86 KNS  Vs=    0.00 KNS
    STAAD SPACE                                              -- PAGE NO.  149
  ___  77J____________________  3350X 300X  400_____________________  75J____
 | 2No12 H 356.   0.TO 1305           2No12 H 356.1626.TO 3350               |
 | 2No12 H  49.   0.TO 3350                                                  |
          ACI 318-11   BEAM  NO.   146   DESIGN RESULTS
     1         49.     2 - 12MM       211.         2050.        NO   YES
   |   CRITICAL POS MOMENT=     11.28 KN-MET  AT  2050.MM, LOAD  607|
   |   REQD STEEL=   136.MM2, RHO=0.0023, RHOMX=0.0193 RHOMN=0.0033 |
     2        306.     2 - 12MM         0.         2050.        YES  YES
   |   CRITICAL NEG MOMENT=     24.66 KN-MET  AT     0.MM, LOAD  600|
   |   REQD STEEL=   223.MM2, RHO=0.0036, RHOMX=0.0193 RHOMN=0.0033 |
          B E A M  N O.   146 D E S I G N  R E S U L T S - SHEAR
    STAAD SPACE                                              -- PAGE NO.  150
    AT START SUPPORT - Vu=    8.85 KNS  Vc=   48.48 KNS  Vs=    0.00 KNS
    Tu=    3.90 KN-MET  Tc=    1.4 KN-MET  Ts=    5.2 KN-MET  LOAD   608
    ADDITIONAL LONGITUDINAL STEEL REQD. FOR TORSIONAL RESISTANCE =   1.59 SQ.CM.
    AT END   SUPPORT - Vu=    1.05 KNS  Vc=   48.99 KNS  Vs=    0.00 KNS
  ___  78J____________________  2049X 200X  350_____________________  35J____
 | 2No12 H 306.|  0.TO 2050|   |               |   |   |   |   |   |   |   | |
 |       2No12 H  49. 211.TO 2050              |   |   |   |   |   |   |   | |
   ********************END OF BEAM DESIGN**************************
   504. DESIGN COLUMN 69 99 110 111 144 145 147 148 153 154 61 TO 64 68 73 TO 80 -
   505. 85 TO 87 97 100 101 103 149 TO 152
    STAAD SPACE                                              -- PAGE NO.  151
        ACI 318-11   COLUMN  NO.    69   DESIGN RESULTS
   FY - 415.0  FC -  25.0 MPA,  SQRE SIZE - 300.0 X 300.0 MMS, TIED
           ONLY MINIMUM STEEL IS REQUIRED.
           AREA OF STEEL REQUIRED =   900.0  SQ. MM
   BAR CONFIGURATION       REINF PCT.   LOAD   LOCATION   PHI
     8 - 12 MM               1.005      500      END     0.650
   (PROVIDE EQUAL NUMBER OF BARS ON EACH FACE)
   TIE BAR NUMBER   12 SPACING 192.00 MM
       COLUMN INTERACTION: MOMENT ABOUT Z -AXIS (KN-MET)
      P0        Pn max    P-bal.    M-bal.     e-bal. (MM)
    2268.75   1815.00    857.23    103.67     120.9
       M0       P-tens.   Des.Pn    Des.Mn     e/h
      47.74   -375.48    163.72      0.07    0.00028
       COLUMN INTERACTION: MOMENT ABOUT Y -AXIS (KN-MET)
      47.74   -375.48    163.72      4.29    0.01690
        ACI 318-11   COLUMN  NO.    99   DESIGN RESULTS
    STAAD SPACE                                              -- PAGE NO.  152
      47.74   -375.48    179.22      0.21    0.00078
      47.74   -375.48    179.22      2.93    0.01090
        ACI 318-11   COLUMN  NO.   110   DESIGN RESULTS
      47.74   -375.48    174.78      5.18    0.01977
      47.74   -375.48    174.78      4.69    0.01789
        ACI 318-11   COLUMN  NO.   111   DESIGN RESULTS
    STAAD SPACE                                              -- PAGE NO.  153
      47.74   -375.48    146.77      0.98    0.00431
      47.74   -375.48    146.77      4.75    0.02087
        ACI 318-11   COLUMN  NO.   144   DESIGN RESULTS
           AREA OF STEEL REQUIRED =  2015.1  SQ. MM
    12 - 16 MM               2.681      600      END     0.650
    2862.53   2290.02    853.42    151.34     177.3
     115.39  -1001.30    165.36     13.91    0.03005
    STAAD SPACE                                              -- PAGE NO.  154
     115.39  -1001.30    165.36    105.38    0.22758
        ACI 318-11   COLUMN  NO.   145   DESIGN RESULTS
      47.74   -375.48    110.93      0.59    0.00189
      47.74   -375.48    110.93     10.85    0.03493
        ACI 318-11   COLUMN  NO.   147   DESIGN RESULTS
    STAAD SPACE                                              -- PAGE NO.  155
      47.74   -375.48     24.35      6.10    0.08945
      47.74   -375.48     24.35      2.64    0.03866
        ACI 318-11   COLUMN  NO.   148   DESIGN RESULTS
           AREA OF STEEL REQUIRED =  1177.2  SQ. MM
     4 - 20 MM               1.396      606      END     0.650
    2407.30   1925.84    835.41    129.25     154.7
      63.88   -521.51    158.98     48.17    0.10822
      63.88   -521.51    158.98     39.61    0.08899
    STAAD SPACE                                              -- PAGE NO.  156
        ACI 318-11   COLUMN  NO.   153   DESIGN RESULTS
      47.74   -375.48    159.77      0.44    0.00202
      47.74   -375.48    159.77     12.56    0.05824
        ACI 318-11   COLUMN  NO.   154   DESIGN RESULTS
    STAAD SPACE                                              -- PAGE NO.  157
      47.74   -375.48    142.81      1.45    0.00752
      47.74   -375.48    142.81     14.74    0.07643
        ACI 318-11   COLUMN  NO.    61   DESIGN RESULTS
           AREA OF STEEL REQUIRED =   981.9  SQ. MM
     4 - 20 MM               1.396      608      END     0.650
      63.88   -521.51    491.93     21.72    0.01523
      63.88   -521.51    491.93     81.14    0.05688
        ACI 318-11   COLUMN  NO.    62   DESIGN RESULTS
    STAAD SPACE                                              -- PAGE NO.  158
           AREA OF STEEL REQUIRED =  1416.6  SQ. MM
     8 - 16 MM               1.787      608      STA     0.650
    2545.85   2036.68    845.75    127.99     151.3
      81.07   -667.53    347.99     29.12    0.02988
      81.07   -667.53    347.99     83.84    0.08605
        ACI 318-11   COLUMN  NO.    63   DESIGN RESULTS
           AREA OF STEEL REQUIRED =  1920.6  SQ. MM
     4 - 25 MM               2.182      600      END     0.650
    2685.62   2148.50    819.89    160.00     195.1
      96.05   -814.84    242.87     30.70    0.04515
    STAAD SPACE                                              -- PAGE NO.  159
      96.05   -814.84    242.87     95.70    0.14073
        ACI 318-11   COLUMN  NO.    64   DESIGN RESULTS
           AREA OF STEEL REQUIRED =  1221.3  SQ. MM
     4 - 20 MM               1.396      600      END     0.650
      63.88   -521.51     91.09     54.50    0.21369
      63.88   -521.51     91.09     26.67    0.10455
        ACI 318-11   COLUMN  NO.    68   DESIGN RESULTS
           AREA OF STEEL REQUIRED =   931.5  SQ. MM
    STAAD SPACE                                              -- PAGE NO.  160
      63.88   -521.51     82.21     43.65    0.18961
      63.88   -521.51     82.21     21.89    0.09508
        ACI 318-11   COLUMN  NO.    73   DESIGN RESULTS
      47.74   -375.48    305.05      7.67    0.00867
      47.74   -375.48    305.05     10.65    0.01203
    STAAD SPACE                                              -- PAGE NO.  161
        ACI 318-11   COLUMN  NO.    74   DESIGN RESULTS
           AREA OF STEEL REQUIRED =  1032.3  SQ. MM
     4 - 20 MM               1.396      605      END     0.650
      63.88   -521.51    366.08     67.22    0.06558
      63.88   -521.51    366.08     31.41    0.03065
        ACI 318-11   COLUMN  NO.    75   DESIGN RESULTS
    STAAD SPACE                                              -- PAGE NO.  162
      47.74   -375.48     96.70      4.00    0.01478
      47.74   -375.48     96.70     12.20    0.04507
        ACI 318-11   COLUMN  NO.    76   DESIGN RESULTS
      63.88   -521.51     81.21     47.03    0.20685
      63.88   -521.51     81.21     23.72    0.10433
        ACI 318-11   COLUMN  NO.    77   DESIGN RESULTS
    STAAD SPACE                                              -- PAGE NO.  163
      47.74   -375.48    395.93      0.06    0.00005
      47.74   -375.48    395.93      4.79    0.00417
        ACI 318-11   COLUMN  NO.    78   DESIGN RESULTS
      47.74   -375.48    263.62      1.15    0.00156
    STAAD SPACE                                              -- PAGE NO.  164
      47.74   -375.48    263.62      5.81    0.00787
        ACI 318-11   COLUMN  NO.    79   DESIGN RESULTS
      47.74   -375.48    135.80      5.53    0.01454
      47.74   -375.48    135.80      5.44    0.01430
        ACI 318-11   COLUMN  NO.    80   DESIGN RESULTS
           AREA OF STEEL REQUIRED =  1208.7  SQ. MM
    STAAD SPACE                                              -- PAGE NO.  165
      63.88   -521.51     91.51     49.53    0.19332
      63.88   -521.51     91.51     31.71    0.12375
        ACI 318-11   COLUMN  NO.    85   DESIGN RESULTS
      47.74   -375.48    153.73      7.45    0.01671
      47.74   -375.48    153.73     13.78    0.03091
    STAAD SPACE                                              -- PAGE NO.  166
        ACI 318-11   COLUMN  NO.    86   DESIGN RESULTS
           AREA OF STEEL REQUIRED =   969.3  SQ. MM
      63.88   -521.51    202.54     50.60    0.08923
      63.88   -521.51    202.54     30.94    0.05456
        ACI 318-11   COLUMN  NO.    87   DESIGN RESULTS
           AREA OF STEEL REQUIRED =  1202.4  SQ. MM
    STAAD SPACE                                              -- PAGE NO.  167
      63.88   -521.51     93.07     25.12    0.09641
      63.88   -521.51     93.07     55.31    0.21224
        ACI 318-11   COLUMN  NO.    97   DESIGN RESULTS
      47.74   -375.48    268.65      4.08    0.01014
      47.74   -375.48    268.65      3.47    0.00861
        ACI 318-11   COLUMN  NO.   100   DESIGN RESULTS
    STAAD SPACE                                              -- PAGE NO.  168
      47.74   -375.48    348.58      1.58    0.00302
      47.74   -375.48    348.58      1.06    0.00202
        ACI 318-11   COLUMN  NO.   101   DESIGN RESULTS
      47.74   -375.48    435.17      1.65    0.00252
    STAAD SPACE                                              -- PAGE NO.  169
      47.74   -375.48    435.17      2.05    0.00314
        ACI 318-11   COLUMN  NO.   103   DESIGN RESULTS
      47.74   -375.48    188.18      4.61    0.01633
      47.74   -375.48    188.18      5.90    0.02092
        ACI 318-11   COLUMN  NO.   149   DESIGN RESULTS
    STAAD SPACE                                              -- PAGE NO.  170
      47.74   -375.48    156.85      6.80    0.01496
      47.74   -375.48    156.85     12.41    0.02728
        ACI 318-11   COLUMN  NO.   150   DESIGN RESULTS
      47.74   -375.48     98.10      6.24    0.02272
      47.74   -375.48     98.10     14.57    0.05304
    STAAD SPACE                                              -- PAGE NO.  171
        ACI 318-11   COLUMN  NO.   151   DESIGN RESULTS
           AREA OF STEEL REQUIRED =  1296.9  SQ. MM
    12 - 12 MM               1.508      600      END     0.650
    2446.88   1957.51    862.51    117.05     135.7
      69.58   -563.22    100.12     25.64    0.09145
      69.58   -563.22    100.12     59.92    0.21373
        ACI 318-11   COLUMN  NO.   152   DESIGN RESULTS
    STAAD SPACE                                              -- PAGE NO.  172
      47.74   -375.48    197.03      7.35    0.02487
      47.74   -375.48    197.03      6.28    0.02126
   ********************END OF COLUMN DESIGN RESULTS********************