ACI 21.6.1 Requirements being applied to Gravity Columns?

I have some interior gravity-only concrete columns that keep getting the error that they don't meet the dimension requirements of ACI 21.6.1. But why would gravity columns need to meet those seismic requirements in the first place? How can i fix this?

Thank You

Parents Reply
  • A shear wall structure in SDC D still needs to have the gravity columns checked against 21.13. Presumably the design displacement in such a structure would be smaller than that of a Moment Frame structure, however.
    The link from 21.13 back to 21.6 should start with 21.6.3 however. I don't see any reason for 21.6.1.1 to be checked on gravity columns. Make sure your frame type is correct (ordinary moment frame in your case) and confirm if you are using the latest version 15.03.