ACI 21.6.1 Requirements being applied to Gravity Columns?

I have some interior gravity-only concrete columns that keep getting the error that they don't meet the dimension requirements of ACI 21.6.1. But why would gravity columns need to meet those seismic requirements in the first place? How can i fix this?

Thank You

Parents Reply
  • I am getting a similar problem with my concrete gravity columns when running the analysis with ACI 318-14. My columns are concrete, gravity only, the project is SDC D and the shear walls take all the lateral load.

    When I run the column analysis I am getting the following warning: Column section dimensions are not acceptable per ACI 318-14 Sec. 18.7.2

    Per the ACI 318-14 code section 18.7.2 (as noted below) is for columns of special moment frames. So its unclear why the columns (gravity only) are being required to meet a standard they are not part of?

    ACI 318-14 REFERENCED SECTION

    18.7—Columns of special moment frames
    18.7.1 Scope
    18.7.1.1 This section shall apply to columns of special moment frames that form part of the seismic-force-resisting system and are proportioned primarily to resist flexure, shear, and axial forces.

    18.7.2 Dimensional limits
    18.7.2.1 Columns shall satisfy (a) and (b):
    (a) The shortest cross-sectional dimension, measured on a straight line passing through the geometric centroid, shall be at least 12" 
    (b) The ratio of the shortest cross-sectional dimension to the perpendicular dimension shall be at least 0.4.