RAM SS Concrete Column Slenderness

Hello,

I have a few questions regarding column slenderness. In my model (v15.0) I am having a few slenderness issues and am trying to resolve them. It appears that the ACI 318 code has changed since 05 in terms of the kl/r limit, which I have found is what RAM enforces, so here are my questions.

1. RAM only flags columns as "failing" in slenderness if the ratio is above 100. Since it appears that this limit is no longer applicable in ACI 318-11, how can I ensure that my column design is per code since this is an old limit?

2. With ACI 318-11, moment magnification is the procedure to account for slenderness effects. Does RAM perform moment magnification? (per 10.10.6 and 10.10.7) If not, would I have to do calculations by hand and/or through another program to check column validity?

Thank you,

Beth

Parents Reply
  • Yes, RAM Structural System does not account for flexural stiffness of two-way slabs when determining K. If the columns supporting the two-way slab are defined as non-sway, I recommend using K=1. If the columns supporting the two-way are defined as sway, I would determine K accounting for an appropriate slab flexural stiffness and assign that value manually.

    There are different slenderness limts for non-sway and sway columns below which slenderness effects can be neglected. These are outlined in ACI 318-14 6.2.5. Those limits can result in different designs for a given K if the column assignment is switched from braced to unbraced.



Children
  • Karl,

    Your last reply has me questioning this, so I'm hoping you can either confirm and/or clarify. For sway columns in a two-way slabs without beams, my understanding is that k only needs to be manually calculated for sway columns if a first order analysis with moment magnification is used. If an elastic second order analysis was performed (P-Delta on in RAM Frame), then k should still be defined as 1 since ACI 318-14 6.7.1.2 directs to ACI 318-14 6.6.4.5 for moment amplification due to deflection along the member length of non-sway members. ACI 318-14 6.6.4.4.3 then states that k may be taken as 1 for non-sway members. Thank you for your help.

  • I do not want to speak for Karl / Bentley, but I agree with your assessment that k=1.0 is appropriate for calculating the moment magnification factor associated with Sections 6.7.1.2 and 6.6.4.5.  I also agree that the P-Delta analysis performed in RAM Frame satisfies the elastic second-order analysis permitted by Section 6.6.4.6.2.  The selected k-value should have no impact on the RAM Frame analysis.

    However, an accurate k-value is needed to properly check the slenderness limits of 6.2.5.  The problem I see is that RAM does not apply different k-values for the slenderness checks of 6.2.5 and the critical buckling load (Pc) in section 6.6.4.4.2.  The user must either apply k=1.0 and risk incorrectly ignoring slenderness effects, or apply k>1.0 and deal with a conservatively large magnification factor which, in some cases, could result in a very conservative column design.

    Karl / Bentley - Can you comment on this assessment?  Much appreciated!

  • CEI Engineer is correct. For sway columns supporting a two-way slab with no beams, a K-value greater than 1 should be assigned to check the slenderness limit of ACI 318-14 6.2.5. When accounting for the second order effects between member ends for the same column using the non-way sway moment magnification procedure, K=1 should be used. However, RAM Concrete Column is incorrectly using the larger K instead. This was logged as Defect #1028340, has now be fixed, and will be included in v17.01.00, which will be released within the next few weeks.



  • Thank you both. I'll keep an eye out for 17.01 to drop and hopefully clear this up. Thanks again.

  • Karl,  

    I'm running RAM SS V17.01.01. Has this issue been addressed? I was unable to find any documentation by Bentley on this. Thanks!