I am designing a foundation to support a 2,000 HP mine fan. This foundation will be designed in accordance with ACI 351.3R-04. In addition to performing manual calculations, I am going to use both Staadpro and Staad Foundation Advanced as computer-based solutions.
*Note - I've just downloaded Staad Foundation Advanced, and I'm aware of the machine foundation wizard. However, I've identified one (maybe two) errors with the output, so I'm likely just going to use that wizard output as a general reference.
Here are a few input parameters that might be of interest:
The foundation block is 37' long x 15' wide x 5' thick. There are also pedestals on top of the block that support the bearings/shaft/impeller and the motor. (I'd like to attach my model, but I'm not seeing that option.)
Ok.....so......as for the Staadpro model........is there a way of having Staadpro calculating the vibration amplitudes (in bold above)? I'm familiar with the Modal Analysis approach in Staadpro, but not so much the Time History function. Do either of these give an output of the vibration amplitudes?
Yes once you carry out the time history analysis you can go to the Postprocessing > Dynamics page and get time history of the velocities, displacements and accelerations as shown in the screenshot below. If you need the time-history data based on which these graphs are plotted, simply right click on the appropriate diagram and choose Save data in a text file ...
Answer Verified By: andysines
Sure. After you read the help documentation it may be useful to take a look at a few examples namely Example 16, 22 and 29 available as part of the help documentation as well. The corresponding STAAD.Pro models can be found within C:\SProV8i SS6\STAAD\Examp\US folder.