Greetings all!
I am designing a truss of 91m clear span and 25m height. I just want to confirm if my design is okay or not.
Some of the members are failed. I will pass these members and proceed for fabrication but before that I want to know if my mechanism is correct or any modification is required in my model.
If anyone can suggest me how to optimize the weight of truss, that would be great.
Also for the top chord of truss at eave location, I have considered the connection to be fixed with column. Is this okay.
Mt model input file is follows...
STAAD PLANESTART JOB INFORMATIONENGINEER DATE 18-Sep-17END JOB INFORMATIONINPUT WIDTH 79UNIT METER KNJOINT COORDINATES1 0 0 0; 2 2.2 0 0; 3 3.7 0 0; 4 5.2 0 0; 5 6.7 0 0; 6 8.2 0 0; 7 9.7 0 0;8 11.2 0 0; 9 12.7 0 0; 10 14.2 0 0; 11 15.7 0 0; 12 17.2 0 0; 13 18.7 0 0;14 20.2 0 0; 15 21.7 0 0; 16 23.2 0 0; 17 24.7 0 0; 18 26.2 0 0; 19 27.7 0 0;20 29.2 0 0; 21 30.7 0 0; 22 32.2 0 0; 23 33.7 0 0; 24 35.2 0 0; 25 36.7 0 0;26 38.2 0 0; 27 39.7 0 0; 28 41.2 0 0; 29 42.7 0 0; 30 44.2 0 0; 31 45.7 0 0;32 47.2 0 0; 33 48.7 0 0; 34 50.2 0 0; 35 51.7 0 0; 36 53.2 0 0; 37 54.7 0 0;38 56.2 0 0; 39 57.7 0 0; 40 59.2 0 0; 41 60.7 0 0; 42 62.2 0 0; 43 63.7 0 0;44 65.2 0 0; 45 66.7 0 0; 46 68.2 0 0; 47 69.7 0 0; 48 71.2 0 0; 49 72.7 0 0;50 74.2 0 0; 51 75.7 0 0; 52 77.2 0 0; 53 78.7 0 0; 54 80.2 0 0; 55 81.7 0 0;56 83.2 0 0; 57 84.7 0 0; 58 86.2 0 0; 59 87.7 0 0; 60 89.2 0 0; 61 91.4 0 0;62 2.2 0.11 0; 63 3.7 0.185 0; 64 5.2 0.26 0; 65 6.7 0.335 0; 66 8.2 0.41 0;67 9.7 0.485 0; 68 11.2 0.56 0; 69 12.7 0.635 0; 70 14.2 0.71 0;71 15.7 0.785 0; 72 17.2 0.86 0; 73 18.7 0.935 0; 74 20.2 1.01 0;75 21.7 1.085 0; 76 23.2 1.16 0; 77 24.7 1.235 0; 78 26.2 1.31 0;79 27.7 1.385 0; 80 29.2 1.46 0; 81 30.7 1.535 0; 82 32.2 1.61 0;83 33.7 1.685 0; 84 35.2 1.76 0; 85 36.7 1.835 0; 86 38.2 1.91 0;87 39.7 1.985 0; 88 41.2 2.06 0; 89 42.7 2.135 0; 90 44.2 2.21 0;91 45.7 2.285 0; 92 47.2 2.21 0; 93 48.7 2.135 0; 94 50.2 2.06 0;95 51.7 1.985 0; 96 53.2 1.91 0; 97 54.7 1.835 0; 98 56.2 1.76 0;99 57.7 1.685 0; 100 59.2 1.61 0; 101 60.7 1.535 0; 102 62.2 1.46 0;103 63.7 1.385 0; 104 65.2 1.31 0; 105 66.7 1.235 0; 106 68.2 1.16 0;107 69.7 1.085 0; 108 71.2 1.01 0; 109 72.7 0.935 0; 110 74.2 0.86 0;111 75.7 0.785 0; 112 77.2 0.71 0; 113 78.7 0.635 0; 114 80.2 0.56 0;115 81.7 0.485 0; 116 83.2 0.41 0; 117 84.7 0.335 0; 118 86.2 0.26 0;119 87.7 0.185 0; 120 89.2 0.11 0; 121 0 -25 0; 122 91.4 -25 0;MEMBER INCIDENCES1 1 2; 2 2 3; 3 3 4; 4 4 5; 5 5 6; 6 6 7; 7 7 8; 8 8 9; 9 9 10; 10 10 11;11 11 12; 12 12 13; 13 13 14; 14 14 15; 15 15 16; 16 16 17; 17 17 18; 18 18 19;19 19 20; 20 20 21; 21 21 22; 22 22 23; 23 23 24; 24 24 25; 25 25 26; 26 26 27;27 27 28; 28 28 29; 29 29 30; 30 30 31; 31 31 32; 32 32 33; 33 33 34; 34 34 35;35 35 36; 36 36 37; 37 37 38; 38 38 39; 39 39 40; 40 40 41; 41 41 42; 42 42 43;43 43 44; 44 44 45; 45 45 46; 46 46 47; 47 47 48; 48 48 49; 49 49 50; 50 50 51;51 51 52; 52 52 53; 53 53 54; 54 54 55; 55 55 56; 56 56 57; 57 57 58; 58 58 59;59 59 60; 60 60 61; 61 1 62; 62 62 63; 63 63 64; 64 64 65; 65 65 66; 66 66 67;67 67 68; 68 68 69; 69 69 70; 70 70 71; 71 71 72; 72 72 73; 73 73 74; 74 74 75;75 75 76; 76 76 77; 77 77 78; 78 78 79; 79 79 80; 80 80 81; 81 81 82; 82 82 83;83 83 84; 84 84 85; 85 85 86; 86 86 87; 87 87 88; 88 88 89; 89 89 90; 90 90 91;91 91 92; 92 92 93; 93 93 94; 94 94 95; 95 95 96; 96 96 97; 97 97 98; 98 98 99;99 99 100; 100 100 101; 101 101 102; 102 102 103; 103 103 104; 104 104 105;105 105 106; 106 106 107; 107 107 108; 108 108 109; 109 109 110; 110 110 111;111 111 112; 112 112 113; 113 113 114; 114 114 115; 115 115 116; 116 116 117;117 117 118; 118 118 119; 119 119 120; 120 120 61; 121 2 62; 122 3 63;123 4 64; 124 5 65; 125 6 66; 126 7 67; 127 8 68; 128 9 69; 129 10 70;130 11 71; 131 12 72; 132 13 73; 133 14 74; 134 15 75; 135 16 76; 136 17 77;137 18 78; 138 19 79; 139 20 80; 140 21 81; 141 22 82; 142 23 83; 143 24 84;144 25 85; 145 26 86; 146 27 87; 147 28 88; 148 29 89; 149 30 90; 150 31 91;151 32 92; 152 33 93; 153 34 94; 154 35 95; 155 36 96; 156 37 97; 157 38 98;158 39 99; 159 40 100; 160 41 101; 161 42 102; 162 43 103; 163 44 104;164 45 105; 165 46 106; 166 47 107; 167 48 108; 168 49 109; 169 50 110;170 51 111; 171 52 112; 172 53 113; 173 54 114; 174 55 115; 175 56 116;176 57 117; 177 58 118; 178 59 119; 179 60 120; 180 3 62; 181 4 63; 182 5 64;183 6 65; 184 7 66; 185 8 67; 186 9 68; 187 10 69; 188 11 70; 189 12 71;190 13 72; 191 14 73; 192 15 74; 193 16 75; 194 17 76; 195 18 77; 196 19 78;197 20 79; 198 21 80; 199 22 81; 200 23 82; 201 24 83; 202 25 84; 203 26 85;204 27 86; 205 28 87; 206 29 88; 207 30 89; 208 31 90; 209 31 92; 210 32 93;211 33 94; 212 34 95; 213 35 96; 214 36 97; 215 37 98; 216 38 99; 217 39 100;218 40 101; 219 41 102; 220 42 103; 221 43 104; 222 44 105; 223 45 106;224 46 107; 225 47 108; 226 48 109; 227 49 110; 228 50 111; 229 51 112;230 52 113; 231 53 114; 232 54 115; 233 55 116; 234 56 117; 235 57 118;236 58 119; 237 59 120; 238 121 1; 239 122 61;DEFINE MATERIAL STARTISOTROPIC STEELE 2.05e+008POISSON 0.3DENSITY 76.8195ALPHA 1.2e-005DAMP 0.03TYPE STEELSTRENGTH FY 253200 FU 407800 RY 1.5 RT 1.2END DEFINE MATERIALMEMBER PROPERTY AMERICAN238 239 TAPERED 2.04 0.016 2.04 0.5 0.0261 TO 120 TAPERED 2.08 0.016 2.08 0.6 0.04180 TO 237 TAPERED 0.5 0.005 0.5 0.15 0.006121 TO 179 TAPERED 0.466 0.005 0.466 0.225 0.01MEMBER PROPERTY1 TO 60 TAPERED 2.06 0.016 2.06 0.6 0.03CONSTANTSMATERIAL STEEL ALLSUPPORTS121 122 FIXEDMEMBER RELEASE1 TO 60 62 TO 119 121 TO 237 START MPZ 0.9991 TO 60 62 TO 119 121 TO 237 END MPZ 0.999999DEFINE IBC 2006SS 0.364 S1 0.13 I 1 RX 3.5 RZ 3.5 SCLASS 4 TL 6SELFWEIGHT 1 MEMBER WEIGHT61 TO 120 UNI 1.65LOAD 1 LOADTYPE Seismic TITLE EQXIBC LOAD X 1PERFORM ANALYSISCHANGELOAD 2 LOADTYPE Seismic TITLE EQX'IBC LOAD X -1PERFORM ANALYSISCHANGELOAD 3 LOADTYPE Dead TITLE DLSELFWEIGHT Y -1 MEMBER LOAD61 TO 120 UNI GY -1.65LOAD 4 LOADTYPE Live TITLE LLMEMBER LOAD61 TO 120 UNI GY -4.7LOAD 5 LOADTYPE Wind TITLE W1MEMBER LOAD238 UNI GX 10.904 2.5 2561 TO 120 UNI GY 9.541239 UNI GX 6.815 2.5 25LOAD 6 LOADTYPE Wind TITLE W2MEMBER LOAD238 UNI GX 6.815 2.5 2561 TO 120 UNI GY 9.541239 UNI GX 10.904 2.5 25LOAD 7 LOADTYPE Wind TITLE W3MEMBER LOAD238 UNI GX 9.541 2.5 2561 TO 120 UNI GY 9.541239 UNI GY 9.541 2.5 25LOAD COMB 8 GENERATED AISC GENERAL 13 1.0 LOAD COMB 9 GENERATED AISC GENERAL 23 1.0 4 1.0 LOAD COMB 10 GENERATED AISC GENERAL 33 1.0 4 0.75 LOAD COMB 11 GENERATED AISC GENERAL 43 1.0 5 1.0 LOAD COMB 12 GENERATED AISC GENERAL 53 1.0 6 1.0 LOAD COMB 13 GENERATED AISC GENERAL 63 1.0 7 1.0 LOAD COMB 14 GENERATED AISC GENERAL 73 1.0 1 0.7 LOAD COMB 15 GENERATED AISC GENERAL 83 1.0 2 0.7 LOAD COMB 16 GENERATED AISC GENERAL 93 1.0 1 -0.7 LOAD COMB 17 GENERATED AISC GENERAL 103 1.0 2 -0.7 LOAD COMB 18 GENERATED AISC GENERAL 113 1.0 4 0.75 5 0.75 LOAD COMB 19 GENERATED AISC GENERAL 123 1.0 4 0.75 6 0.75 LOAD COMB 20 GENERATED AISC GENERAL 133 1.0 4 0.75 7 0.75 LOAD COMB 21 GENERATED AISC GENERAL 143 1.0 4 0.75 1 0.525 LOAD COMB 22 GENERATED AISC GENERAL 153 1.0 4 0.75 2 0.525 LOAD COMB 23 GENERATED AISC GENERAL 163 1.0 4 0.75 1 -0.525 LOAD COMB 24 GENERATED AISC GENERAL 173 1.0 4 0.75 2 -0.525 LOAD COMB 25 GENERATED AISC GENERAL 183 0.6 5 1.0 LOAD COMB 26 GENERATED AISC GENERAL 193 0.6 6 1.0 LOAD COMB 27 GENERATED AISC GENERAL 203 0.6 7 1.0 LOAD COMB 28 GENERATED AISC GENERAL 213 0.6 1 0.7 LOAD COMB 29 GENERATED AISC GENERAL 223 0.6 2 0.7 LOAD COMB 30 GENERATED AISC GENERAL 233 0.6 1 -0.7 LOAD COMB 31 GENERATED AISC GENERAL 243 0.6 2 -0.7 PERFORM ANALYSIS PRINT ALLPARAMETER 1CODE AISC UNIFIED 2005MAIN 200 MEMB 121 TO 179 238 239METHOD ASDSTP 2 ALLUNT 1.5 MEMB 61 TO 120LY 2.5 MEMB 238 239UNB 2.5 MEMB 238 239UNT 2.5 MEMB 238 239CHECK CODE ALLPARAMETER 2CODE AISC UNIFIED 2005STEEL MEMBER TAKE OFF ALLPARAMETER 3CODE AISC UNIFIED 2005STEEL TAKE OFF ALLFINISH
Hi Nouman Mukhtar,
Please check the truss geometry - the actual height is only 2.2 m with 25 m columns - is this correct?
Answer Verified By: Nouman Mukhtar
Hi AndrejLogunov,
Yes it is correct. This height of truss is 2.285m and height of column is 25m.
The geometry looks little odd. Please check the rendered view of the model and see if this looks correct. The top and bottom chord members seem to overlap.
You should not release Mz for the top and bottom chord members. Releases are Ok for the braces and struts connecting the chords.
Depending on how the truss is connected to the column and whether that connection can take moment or not, you should decide on whether to apply the release at that junction to the members.
I saw that you use tapered I to define the cross sections even though your start and end depths are same. For nonstandard I shapes of uniform depth, one should preferably use User table Wide flange sections ( accessible through Tools > Create User Table in SS6 and lower versions and accessible though Specification > User table > Create User table in CE )
To get least weight structure, you may need to use SELECT as opposed to CHECK CODE. You can follow the Examp01.std available within C:\SProV8i SS6\STAAD\Examp\US for guidance. The design process is also explained in detail as part of the Application Example manual ( Help > Content > Application Examples > American Examples > 1.Plane Frame With Steel Design )
Thank you sir for your help. I will do as you advised and revert back to you.
Dear Mr. Sye,
I have modified my truss geometry and done the required changes. I have designed the truss with two options.
First option is moments releases in given in all truss members except the top chord members at eave. (Connection with main columns)
The file is as follows...
STAAD PLANESTART JOB INFORMATIONENGINEER DATE 18-Sep-17END JOB INFORMATIONINPUT WIDTH 79UNIT METER KNJOINT COORDINATES1 0 -2 0; 2 2.2 -2 0; 3 3.7 -2 0; 4 5.2 -2 0; 5 6.7 -2 0; 6 8.2 -2 0;7 9.7 -2 0; 8 11.2 -2 0; 9 12.7 -2 0; 10 14.2 -2 0; 11 15.7 -2 0; 12 17.2 -2 0;13 18.7 -2 0; 14 20.2 -2 0; 15 21.7 -2 0; 16 23.2 -2 0; 17 24.7 -2 0;18 26.2 -2 0; 19 27.7 -2 0; 20 29.2 -2 0; 21 30.7 -2 0; 22 32.2 -2 0;23 33.7 -2 0; 24 35.2 -2 0; 25 36.7 -2 0; 26 38.2 -2 0; 27 39.7 -2 0;28 41.2 -2 0; 29 42.7 -2 0; 30 44.2 -2 0; 31 45.7 -2 0; 32 47.2 -2 0;33 48.7 -2 0; 34 50.2 -2 0; 35 51.7 -2 0; 36 53.2 -2 0; 37 54.7 -2 0;38 56.2 -2 0; 39 57.7 -2 0; 40 59.2 -2 0; 41 60.7 -2 0; 42 62.2 -2 0;43 63.7 -2 0; 44 65.2 -2 0; 45 66.7 -2 0; 46 68.2 -2 0; 47 69.7 -2 0;48 71.2 -2 0; 49 72.7 -2 0; 50 74.2 -2 0; 51 75.7 -2 0; 52 77.2 -2 0;53 78.7 -2 0; 54 80.2 -2 0; 55 81.7 -2 0; 56 83.2 -2 0; 57 84.7 -2 0;58 86.2 -2 0; 59 87.7 -2 0; 60 89.2 -2 0; 61 91.4 -2 0; 62 2.2 0.11 0;63 3.7 0.185 0; 64 5.2 0.26 0; 65 6.7 0.335 0; 66 8.2 0.41 0; 67 9.7 0.485 0;68 11.2 0.56 0; 69 12.7 0.635 0; 70 14.2 0.71 0; 71 15.7 0.785 0;72 17.2 0.86 0; 73 18.7 0.935 0; 74 20.2 1.01 0; 75 21.7 1.085 0;76 23.2 1.16 0; 77 24.7 1.235 0; 78 26.2 1.31 0; 79 27.7 1.385 0;80 29.2 1.46 0; 81 30.7 1.535 0; 82 32.2 1.61 0; 83 33.7 1.685 0;84 35.2 1.76 0; 85 36.7 1.835 0; 86 38.2 1.91 0; 87 39.7 1.985 0;88 41.2 2.06 0; 89 42.7 2.135 0; 90 44.2 2.21 0; 91 45.7 2.285 0;92 47.2 2.21 0; 93 48.7 2.135 0; 94 50.2 2.06 0; 95 51.7 1.985 0;96 53.2 1.91 0; 97 54.7 1.835 0; 98 56.2 1.76 0; 99 57.7 1.685 0;100 59.2 1.61 0; 101 60.7 1.535 0; 102 62.2 1.46 0; 103 63.7 1.385 0;104 65.2 1.31 0; 105 66.7 1.235 0; 106 68.2 1.16 0; 107 69.7 1.085 0;108 71.2 1.01 0; 109 72.7 0.935 0; 110 74.2 0.86 0; 111 75.7 0.785 0;112 77.2 0.71 0; 113 78.7 0.635 0; 114 80.2 0.56 0; 115 81.7 0.485 0;116 83.2 0.41 0; 117 84.7 0.335 0; 118 86.2 0.26 0; 119 87.7 0.185 0;120 89.2 0.11 0; 121 0 -27 0; 122 91.4 -27 0; 123 0 0 0; 124 91.4 0 0;MEMBER INCIDENCES1 1 2; 2 2 3; 3 3 4; 4 4 5; 5 5 6; 6 6 7; 7 7 8; 8 8 9; 9 9 10; 10 10 11;11 11 12; 12 12 13; 13 13 14; 14 14 15; 15 15 16; 16 16 17; 17 17 18; 18 18 19;19 19 20; 20 20 21; 21 21 22; 22 22 23; 23 23 24; 24 24 25; 25 25 26; 26 26 27;27 27 28; 28 28 29; 29 29 30; 30 30 31; 31 31 32; 32 32 33; 33 33 34; 34 34 35;35 35 36; 36 36 37; 37 37 38; 38 38 39; 39 39 40; 40 40 41; 41 41 42; 42 42 43;43 43 44; 44 44 45; 45 45 46; 46 46 47; 47 47 48; 48 48 49; 49 49 50; 50 50 51;51 51 52; 52 52 53; 53 53 54; 54 54 55; 55 55 56; 56 56 57; 57 57 58; 58 58 59;59 59 60; 60 60 61; 62 62 63; 63 63 64; 64 64 65; 65 65 66; 66 66 67; 67 67 68;68 68 69; 69 69 70; 70 70 71; 71 71 72; 72 72 73; 73 73 74; 74 74 75; 75 75 76;76 76 77; 77 77 78; 78 78 79; 79 79 80; 80 80 81; 81 81 82; 82 82 83; 83 83 84;84 84 85; 85 85 86; 86 86 87; 87 87 88; 88 88 89; 89 89 90; 90 90 91; 91 91 92;92 92 93; 93 93 94; 94 94 95; 95 95 96; 96 96 97; 97 97 98; 98 98 99;99 99 100; 100 100 101; 101 101 102; 102 102 103; 103 103 104; 104 104 105;105 105 106; 106 106 107; 107 107 108; 108 108 109; 109 109 110; 110 110 111;111 111 112; 112 112 113; 113 113 114; 114 114 115; 115 115 116; 116 116 117;117 117 118; 118 118 119; 119 119 120; 121 2 62; 122 3 63; 123 4 64; 124 5 65;125 6 66; 126 7 67; 127 8 68; 128 9 69; 129 10 70; 130 11 71; 131 12 72;132 13 73; 133 14 74; 134 15 75; 135 16 76; 136 17 77; 137 18 78; 138 19 79;139 20 80; 140 21 81; 141 22 82; 142 23 83; 143 24 84; 144 25 85; 145 26 86;146 27 87; 147 28 88; 148 29 89; 149 30 90; 150 31 91; 151 32 92; 152 33 93;153 34 94; 154 35 95; 155 36 96; 156 37 97; 157 38 98; 158 39 99; 159 40 100;160 41 101; 161 42 102; 162 43 103; 163 44 104; 164 45 105; 165 46 106;166 47 107; 167 48 108; 168 49 109; 169 50 110; 170 51 111; 171 52 112;172 53 113; 173 54 114; 174 55 115; 175 56 116; 176 57 117; 177 58 118;178 59 119; 179 60 120; 180 3 62; 181 4 63; 182 5 64; 183 6 65; 184 7 66;185 8 67; 186 9 68; 187 10 69; 188 11 70; 189 12 71; 190 13 72; 191 14 73;192 15 74; 193 16 75; 194 17 76; 195 18 77; 196 19 78; 197 20 79; 198 21 80;199 22 81; 200 23 82; 201 24 83; 202 25 84; 203 26 85; 204 27 86; 205 28 87;206 29 88; 207 30 89; 208 31 90; 209 31 92; 210 32 93; 211 33 94; 212 34 95;213 35 96; 214 36 97; 215 37 98; 216 38 99; 217 39 100; 218 40 101; 219 41 102;220 42 103; 221 43 104; 222 44 105; 223 45 106; 224 46 107; 225 47 108;226 48 109; 227 49 110; 228 50 111; 229 51 112; 230 52 113; 231 53 114;232 54 115; 233 55 116; 234 56 117; 235 57 118; 236 58 119; 237 59 120;238 121 1; 239 122 61; 240 1 123; 241 123 62; 242 61 124; 243 124 120;244 2 123; 245 60 124;START USER TABLETABLE 1UNIT METER KNWIDE FLANGEW1000X16X300X160.02752 1.01 0.016 0.3 0.02 0.0041576 9.03311e-005 2.92437e-006 0.01616 0.012W500X5X200X80.00562 0.5 0.005 0.2 0.008 0.00024091 1.06717e-005 8.84333e-008 0.0025 0.0032W1000X12X300X200.024 1.04 0.012 0.3 0.02 0.0041216 9.0144e-005 2.176e-006 0.01248 0.012TABLE 2UNIT METER KNWIDE FLANGEW500X5X200X160.00482 0.5 0.005 0.15 0.008 0.000192493 4.50504e-006 7.13667e-008 -0.0025 0.0024ENDDEFINE MATERIAL STARTISOTROPIC STEELE 2.05e+008POISSON 0.3DENSITY 76.8195ALPHA 1.2e-005DAMP 0.03TYPE STEELSTRENGTH FY 253200 FU 407800 RY 1.5 RT 1.2END DEFINE MATERIALMEMBER PROPERTY AMERICAN121 TO 237 244 245 TAPERED 0.516 0.005 0.516 0.2 0.0081 TO 60 62 TO 119 241 243 TAPERED 1.54 0.012 1.54 0.3 0.02MEMBER PROPERTY AMERICAN238 TO 240 242 TAPERED 1.54 0.016 1.54 0.5 0.025CONSTANTSMATERIAL STEEL ALLSUPPORTS121 122 FIXEDMEMBER RELEASE1 TO 60 62 TO 119 121 TO 237 244 245 START MPZ 11 TO 60 62 TO 119 121 TO 237 244 245 END MPZ 1DEFINE IBC 2006SS 0.364 S1 0.13 I 1 RX 3.5 RZ 3.5 SCLASS 4 TL 6SELFWEIGHT 1 MEMBER WEIGHT62 TO 119 241 243 UNI 1.65LOAD 1 LOADTYPE Seismic TITLE EQXIBC LOAD X 1PERFORM ANALYSISCHANGELOAD 2 LOADTYPE Seismic TITLE EQX'IBC LOAD X -1PERFORM ANALYSISCHANGELOAD 3 LOADTYPE Dead TITLE DLSELFWEIGHT Y -1 MEMBER LOAD62 TO 119 241 243 UNI GY -1.65LOAD 4 LOADTYPE Live TITLE LLMEMBER LOAD62 TO 119 241 243 UNI GY -4.7LOAD 5 LOADTYPE Wind TITLE W1MEMBER LOAD238 UNI GX 10.904 2.5 2562 TO 119 241 243 UNI GY 9.541239 UNI GX 6.815 2.5 25240 UNI GX 10.904242 UNI GX 6.815LOAD 6 LOADTYPE Wind TITLE W2MEMBER LOAD238 UNI GX 6.815 2.5 2562 TO 119 241 243 UNI GY 9.541239 UNI GX 10.904 2.5 25240 UNI GX 6.815242 UNI GX 10.904LOAD 7 LOADTYPE Wind TITLE W3MEMBER LOAD238 UNI GX 9.541 2.5 2562 TO 119 241 243 UNI GY 9.541239 UNI GX 9.541 2.5 25240 UNI GX 9.541242 UNI GX 9.541LOAD COMB 8 GENERATED AISC GENERAL 13 1.0 LOAD COMB 9 GENERATED AISC GENERAL 23 1.0 4 1.0 LOAD COMB 10 GENERATED AISC GENERAL 33 1.0 4 0.75 LOAD COMB 11 GENERATED AISC GENERAL 43 1.0 5 1.0 LOAD COMB 12 GENERATED AISC GENERAL 53 1.0 6 1.0 LOAD COMB 13 GENERATED AISC GENERAL 63 1.0 7 1.0 LOAD COMB 14 GENERATED AISC GENERAL 73 1.0 1 0.7 LOAD COMB 15 GENERATED AISC GENERAL 83 1.0 2 0.7 LOAD COMB 16 GENERATED AISC GENERAL 93 1.0 1 -0.7 LOAD COMB 17 GENERATED AISC GENERAL 103 1.0 2 -0.7 LOAD COMB 18 GENERATED AISC GENERAL 113 1.0 4 0.75 5 0.75 LOAD COMB 19 GENERATED AISC GENERAL 123 1.0 4 0.75 6 0.75 LOAD COMB 20 GENERATED AISC GENERAL 133 1.0 4 0.75 7 0.75 LOAD COMB 21 GENERATED AISC GENERAL 143 1.0 4 0.75 1 0.525 LOAD COMB 22 GENERATED AISC GENERAL 153 1.0 4 0.75 2 0.525 LOAD COMB 23 GENERATED AISC GENERAL 163 1.0 4 0.75 1 -0.525 LOAD COMB 24 GENERATED AISC GENERAL 173 1.0 4 0.75 2 -0.525 LOAD COMB 25 GENERATED AISC GENERAL 183 0.6 5 1.0 LOAD COMB 26 GENERATED AISC GENERAL 193 0.6 6 1.0 LOAD COMB 27 GENERATED AISC GENERAL 203 0.6 7 1.0 LOAD COMB 28 GENERATED AISC GENERAL 213 0.6 1 0.7 LOAD COMB 29 GENERATED AISC GENERAL 223 0.6 2 0.7 LOAD COMB 30 GENERATED AISC GENERAL 233 0.6 1 -0.7 LOAD COMB 31 GENERATED AISC GENERAL 243 0.6 2 -0.7 PERFORM ANALYSIS PRINT ALLPARAMETER 1CODE AISC UNIFIED 2005MAIN 200 ALLMETHOD ASDSTP 2 ALLUNT 1.5 MEMB 62 TO 119 241 243LY 2.5 MEMB 238 239UNB 2.5 MEMB 238 239UNT 2.5 MEMB 238 239CHECK CODE ALLPARAMETER 2CODE AISC UNIFIED 2005STEEL MEMBER TAKE OFF ALLPARAMETER 3CODE AISC UNIFIED 2005STEEL TAKE OFF ALLFINISH