RAM CONCEPT: Large Stabilizing Reaction Floating Loading

I have a two way flat plate. When import from Ram SS, I imported lateral analysis loads too. It created lateral layers i.e. wind, seismic. However, when calculate, there is this "large Stabilizing Reaction Floating Loading" on every lateral layer. Should I not import lateral analysis load or how do I resolve this error?

Parents
  • The error appear to be associated with the slab edges on the Level C Layout that are defined with 0" offsets and are snapped to the centerlines of beams and columns.

    To resolve the problem, replace these slab edges with new ones that have a non-zero offset and redefine the decks so they extend to the new slab edge boundary. In RAM Frame, click on Assign - Nodes - Diaphragm Connection and reassign the Global condition to all nodes. I am not sure why this is required, but I generated unexpected warnings during the analysis if this was not done. After re-running the analyses, reimport into RAM Concept and you should find that the error no longer occurs.

    Please post back and confirm that you are also able to eliminate the errors using these steps.  



    Answer Verified By: Ang Liu 

  • I followed all these steps and the error is till there. I do not know a better way to exactly locate the slab edge o the wall/ column surface but I basically set them at non zero. When you do it, did you set the slab edge at a certain point to make it correct? Also with the offset, I saw punching shear issue with columns sitting in the wall, which is weird. Can you advice what to do here? I can reupload the model if necessary. Thanks.

  • Please upload your revised model for review. I will send you a working model back via a private message.



Reply Children
  • There are 3 remaining slab edge segments defined with 0" offset in the model. These are marked in the screen capture below. Replace these segments with slab edge segments with non-zero offsets and then redefine the decks sot that they extend to the new slab edge. This should resolve the problem.

    Punching checks in RAM Concept do not account for walls that are connected to the column. The critical section is based on the column shape only. Also, the punching shear stress is based on the column reaction only and excludes any force in the walls. If a punching check is needed at these locations, it would be better to check it outside the program for these reasons.



    Answer Verified By: Ang Liu 

  • It worked!!! I will have to import new lateral analysis load to run the updated model. Thanks for all the effort you put in Karl. 

    Other than running it by hand, is there any Bentley program can perform punching check with the situation we have where columns sitting in the wall? Please let me know.