Large Displacements
I modeled a 25 storey building frame and analyzed it for standard dead loads and live load and wind loads. But the results are showing very large displacements node to node as well as in beams for about 46 inches. Is there something wrong with the procedure?
  • Which product are you talking about? Could you attach the related model?
  • staad pro model. here is a sample staad editor input
    STAAD SPACE
    START JOB INFORMATION
    ENGINEER DATE 27-Nov-17
    END JOB INFORMATION
    INPUT WIDTH 79
    UNIT FEET KIP
    JOINT COORDINATES
    1 0 0 0; 2 13.33 0 0; 3 26.66 0 0; 4 39.99 0 0; 5 49.32 0 0; 6 62.65 0 0;
    7 75.98 0 0; 8 89.3 0 0; 9 0 0 15.625; 10 13.33 0 15.625; 11 26.66 0 15.625;
    12 39.99 0 15.625; 13 49.32 0 15.625; 14 62.65 0 15.625; 15 75.98 0 15.625;
    16 89.3 0 15.625; 17 0 0 31.25; 18 13.33 0 31.25; 19 26.66 0 31.25;
    20 39.99 0 31.25; 21 49.32 0 31.25; 22 62.65 0 31.25; 23 75.98 0 31.25;
    24 89.3 0 31.25; 25 0 0 68.5; 26 13.33 0 68.5; 27 26.66 0 68.5;
    28 39.99 0 68.5; 29 49.32 0 68.5; 30 62.65 0 68.5; 31 75.98 0 68.5;
    32 89.3 0 68.5; 33 0 0 52.875; 34 13.33 0 52.875; 35 26.66 0 52.875;
    36 39.99 0 52.875; 37 49.32 0 52.875; 38 62.65 0 52.875; 39 75.98 0 52.875;
    40 89.3 0 52.875; 41 0 0 37.25; 42 13.33 0 37.25; 43 26.66 0 37.25;
    44 39.99 0 37.25; 45 49.32 0 37.25; 46 62.65 0 37.25; 47 75.98 0 37.25;
    48 89.3 0 37.25; 49 0 -29 0; 50 0 -29 15.625; 51 0 -29 31.25; 52 0 -29 68.5;
    53 0 -29 52.875; 54 0 -29 37.25; 55 13.33 -25.43 0; 56 13.33 -25.43 15.625;
    57 13.33 -25.43 31.25; 58 13.33 -25.43 68.5; 59 13.33 -25.43 52.875;
    60 13.33 -25.43 37.25; 61 26.66 -21.86 0; 62 26.66 -21.86 15.625;
    63 26.66 -21.86 31.25; 64 26.66 -21.86 68.5; 65 26.66 -21.86 52.875;
    66 26.66 -21.86 37.25; 67 39.99 -18.29 0; 68 39.99 -18.29 15.625;
    69 39.99 -18.29 31.25; 70 39.99 -18.29 68.5; 71 39.99 -18.29 52.875;
    72 39.99 -18.29 37.25; 73 49.32 -15.8 0; 74 49.32 -15.8 15.625;
    75 49.32 -15.8 31.25; 76 49.32 -15.8 68.5; 77 49.32 -15.8 52.875;
    78 49.32 -15.8 37.25; 79 62.65 -12.23 0; 80 62.65 -12.23 15.625;
    81 62.65 -12.23 31.25; 82 62.65 -12.23 68.5; 83 62.65 -12.23 52.875;
    84 62.65 -12.23 37.25; 85 75.98 -8.66 0; 86 75.98 -8.66 15.625;
    87 75.98 -8.66 31.25; 88 75.98 -8.66 68.5; 89 75.98 -8.66 52.875;
    90 75.98 -8.66 37.25; 91 89.3 -5.09 0; 92 89.3 -5.09 15.625;
    93 89.3 -5.09 31.25; 94 89.3 -5.09 68.5; 95 89.3 -5.09 52.875;
    96 89.3 -5.09 37.25; 97 0 10 0; 98 13.33 10 0; 99 26.66 10 0; 100 39.99 10 0;
    101 49.32 10 0; 102 62.65 10 0; 103 75.98 10 0; 104 89.3 10 0; 105 0 10 15.625;
    106 13.33 10 15.625; 107 26.66 10 15.625; 108 39.99 10 15.625;
    109 49.32 10 15.625; 110 62.65 10 15.625; 111 75.98 10 15.625;
    112 89.3 10 15.625; 113 0 10 31.25; 114 13.33 10 31.25; 115 26.66 10 31.25;
    116 39.99 10 31.25; 117 49.32 10 31.25; 118 62.65 10 31.25; 119 75.98 10 31.25;
    120 89.3 10 31.25; 121 0 10 68.5; 122 13.33 10 68.5; 123 26.66 10 68.5;
    124 39.99 10 68.5; 125 49.32 10 68.5; 126 62.65 10 68.5; 127 75.98 10 68.5;
    128 89.3 10 68.5; 129 0 10 52.875; 130 13.33 10 52.875; 131 26.66 10 52.875;
    132 39.99 10 52.875; 133 49.32 10 52.875; 134 62.65 10 52.875;
    135 75.98 10 52.875; 136 89.3 10 52.875; 137 0 10 37.25; 138 13.33 10 37.25;
    139 26.66 10 37.25; 140 39.99 10 37.25; 141 49.32 10 37.25; 142 62.65 10 37.25;
    143 75.98 10 37.25; 144 89.3 10 37.25; 145 0 20 0; 146 13.33 20 0;
    147 26.66 20 0; 148 39.99 20 0; 149 49.32 20 0; 150 62.65 20 0; 151 75.98 20 0;
    152 89.3 20 0; 153 0 20 15.625; 154 13.33 20 15.625; 155 26.66 20 15.625;
    156 39.99 20 15.625; 157 49.32 20 15.625; 158 62.65 20 15.625;
    159 75.98 20 15.625; 160 89.3 20 15.625; 161 0 20 31.25; 162 13.33 20 31.25;
    163 26.66 20 31.25; 164 39.99 20 31.25; 165 49.32 20 31.25; 166 62.65 20 31.25;
    167 75.98 20 31.25; 168 89.3 20 31.25; 169 0 20 68.5; 170 13.33 20 68.5;
    171 26.66 20 68.5; 172 39.99 20 68.5; 173 49.32 20 68.5; 174 62.65 20 68.5;
    175 75.98 20 68.5; 176 89.3 20 68.5; 177 0 20 52.875; 178 13.33 20 52.875;
    179 26.66 20 52.875; 180 39.99 20 52.875; 181 49.32 20 52.875;
    182 62.65 20 52.875; 183 75.98 20 52.875; 184 89.3 20 52.875; 185 0 20 37.25;
    186 13.33 20 37.25; 187 26.66 20 37.25; 188 39.99 20 37.25; 189 49.32 20 37.25;
    190 62.65 20 37.25; 191 75.98 20 37.25; 192 89.3 20 37.25; 193 0 30 0;
    194 13.33 30 0; 195 26.66 30 0; 196 39.99 30 0; 197 49.32 30 0; 198 62.65 30 0;
    199 75.98 30 0; 200 89.3 30 0; 201 0 30 15.625; 202 13.33 30 15.625;
    203 26.66 30 15.625; 204 39.99 30 15.625; 205 49.32 30 15.625;
    206 62.65 30 15.625; 207 75.98 30 15.625; 208 89.3 30 15.625; 209 0 30 31.25;
    210 13.33 30 31.25; 211 26.66 30 31.25; 212 39.99 30 31.25; 213 49.32 30 31.25;
    214 62.65 30 31.25; 215 75.98 30 31.25; 216 89.3 30 31.25; 217 0 30 68.5;
    218 13.33 30 68.5; 219 26.66 30 68.5; 220 39.99 30 68.5; 221 49.32 30 68.5;
    222 62.65 30 68.5; 223 75.98 30 68.5; 224 89.3 30 68.5; 225 0 30 52.875;
    226 13.33 30 52.875; 227 26.66 30 52.875; 228 39.99 30 52.875;
    229 49.32 30 52.875; 230 62.65 30 52.875; 231 75.98 30 52.875;
    232 89.3 30 52.875; 233 0 30 37.25; 234 13.33 30 37.25; 235 26.66 30 37.25;
    236 39.99 30 37.25; 237 49.32 30 37.25; 238 62.65 30 37.25; 239 75.98 30 37.25;
    240 89.3 30 37.25; 241 0 40 0; 242 13.33 40 0; 243 26.66 40 0; 244 39.99 40 0;
    245 49.32 40 0; 246 62.65 40 0; 247 75.98 40 0; 248 89.3 40 0; 249 0 40 15.625;
    250 13.33 40 15.625; 251 26.66 40 15.625; 252 39.99 40 15.625;
    253 49.32 40 15.625; 254 62.65 40 15.625; 255 75.98 40 15.625;
    256 89.3 40 15.625; 257 0 40 31.25; 258 13.33 40 31.25; 259 26.66 40 31.25;
    260 39.99 40 31.25; 261 49.32 40 31.25; 262 62.65 40 31.25; 263 75.98 40 31.25;
    264 89.3 40 31.25; 265 0 40 68.5; 266 13.33 40 68.5; 267 26.66 40 68.5;
    268 39.99 40 68.5; 269 49.32 40 68.5; 270 62.65 40 68.5; 271 75.98 40 68.5;
    272 89.3 40 68.5; 273 0 40 52.875; 274 13.33 40 52.875; 275 26.66 40 52.875;
    276 39.99 40 52.875; 277 49.32 40 52.875; 278 62.65 40 52.875;
    279 75.98 40 52.875; 280 89.3 40 52.875; 281 0 40 37.25; 282 13.33 40 37.25;
    283 26.66 40 37.25; 284 39.99 40 37.25; 285 49.32 40 37.25; 286 62.65 40 37.25;
    287 75.98 40 37.25; 288 89.3 40 37.25; 289 0 50 0; 290 13.33 50 0;
    291 26.66 50 0; 292 39.99 50 0; 293 49.32 50 0; 294 62.65 50 0; 295 75.98 50 0;
    296 89.3 50 0; 297 0 50 15.625; 298 13.33 50 15.625; 299 26.66 50 15.625;
    300 39.99 50 15.625; 301 49.32 50 15.625; 302 62.65 50 15.625;
    303 75.98 50 15.625; 304 89.3 50 15.625; 305 0 50 31.25; 306 13.33 50 31.25;
    307 26.66 50 31.25; 308 39.99 50 31.25; 309 49.32 50 31.25; 310 62.65 50 31.25;
    311 75.98 50 31.25; 312 89.3 50 31.25; 313 0 50 68.5; 314 13.33 50 68.5;
    315 26.66 50 68.5; 316 39.99 50 68.5; 317 49.32 50 68.5; 318 62.65 50 68.5;
    319 75.98 50 68.5; 320 89.3 50 68.5; 321 0 50 52.875; 322 13.33 50 52.875;
    323 26.66 50 52.875; 324 39.99 50 52.875; 325 49.32 50 52.875;
    326 62.65 50 52.875; 327 75.98 50 52.875; 328 89.3 50 52.875; 329 0 50 37.25;
    330 13.33 50 37.25; 331 26.66 50 37.25; 332 39.99 50 37.25; 333 49.32 50 37.25;
    334 62.65 50 37.25; 335 75.98 50 37.25; 336 89.3 50 37.25; 337 0 60 0;
    338 13.33 60 0; 339 26.66 60 0; 340 39.99 60 0; 341 49.32 60 0; 342 62.65 60 0;
    343 75.98 60 0; 344 89.3 60 0; 345 0 60 15.625; 346 13.33 60 15.625;
    347 26.66 60 15.625; 348 39.99 60 15.625; 349 49.32 60 15.625;
    350 62.65 60 15.625; 351 75.98 60 15.625; 352 89.3 60 15.625; 353 0 60 31.25;
    354 13.33 60 31.25; 355 26.66 60 31.25; 356 39.99 60 31.25; 357 49.32 60 31.25;
    358 62.65 60 31.25; 359 75.98 60 31.25; 360 89.3 60 31.25; 361 0 60 68.5;
    362 13.33 60 68.5; 363 26.66 60 68.5; 364 39.99 60 68.5; 365 49.32 60 68.5;
    366 62.65 60 68.5; 367 75.98 60 68.5; 368 89.3 60 68.5; 369 0 60 52.875;
    370 13.33 60 52.875; 371 26.66 60 52.875; 372 39.99 60 52.875;
    373 49.32 60 52.875; 374 62.65 60 52.875; 375 75.98 60 52.875;
    376 89.3 60 52.875; 377 0 60 37.25; 378 13.33 60 37.25; 379 26.66 60 37.25;
    380 39.99 60 37.25; 381 49.32 60 37.25; 382 62.65 60 37.25; 383 75.98 60 37.25;
    384 89.3 60 37.25; 385 0 70 0; 386 13.33 70 0; 387 26.66 70 0; 388 39.99 70 0;
    389 49.32 70 0; 390 62.65 70 0; 391 75.98 70 0; 392 89.3 70 0; 393 0 70 15.625;
    394 13.33 70 15.625; 395 26.66 70 15.625; 396 39.99 70 15.625;
    397 49.32 70 15.625; 398 62.65 70 15.625; 399 75.98 70 15.625;
    400 89.3 70 15.625; 401 0 70 31.25; 402 13.33 70 31.25; 403 26.66 70 31.25;
    404 39.99 70 31.25; 405 49.32 70 31.25; 406 62.65 70 31.25; 407 75.98 70 31.25;
    408 89.3 70 31.25; 409 0 70 68.5; 410 13.33 70 68.5; 411 26.66 70 68.5;
    412 39.99 70 68.5; 413 49.32 70 68.5; 414 62.65 70 68.5; 415 75.98 70 68.5;
    416 89.3 70 68.5; 417 0 70 52.875; 418 13.33 70 52.875; 419 26.66 70 52.875;
    420 39.99 70 52.875; 421 49.32 70 52.875; 422 62.65 70 52.875;
    423 75.98 70 52.875; 424 89.3 70 52.875; 425 0 70 37.25; 426 13.33 70 37.25;
    427 26.66 70 37.25; 428 39.99 70 37.25; 429 49.32 70 37.25; 430 62.65 70 37.25;
    431 75.98 70 37.25; 432 89.3 70 37.25; 433 0 80 0; 434 13.33 80 0;
    435 26.66 80 0; 436 39.99 80 0; 437 49.32 80 0; 438 62.65 80 0; 439 75.98 80 0;
    440 89.3 80 0; 441 0 80 15.625; 442 13.33 80 15.625; 443 26.66 80 15.625;
    444 39.99 80 15.625; 445 49.32 80 15.625; 446 62.65 80 15.625;
    447 75.98 80 15.625; 448 89.3 80 15.625; 449 0 80 31.25; 450 13.33 80 31.25;
    451 26.66 80 31.25; 452 39.99 80 31.25; 453 49.32 80 31.25; 454 62.65 80 31.25;
    455 75.98 80 31.25; 456 89.3 80 31.25; 457 0 80 68.5; 458 13.33 80 68.5;
    459 26.66 80 68.5; 460 39.99 80 68.5; 461 49.32 80 68.5; 462 62.65 80 68.5;
    463 75.98 80 68.5; 464 89.3 80 68.5; 465 0 80 52.875; 466 13.33 80 52.875;
    467 26.66 80 52.875; 468 39.99 80 52.875; 469 49.32 80 52.875;
    470 62.65 80 52.875; 471 75.98 80 52.875; 472 89.3 80 52.875; 473 0 80 37.25;
    474 13.33 80 37.25; 475 26.66 80 37.25; 476 39.99 80 37.25; 477 49.32 80 37.25;
    478 62.65 80 37.25; 479 75.98 80 37.25; 480 89.3 80 37.25; 481 0 90 0;
    482 13.33 90 0; 483 26.66 90 0; 484 39.99 90 0; 485 49.32 90 0; 486 62.65 90 0;
    487 75.98 90 0; 488 89.3 90 0; 489 0 90 15.625; 490 13.33 90 15.625;
    491 26.66 90 15.625; 492 39.99 90 15.625; 493 49.32 90 15.625;
    494 62.65 90 15.625; 495 75.98 90 15.625; 496 89.3 90 15.625; 497 0 90 31.25;
    498 13.33 90 31.25; 499 26.66 90 31.25; 500 39.99 90 31.25; 501 49.32 90 31.25;
    502 62.65 90 31.25; 503 75.98 90 31.25; 504 89.3 90 31.25; 505 0 90 68.5;
    506 13.33 90 68.5; 507 26.66 90 68.5; 508 39.99 90 68.5; 509 49.32 90 68.5;
    510 62.65 90 68.5; 511 75.98 90 68.5; 512 89.3 90 68.5; 513 0 90 52.875;
    514 13.33 90 52.875; 515 26.66 90 52.875; 516 39.99 90 52.875;
    517 49.32 90 52.875; 518 62.65 90 52.875; 519 75.98 90 52.875;
    520 89.3 90 52.875; 521 0 90 37.25; 522 13.33 90 37.25; 523 26.66 90 37.25;
    524 39.99 90 37.25; 525 49.32 90 37.25; 526 62.65 90 37.25; 527 75.98 90 37.25;
    528 89.3 90 37.25; 529 0 100 0; 530 13.33 100 0; 531 26.66 100 0;
    532 39.99 100 0; 533 49.32 100 0; 534 62.65 100 0; 535 75.98 100 0;
    536 89.3 100 0; 537 0 100 15.625; 538 13.33 100 15.625; 539 26.66 100 15.625;
    540 39.99 100 15.625; 541 49.32 100 15.625; 542 62.65 100 15.625;
    543 75.98 100 15.625; 544 89.3 100 15.625; 545 0 100 31.25;
    546 13.33 100 31.25; 547 26.66 100 31.25; 548 39.99 100 31.25;
    549 49.32 100 31.25; 550 62.65 100 31.25; 551 75.98 100 31.25;
    552 89.3 100 31.25; 553 0 100 68.5; 554 13.33 100 68.5; 555 26.66 100 68.5;
    556 39.99 100 68.5; 557 49.32 100 68.5; 558 62.65 100 68.5; 559 75.98 100 68.5;
    560 89.3 100 68.5; 561 0 100 52.875; 562 13.33 100 52.875;
    563 26.66 100 52.875; 564 39.99 100 52.875; 565 49.32 100 52.875;
    566 62.65 100 52.875; 567 75.98 100 52.875; 568 89.3 100 52.875;
    569 0 100 37.25; 570 13.33 100 37.25; 571 26.66 100 37.25; 572 39.99 100 37.25;
    573 49.32 100 37.25; 574 62.65 100 37.25; 575 75.98 100 37.25;
    576 89.3 100 37.25; 577 0 110 0; 578 13.33 110 0; 579 26.66 110 0;
    580 39.99 110 0; 581 49.32 110 0; 582 62.65 110 0; 583 75.98 110 0;
    584 89.3 110 0; 585 0 110 15.625; 586 13.33 110 15.625; 587 26.66 110 15.625;
    588 39.99 110 15.625; 589 49.32 110 15.625; 590 62.65 110 15.625;
    591 75.98 110 15.625; 592 89.3 110 15.625; 593 0 110 31.25;
    594 13.33 110 31.25; 595 26.66 110 31.25; 596 39.99 110 31.25;
    597 49.32 110 31.25; 598 62.65 110 31.25; 599 75.98 110 31.25;
    600 89.3 110 31.25; 601 0 110 68.5; 602 13.33 110 68.5; 603 26.66 110 68.5;
    604 39.99 110 68.5; 605 49.32 110 68.5; 606 62.65 110 68.5; 607 75.98 110 68.5;
    608 89.3 110 68.5; 609 0 110 52.875; 610 13.33 110 52.875;
    611 26.66 110 52.875; 612 39.99 110 52.875; 613 49.32 110 52.875;
    614 62.65 110 52.875; 615 75.98 110 52.875; 616 89.3 110 52.875;
    617 0 110 37.25; 618 13.33 110 37.25; 619 26.66 110 37.25; 620 39.99 110 37.25;
    621 49.32 110 37.25; 622 62.65 110 37.25; 623 75.98 110 37.25;
    624 89.3 110 37.25; 625 0 120 0; 626 13.33 120 0; 627 26.66 120 0;
    628 39.99 120 0; 629 49.32 120 0; 630 62.65 120 0; 631 75.98 120 0;
    632 89.3 120 0; 633 0 120 15.625; 634 13.33 120 15.625; 635 26.66 120 15.625;
    636 39.99 120 15.625; 637 49.32 120 15.625; 638 62.65 120 15.625;
    639 75.98 120 15.625; 640 89.3 120 15.625; 641 0 120 31.25;
    642 13.33 120 31.25; 643 26.66 120 31.25; 644 39.99 120 31.25;
    645 49.32 120 31.25; 646 62.65 120 31.25; 647 75.98 120 31.25;
    648 89.3 120 31.25; 649 0 120 68.5; 650 13.33 120 68.5; 651 26.66 120 68.5;
    652 39.99 120 68.5; 653 49.32 120 68.5; 654 62.65 120 68.5; 655 75.98 120 68.5;
    656 89.3 120 68.5; 657 0 120 52.875; 658 13.33 120 52.875;
    659 26.66 120 52.875; 660 39.99 120 52.875; 661 49.32 120 52.875;
    662 62.65 120 52.875; 663 75.98 120 52.875; 664 89.3 120 52.875;
    665 0 120 37.25; 666 13.33 120 37.25; 667 26.66 120 37.25; 668 39.99 120 37.25;
    669 49.32 120 37.25; 670 62.65 120 37.25; 671 75.98 120 37.25;
    672 89.3 120 37.25; 673 0 130 0; 674 13.33 130 0; 675 26.66 130 0;
    676 39.99 130 0; 677 49.32 130 0; 678 62.65 130 0; 679 75.98 130 0;
    680 89.3 130 0; 681 0 130 15.625; 682 13.33 130 15.625; 683 26.66 130 15.625;
    684 39.99 130 15.625; 685 49.32 130 15.625; 686 62.65 130 15.625;
    687 75.98 130 15.625; 688 89.3 130 15.625; 689 0 130 31.25;
    690 13.33 130 31.25; 691 26.66 130 31.25; 692 39.99 130 31.25;
    693 49.32 130 31.25; 694 62.65 130 31.25; 695 75.98 130 31.25;
    696 89.3 130 31.25; 697 0 130 68.5; 698 13.33 130 68.5; 699 26.66 130 68.5;
    700 39.99 130 68.5; 701 49.32 130 68.5; 702 62.65 130 68.5; 703 75.98 130 68.5;
    704 89.3 130 68.5; 705 0 130 52.875; 706 13.33 130 52.875;
    707 26.66 130 52.875; 708 39.99 130 52.875; 709 49.32 130 52.875;
    710 62.65 130 52.875; 711 75.98 130 52.875; 712 89.3 130 52.875;
    713 0 130 37.25; 714 13.33 130 37.25; 715 26.66 130 37.25; 716 39.99 130 37.25;
    717 49.32 130 37.25; 718 62.65 130 37.25; 719 75.98 130 37.25;
    720 89.3 130 37.25; 721 0 140 0; 722 13.33 140 0; 723 26.66 140 0;
    724 39.99 140 0; 725 49.32 140 0; 726 62.65 140 0; 727 75.98 140 0;
    728 89.3 140 0; 729 0 140 15.625; 730 13.33 140 15.625; 731 26.66 140 15.625;
    732 39.99 140 15.625; 733 49.32 140 15.625; 734 62.65 140 15.625;
    735 75.98 140 15.625; 736 89.3 140 15.625; 737 0 140 31.25;
    738 13.33 140 31.25; 739 26.66 140 31.25; 740 39.99 140 31.25;
    741 49.32 140 31.25; 742 62.65 140 31.25; 743 75.98 140 31.25;
    744 89.3 140 31.25; 745 0 140 68.5; 746 13.33 140 68.5; 747 26.66 140 68.5;
    748 39.99 140 68.5; 749 49.32 140 68.5; 750 62.65 140 68.5; 751 75.98 140 68.5;
    752 89.3 140 68.5; 753 0 140 52.875; 754 13.33 140 52.875;
    755 26.66 140 52.875; 756 39.99 140 52.875; 757 49.32 140 52.875;
    758 62.65 140 52.875; 759 75.98 140 52.875; 760 89.3 140 52.875;
    761 0 140 37.25; 762 13.33 140 37.25; 763 26.66 140 37.25; 764 39.99 140 37.25;
    765 49.32 140 37.25; 766 62.65 140 37.25; 767 75.98 140 37.25;
    768 89.3 140 37.25; 769 0 150 0; 770 13.33 150 0; 771 26.66 150 0;
    772 39.99 150 0; 773 49.32 150 0; 774 62.65 150 0; 775 75.98 150 0;
    776 89.3 150 0; 777 0 150 15.625; 778 13.33 150 15.625; 779 26.66 150 15.625;
    780 39.99 150 15.625; 781 49.32 150 15.625; 782 62.65 150 15.625;
    783 75.98 150 15.625; 784 89.3 150 15.625; 785 0 150 31.25;
    786 13.33 150 31.25; 787 26.66 150 31.25; 788 39.99 150 31.25;
    789 49.32 150 31.25; 790 62.65 150 31.25; 791 75.98 150 31.25;
    792 89.3 150 31.25; 793 0 150 68.5; 794 13.33 150 68.5; 795 26.66 150 68.5;
    796 39.99 150 68.5; 797 49.32 150 68.5; 798 62.65 150 68.5; 799 75.98 150 68.5;
    800 89.3 150 68.5; 801 0 150 52.875; 802 13.33 150 52.875;
    803 26.66 150 52.875; 804 39.99 150 52.875; 805 49.32 150 52.875;
    806 62.65 150 52.875; 807 75.98 150 52.875; 808 89.3 150 52.875;
    809 0 150 37.25; 810 13.33 150 37.25; 811 26.66 150 37.25; 812 39.99 150 37.25;
    813 49.32 150 37.25; 814 62.65 150 37.25; 815 75.98 150 37.25;
    816 89.3 150 37.25; 817 0 160 0; 818 13.33 160 0; 819 26.66 160 0;
    820 39.99 160 0; 821 49.32 160 0; 822 62.65 160 0; 823 75.98 160 0;
    824 89.3 160 0; 825 0 160 15.625; 826 13.33 160 15.625; 827 26.66 160 15.625;
    828 39.99 160 15.625; 829 49.32 160 15.625; 830 62.65 160 15.625;
    831 75.98 160 15.625; 832 89.3 160 15.625; 833 0 160 31.25;
    834 13.33 160 31.25; 835 26.66 160 31.25; 836 39.99 160 31.25;
    837 49.32 160 31.25; 838 62.65 160 31.25; 839 75.98 160 31.25;
    840 89.3 160 31.25; 841 0 160 68.5; 842 13.33 160 68.5; 843 26.66 160 68.5;
    844 39.99 160 68.5; 845 49.32 160 68.5; 846 62.65 160 68.5; 847 75.98 160 68.5;
    848 89.3 160 68.5; 849 0 160 52.875; 850 13.33 160 52.875;
    851 26.66 160 52.875; 852 39.99 160 52.875; 853 49.32 160 52.875;
    854 62.65 160 52.875; 855 75.98 160 52.875; 856 89.3 160 52.875;
    857 0 160 37.25; 858 13.33 160 37.25; 859 26.66 160 37.25; 860 39.99 160 37.25;
    861 49.32 160 37.25; 862 62.65 160 37.25; 863 75.98 160 37.25;
    864 89.3 160 37.25; 865 0 170 0; 866 13.33 170 0; 867 26.66 170 0;
    868 39.99 170 0; 869 49.32 170 0; 870 62.65 170 0; 871 75.98 170 0;
    872 89.3 170 0; 873 0 170 15.625; 874 13.33 170 15.625; 875 26.66 170 15.625;
    876 39.99 170 15.625; 877 49.32 170 15.625; 878 62.65 170 15.625;
    879 75.98 170 15.625; 880 89.3 170 15.625; 881 0 170 31.25;
    882 13.33 170 31.25; 883 26.66 170 31.25; 884 39.99 170 31.25;
    885 49.32 170 31.25; 886 62.65 170 31.25; 887 75.98 170 31.25;
    888 89.3 170 31.25; 889 0 170 68.5; 890 13.33 170 68.5; 891 26.66 170 68.5;
    892 39.99 170 68.5; 893 49.32 170 68.5; 894 62.65 170 68.5; 895 75.98 170 68.5;
    896 89.3 170 68.5; 897 0 170 52.875; 898 13.33 170 52.875;
    899 26.66 170 52.875; 900 39.99 170 52.875; 901 49.32 170 52.875;
    902 62.65 170 52.875; 903 75.98 170 52.875; 904 89.3 170 52.875;
    905 0 170 37.25; 906 13.33 170 37.25; 907 26.66 170 37.25; 908 39.99 170 37.25;
    909 49.32 170 37.25; 910 62.65 170 37.25; 911 75.98 170 37.25;
    912 89.3 170 37.25; 913 0 180 0; 914 13.33 180 0; 915 26.66 180 0;
    916 39.99 180 0; 917 49.32 180 0; 918 62.65 180 0; 919 75.98 180 0;
    920 89.3 180 0; 921 0 180 15.625; 922 13.33 180 15.625; 923 26.66 180 15.625;
    924 39.99 180 15.625; 925 49.32 180 15.625; 926 62.65 180 15.625;
    927 75.98 180 15.625; 928 89.3 180 15.625; 929 0 180 31.25;
    930 13.33 180 31.25; 931 26.66 180 31.25; 932 39.99 180 31.25;
    933 49.32 180 31.25; 934 62.65 180 31.25; 935 75.98 180 31.25;
    936 89.3 180 31.25; 937 0 180 68.5; 938 13.33 180 68.5; 939 26.66 180 68.5;
    940 39.99 180 68.5; 941 49.32 180 68.5; 942 62.65 180 68.5; 943 75.98 180 68.5;
    944 89.3 180 68.5; 945 0 180 52.875; 946 13.33 180 52.875;
    947 26.66 180 52.875; 948 39.99 180 52.875; 949 49.32 180 52.875;
    950 62.65 180 52.875; 951 75.98 180 52.875; 952 89.3 180 52.875;
    953 0 180 37.25; 954 13.33 180 37.25; 955 26.66 180 37.25; 956 39.99 180 37.25;
    957 49.32 180 37.25; 958 62.65 180 37.25; 959 75.98 180 37.25;
    960 89.3 180 37.25; 961 0 190 0; 962 13.33 190 0; 963 26.66 190 0;
    964 39.99 190 0; 965 49.32 190 0; 966 62.65 190 0; 967 75.98 190 0;
    968 89.3 190 0; 969 0 190 15.625; 970 13.33 190 15.625; 971 26.66 190 15.625;
    972 39.99 190 15.625; 973 49.32 190 15.625; 974 62.65 190 15.625;
    975 75.98 190 15.625; 976 89.3 190 15.625; 977 0 190 31.25;
    978 13.33 190 31.25; 979 26.66 190 31.25; 980 39.99 190 31.25;
    981 49.32 190 31.25; 982 62.65 190 31.25; 983 75.98 190 31.25;
    984 89.3 190 31.25; 985 0 190 68.5; 986 13.33 190 68.5; 987 26.66 190 68.5;
    988 39.99 190 68.5; 989 49.32 190 68.5; 990 62.65 190 68.5; 991 75.98 190 68.5;
    992 89.3 190 68.5; 993 0 190 52.875; 994 13.33 190 52.875;
    995 26.66 190 52.875; 996 39.99 190 52.875; 997 49.32 190 52.875;
    998 62.65 190 52.875; 999 75.98 190 52.875; 1000 89.3 190 52.875;
    1001 0 190 37.25; 1002 13.33 190 37.25; 1003 26.66 190 37.25;
    1004 39.99 190 37.25; 1005 49.32 190 37.25; 1006 62.65 190 37.25;
    1007 75.98 190 37.25; 1008 89.3 190 37.25; 1009 0 200 0; 1010 13.33 200 0;
    1011 26.66 200 0; 1012 39.99 200 0; 1013 49.32 200 0; 1014 62.65 200 0;
    1015 75.98 200 0; 1016 89.3 200 0; 1017 0 200 15.625; 1018 13.33 200 15.625;
    1019 26.66 200 15.625; 1020 39.99 200 15.625; 1021 49.32 200 15.625;
    1022 62.65 200 15.625; 1023 75.98 200 15.625; 1024 89.3 200 15.625;
    1025 0 200 31.25; 1026 13.33 200 31.25; 1027 26.66 200 31.25;
    1028 39.99 200 31.25; 1029 49.32 200 31.25; 1030 62.65 200 31.25;
    1031 75.98 200 31.25; 1032 89.3 200 31.25; 1033 0 200 68.5;
    1034 13.33 200 68.5; 1035 26.66 200 68.5; 1036 39.99 200 68.5;
    1037 49.32 200 68.5; 1038 62.65 200 68.5; 1039 75.98 200 68.5;
    1040 89.3 200 68.5; 1041 0 200 52.875; 1042 13.33 200 52.875;
    1043 26.66 200 52.875; 1044 39.99 200 52.875; 1045 49.32 200 52.875;
    1046 62.65 200 52.875; 1047 75.98 200 52.875; 1048 89.3 200 52.875;
    1049 0 200 37.25; 1050 13.33 200 37.25; 1051 26.66 200 37.25;
    1052 39.99 200 37.25; 1053 49.32 200 37.25; 1054 62.65 200 37.25;
    1055 75.98 200 37.25; 1056 89.3 200 37.25; 1057 0 210 0; 1058 13.33 210 0;
    1059 26.66 210 0; 1060 39.99 210 0; 1061 49.32 210 0; 1062 62.65 210 0;
    1063 75.98 210 0; 1064 89.3 210 0; 1065 0 210 15.625; 1066 13.33 210 15.625;
    1067 26.66 210 15.625; 1068 39.99 210 15.625; 1069 49.32 210 15.625;
    1070 62.65 210 15.625; 1071 75.98 210 15.625; 1072 89.3 210 15.625;
    1073 0 210 31.25; 1074 13.33 210 31.25; 1075 26.66 210 31.25;
    1076 39.99 210 31.25; 1077 49.32 210 31.25; 1078 62.65 210 31.25;
    1079 75.98 210 31.25; 1080 89.3 210 31.25; 1081 0 210 68.5;
    1082 13.33 210 68.5; 1083 26.66 210 68.5; 1084 39.99 210 68.5;
    1085 49.32 210 68.5; 1086 62.65 210 68.5; 1087 75.98 210 68.5;
    1088 89.3 210 68.5; 1089 0 210 52.875; 1090 13.33 210 52.875;
    1091 26.66 210 52.875; 1092 39.99 210 52.875; 1093 49.32 210 52.875;
    1094 62.65 210 52.875; 1095 75.98 210 52.875; 1096 89.3 210 52.875;
    1097 0 210 37.25; 1098 13.33 210 37.25; 1099 26.66 210 37.25;
    1100 39.99 210 37.25; 1101 49.32 210 37.25; 1102 62.65 210 37.25;
    1103 75.98 210 37.25; 1104 89.3 210 37.25;
    MEMBER INCIDENCES
    1 1 2; 2 2 3; 3 3 4; 4 5 6; 5 6 7; 6 7 8; 7 1 9; 8 2 10; 9 3 11; 10 4 12;
    11 5 13; 12 6 14; 13 7 15; 14 8 16; 15 9 10; 16 10 11; 17 11 12; 18 13 14;
    19 14 15; 20 15 16; 21 9 17; 22 10 18; 23 11 19; 24 12 20; 25 13 21; 26 14 22;
    27 15 23; 28 16 24; 29 17 18; 30 18 19; 31 19 20; 32 21 22; 33 22 23; 34 23 24;
    35 25 26; 36 26 27; 37 27 28; 38 29 30; 39 30 31; 40 31 32; 41 25 33; 42 26 34;
    43 27 35; 44 28 36; 45 29 37; 46 30 38; 47 31 39; 48 32 40; 49 33 34; 50 34 35;
    51 35 36; 52 37 38; 53 38 39; 54 39 40; 55 33 41; 56 34 42; 57 35 43; 58 36 44;
    59 37 45; 60 38 46; 61 39 47; 62 40 48; 63 41 42; 64 42 43; 65 43 44; 66 45 46;
    67 46 47; 68 47 48; 69 17 41; 70 18 42; 71 19 43; 72 20 44; 73 20 21; 74 44 45;
    75 21 45; 76 22 46; 77 23 47; 78 24 48; 79 1 49; 80 9 50; 81 17 51; 82 25 52;
    83 33 53; 84 41 54; 85 2 55; 86 10 56; 87 18 57; 88 26 58; 89 34 59; 90 42 60;
    91 3 61; 92 11 62; 93 19 63; 94 27 64; 95 35 65; 96 43 66; 97 4 67; 98 12 68;
    99 20 69; 100 28 70; 101 36 71; 102 44 72; 103 5 73; 104 13 74; 105 21 75;
    106 29 76; 107 37 77; 108 45 78; 109 6 79; 110 14 80; 111 22 81; 112 30 82;
    113 38 83; 114 46 84; 115 7 85; 116 15 86; 117 23 87; 118 31 88; 119 39 89;
    120 47 90; 121 8 91; 122 16 92; 123 24 93; 124 32 94; 125 40 95; 126 48 96;
    127 1 97; 128 2 98; 129 3 99; 130 4 100; 131 5 101; 132 6 102; 133 7 103;
    134 8 104; 135 9 105; 136 10 106; 137 11 107; 138 12 108; 139 13 109;
    140 14 110; 141 15 111; 142 16 112; 143 17 113; 144 18 114; 145 19 115;
    146 20 116; 147 21 117; 148 22 118; 149 23 119; 150 24 120; 151 25 121;
    152 26 122; 153 27 123; 154 28 124; 155 29 125; 156 30 126; 157 31 127;
    158 32 128; 159 33 129; 160 34 130; 161 35 131; 162 36 132; 163 37 133;
    164 38 134; 165 39 135; 166 40 136; 167 41 137; 168 42 138; 169 43 139;
    170 44 140; 171 45 141; 172 46 142; 173 47 143; 174 48 144; 175 97 98;
    176 98 99; 177 99 100; 178 101 102; 179 102 103; 180 103 104; 181 97 105;
    182 98 106; 183 99 107; 184 100 108; 185 101 109; 186 102 110; 187 103 111;
    188 104 112; 189 105 106; 190 106 107; 191 107 108; 192 109 110; 193 110 111;
    194 111 112; 195 105 113; 196 106 114; 197 107 115; 198 108 116; 199 109 117;
    200 110 118; 201 111 119; 202 112 120; 203 113 114; 204 114 115; 205 115 116;
    206 117 118; 207 118 119; 208 119 120; 209 121 122; 210 122 123; 211 123 124;
    212 125 126; 213 126 127; 214 127 128; 215 121 129; 216 122 130; 217 123 131;
    218 124 132; 219 125 133; 220 126 134; 221 127 135; 222 128 136; 223 129 130;
    224 130 131; 225 131 132; 226 133 134; 227 134 135; 228 135 136; 229 129 137;
    230 130 138; 231 131 139; 232 132 140; 233 133 141; 234 134 142; 235 135 143;
    236 136 144; 237 137 138; 238 138 139; 239 139 140; 240 141 142; 241 142 143;
    242 143 144; 243 113 137; 244 114 138; 245 115 139; 246 116 140; 247 116 117;
    248 140 141; 249 117 141; 250 118 142; 251 119 143; 252 120 144; 253 97 145;
    254 98 146; 255 99 147; 256 100 148; 257 101 149; 258 102 150; 259 103 151;
    260 104 152; 261 105 153; 262 106 154; 263 107 155; 264 108 156; 265 109 157;
    266 110 158; 267 111 159; 268 112 160; 269 113 161; 270 114 162; 271 115 163;
    272 116 164; 273 117 165; 274 118 166; 275 119 167; 276 120 168; 277 121 169;
    278 122 170; 279 123 171; 280 124 172; 281 125 173; 282 126 174; 283 127 175;
    284 128 176; 285 129 177; 286 130 178; 287 131 179; 288 132 180; 289 133 181;
    290 134 182; 291 135 183; 292 136 184; 293 137 185; 294 138 186; 295 139 187;
    296 140 188; 297 141 189; 298 142 190; 299 143 191; 300 144 192; 301 145 146;
    302 146 147; 303 147 148; 304 149 150; 305 150 151; 306 151 152; 307 145 153;
    308 146 154; 309 147 155; 310 148 156; 311 149 157; 312 150 158; 313 151 159;
    314 152 160; 315 153 154; 316 154 155; 317 155 156; 318 157 158; 319 158 159;
    320 159 160; 321 153 161; 322 154 162; 323 155 163; 324 156 164; 325 157 165;
    326 158 166; 327 159 167; 328 160 168; 329 161 162; 330 162 163; 331 163 164;
    332 165 166; 333 166 167; 334 167 168; 335 169 170; 336 170 171; 337 171 172;
    338 173 174; 339 174 175; 340 175 176; 341 169 177; 342 170 178; 343 171 179;
    344 172 180; 345 173 181; 346 174 182; 347 175 183; 348 176 184; 349 177 178;
    350 178 179; 351 179 180; 352 181 182; 353 182 183; 354 183 184; 355 177 185;
    356 178 186; 357 179 187; 358 180 188; 359 181 189; 360 182 190; 361 183 191;
    362 184 192; 363 185 186; 364 186 187; 365 187 188; 366 189 190; 367 190 191;
    368 191 192; 369 161 185; 370 162 186; 371 163 187; 372 164 188; 373 164 165;
    374 188 189; 375 165 189; 376 166 190; 377 167 191; 378 168 192; 379 145 193;
    380 146 194; 381 147 195; 382 148 196; 383 149 197; 384 150 198; 385 151 199;
    386 152 200; 387 153 201; 388 154 202; 389 155 203; 390 156 204; 391 157 205;
    392 158 206; 393 159 207; 394 160 208; 395 161 209; 396 162 210; 397 163 211;
    398 164 212; 399 165 213; 400 166 214; 401 167 215; 402 168 216; 403 169 217;
    404 170 218; 405 171 219; 406 172 220; 407 173 221; 408 174 222; 409 175 223;
    410 176 224; 411 177 225; 412 178 226; 413 179 227; 414 180 228; 415 181 229;
    416 182 230; 417 183 231; 418 184 232; 419 185 233; 420 186 234; 421 187 235;
    422 188 236; 423 189 237; 424 190 238; 425 191 239; 426 192 240; 427 193 194;
    428 194 195; 429 195 196; 430 197 198; 431 198 199; 432 199 200; 433 193 201;
    434 194 202; 435 195 203; 436 196 204; 437 197 205; 438 198 206; 439 199 207;
    440 200 208; 441 201 202; 442 202 203; 443 203 204; 444 205 206; 445 206 207;
    446 207 208; 447 201 209; 448 202 210; 449 203 211; 450 204 212; 451 205 213;
    452 206 214; 453 207 215; 454 208 216; 455 209 210; 456 210 211; 457 211 212;
    458 213 214; 459 214 215; 460 215 216; 461 217 218; 462 218 219; 463 219 220;
    464 221 222; 465 222 223; 466 223 224; 467 217 225; 468 218 226; 469 219 227;
    470 220 228; 471 221 229; 472 222 230; 473 223 231; 474 224 232; 475 225 226;
    476 226 227; 477 227 228; 478 229 230; 479 230 231; 480 231 232; 481 225 233;
    482 226 234; 483 227 235; 484 228 236; 485 229 237; 486 230 238; 487 231 239;
    488 232 240; 489 233 234; 490 234 235; 491 235 236; 492 237 238; 493 238 239;
    494 239 240; 495 209 233; 496 210 234; 497 211 235; 498 212 236; 499 212 213;
    500 236 237; 501 213 237; 502 214 238; 503 215 239; 504 216 240; 505 193 241;
    506 194 242; 507 195 243; 508 196 244; 509 197 245; 510 198 246; 511 199 247;
    512 200 248; 513 201 249; 514 202 250; 515 203 251; 516 204 252; 517 205 253;
    518 206 254; 519 207 255; 520 208 256; 521 209 257; 522 210 258; 523 211 259;
    524 212 260; 525 213 261; 526 214 262; 527 215 263; 528 216 264; 529 217 265;
    530 218 266; 531 219 267; 532 220 268; 533 221 269; 534 222 270; 535 223 271;
    536 224 272; 537 225 273; 538 226 274; 539 227 275; 540 228 276; 541 229 277;
    542 230 278; 543 231 279; 544 232 280; 545 233 281; 546 234 282; 547 235 283;
    548 236 284; 549 237 285; 550 238 286; 551 239 287; 552 240 288; 553 241 242;
    554 242 243; 555 243 244; 556 245 246; 557 246 247; 558 247 248; 559 241 249;
    560 242 250; 561 243 251; 562 244 252; 563 245 253; 564 246 254; 565 247 255;
    566 248 256; 567 249 250; 568 250 251; 569 251 252; 570 253 254; 571 254 255;
    572 255 256; 573 249 257; 574 250 258; 575 251 259; 576 252 260; 577 253 261;
    578 254 262; 579 255 263; 580 256 264; 581 257 258; 582 258 259; 583 259 260;
    584 261 262; 585 262 263; 586 263 264; 587 265 266; 588 266 267; 589 267 268;
    590 269 270; 591 270 271; 592 271 272; 593 265 273; 594 266 274; 595 267 275;
    596 268 276; 597 269 277; 598 270 278; 599 271 279; 600 272 280; 601 273 274;
    602 274 275; 603 275 276; 604 277 278; 605 278 279; 606 279 280; 607 273 281;
    608 274 282; 609 275 283; 610 276 284; 611 277 285; 612 278 286; 613 279 287;
    614 280 288; 615 281 282; 616 282 283; 617 283 284; 618 285 286; 619 286 287;
    620 287 288; 621 257 281; 622 258 282; 623 259 283; 624 260 284; 625 260 261;
    626 284 285; 627 261 285; 628 262 286; 629 263 287; 630 264 288; 631 241 289;
    632 242 290; 633 243 291; 634 244 292; 635 245 293; 636 246 294; 637 247 295;
    638 248 296; 639 249 297; 640 250 298; 641 251 299; 642 252 300; 643 253 301;
    644 254 302; 645 255 303; 646 256 304; 647 257 305; 648 258 306; 649 259 307;
    650 260 308; 651 261 309; 652 262 310; 653 263 311; 654 264 312; 655 265 313;
    656 266 314; 657 267 315; 658 268 316; 659 269 317; 660 270 318; 661 271 319;
    662 272 320; 663 273 321; 664 274 322; 665 275 323; 666 276 324; 667 277 325;
    668 278 326; 669 279 327; 670 280 328; 671 281 329; 672 282 330; 673 283 331;
    674 284 332; 675 285 333; 676 286 334; 677 287 335; 678 288 336; 679 289 290;
    680 290 291; 681 291 292; 682 293 294; 683 294 295; 684 295 296; 685 289 297;
    686 290 298; 687 291 299; 688 292 300; 689 293 301; 690 294 302; 691 295 303;
    692 296 304; 693 297 298; 694 298 299; 695 299 300; 696 301 302; 697 302 303;
    698 303 304; 699 297 305; 700 298 306; 701 299 307; 702 300 308; 703 301 309;
    704 302 310; 705 303 311; 706 304 312; 707 305 306; 708 306 307; 709 307 308;
    710 309 310; 711 310 311; 712 311 312; 713 313 314; 714 314 315; 715 315 316;
    716 317 318; 717 318 319; 718 319 320; 719 313 321; 720 314 322; 721 315 323;
    722 316 324; 723 317 325; 724 318 326; 725 319 327; 726 320 328; 727 321 322;
    728 322 323; 729 323 324; 730 325 326; 731 326 327; 732 327 328; 733 321 329;
    734 322 330; 735 323 331; 736 324 332; 737 325 333; 738 326 334; 739 327 335;
    740 328 336; 741 329 330; 742 330 331; 743 331 332; 744 333 334; 745 334 335;
    746 335 336; 747 305 329; 748 306 330; 749 307 331; 750 308 332; 751 308 309;
    752 332 333; 753 309 333; 754 310 334; 755 311 335; 756 312 336; 757 289 337;
    758 290 338; 759 291 339; 760 292 340; 761 293 341; 762 294 342; 763 295 343;
    764 296 344; 765 297 345; 766 298 346; 767 299 347; 768 300 348; 769 301 349;
    770 302 350; 771 303 351; 772 304 352; 773 305 353; 774 306 354; 775 307 355;
    776 308 356; 777 309 357; 778 310 358; 779 311 359; 780 312 360; 781 313 361;
    782 314 362; 783 315 363; 784 316 364; 785 317 365; 786 318 366; 787 319 367;
    788 320 368; 789 321 369; 790 322 370; 791 323 371; 792 324 372; 793 325 373;
    794 326 374; 795 327 375; 796 328 376; 797 329 377; 798 330 378; 799 331 379;
    800 332 380; 801 333 381; 802 334 382; 803 335 383; 804 336 384; 805 337 338;
    806 338 339; 807 339 340; 808 341 342; 809 342 343; 810 343 344; 811 337 345;
    812 338 346; 813 339 347; 814 340 348; 815 341 349; 816 342 350; 817 343 351;
    818 344 352; 819 345 346; 820 346 347; 821 347 348; 822 349 350; 823 350 351;
    824 351 352; 825 345 353; 826 346 354; 827 347 355; 828 348 356; 829 349 357;
    830 350 358; 831 351 359; 832 352 360; 833 353 354; 834 354 355; 835 355 356;
    836 357 358; 837 358 359; 838 359 360; 839 361 362; 840 362 363; 841 363 364;
    842 365 366; 843 366 367; 844 367 368; 845 361 369; 846 362 370; 847 363 371;
    848 364 372; 849 365 373; 850 366 374; 851 367 375; 852 368 376; 853 369 370;
    854 370 371; 855 371 372; 856 373 374; 857 374 375; 858 375 376; 859 369 377;
    860 370 378; 861 371 379; 862 372 380; 863 373 381; 864 374 382; 865 375 383;
    866 376 384; 867 377 378; 868 378 379; 869 379 380; 870 381 382; 871 382 383;
    872 383 384; 873 353 377; 874 354 378; 875 355 379; 876 356 380; 877 356 357;
    878 380 381; 879 357 381; 880 358 382; 881 359 383; 882 360 384; 883 337 385;
    884 338 386; 885 339 387; 886 340 388; 887 341 389; 888 342 390; 889 343 391;
    890 344 392; 891 345 393; 892 346 394; 893 347 395; 894 348 396; 895 349 397;
    896 350 398; 897 351 399; 898 352 400; 899 353 401; 900 354 402; 901 355 403;
    902 356 404; 903 357 405; 904 358 406; 905 359 407; 906 360 408; 907 361 409;
    908 362 410; 909 363 411; 910 364 412; 911 365 413; 912 366 414; 913 367 415;
    914 368 416; 915 369 417; 916 370 418; 917 371 419; 918 372 420; 919 373 421;
    920 374 422; 921 375 423; 922 376 424; 923 377 425; 924 378 426; 925 379 427;
    926 380 428; 927 381 429; 928 382 430; 929 383 431; 930 384 432; 931 385 386;
    932 386 387; 933 387 388; 934 389 390; 935 390 391; 936 391 392; 937 385 393;
    938 386 394; 939 387 395; 940 388 396; 941 389 397; 942 390 398; 943 391 399;
    944 392 400; 945 393 394; 946 394 395; 947 395 396; 948 397 398; 949 398 399;
    950 399 400; 951 393 401; 952 394 402; 953 395 403; 954 396 404; 955 397 405;
    956 398 406; 957 399 407; 958 400 408; 959 401 402; 960 402 403; 961 403 404;
    962 405 406; 963 406 407; 964 407 408; 965 409 410; 966 410 411; 967 411 412;
    968 413 414; 969 414 415; 970 415 416; 971 409 417; 972 410 418; 973 411 419;
    974 412 420; 975 413 421; 976 414 422; 977 415 423; 978 416 424; 979 417 418;
    980 418 419; 981 419 420; 982 421 422; 983 422 423; 984 423 424; 985 417 425;
    986 418 426; 987 419 427; 988 420 428; 989 421 429; 990 422 430; 991 423 431;
    992 424 432; 993 425 426; 994 426 427; 995 427 428; 996 429 430; 997 430 431;
    998 431 432; 999 401 425; 1000 402 426; 1001 403 427; 1002 404 428;
    1003 404 405; 1004 428 429; 1005 405 429; 1006 406 430; 1007 407 431;
    1008 408 432; 1009 385 433; 1010 386 434; 1011 387 435; 1012 388 436;
    1013 389 437; 1014 390 438; 1015 391 439; 1016 392 440; 1017 393 441;
    1018 394 442; 1019 395 443; 1020 396 444; 1021 397 445; 1022 398 446;
    1023 399 447; 1024 400 448; 1025 401 449; 1026 402 450; 1027 403 451;
    1028 404 452; 1029 405 453; 1030 406 454; 1031 407 455; 1032 408 456;
    1033 409 457; 1034 410 458; 1035 411 459; 1036 412 460; 1037 413 461;
    1038 414 462; 1039 415 463; 1040 416 464; 1041 417 465; 1042 418 466;
    1043 419 467; 1044 420 468; 1045 421 469; 1046 422 470; 1047 423 471;
    1048 424 472; 1049 425 473; 1050 426 474; 1051 427 475; 1052 428 476;
    1053 429 477; 1054 430 478; 1055 431 479; 1056 432 480; 1057 433 434;
    1058 434 435; 1059 435 436; 1060 437 438; 1061 438 439; 1062 439 440;
    1063 433 441; 1064 434 442; 1065 435 443; 1066 436 444; 1067 437 445;
    1068 438 446; 1069 439 447; 1070 440 448; 1071 441 442; 1072 442 443;
    1073 443 444; 1074 445 446; 1075 446 447; 1076 447 448; 1077 441 449;
    1078 442 450; 1079 443 451; 1080 444 452; 1081 445 453; 1082 446 454;
    1083 447 455; 1084 448 456; 1085 449 450; 1086 450 451; 1087 451 452;
    1088 453 454; 1089 454 455; 1090 455 456; 1091 457 458; 1092 458 459;
    1093 459 460; 1094 461 462; 1095 462 463; 1096 463 464; 1097 457 465;
    1098 458 466; 1099 459 467; 1100 460 468; 1101 461 469; 1102 462 470;
    1103 463 471; 1104 464 472; 1105 465 466; 1106 466 467; 1107 467 468;
    1108 469 470; 1109 470 471; 1110 471 472; 1111 465 473; 1112 466 474;
    1113 467 475; 1114 468 476; 1115 469 477; 1116 470 478; 1117 471 479;
    1118 472 480; 1119 473 474; 1120 474 475; 1121 475 476; 1122 477 478;
    1123 478 479; 1124 479 480; 1125 449 473; 1126 450 474; 1127 451 475;
    1128 452 476; 1129 452 453; 1130 476 477; 1131 453 477; 1132 454 478;
    1133 455 479; 1134 456 480; 1135 433 481; 1136 434 482; 1137 435 483;
    1138 436 484; 1139 437 485; 1140 438 486; 1141 439 487; 1142 440 488;
    1143 441 489; 1144 442 490; 1145 443 491; 1146 444 492; 1147 445 493;
    1148 446 494; 1149 447 495; 1150 448 496; 1151 449 497; 1152 450 498;
    1153 451 499; 1154 452 500; 1155 453 501; 1156 454 502; 1157 455 503;
    1158 456 504; 1159 457 505; 1160 458 506; 1161 459 507; 1162 460 508;
    1163 461 509; 1164 462 510; 1165 463 511; 1166 464 512; 1167 465 513;
    1168 466 514; 1169 467 515; 1170 468 516; 1171 469 517; 1172 470 518;
    1173 471 519; 1174 472 520; 1175 473 521; 1176 474 522; 1177 475 523;
    1178 476 524; 1179 477 525; 1180 478 526; 1181 479 527; 1182 480 528;
    1183 481 482; 1184 482 483; 1185 483 484; 1186 485 486; 1187 486 487;
    1188 487 488; 1189 481 489; 1190 482 490; 1191 483 491; 1192 484 492;
    1193 485 493; 1194 486 494; 1195 487 495; 1196 488 496; 1197 489 490;
    1198 490 491; 1199 491 492; 1200 493 494; 1201 494 495; 1202 495 496;
    1203 489 497; 1204 490 498; 1205 491 499; 1206 492 500; 1207 493 501;
    1208 494 502; 1209 495 503; 1210 496 504; 1211 497 498; 1212 498 499;
    1213 499 500; 1214 501 502; 1215 502 503; 1216 503 504; 1217 505 506;
    1218 506 507; 1219 507 508; 1220 509 510; 1221 510 511; 1222 511 512;
    1223 505 513; 1224 506 514; 1225 507 515; 1226 508 516; 1227 509 517;
    1228 510 518; 1229 511 519; 1230 512 520; 1231 513 514; 1232 514 515;
    1233 515 516; 1234 517 518; 1235 518 519; 1236 519 520; 1237 513 521;
    1238 514 522; 1239 515 523; 1240 516 524; 1241 517 525; 1242 518 526;
    1243 519 527; 1244 520 528; 1245 521 522; 1246 522 523; 1247 523 524;
    1248 525 526; 1249 526 527; 1250 527 528; 1251 497 521; 1252 498 522;
    1253 499 523; 1254 500 524; 1255 500 501; 1256 524 525; 1257 501 525;
    1258 502 526; 1259 503 527; 1260 504 528; 1261 481 529; 1262 482 530;
    1263 483 531; 1264 484 532; 1265 485 533; 1266 486 534; 1267 487 535;
    1268 488 536; 1269 489 537; 1270 490 538; 1271 491 539; 1272 492 540;
    1273 493 541; 1274 494 542; 1275 495 543; 1276 496 544; 1277 497 545;
    1278 498 546; 1279 499 547; 1280 500 548; 1281 501 549; 1282 502 550;
    1283 503 551; 1284 504 552; 1285 505 553; 1286 506 554; 1287 507 555;
    1288 508 556; 1289 509 557; 1290 510 558; 1291 511 559; 1292 512 560;
    1293 513 561; 1294 514 562; 1295 515 563; 1296 516 564; 1297 517 565;
    1298 518 566; 1299 519 567; 1300 520 568; 1301 521 569; 1302 522 570;
    1303 523 571; 1304 524 572; 1305 525 573; 1306 526 574; 1307 527 575;
    1308 528 576; 1309 529 530; 1310 530 531; 1311 531 532; 1312 533 534;
    1313 534 535; 1314 535 536; 1315 529 537; 1316 530 538; 1317 531 539;
    1318 532 540; 1319 533 541; 1320 534 542; 1321 535 543; 1322 536 544;
    1323 537 538; 1324 538 539; 1325 539 540; 1326 541 542; 1327 542 543;
    1328 543 544; 1329 537 545; 1330 538 546; 1331 539 547; 1332 540 548;
    1333 541 549; 1334 542 550; 1335 543 551; 1336 544 552; 1337 545 546;
    1338 546 547; 1339 547 548; 1340 549 550; 1341 550 551; 1342 551 552;
    1343 553 554; 1344 554 555; 1345 555 556; 1346 557 558; 1347 558 559;
    1348 559 560; 1349 553 561; 1350 554 562; 1351 555 563; 1352 556 564;
    1353 557 565; 1354 558 566; 1355 559 567; 1356 560 568; 1357 561 562;
    1358 562 563; 1359 563 564; 1360 565 566; 1361 566 567; 1362 567 568;
    1363 561 569; 1364 562 570; 1365 563 571; 1366 564 572; 1367 565 573;
    1368 566 574; 1369 567 575; 1370 568 576; 1371 569 570; 1372 570 571;
    1373 571 572; 1374 573 574; 1375 574 575; 1376 575 576; 1377 545 569;
    1378 546 570; 1379 547 571; 1380 548 572; 1381 548 549; 1382 572 573;
    1383 549 573; 1384 550 574; 1385 551 575; 1386 552 576; 1387 529 577;
    1388 530 578; 1389 531 579; 1390 532 580; 1391 533 581; 1392 534 582;
    1393 535 583; 1394 536 584; 1395 537 585; 1396 538 586; 1397 539 587;
    1398 540 588; 1399 541 589; 1400 542 590; 1401 543 591; 1402 544 592;
    1403 545 593; 1404 546 594; 1405 547 595; 1406 548 596; 1407 549 597;
    1408 550 598; 1409 551 599; 1410 552 600; 1411 553 601; 1412 554 602;
    1413 555 603; 1414 556 604; 1415 557 605; 1416 558 606; 1417 559 607;
    1418 560 608; 1419 561 609; 1420 562 610; 1421 563 611; 1422 564 612;
    1423 565 613; 1424 566 614; 1425 567 615; 1426 568 616; 1427 569 617;
    1428 570 618; 1429 571 619; 1430 572 620; 1431 573 621; 1432 574 622;
    1433 575 623; 1434 576 624; 1435 577 578; 1436 578 579; 1437 579 580;
    1438 581 582; 1439 582 583; 1440 583 584; 1441 577 585; 1442 578 586;
    1443 579 587; 1444 580 588; 1445 581 589; 1446 582 590; 1447 583 591;
    1448 584 592; 1449 585 586; 1450 586 587; 1451 587 588; 1452 589 590;
    1453 590 591; 1454 591 592; 1455 585 593; 1456 586 594; 1457 587 595;
    1458 588 596; 1459 589 597; 1460 590 598; 1461 591 599; 1462 592 600;
    1463 593 594; 1464 594 595; 1465 595 596; 1466 597 598; 1467 598 599;
    1468 599 600; 1469 601 602; 1470 602 603; 1471 603 604; 1472 605 606;
    1473 606 607; 1474 607 608; 1475 601 609; 1476 602 610; 1477 603 611;
    1478 604 612; 1479 605 613; 1480 606 614; 1481 607 615; 1482 608 616;
    1483 609 610; 1484 610 611; 1485 611 612; 1486 613 614; 1487 614 615;
    1488 615 616; 1489 609 617; 1490 610 618; 1491 611 619; 1492 612 620;
    1493 613 621; 1494 614 622; 1495 615 623; 1496 616 624; 1497 617 618;
    1498 618 619; 1499 619 620; 1500 621 622; 1501 622 623; 1502 623 624;
    1503 593 617; 1504 594 618; 1505 595 619; 1506 596 620; 1507 596 597;
    1508 620 621; 1509 597 621; 1510 598 622; 1511 599 623; 1512 600 624;
    1513 577 625; 1514 578 626; 1515 579 627; 1516 580 628; 1517 581 629;
    1518 582 630; 1519 583 631; 1520 584 632; 1521 585 633; 1522 586 634;
    1523 587 635; 1524 588 636; 1525 589 637; 1526 590 638; 1527 591 639;
    1528 592 640; 1529 593 641; 1530 594 642; 1531 595 643; 1532 596 644;
    1533 597 645; 1534 598 646; 1535 599 647; 1536 600 648; 1537 601 649;
    1538 602 650; 1539 603 651; 1540 604 652; 1541 605 653; 1542 606 654;
    1543 607 655; 1544 608 656; 1545 609 657; 1546 610 658; 1547 611 659;
    1548 612 660; 1549 613 661; 1550 614 662; 1551 615 663; 1552 616 664;
    1553 617 665; 1554 618 666; 1555 619 667; 1556 620 668; 1557 621 669;
    1558 622 670; 1559 623 671; 1560 624 672; 1561 625 626; 1562 626 627;
    1563 627 628; 1564 629 630; 1565 630 631; 1566 631 632; 1567 625 633;
    1568 626 634; 1569 627 635; 1570 628 636; 1571 629 637; 1572 630 638;
    1573 631 639; 1574 632 640; 1575 633 634; 1576 634 635; 1577 635 636;
    1578 637 638; 1579 638 639; 1580 639 640; 1581 633 641; 1582 634 642;
    1583 635 643; 1584 636 644; 1585 637 645; 1586 638 646; 1587 639 647;
    1588 640 648; 1589 641 642; 1590 642 643; 1591 643 644; 1592 645 646;
    1593 646 647; 1594 647 648; 1595 649 650; 1596 650 651; 1597 651 652;
    1598 653 654; 1599 654 655; 1600 655 656; 1601 649 657; 1602 650 658;
    1603 651 659; 1604 652 660; 1605 653 661; 1606 654 662; 1607 655 663;
    1608 656 664; 1609 657 658; 1610 658 659; 1611 659 660; 1612 661 662;
    1613 662 663; 1614 663 664; 1615 657 665; 1616 658 666; 1617 659 667;
    1618 660 668; 1619 661 669; 1620 662 670; 1621 663 671; 1622 664 672;
    1623 665 666; 1624 666 667; 1625 667 668; 1626 669 670; 1627 670 671;
    1628 671 672; 1629 641 665; 1630 642 666; 1631 643 667; 1632 644 668;
    1633 644 645; 1634 668 669; 1635 645 669; 1636 646 670; 1637 647 671;
    1638 648 672; 1639 625 673; 1640 626 674; 1641 627 675; 1642 628 676;
    1643 629 677; 1644 630 678; 1645 631 679; 1646 632 680; 1647 633 681;
    1648 634 682; 1649 635 683; 1650 636 684; 1651 637 685; 1652 638 686;
    1653 639 687; 1654 640 688; 1655 641 689; 1656 642 690; 1657 643 691;
    1658 644 692; 1659 645 693; 1660 646 694; 1661 647 695; 1662 648 696;
    1663 649 697; 1664 650 698; 1665 651 699; 1666 652 700; 1667 653 701;
    1668 654 702; 1669 655 703; 1670 656 704; 1671 657 705; 1672 658 706;
    1673 659 707; 1674 660 708; 1675 661 709; 1676 662 710; 1677 663 711;
    1678 664 712; 1679 665 713; 1680 666 714; 1681 667 715; 1682 668 716;
    1683 669 717; 1684 670 718; 1685 671 719; 1686 672 720; 1687 673 674;
    1688 674 675; 1689 675 676; 1690 677 678; 1691 678 679; 1692 679 680;
    1693 673 681; 1694 674 682; 1695 675 683; 1696 676 684; 1697 677 685;
    1698 678 686; 1699 679 687; 1700 680 688; 1701 681 682; 1702 682 683;
    1703 683 684; 1704 685 686; 1705 686 687; 1706 687 688; 1707 681 689;
    1708 682 690; 1709 683 691; 1710 684 692; 1711 685 693; 1712 686 694;
    1713 687 695; 1714 688 696; 1715 689 690; 1716 690 691; 1717 691 692;
    1718 693 694; 1719 694 695; 1720 695 696; 1721 697 698; 1722 698 699;
    1723 699 700; 1724 701 702; 1725 702 703; 1726 703 704; 1727 697 705;
    1728 698 706; 1729 699 707; 1730 700 708; 1731 701 709; 1732 702 710;
    1733 703 711; 1734 704 712; 1735 705 706; 1736 706 707; 1737 707 708;
    1738 709 710; 1739 710 711; 1740 711 712; 1741 705 713; 1742 706 714;
    1743 707 715; 1744 708 716; 1745 709 717; 1746 710 718; 1747 711 719;
    1748 712 720; 1749 713 714; 1750 714 715; 1751 715 716; 1752 717 718;
    1753 718 719; 1754 719 720; 1755 689 713; 1756 690 714; 1757 691 715;
    1758 692 716; 1759 692 693; 1760 716 717; 1761 693 717; 1762 694 718;
    1763 695 719; 1764 696 720; 1765 673 721; 1766 674 722; 1767 675 723;
    1768 676 724; 1769 677 725; 1770 678 726; 1771 679 727; 1772 680 728;
    1773 681 729; 1774 682 730; 1775 683 731; 1776 684 732; 1777 685 733;
    1778 686 734; 1779 687 735; 1780 688 736; 1781 689 737; 1782 690 738;
    1783 691 739; 1784 692 740; 1785 693 741; 1786 694 742; 1787 695 743;
    1788 696 744; 1789 697 745; 1790 698 746; 1791 699 747; 1792 700 748;
    1793 701 749; 1794 702 750; 1795 703 751; 1796 704 752; 1797 705 753;
    1798 706 754; 1799 707 755; 1800 708 756; 1801 709 757; 1802 710 758;
    1803 711 759; 1804 712 760; 1805 713 761; 1806 714 762; 1807 715 763;
    1808 716 764; 1809 717 765; 1810 718 766; 1811 719 767; 1812 720 768;
    1813 721 722; 1814 722 723; 1815 723 724; 1816 725 726; 1817 726 727;
    1818 727 728; 1819 721 729; 1820 722 730; 1821 723 731; 1822 724 732;
    1823 725 733; 1824 726 734; 1825 727 735; 1826 728 736; 1827 729 730;
    1828 730 731; 1829 731 732; 1830 733 734; 1831 734 735; 1832 735 736;
    1833 729 737; 1834 730 738; 1835 731 739; 1836 732 740; 1837 733 741;
    1838 734 742; 1839 735 743; 1840 736 744; 1841 737 738; 1842 738 739;
    1843 739 740; 1844 741 742; 1845 742 743; 1846 743 744; 1847 745 746;
    1848 746 747; 1849 747 748; 1850 749 750; 1851 750 751; 1852 751 752;
    1853 745 753; 1854 746 754; 1855 747 755; 1856 748 756; 1857 749 757;
    1858 750 758; 1859 751 759; 1860 752 760; 1861 753 754; 1862 754 755;
    1863 755 756; 1864 757 758; 1865 758 759; 1866 759 760; 1867 753 761;
    1868 754 762; 1869 755 763; 1870 756 764; 1871 757 765; 1872 758 766;
    1873 759 767; 1874 760 768; 1875 761 762; 1876 762 763; 1877 763 764;
    1878 765 766; 1879 766 767; 1880 767 768; 1881 737 761; 1882 738 762;
    1883 739 763; 1884 740 764; 1885 740 741; 1886 764 765; 1887 741 765;
    1888 742 766; 1889 743 767; 1890 744 768; 1891 721 769; 1892 722 770;
    1893 723 771; 1894 724 772; 1895 725 773; 1896 726 774; 1897 727 775;
    1898 728 776; 1899 729 777; 1900 730 778; 1901 731 779; 1902 732 780;
    1903 733 781; 1904 734 782; 1905 735 783; 1906 736 784; 1907 737 785;
    1908 738 786; 1909 739 787; 1910 740 788; 1911 741 789; 1912 742 790;
    1913 743 791; 1914 744 792; 1915 745 793; 1916 746 794; 1917 747 795;
    1918 748 796; 1919 749 797; 1920 750 798; 1921 751 799; 1922 752 800;
    1923 753 801; 1924 754 802; 1925 755 803; 1926 756 804; 1927 757 805;
    1928 758 806; 1929 759 807; 1930 760 808; 1931 761 809; 1932 762 810;
    1933 763 811; 1934 764 812; 1935 765 813; 1936 766 814; 1937 767 815;
    1938 768 816; 1939 769 770; 1940 770 771; 1941 771 772; 1942 773 774;
    1943 774 775; 1944 775 776; 1945 769 777; 1946 770 778; 1947 771 779;
    1948 772 780; 1949 773 781; 1950 774 782; 1951 775 783; 1952 776 784;
    1953 777 778; 1954 778 779; 1955 779 780; 1956 781 782; 1957 782 783;
    1958 783 784; 1959 777 785; 1960 778 786; 1961 779 787; 1962 780 788;
    1963 781 789; 1964 782 790; 1965 783 791; 1966 784 792; 1967 785 786;
    1968 786 787; 1969 787 788; 1970 789 790; 1971 790 791; 1972 791 792;
    1973 793 794; 1974 794 795; 1975 795 796; 1976 797 798; 1977 798 799;
    1978 799 800; 1979 793 801; 1980 794 802; 1981 795 803; 1982 796 804;
    1983 797 805; 1984 798 806; 1985 799 807; 1986 800 808; 1987 801 802;
    1988 802 803; 1989 803 804; 1990 805 806; 1991 806 807; 1992 807 808;
    1993 801 809; 1994 802 810; 1995 803 811; 1996 804 812; 1997 805 813;
    1998 806 814; 1999 807 815; 2000 808 816; 2001 809 810; 2002 810 811;
    2003 811 812; 2004 813 814; 2005 814 815; 2006 815 816; 2007 785 809;
    2008 786 810; 2009 787 811; 2010 788 812; 2011 788 789; 2012 812 813;
    2013 789 813; 2014 790 814; 2015 791 815; 2016 792 816; 2017 769 817;
    2018 770 818; 2019 771 819; 2020 772 820; 2021 773 821; 2022 774 822;
    2023 775 823; 2024 776 824; 2025 777 825; 2026 778 826; 2027 779 827;
    2028 780 828; 2029 781 829; 2030 782 830; 2031 783 831; 2032 784 832;
    2033 785 833; 2034 786 834; 2035 787 835; 2036 788 836; 2037 789 837;
    2038 790 838; 2039 791 839; 2040 792 840; 2041 793 841; 2042 794 842;
    2043 795 843; 2044 796 844; 2045 797 845; 2046 798 846; 2047 799 847;
    2048 800 848; 2049 801 849; 2050 802 850; 2051 803 851; 2052 804 852;
    2053 805 853; 2054 806 854; 2055 807 855; 2056 808 856; 2057 809 857;
    2058 810 858; 2059 811 859; 2060 812 860; 2061 813 861; 2062 814 862;
    2063 815 863; 2064 816 864; 2065 817 818; 2066 818 819; 2067 819 820;
    2068 821 822; 2069 822 823; 2070 823 824; 2071 817 825; 2072 818 826;
    2073 819 827; 2074 820 828; 2075 821 829; 2076 822 830; 2077 823 831;
    2078 824 832; 2079 825 826; 2080 826 827; 2081 827 828; 2082 829 830;
    2083 830 831; 2084 831 832; 2085 825 833; 2086 826 834; 2087 827 835;
    2088 828 836; 2089 829 837; 2090 830 838; 2091 831 839; 2092 832 840;
    2093 833 834; 2094 834 835; 2095 835 836; 2096 837 838; 2097 838 839;
    2098 839 840; 2099 841 842; 2100 842 843; 2101 843 844; 2102 845 846;
    2103 846 847; 2104 847 848; 2105 841 849; 2106 842 850; 2107 843 851;
    2108 844 852; 2109 845 853; 2110 846 854; 2111 847 855; 2112 848 856;
    2113 849 850; 2114 850 851; 2115 851 852; 2116 853 854; 2117 854 855;
    2118 855 856; 2119 849 857; 2120 850 858; 2121 851 859; 2122 852 860;
    2123 853 861; 2124 854 862; 2125 855 863; 2126 856 864; 2127 857 858;
    2128 858 859; 2129 859 860; 2130 861 862; 2131 862 863; 2132 863 864;
    2133 833 857; 2134 834 858; 2135 835 859; 2136 836 860; 2137 836 837;
    2138 860 861; 2139 837 861; 2140 838 862; 2141 839 863; 2142 840 864;
    2143 817 865; 2144 818 866; 2145 819 867; 2146 820 868; 2147 821 869;
    2148 822 870; 2149 823 871; 2150 824 872; 2151 825 873; 2152 826 874;
    2153 827 875; 2154 828 876; 2155 829 877; 2156 830 878; 2157 831 879;
    2158 832 880; 2159 833 881; 2160 834 882; 2161 835 883; 2162 836 884;
    2163 837 885; 2164 838 886; 2165 839 887; 2166 840 888; 2167 841 889;
    2168 842 890; 2169 843 891; 2170 844 892; 2171 845 893; 2172 846 894;
    2173 847 895; 2174 848 896; 2175 849 897; 2176 850 898; 2177 851 899;
    2178 852 900; 2179 853 901; 2180 854 902; 2181 855 903; 2182 856 904;
    2183 857 905; 2184 858 906; 2185 859 907; 2186 860 908; 2187 861 909;
    2188 862 910; 2189 863 911; 2190 864 912; 2191 865 866; 2192 866 867;
    2193 867 868; 2194 869 870; 2195 870 871; 2196 871 872; 2197 865 873;
    2198 866 874; 2199 867 875; 2200 868 876; 2201 869 877; 2202 870 878;
    2203 871 879; 2204 872 880; 2205 873 874; 2206 874 875; 2207 875 876;
    2208 877 878; 2209 878 879; 2210 879 880; 2211 873 881; 2212 874 882;
    2213 875 883; 2214 876 884; 2215 877 885; 2216 878 886; 2217 879 887;
    2218 880 888; 2219 881 882; 2220 882 883; 2221 883 884; 2222 885 886;
    2223 886 887; 2224 887 888; 2225 889 890; 2226 890 891; 2227 891 892;
    2228 893 894; 2229 894 895; 2230 895 896; 2231 889 897; 2232 890 898;
    2233 891 899; 2234 892 900; 2235 893 901; 2236 894 902; 2237 895 903;
    2238 896 904; 2239 897 898; 2240 898 899; 2241 899 900; 2242 901 902;
    2243 902 903; 2244 903 904; 2245 897 905; 2246 898 906; 2247 899 907;
    2248 900 908; 2249 901 909; 2250 902 910; 2251 903 911; 2252 904 912;
    2253 905 906; 2254 906 907; 2255 907 908; 2256 909 910; 2257 910 911;
    2258 911 912; 2259 881 905; 2260 882 906; 2261 883 907; 2262 884 908;
    2263 884 885; 2264 908 909; 2265 885 909; 2266 886 910; 2267 887 911;
    2268 888 912; 2269 865 913; 2270 866 914; 2271 867 915; 2272 868 916;
    2273 869 917; 2274 870 918; 2275 871 919; 2276 872 920; 2277 873 921;
    2278 874 922; 2279 875 923; 2280 876 924; 2281 877 925; 2282 878 926;
    2283 879 927; 2284 880 928; 2285 881 929; 2286 882 930; 2287 883 931;
    2288 884 932; 2289 885 933; 2290 886 934; 2291 887 935; 2292 888 936;
    2293 889 937; 2294 890 938; 2295 891 939; 2296 892 940; 2297 893 941;
    2298 894 942; 2299 895 943; 2300 896 944; 2301 897 945; 2302 898 946;
    2303 899 947; 2304 900 948; 2305 901 949; 2306 902 950; 2307 903 951;
    2308 904 952; 2309 905 953; 2310 906 954; 2311 907 955; 2312 908 956;
    2313 909 957; 2314 910 958; 2315 911 959; 2316 912 960; 2317 913 914;
    2318 914 915; 2319 915 916; 2320 917 918; 2321 918 919; 2322 919 920;
    2323 913 921; 2324 914 922; 2325 915 923; 2326 916 924; 2327 917 925;
    2328 918 926; 2329 919 927; 2330 920 928; 2331 921 922; 2332 922 923;
    2333 923 924; 2334 925 926; 2335 926 927; 2336 927 928; 2337 921 929;
    2338 922 930; 2339 923 931; 2340 924 932; 2341 925 933; 2342 926 934;
    2343 927 935; 2344 928 936; 2345 929 930; 2346 930 931; 2347 931 932;
    2348 933 934; 2349 934 935; 2350 935 936; 2351 937 938; 2352 938 939;
    2353 939 940; 2354 941 942; 2355 942 943; 2356 943 944; 2357 937 945;
    2358 938 946; 2359 939 947; 2360 940 948; 2361 941 949; 2362 942 950;
    2363 943 951; 2364 944 952; 2365 945 946; 2366 946 947; 2367 947 948;
    2368 949 950; 2369 950 951; 2370 951 952; 2371 945 953; 2372 946 954;
    2373 947 955; 2374 948 956; 2375 949 957; 2376 950 958; 2377 951 959;
    2378 952 960; 2379 953 954; 2380 954 955; 2381 955 956; 2382 957 958;
    2383 958 959; 2384 959 960; 2385 929 953; 2386 930 954; 2387 931 955;
    2388 932 956; 2389 932 933; 2390 956 957; 2391 933 957; 2392 934 958;
    2393 935 959; 2394 936 960; 2395 913 961; 2396 914 962; 2397 915 963;
    2398 916 964; 2399 917 965; 2400 918 966; 2401 919 967; 2402 920 968;
    2403 921 969; 2404 922 970; 2405 923 971; 2406 924 972; 2407 925 973;
    2408 926 974; 2409 927 975; 2410 928 976; 2411 929 977; 2412 930 978;
    2413 931 979; 2414 932 980; 2415 933 981; 2416 934 982; 2417 935 983;
    2418 936 984; 2419 937 985; 2420 938 986; 2421 939 987; 2422 940 988;
    2423 941 989; 2424 942 990; 2425 943 991; 2426 944 992; 2427 945 993;
    2428 946 994; 2429 947 995; 2430 948 996; 2431 949 997; 2432 950 998;
    2433 951 999; 2434 952 1000; 2435 953 1001; 2436 954 1002; 2437 955 1003;
    2438 956 1004; 2439 957 1005; 2440 958 1006; 2441 959 1007; 2442 960 1008;
    2443 961 962; 2444 962 963; 2445 963 964; 2446 965 966; 2447 966 967;
    2448 967 968; 2449 961 969; 2450 962 970; 2451 963 971; 2452 964 972;
    2453 965 973; 2454 966 974; 2455 967 975; 2456 968 976; 2457 969 970;
    2458 970 971; 2459 971 972; 2460 973 974; 2461 974 975; 2462 975 976;
    2463 969 977; 2464 970 978; 2465 971 979; 2466 972 980; 2467 973 981;
    2468 974 982; 2469 975 983; 2470 976 984; 2471 977 978; 2472 978 979;
    2473 979 980; 2474 981 982; 2475 982 983; 2476 983 984; 2477 985 986;
    2478 986 987; 2479 987 988; 2480 989 990; 2481 990 991; 2482 991 992;
    2483 985 993; 2484 986 994; 2485 987 995; 2486 988 996; 2487 989 997;
    2488 990 998; 2489 991 999; 2490 992 1000; 2491 993 994; 2492 994 995;
    2493 995 996; 2494 997 998; 2495 998 999; 2496 999 1000; 2497 993 1001;
    2498 994 1002; 2499 995 1003; 2500 996 1004; 2501 997 1005; 2502 998 1006;
    2503 999 1007; 2504 1000 1008; 2505 1001 1002; 2506 1002 1003; 2507 1003 1004;
    2508 1005 1006; 2509 1006 1007; 2510 1007 1008; 2511 977 1001; 2512 978 1002;
    2513 979 1003; 2514 980 1004; 2515 980 981; 2516 1004 1005; 2517 981 1005;
    2518 982 1006; 2519 983 1007; 2520 984 1008; 2521 961 1009; 2522 962 1010;
    2523 963 1011; 2524 964 1012; 2525 965 1013; 2526 966 1014; 2527 967 1015;
    2528 968 1016; 2529 969 1017; 2530 970 1018; 2531 971 1019; 2532 972 1020;
    2533 973 1021; 2534 974 1022; 2535 975 1023; 2536 976 1024; 2537 977 1025;
    2538 978 1026; 2539 979 1027; 2540 980 1028; 2541 981 1029; 2542 982 1030;
    2543 983 1031; 2544 984 1032; 2545 985 1033; 2546 986 1034; 2547 987 1035;
    2548 988 1036; 2549 989 1037; 2550 990 1038; 2551 991 1039; 2552 992 1040;
    2553 993 1041; 2554 994 1042; 2555 995 1043; 2556 996 1044; 2557 997 1045;
    2558 998 1046; 2559 999 1047; 2560 1000 1048; 2561 1001 1049; 2562 1002 1050;
    2563 1003 1051; 2564 1004 1052; 2565 1005 1053; 2566 1006 1054; 2567 1007 1055;
    2568 1008 1056; 2569 1009 1010; 2570 1010 1011; 2571 1011 1012; 2572 1013 1014;
    2573 1014 1015; 2574 1015 1016; 2575 1009 1017; 2576 1010 1018; 2577 1011 1019;
    2578 1012 1020; 2579 1013 1021; 2580 1014 1022; 2581 1015 1023; 2582 1016 1024;
    2583 1017 1018; 2584 1018 1019; 2585 1019 1020; 2586 1021 1022; 2587 1022 1023;
    2588 1023 1024; 2589 1017 1025; 2590 1018 1026; 2591 1019 1027; 2592 1020 1028;
    2593 1021 1029; 2594 1022 1030; 2595 1023 1031; 2596 1024 1032; 2597 1025 1026;
    2598 1026 1027; 2599 1027 1028; 2600 1029 1030; 2601 1030 1031; 2602 1031 1032;
    2603 1033 1034; 2604 1034 1035; 2605 1035 1036; 2606 1037 1038; 2607 1038 1039;
    2608 1039 1040; 2609 1033 1041; 2610 1034 1042; 2611 1035 1043; 2612 1036 1044;
    2613 1037 1045; 2614 1038 1046; 2615 1039 1047; 2616 1040 1048; 2617 1041 1042;
    2618 1042 1043; 2619 1043 1044; 2620 1045 1046; 2621 1046 1047; 2622 1047 1048;
    2623 1041 1049; 2624 1042 1050; 2625 1043 1051; 2626 1044 1052; 2627 1045 1053;
    2628 1046 1054; 2629 1047 1055; 2630 1048 1056; 2631 1049 1050; 2632 1050 1051;
    2633 1051 1052; 2634 1053 1054; 2635 1054 1055; 2636 1055 1056; 2637 1025 1049;
    2638 1026 1050; 2639 1027 1051; 2640 1028 1052; 2641 1028 1029; 2642 1052 1053;
    2643 1029 1053; 2644 1030 1054; 2645 1031 1055; 2646 1032 1056; 2647 1009 1057;
    2648 1010 1058; 2649 1011 1059; 2650 1012 1060; 2651 1013 1061; 2652 1014 1062;
    2653 1015 1063; 2654 1016 1064; 2655 1017 1065; 2656 1018 1066; 2657 1019 1067;
    2658 1020 1068; 2659 1021 1069; 2660 1022 1070; 2661 1023 1071; 2662 1024 1072;
    2663 1025 1073; 2664 1026 1074; 2665 1027 1075; 2666 1028 1076; 2667 1029 1077;
    2668 1030 1078; 2669 1031 1079; 2670 1032 1080; 2671 1033 1081; 2672 1034 1082;
    2673 1035 1083; 2674 1036 1084; 2675 1037 1085; 2676 1038 1086; 2677 1039 1087;
    2678 1040 1088; 2679 1041 1089; 2680 1042 1090; 2681 1043 1091; 2682 1044 1092;
    2683 1045 1093; 2684 1046 1094; 2685 1047 1095; 2686 1048 1096; 2687 1049 1097;
    2688 1050 1098; 2689 1051 1099; 2690 1052 1100; 2691 1053 1101; 2692 1054 1102;
    2693 1055 1103; 2694 1056 1104; 2695 1057 1058; 2696 1058 1059; 2697 1059 1060;
    2698 1061 1062; 2699 1062 1063; 2700 1063 1064; 2701 1057 1065; 2702 1058 1066;
    2703 1059 1067; 2704 1060 1068; 2705 1061 1069; 2706 1062 1070; 2707 1063 1071;
    2708 1064 1072; 2709 1065 1066; 2710 1066 1067; 2711 1067 1068; 2712 1069 1070;
    2713 1070 1071; 2714 1071 1072; 2715 1065 1073; 2716 1066 1074; 2717 1067 1075;
    2718 1068 1076; 2719 1069 1077; 2720 1070 1078; 2721 1071 1079; 2722 1072 1080;
    2723 1073 1074; 2724 1074 1075; 2725 1075 1076; 2726 1077 1078; 2727 1078 1079;
    2728 1079 1080; 2729 1081 1082; 2730 1082 1083; 2731 1083 1084; 2732 1085 1086;
    2733 1086 1087; 2734 1087 1088; 2735 1081 1089; 2736 1082 1090; 2737 1083 1091;
    2738 1084 1092; 2739 1085 1093; 2740 1086 1094; 2741 1087 1095; 2742 1088 1096;
    2743 1089 1090; 2744 1090 1091; 2745 1091 1092; 2746 1093 1094; 2747 1094 1095;
    2748 1095 1096; 2749 1089 1097; 2750 1090 1098; 2751 1091 1099; 2752 1092 1100;
    2753 1093 1101; 2754 1094 1102; 2755 1095 1103; 2756 1096 1104; 2757 1097 1098;
    2758 1098 1099; 2759 1099 1100; 2760 1101 1102; 2761 1102 1103; 2762 1103 1104;
    2763 1073 1097; 2764 1074 1098; 2765 1075 1099; 2766 1076 1100; 2767 1076 1077;
    2768 1100 1101; 2769 1077 1101; 2770 1078 1102; 2771 1079 1103; 2772 1080 1104;
    DEFINE MATERIAL START
    ISOTROPIC CONCRETE
    E 453600
    POISSON 0.17
    DENSITY 0.14999
    ALPHA 5.5e-006
    DAMP 0.05
    END DEFINE MATERIAL
    MEMBER PROPERTY AMERICAN
    79 TO 174 253 TO 300 379 TO 426 505 TO 552 631 TO 678 757 TO 804 883 TO 930 -
    1009 TO 1056 1135 TO 1182 1261 TO 1308 1387 TO 1434 1513 TO 1560 -
    1639 TO 1686 1765 TO 1812 1891 TO 1938 2017 TO 2064 2143 TO 2190 -
    2269 TO 2316 2395 TO 2442 2521 TO 2568 2647 TO 2693 -
    2694 PRIS YD 2.08333 ZD 2.08333
    1 TO 78 175 TO 252 301 TO 378 427 TO 504 553 TO 630 679 TO 756 805 TO 882 -
    931 TO 1008 1057 TO 1134 1183 TO 1260 1309 TO 1386 1435 TO 1512 1561 TO 1638 -
    1687 TO 1764 1813 TO 1890 1939 TO 2016 2065 TO 2142 2191 TO 2268 -
    2317 TO 2394 2443 TO 2520 2569 TO 2646 2695 TO 2772 PRIS YD 1 ZD 2
    CONSTANTS
    MATERIAL CONCRETE ALL
    SUPPORTS
    49 TO 96 FIXED
    DEFINE WIND LOAD
    TYPE 1
    INT 0.12455 0.13592 0.15429 0.1693 0.18197 0.19343 0.20331 0.21224 0.22075 -
    0.22867 0.23575 0.243 0.24955 0.25583 0.26193 0.26741 0.27297 0.27845 0.2836 -
    0.28868 0.29342 HEIG 24 34 44 54 64 74 84 94 104 114 124 134 144 -
    154 164 174 184 194 204 214 224
    EXP 1 JOINT 1 TO 864
    LOAD 1 LOADTYPE Dead TITLE DEAD LOAD
    SELFWEIGHT Y -1 LIST 1 TO 2142
    MEMBER LOAD
    2317 TO 2394 2443 TO 2520 2569 TO 2646 2695 TO 2772 UNI GY -1
    FLOOR LOAD
    YRANGE 7 250 FLOAD -0.075 GY
    LOAD 2 LOADTYPE Live REDUCIBLE TITLE LIVE LOAD
    FLOOR LOAD
    YRANGE 7 250 FLOAD -0.04 GY
    LOAD 3 LOADTYPE Wind TITLE WIND
    WIND LOAD X 1 TYPE 1 YR 7 250
    WIND LOAD Z 1 TYPE 1 YR 7 250
    WIND LOAD -X 1 TYPE 1 YR 7 250
    WIND LOAD -Z 1 TYPE 1 YR 7 250
    LOAD COMB 4 COMBINATION LOAD CASE 4
    1 1.4 2 1.4 3 1.4
    PERFORM ANALYSIS
    FINISH
  • The model seems to be correct (except that selfweight is applied not to all structure). It seems that the high displacements are due to wind loading. Check if wind intensity numbers are provided correctly in your wind load definition. If yes, then the displacement probably are reasonable having in mind building geometry and sections.
    Please note that usually wind load in each direction is applied under a separate load case and then combined in the load combination if required.
  • untitled.txt Hi Modestas. Hope you or any of your colleague can help me with the same problem. checked everything, loading and parameters. everything seems correct. Members group in PR2 is just a mirror image of group PR1 but the joint displacement is very unrealistic in PR2. Thank you in advance. PS the strucuture is huge.